Open Neutral you say? A story of carnage at Gooontrons house.
  • goontron
    5000!
    • Dec 2011
    • 4108
    • US
    To preface, this is 100% my fault. I installed the plug in the dead of winter, and i didn't manage to torque anything to spec... (off site images warning)
    This is what happens when the cord that powers all 50 amps of a mobile home gets pulled out of the plug assembly.
    This really is a shit design. The live(s) should disconnect before the return, but US plug standards so...
    Yep. You lose neutral first! It started with Neutral getting pulled, then next came the red phase. As you can see, white has been warm for some time....
    Heres the extent of the damage, the controller of an evap cooler. Some blown fuses otherwise.
    Real lucky on this one!
    Here's the MOV since the one on the surge suppressor did jack for shit!
    I think i might make jewelry out of it.... It already has a hole punched in it!
    Here's the surge suppressor that was running the AV system. (all 120-240v systems)
    It did its job. And without starting a fire!
    Not much damage to speak of.
    No load disconnect?
    This one was on countertop duty what for the microwave and whatnot.
    Load disconnect. Good! A little soot. Not teabag!
    Hmm. On the older side for sure.... Did its job! I ripped the trace.... Oops.
    This bastard did its damndest to burn the place down! This is what ran my bench.
    Nice soot. No disconnect here either!
    Jesus fuck! I don't think the thermal fuses are real here....
    Nope! That's why it blew sparks that lit my bowl of cotton buds on fire.
    Now for the protectors that did jack shit for all. Belkin. This is what the evap was plugged into!
    Belkin. A white and a black one. Both the same (lack of) failure mode!
    Nope. Not the boards fault!
    Sadly, the black one was powering my Radios, both Ham and broadcast. The ham radios switch modes swallowed it and burped, while the Yamaha receiver was saved by a line noise filter i installed that included surge protection. It clamped and blew the fuse. I pulled the module and bypassed it, but after testing, it would seem to still work, surge and all, so i reinstalled it. My furnace i thought had blown the trafo. But i found a note scribbled in pencil on the sheet metal about an edison screw fuse service center in the air-space above the furnace. The 15 amp fuse had blown. I replaced it and all was good.
    Now for the "surge suppressor" that ran my 13/5 Centimeter packet and part 15 data wireless "rack"
    *cough* i'm an idiot *cough* This had a shit-ton of switch mode "Wall Warts" plugged in. They all are rated 110-240v. No damage here! I got lucky. This won't do jack shit for surges! Make sure your surge suppressors, are surge suppressors! Sadly, this is dead as well as i had to break the case to open it.
    If i can find the fuses (and i'm asked) i will post those as well.
    Follow the white rabbit.
  • eccerr0r
    Solder Sloth
    • Nov 2012
    • 8701
    Re: Open Neutral you say? A story of carnage at Gooontrons house.
    I have a surge protector that just has a single MOV with a fuse in series... it is a surge protector, alas there's no way to tell if it's still surge protecting or not...
    I have this other surge protector that has an LED that indicates whether it's surge protecting or not. Turns out it's just hooked up to power and has no bearing of the status of the surge protection. The MOV actually looks like it's still good...
      • Jul 2011
      • 6057
      These surge protector are real shit I feel real safe
      So what surge protector are left that really works
      • CapLeaker
        Leaking Member
        • 8286
        Geez goon, that really sucks. Luckily I gave up my trailer and the truck 8 years ago. But I miss my nights hamming inside that shoe box parked on a hill very close to the ocean calling CQ. Good luck getting all that repaired!
          • 31137
          plug should have had a good cable-grip.
          also it should have been locking.
          like this:
            • 31137
            they are for spikes, not a continuous voltage.
            • goontron
              5000!
              • Dec 2011
              • 4108
              • US
              like this:
              [img]
              Now, you see, that's one i would trust. Instead we have https://www.amazon.com/30-50A-BLK-Ra.../dp/B00GRTSRSK
              Looks sturdy, eh?
              Think we got some terms wrong here, don't worry, we confuse the canadians who come down here to Wy during hunting season as well
              Mobile/Manufactured homes are called trailers here, and pull behind trailers are called campers....
