Panasonic Inverter Refrigerator model NR-BY602XS - suddenly not cold overnight
first of all - this refrigerator has a control bd that drives an inverter board that controls the compressor. The voltage coming from the inverter bd driving the compressor is 80 - 230 VAC. 1. test the compressor windings - should ohm out all the same. If all the same ohms between the 3 pins - compressor is probably good. 2. test the control bd by testing for 4V-6V volts going to the input of the inverter board - this is the voltage that drives the inverter board to put DC voltage to the compressor. Also test for 120 VAC going into the inverter bd. If no 4 VDC - 6 VDC voltage going to the inverter bd than control board is bad or a temp sensor is bad going to the control bd. 3. Look at the inverter board for burn marks.4. next I would test the amp draw of the inverter bd (should fluctuate between 1 - 3 amps) by using an amp meter on the 120 VAC input to the inverter bd - if its zer0 than the inverter bd is bad. If the amperage jumps to 4 amps and then declines to zero (this will cycle as the control bd realizes the compressor is not starting) - compressor is probably bad. 5. If you got this far and everything is good - the next test is to test the invert bd output with a phase detector (expensive piece of equipment) 6. finally either the compressor is weak or the system has a leak and is low on fluid. This is a closed system and no fluids should ever leak out. The inverter board is usually the culprit but not always. hope this helps !Leave a comment:
first of all - this refrigerator has a control bd that drives an inverter board that controls the compressor. The voltage coming from the inverter bd driving the compressor is 80 - 230 VAC. 1. test the compressor windings - should ohm out all the same. If all the same ohms between the 3 pins - compressor is probably good. 2. test the control bd by testing for 4V-6V volts going to the input of the inverter board - this is the voltage that drives the inverter board to put DC voltage to the compressor. Also test for 120 VAC going into the inverter bd. If no 4 VDC - 6 VDC voltage going to the inverter bd than control board is bad or a temp sensor is bad going to the control bd. 3. Look at the inverter board for burn marks.4. next I would test the amp draw of the inverter bd (should fluctuate between 1 - 3 amps) by using an amp meter on the 120 VAC input to the inverter bd - if its zer0 than the inverter bd is bad. If the amperage jumps to 4 amps and then declines to zero (this will cycle as the control bd realizes the compressor is not starting) - compressor is probably bad. 5. If you got this far and everything is good - the next test is to test the invert bd output with a phase detector (expensive piece of equipment) 6. finally either the compressor is weak or the system has a leak and is low on fluid. This is a closed system and no fluids should ever leak out. The inverter board is usually the culprit but not always. hope this helps !Last edited by ajshoe; 10-01-2024, 08:09 PM.Leave a comment:
I have same model and about the same problem. Did you solved yours? My compressor doesn't spin. replaced with bulbs no lights. replaced IPM same problem. seems like this problem Communication error between IC1 & IC201 based on blink codeLeave a comment:
Re: Panasonic Inverter Refrigerator model NR-BY602XS - suddenly not cold overnight
OK... Looks like it's praying for a kind donor, or paying for a reasonable price used unit as tuition fee.
I have started browsing and found a few identical model, but price a little stiff after costing in transportation.
I guess will need a little more time to catch one...Leave a comment:
OK. Let me summarize the options to move forward:
1) Refill refrigerant - this will determine if there is leakage. Maybe worthwhile (probably not)
2) Replace controller board - If a used fridge of same model can be found at low price. ( good idea if you can find one )
3) Replace some of the tubing - this will determine if there is blockage or restriction. Probably too costly for a old fridge..
3) Replace compressor - not worth the money..
Any feedback on these options? Or any other viable options?Last edited by sam_sam_sam; 04-29-2020, 11:17 AM.Leave a comment:
Any feedback on these options? Or any other viable options?Leave a comment:
When hear the liquid flowing like this is not a good sign and not getting cold
There is not much refrigerant in theses units so if have a leak or a restriction it does not take it long for it not workLast edited by sam_sam_sam; 04-28-2020, 12:15 PM.Leave a comment:
That what I thought ( “gurgling liquid flowing” ) I being to think that either the compressor ( will not run at full speed )[Controller issues] or [ compressor pumping issues ]
OR
You have a restriction in filter dryer ( OR ) cap-tube
OR
You have a gas leak
This is where you would need a set service gauges and a specific type of amp probe to figure out what going on with this systemLast edited by sam_sam_sam; 04-28-2020, 12:04 PM.Leave a comment:
Look at the end of the ( evaporator coil ) and see where very small tube is on one of coil and see if ice is forming there if so and only in one spot and does not grow then you have restriction or a gas leak
Also remove the temperature sensor and warm it with your hand and see if the compressor will run at full speed
After power up for a few minutes, I place both defrost and freezer sensors in a cup of semi-hot water (around 50degC I guessed), but cannot really tell if the compressor is running at full speed or not.
After 10-15 minutes, no observable difference in term of coldness in both compartments.
How long does a normal fully working fridge takes to start feeling coldness if you place your hands in the freezer compartment?Last edited by beetle1303; 04-28-2020, 09:21 AM.Leave a comment:
By data plate do you mean this in the pic below?
I am just curious - if the compressor runs at whatever speed, and the inlet is slight cool, the outlet is warm (not hot), and the evaporator coil has refrigerant flowing with gurgling sound, etc, shouldn't the evaporator coil be slightly cool the the touch?
