Upgrading Whole Home Surge Protector MOVs (Eaton CHSPT2SURGE)

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • nobbnobb1
    Senior Member
    • Nov 2019
    • 76
    • Canada

    #1

    Upgrading Whole Home Surge Protector MOVs (Eaton CHSPT2SURGE)

    I have a whole home surge protector (Eaton CHSPT2SURGE). This is the lower end model as compared to the CHSPT2ULTRA. When I took it apart, I noticed it's basically the same PCB as the higher end model, just missing the extra MOVs for higher capacity. Coincidentally, I have a pack of brand new Bourns 20D241K MOVs laying around:
    https://www.digikey.ca/en/products/d...0D241K/2799098

    The only thing I noticed is that these Bourns MOVs are not thermally protected with a fuse. I'm wondering if it's safe to just simply install these extra MOVs for extra capacity, or is it absolutely required to get a thermally protected version such as these:
    https://canada.newark.com/littelfuse...50v/dp/01P8113

    Thermally protected MOVs are quite expensive, especially if trying to get one with a lower clamping voltage rating.

    Also, even with the MOV upgrade I'm assuming I would leave the circuit breaker at the same rating (15A double pole).

    Love to hear your thoughts.
    Attached Files
  • stj
    Great Sage 齊天大聖
    • Dec 2009
    • 31014
    • Albion

    #2
    never do that.
    MOV's always fail short, and a big one will make a real bang - specially if it's got a big supply current

    Comment

    • truclacicr
      Badcaps Veteran
      • Apr 2019
      • 304
      • australia

      #3
      Those surge "protectors" are crap.

      If you must use one of these devices, then I would pay the extra money for something like this:

      https://tripplite.eaton.com/products...tors-explained
      Last edited by truclacicr; 06-04-2025, 01:20 PM.

      Comment

      • PeteS in CA
        Badcaps Legend
        • Aug 2005
        • 3579
        • USA, Unsure of Planet

        #4
        Adding to what stj posted, MOVs are damaged by every surge they absorb. With every surge, the firing voltage decreases a little. Eventually, with many surges, the firing voltage drops to or near the nominal line voltage, at which tome conduction becomes continuous and the MOVs short and/or explode. Depending on the surges' intensity and frequency of occurrence, it may take years to reach the point of self-destruction, but if there are surges it is a question of "when", not "if".
        PeteS in CA

        Power Supplies should be boring: No loud noises, no bright flashes, and no bad smells.
        ****************************
        To kill personal responsibility, initiative or success, punish it by taxing it. To encourage irresponsibility, improvidence, dependence and failure, reward it by subsidizing it.
        ****************************

        Comment

        • momaka
          master hoarder
          • May 2008
          • 12170
          • Bulgaria

          #5
          Surge "protector" devices are over-rated anyways - that is, most electronics are damaged by the large EM pulses from nearby lightning strikes, particularly the generation of voltage on long external conductors (wires) on most electronics (e.g. signal cables.) Shielded wires tend to be affected a little less, but can still generate potential differences large enough to damage ICs if the lightning strike is very nearby. Also, most electronics have MOVs in their PSUs already, so the extra "whole house surge protection" is really not needed (nor very effective, since you want your surge protector to capture the spike and disconnect the load if the spike goes way too high / has too much power to open up the MOVs.)

          Back to the topic at hand, you could use regular MOVs perhaps with a fuse (ceramic type, not glass) in series so the fuse blows if the MOV shorts out. As for the fuse rating, not sure what would go for the calculation of that. If you want to be "extra-fancy", add 2 series resistors in the 100's KOhms range, a diode, and an LED all in series across the fuse. So if the MOV shorts out and blows the fuse, the LED will light up to indicate that it's blown (and the MOV shorted.) But really, that's more of an idea to toy around with than anything too serious. I've seen similar schemes employed in some powers strips that employ surge protection. Actually, when I get time, I have a US/Canada/North American power strip here that needs attention/fixing. Apparently someone brought it over to Europe and plugged it into 230V AC without knowing what will happen. There's a nice black splatter spot on the back of the plastic of this power strip.

          Comment

          Related Topics

          Collapse

          • Pentium4
            Replacing MOVs in surge protectors?
            by Pentium4
            I know most people would just buy a new one at the store. But hey... this is Badcaps afterall, right?

            For quite some time I've had the crazy and naive notion that surge protectors just worked, and lasted forever I have been occasionally buying new units because you can't really tell how many joules are left in the MOVs after a few power surges. Some units I have had for 10 years and surely their MOVs are toast by now. Instead of buying new ones and funneling money over to china, I thought about just replacing the MOVs in the existing ones I have. All of the plugs still...
            12-14-2021, 01:15 AM
          • m4a2t0t
            Thermal Cutoff/Fuse ID -Surge Protector
            by m4a2t0t
            According to This PDF Its rated 109c functioning and 103c holding but all I can find is 109c functioning and 83c (10A) / 88c (15A) holding or 128c functioning and 103c holding.

            It is labeled D108 PPqH

            Should I try and match the functioning temp or the holding temp?

            The protector is 6 outlets rated at 15A. That PDF shows 25A @ 240v but say 5 LRA @ 120V. I can only find 10A and 15A versions.

            Thanks for any help...
            01-12-2022, 09:36 PM
          • xTomtom
            Treadmill hit with power surge
            by xTomtom
            Hi everyone,

            Recently I acquired a treadmill that was hit by a power surge (I assume). On the control board, there was a varistor that was blown apart and two traces that were partially blown out. I replaced the varistor (to my knowledge it is a matching one) and wired back where the traces were with some 22 awg solid copper wire. When I went to power it on, still nothing. On a quick inspection with my meter, I was getting incoming voltage on the AC in terminal.

            The board is a MC2100LS-30 treadmill controller.

            Visibly, there are no other problems....
            05-09-2023, 08:06 PM
          • Bubbsy 2002
            Kiddie smoke alarm (120v with 9v battery backup) experienced 180v power surge (Newfoundland Power company).
            by Bubbsy 2002
            Hi to all, I was diagnosing 2 smoke detectors that experienced power surge. I opened one up and found a weird fuse/resistor, which now has open circuit. I can't find this part.
            Forgot to mention they both light up and I believe the test function works, but when I put smoke to them no alarm!

            Any help in this regard would be greatly appreciated.

            Thanks,...
            01-02-2024, 09:11 AM
          • x0x0x
            FAN 007 error at UPS Eaton ( in my case EX 3000 RT )
            by x0x0x
            Hi, there!
            I'd like to share my recent experience with FAN 007 error on 2 pcs. UPS Eaton EX 3000 RT.
            I tried different ways to resolve it:
            changed the fan with equal ( didn't find the same ) - didn't efect
            put a resistor betwin + and graund on el.motor ( to simulate the same statick resist ) - didn't efect
            add capasitor ( as a filter ) - didn't efect
            and the end - simply changed the ball bearings on original fans ( there are 2 pcs on a fan ) and clean them and UPS's continued to work perfeckt.
            06-26-2023, 11:19 AM
          • Loading...
          • No more items.
          Working...