              • PeteS in CA
                • Aug 2005
                • 3581
                • USA, Unsure of Planet
                Mehhhh. The picture stj posted was an IEC-309 connector, basically for industrial use rather than home use. This would be the closest US equivalent AC plug:
                FWIW, Hubbell, who makes the connector pictured above also makes and sells IEC-309 connectors. IEC-309 connectors are reasonably available in the US. If you've been in a McDonald's in the past 5 or 20 years you've probably seen IEC-309 connectors in their kitchen area, like these:
                The real advantage IEC-309 connectors have over regular Twist-Lok connectors is that they are, in varying degrees depending on the type, moisture-proof. But they still have to be hand-wired, like a Twist-Lok or the appliance type you pictured.
                PeteS in CA
                  • 31137
                  yes, the minimum is splashproof, the highest are potentially submersible!
                  and they all lock.
                  they cost nothing like that robbery you posted at Amazion btw!
                  oh yes, in Europe we use them on campers and caravans as standard - because they are rain-proof.
                  • PeteS in CA
                    • Aug 2005
                    • 3581
                    and they all lock....
                    The pic you posted above is in the higher end of degrees of watertightness. That ribbed ring screws onto the mating connector, and that gray ring is a nice rubber gasket. At the other end of the white shell (where the cable enters the shell) is another rubber gasket.
                    PeteS in CA
                    • goontron
                      5000!
                      • Dec 2011
                      • 4108
                      • US
                      and they all lock.
                      Im not sure what that seller is smoking, but i got the one i have from an Osram retailer here in Wy for $17.
                      • Stefan Payne
                        • 1267
                        Depends on where you live and what you need...
                        Here in Germany we rarely use anything else than that.
                        There is the Perilex system wich looks like Schuko for 3 Phases but nobody uses them anymore. And if you have a 3 phase device, you need to change the plug anyways (they all come with the IEC these days)...
                        OF course those Perilex things look better in a living enviroment...
                        And you can still get both if you want to...
                        Besides: How do you americans connect your electric stove/cooctops??
                        Here we use 3x230VAC, 16A (because against Neutral, not each other)...
                        • goontron
                          5000!
                          • Dec 2011
                          • 4108
                          • US
                          ^ the plug on amazon i posted... The only difference from using that on a stove and a mobile home is that its uprated to 60 amps for mobile home mains feed use... Stovetop use is 50 amps....
                            • 31137
                            in the u.k. we just have a single-phase 240v 45A wall outlet!
                            real power, none of that low voltage multi-phase crap!
                            • dmill89
                              • Dec 2011
                              • 2534
                              Tripp-lite Isobars are pretty good, but pricy (from $25 for the basic 2-outlet unit to well over $100 for the large rack-mount units, with the popular 6-8 outlet units running from $50-$80). Most UPS units should offer decent protection as well.
                                master hoarder
                                • May 2008
                                • 12175
                                • Bulgaria
                                Similar as our driers: a beefed up plug, providing two phases, a neutral, and more recently a ground. Most US driers and ovens/cooktops are rated for 240 or 208V. Typically residential homes get two 120V phases 180 degrees apart (so phase-phase voltage is 240) from a center-tapped transformer (center tap is tied to neutral). But in commercial areas or buildings with 3-phase power, the voltage is 208V between any two phases, so that is used instead. That's why most US ovens and cooktops will say on the back they are rated for 208/240V.
                                As for the plug itself, it varies depending on the vintage of the home. But this page will show you some examples:
                                https://en.wikipedia.org/wiki/NEMA_c...r#Nomenclature
                                  master hoarder
                                  • May 2008
                                  • 12175
                                  • Bulgaria
                                  Shouldn't matter. After enough spikes, most MOVs will go short-circuit, so they definitely need some type of a breaker/disconnect/fuse circuit - preferably one that will disconnect the whole surge protector too and not just the MOVs, because otherwise, it will no longer be a surge suppressor.
                                    • 31137
                                    https://www.youtube.com/watch?v=FQXecTM8yuo
                                    • joshnz
                                      • Feb 2011
                                      • 969
                                      • New Zealand
                                      I like our system here open neutral = low voltage
                                      If earth bonding is bad electric shock hazard as the taps outside will become live with respect to ground.
                                      We used to have 2 phase into houses one was continuous and the other was controlled for load shedding would run night store or hot water heater.
                                      now we use one phase with a remote control. or use a smart meter.