Also remove the temperature sensor and warm it with your hand and see if the compressor will run at full speedLeave a comment:
Here's the summary of the Self Diagnostics done:
1) Page7 - In process Inspection
- after 1 minute: Illuminance Sensor LED is On, indicating BAD
- after 30 minutes: All Freezer Control LEDs blinking - indicating BAD
** no description of what is BAD...
2) Page 11 - SELF DIAGNOSING FUNCTION
- based on the initial blinks (before they go off): PCD is BAD
3) Page 15 - Not cool at all [ Both PC & FC (compressor does not operate) ]
• Defect of control PCB.
• Communication error between IC1 & IC201
4) Page 16 - Cool, not enough [ Both PC & FC (compressor operates) ]
• Defect of communication circuit and EEPROM circuit of control PCB.
• Plug out and after 7 minute plug in again.
Same outcomes in repeated tests. If these tests are done correctly, and the outcomes interpreted correctly - all seems to point to PCB Board faulty. Or possibly some setting is locked permanently like "compressor lock", or "defrost on", etc...Leave a comment:
Ahh.. MP, not MB. Thanks, all good now.Leave a comment:
I am just curious - if the compressor runs at whatever speed, and the inlet is slight cool, the outlet is warm (not hot), and the evaporator coil has refrigerant flowing with gurgling sound, etc, shouldn't the evaporator coil be slightly cool the the touch?Last edited by R_J; 04-27-2020, 08:19 PM.Leave a comment:
I.e. resize from 15 megapixels to something smaller...
4608 x 3456 = 15925248 or 15.93 megapixelsLast edited by Per Hansson; 04-27-2020, 09:52 AM.Leave a comment:
I see a couple of problem with the power to the compressor
The compressor data label clearly state that the voltage is 240 volts
Why are you only getting 160 volts number one
Why is your amperage look low to me this might be issues number 2
Issues number 3 is you say that when the compressor run it is not very cool and the heat comes from the condenser coil is not very hot I being to think that something might be wrong with the compressor or your meter device or you might have a gas leak
Does this unit have a data plate on it if it does can you post a picture of it
I am just curious - if the compressor runs at whatever speed, and the inlet is slight cool, the outlet is warm (not hot), and the evaporator coil has refrigerant flowing with gurgling sound, etc, shouldn't the evaporator coil be slightly cool the the touch?Leave a comment:
- The bulb lights up for a about 1 second, then goes off, and remains off.
- It grows from nothing to peak (about 10% of normal I guessed) and dims down to nothing all within a second, then remained off for next few minutes during tests.
- The compressor never get turned on from the start! But the evaporator fan is on, interior lights are one, and panel indicators are on.Last edited by beetle1303; 04-27-2020, 03:37 AM.Leave a comment:
But I have since tried loading file sizes bigger than 4MB, all OK now. Thank you.Leave a comment:
by SuperAmanHi, I have a Hitachi Refrigerator R-Z270AUN7KV. The fridge is on the bottom and the freezer is on the top. My problem is no matter what setting (1-9) the freezer is, the fridge is not getting cold but the freezer is always cold. I have tried all combination of settings for the fridge (Min, Mid, Max) but nothing. Fridge is always hot now. Before it would sometimes do this but now always fridge is hot. I believe the service center peeled some of the foil from the thermostat and that seemed to help a few years back. I replaced the thermostat recently and it worked off and on for a few weeks but now...
by x_orange90_xI just got this tv today and it appeared to have no backlight on. After taking off the rear cover and checking again in the dark I can see that MAYBE one quadrant is lit.. But still it's quite dim. I was going to check the LEDs with my tester, and I found LED 1 and LED 2 + pins on the wire from the inverter, but I couldn't identify a ground. Nonetheless I tried using a mounting screw on the inverter board and also the chassis as ground but regardless my tester reads 300 which is what it reads when there is no voltage draw.
I don't know how exactly to test the inverter itself. Is it... -
by GentianI have a tripp-lite aspint 3636vr inverter charger which blow some of mosfet transistors. I replaced them repaired also the driver circuit and tested but the mosfets burn again.
It work very well as inverter and also as charger if I let the rear switch in auto mode (inverter) and charger only(charging) but in auto when I connect the feed line 220V AC first time it pass ok to line and start charging the batteries but when I remove the feed line it pass to inverter mode and if I do it again the second time when passing from charging to inverter the Main transformer start making a...03-06-2023, 07:07 AM -
by valvashonFor some reason I'm just not going to let this 19" TV defeat me. I guess because I have a schematic to work from I feel like I'm oh so close.
History- while adding a turn-on circuit I let a small screw roll under the power board. Worked through all of that circuitry, probably replacing a MOSFET and PWM controller that were not bad but I was following the service manual. Finally figured out that the power supply is in working order when the inverter section (for the backlights) is disconnected. When the +12 supply to the inverter is disconnected the +12 and +5 will come up...1 Photo -
by eccerr0rIf I had a solar fed grid tie inverter (GTI), a modified sine wave inverter, and a power outage occurred, what would happen if you disconnected mains, backfed the modified sinewave inverter (MSI) into house power, and hooked up the GTI to the output of the MSI, would it work?
Next thing is trying to charge the batteries using solar power, but that's another issue ... - Loading...
