Heat pump tumble dryer regas
  • Shagreobe
    Confused Newbie
    • Oct 2022
    • 16
    Re: Heat pump tumble dryer regas
    If both the large (suction) and the smaller (discharge) lines are the same temperature, then most likely you are out of refrigerant. Look around all of the copper lines, especially the soldered/welded joints for an oily residue, thats where your leak is.
    Be very careful if you connect gauges to it. Refrigerant burns are not fun.
    Can you post a picture of the machines data plate? that tells alot of information.
    • notallbad
      • Oct 2012
      • 1190
      There doesnt appear to be any kind of oily residue anywhere and all joints seem to look good.
      Of course, safety gloves will be worn.
      Photo of data plate and machine data attached.
        • Jul 2011
        • 6070
        Before you break into the sealed system do you have an amp meter check the amperage on the compressor check all three wires and posted your results
        Check and see if there is an electrical data plate on this unit and if so please take a picture of it
        • notallbad
          • Oct 2012
          • 1190
          ok shall get those readings as soon as I can meanwhile photo of compressor plate data
          • notallbad
            • Oct 2012
            • 1190
            I have 2 amp meters both give slightly differing readings
            meter 1
            Black - 1.6a
            Red - 0.8a
            White - 0.9a
            meter 2
            Black - 1.6a
            Red - 0.98a
            White - 0.98a
              • Jul 2011
              • 6070
              This looks about right for this size compressor and considering that it is being used as a dehumidifier setup the idea is to remove the humidity from the air and the air coming from the condenser is going to be a little warm and this should be normal but the humidity in the air coming out of condenser should be a lot dryer than what was going in
              Depending on how much humidity is in the air where you live might determine weather or you condensation coming from the evaporator coil
              This is how this dryer works if it is designed correctly the moisture in the cloth that goes in the dryer should become dry now with it take longer than a gas dryer possibly but do not compare the two on how fast they dry cloths
              The correct way to measure the temperature of the condenser and evaporator coil is use a electronic thermometer with temperature sensors that you actually put on the copper pipe line and measure the temperature
              There might be a problem with the system but it going be a little bit difficult to determine with this said the the next time you run the system put the amp probe on the compressor wire that has over one amp reading but this time run it with the fan running and see if there is a difference in the amount of amperage
              The other thing I would like you to do is when the compressor is running after a couple of minutes turn off the compressor and then turn it right back on dose the compressor start right back up or dose it hum and dose not start up if it does not restart then do the same test again but this time leave it off for at least a minute and see if it will restart if not wait another minute and see if it restart ( one note do not leave it until the temperature over load trips the purpose of this test is a way to determine if the system is very low on Freon or if the system is a little bit restricted or not )
              Now if the compressor restart right after you turn it off and right back on then either it is very low on Freon or the compressor has an issue with pumping the Freon and bring the system pressure where it should be in this situation you will need to use gauges to determine what the issue is
              One other thing you can try is when you first turn the unit on when it has been off for many hours when you turn it on feel the bottom of compressor does the compressor feel very cold or does it get warm to hot very quickly and never get cold if so it might be very low on Freon feel the bottom of the compressor until the compressor gets warm until you can not leave your hand on it but time how long this takes because this will tell more of what is going with the system
              • notallbad
                • Oct 2012
                • 1190
                quote "One other thing you can try is when you first turn the unit on when it has been off for many hours when you turn it on feel the bottom of compressor does the compressor feel very cold or does it get warm to hot very quickly and never get cold if so it might be very low on Freon feel the bottom of the compressor until the compressor gets warm until you can not leave your hand on it but time how long this takes because this will tell more of what is going with the system"
                Wouldnt say it feels very cold after being sat for several hours.
                Approx after around 15 minutes of running it becomes uncomfortable to touch for more than 5 secs, it continues to be like this until up to around an hour when its more like 3 secs.
                • notallbad
                  • Oct 2012
                  • 1190
                  quote "
                  There might be a problem with the system but it going be a little bit difficult to determine with this said the the next time you run the system put the amp probe on the compressor wire that has over one amp reading but this time run it with the fan running and see if there is a difference in the amount of amperage"
                  with the machine re-assembled the amps on the black wire (common) reads around 0.98a.
                  Being reassembled there is air flow across the evaporator/condenser.
                  The fan that blows air across the compressor doesnt come on even after being on for an hour.