                                      in larger dwellings so 2 or more 2 or 3 phase will be found open neutral could expose the equipment in the dwelling to 415V but requires your neighbors to have lot's of power hungry devices. more of a issues for 2 phase supplies i think as floating neutral will balance better with 3 phase.
                                      My pc
                                      CPU : AMD PHENOM II x4 @ 3.5Ghz
                                      MB : ASUS M4A89TD PRO USB3
                                      RAM : Kingston ValueRAM 16gb DDR3
                                      PSU : Cooler Master 850W Silent Pro
                                      GPU : ATI Radeon HD 6850
                                      • goontron
                                        5000!
                                        • Dec 2011
                                        • 4108
                                        • US
                                        Well, just an update. The control transformer on the furnace puked. It got roasted by the looks of it... Im surprised it lasted more than a year.
                                        As for 240v appliances, still none. Nat. gas is cheap. The cost of electricity went UP when we switched over to the wind turbine farm to the west of me. $0.04/KWh maintenance fee, yay....
                                        • SolomonMan
                                          Antenna...
                                          by SolomonMan
                                          All,
                                          I recently moved to a very rural area. I am about 25 miles from the nearest urban settings (2 separate College Towns). 45-50 miles from a Urban City (Toledo Ohio)
                                          There was a Omni-directional Wineguard Antenna (amplified) that was mounted on the house originally. Came with the house. Center of the top of Roof a few feet from Chimney on a 4 foot pole. The 75 ohm line went from the roof down 2-3 stories to the small Wineguard amplifier and then it split to the living room and master bedroom. Currently a Very simple setup.
                                          Since we moved in, 8 years ago,...
                                          10-05-2023, 02:37 PM
                                          High Pressure Sodium Yard light when air conditioner turns light momentarily turns of
                                          by sam_sam_sam
                                          I have had these 70 watt high pressure sodium yard lights for many years now probably at least 15 years or more and there is a protection diode that after several years starts to go bad and when it does this it has momentarily shutting down the light and then a few minutes later it starts working again
                                          This about the forth time I have fixed this one and you can tell if it the diode or not if it lights up and it only shuts down when the air conditioner turns on then it is the diode
                                          If it cycling on and off constantly then it is the bulb itself that is the issue
                                          06-03-2023, 05:24 PM
                                        • nobbnobb1
                                          Upgrading Whole Home Surge Protector MOVs (Eaton CHSPT2SURGE)
                                          by nobbnobb1
                                          I have a whole home surge protector (Eaton CHSPT2SURGE). This is the lower end model as compared to the CHSPT2ULTRA. When I took it apart, I noticed it's basically the same PCB as the higher end model, just missing the extra MOVs for higher capacity. Coincidentally, I have a pack of brand new Bourns 20D241K MOVs laying around:
                                          https://www.digikey.ca/en/products/d...0D241K/2799098
                                          The only thing I noticed is that these Bourns MOVs are not thermally protected with a fuse. I'm wondering if it's safe to just simply install these extra MOVs for extra capacity,...
                                          06-04-2025, 08:40 AM
                                        • SluggerB
                                          Panasonic TH-50PX80 killed by lightning strike, help me save her!
                                          by SluggerB
                                          Yes it's a 17 year old Panasonic plasma!
                                          I was watching TV when there was a huge lighting strike nearby my house that shook the house. When that happened, the picture on the TV froze and the TV wouldn't turn off except by pulling the power cable. Now if you plug in the TV, it seems to turn on (it makes the turn on "clikcs" it always does, the red power light comes on but there is no picture, although I can see the back light around the edges. And the TV doesn't respond to the power button on the remote to turn off, and doesn't respond to the manual power button on the front...
                                          06-04-2025, 07:02 PM
                                        • xTomtom
                                          Treadmill hit with power surge
                                          by xTomtom
                                          Recently I acquired a treadmill that was hit by a power surge (I assume). On the control board, there was a varistor that was blown apart and two traces that were partially blown out. I replaced the varistor (to my knowledge it is a matching one) and wired back where the traces were with some 22 awg solid copper wire. When I went to power it on, still nothing. On a quick inspection with my meter, I was getting incoming voltage on the AC in terminal.
                                          The board is a MC2100LS-30 treadmill controller.
                                          Visibly, there are no other problems....
                                          05-09-2023, 08:06 PM