                  • notallbad
                    • Oct 2012
                    • 1190
                    quote"
                    The other thing I would like you to do is when the compressor is running after a couple of minutes turn off the compressor and then turn it right back on dose the compressor start right back up or dose it hum and dose not start up if it does not restart then do the same test again but this time leave it off for at least a minute and see if it will restart if not wait another minute and see if it restart ( one note do not leave it until the temperature over load trips the purpose of this test is a way to determine if the system is very low on Freon or if the system is a little bit restricted or not )"
                    With it reassembled if I pause it then restart it the compressor takes 1 minute to start up again. This may be to do with the control board so think this test with the control board connected/controlling the compressor is inconclusive at the moment.
                    • notallbad
                      • Oct 2012
                      • 1190
                      quote"Now if the compressor restart right after you turn it off and right back on then either it is very low on Freon or the compressor has an issue with pumping the Freon and bring the system pressure where it should be in this situation you will need to use gauges to determine what the issue is"
                      Ok so this test with the compressor standalone, i.e disconnected from the control board and directly connected to 230v ac via the start cap it does indeed start right back up after running for 2 minutes.
                      What gauges/setup would you recommend getting?
                        • Jul 2011
                        • 6070
                        Something like this would be preferable because it has the pressure temperature chart on the garages for 134A
                        https://www.amazon.com/Diagnostic-Ma...1zcF9tdGY&th=1
                        You would also need some of these as well ( but make sure that you remove the value before you braze them in place )
                        https://www.amazon.com/gohantee-10PC...a-815245751459
                        You would also need someone that knows how braze copper tubing as well
                        You would also need access to a vacuum pump for refrigeration would be preferable as well
                        You need access to some type of leak detector to know where the leak is
                        You will need access to nitrogen to boost the system pressure to around 350 psi this is to aid in the leak detection with the use of a leak detector
                        Your evaporator temperature should not be lower than 40*F otherwise you will ice up the evaporator coil
                        I hope this helps you with getting this device repaired
                        One note ( if you want to quote something please use the quote button and just delete what you do not want to quote ) it makes it much easier to read the section that you are commenting about thanks
                        • petehall347
                          • Jan 2015
                          • 4450
                          • United Kingdom
                          #32
                          been following this post and it makes me happy that i have a washing line . or rather hang up inside and put the dehumidifier on .
                          i dont know your area but some people buy broken clothes driers and that money could go towards a new one .
                          • notallbad
                            • Oct 2012
                            • 1190
                            But we are a family of 7 and having clothes lying around drying would be like living in a clothes shop.
                            Why let someone else have all the fun!
                            I was offered £20 for it and that wouldnt go far towards a new replacement, a secondhand unit possibly but then theres the possibility it wont last long unless you can find an honest seller. So many crooks about selling rubbish.
                            • notallbad
                              • Oct 2012
                              • 1190
                              Thanks.
                              Would I be correct in saying that the refrigerant would need recovering first with a bullet piercing valve on the low side, then remove the bullet piercing valve and replace with a brazed valve whilst also brazing a valve on the high side, to then hold vacuum on the low side for 30 mins or so before then replenishing the refrigerant at the correct pressure/temperature.
                              • notallbad
                                • Oct 2012
                                • 1190
                                How does this system differ to that of a cars/automobiles air con system? These generally require topping up or replacing every 2 years or so and not due to system failures but just part of a maintenance procedure.
                                What I'm really getting at I guess is that this dryer is 4/5 years old so would it not just likely be a case of needing similar maintenance/top-up as an aircon on a car?
                                Of course, doing a pressure test would eliminate any leak faults and save on the cost of wasting refrigerant but the nitrogen for a ptessure test would probably be far more expensive if even available to joe bloggs and a vacuum test would highlight any major leaks of concern.
                                • diif
                                  • Feb 2014
                                  • 6978
                                  • England
                                  #36
                                  Did it stop drying gradually or was it quick ?
                                  • notallbad
                                    • Oct 2012
                                    • 1190
                                    History of the dryer is unknown.
                                    If it were sudden I would imagine there would be obvious signs of refrigerant leaked and a vacuum test would show this up which is yet to be done.
                                      • Jul 2011
                                      • 6070
                                      You can do a vacuum test but let be clear it not as good as a pressure test with nitrogen as the boost the system pressure but if this dryer is 4 or 5 years old there is a good possibility that it might be a restriction in the cap tube or the filter dryer if you do not any leaks but your system pressures will verify if it is a restriction issue because you will not be able to get the pressure correct
                                      • notallbad
                                        • Oct 2012
                                        • 1190
                                        What is this part thats connected directly to the bottom of the compressor? Which is on the low side.
                                          • Jul 2011
                                          • 6070
                                          The part you are referring to is known as the “ accumulator ” ( where the RED arrow is located at ) this is used so that it you still have some liquid refrigerant still in the suction line still has a chance to turn into a gas and not damage the compressor
                                          To answer your second question I have answered it with where the low side and where the high side of the system and where the filter dryer and where the accumulator is located at and that is where you would want to put your value at
                                          I caution you that not knowing weather or not it is that the system is low on refrigerant or is restricted or you have a compressor issue you need to know what the high side and low side pressures are in the system when the compressor is running ( you can not assume that it is low on refrigerant without knowing what the system pressures are when adding refrigerant to the system because if it restricted you can easily add a lot of refrigerant in the system and not know it if you are not careful it has happened to me before I have been doing air conditioning and refrigeration for many years and depending on how much it is restricted sometimes it can fool you and it being that the metering device is a cap-tube this is more likely to happen )
                                          When you have gauges hooked up to the system if you would please take a picture of gauges when the compressor running and before you add refrigerant unless you loose the hole charge of the system because of not having the right equipment to just check the system pressure correctly then this another story
                                          Because if you loose the hole charge of the system then your next step would be to add some refrigerant and some nitrogen to the system to have a pressure of around 350 psi ( no higher 400 psi ) and then use a leak detector and very slowly go around all of the brazing joints and coils and the compressor terminals and check for leaks no matter how small you should have NO leaks whatsoever if you do where are they and take a picture of where it is leaking if you have a leak in the system
                                          Under No circumstances should you run the compressor when you have refrigerant and nitrogen in the system you will probably ruin the compressor if you were to do this also when you have the system vacuum out also do not run the compressor then either because the same thing could happen
                                          I hope this helps you with this repair
                                          • Petros_Z
                                            candy tumble dryer (evoc 981 at-s) Component 738
                                            by Petros_Z
                                            Hello. I have a board of a candy tumble dryer (evoc 981 at-s).
                                            It does not give an error but it keeps drying even without load. It has 3 ntc. Two are for the clothes and one for the compressor. I measure them and they look ok. I went to the board to measure the voltage given to them. It gives about 4v and it is going down as the ntc value going down.
                                            Because I wanted to measure more easily I tried to solder wires on the board. Probably I manage to destroy the component of the title. It looks like as a smd resistor. Hopefully there were other two same components. I disorder them and...
                                            01-04-2025, 02:17 AM
                                          • spleenharvester
                                            Beko Tumble Dryer DTLCE80021W cutting out/tripping RCD
                                            by spleenharvester
                                            This dryer is several years old and has previously had a new motor cap. Currently it's behaving erratically - sometimes it finishes the cycle fine, other times it cuts out after a random period of time (just stops with no LEDs as if it has finished normally), and occasionally it trips the RCD. There's always steam coming off the clothes at the time it cuts out.
                                            Going to pull it apart tomorrow, before I lob a new heating element at it is there anything else worth checking? It's £70 for a new heating element and the whole machine only cost £180 to begin with...
                                            Cheers
                                            12-16-2024, 03:36 PM
                                          • Eaglecrest
                                            Whirlpool dryer control board
                                            by Eaglecrest
                                            I have a Whirlpool dryer that runs for a while then stops with a blinking timer screen. The dryer can't be reset by hitting any input and if you pull the plug and plug it back in it also won't respond. Light is on in the drum when you open the door, but no other sign of life. If I leave it unplugged for a period of time, which is multiple days, it runs again. May be able to get a load done, but now seems to be less than full load before it errors out.
                                            Since unplugging will get it to work, I am assuming that there is an error condition that is causing the onboard processor to shut...
                                            11-05-2025, 07:09 PM
                                          • BigPete
                                            Panasonic Heatpump Dryer Repair
                                            by BigPete
                                            I picked up a Panasonic NH-P70G2, though it would apply to the NH-P80G2, NH-P70G1 and NH-P80G1 models as well, as maybe some other models. This one was coming up with a H86 error. After lots of testing and googling it was an error with one of the thermistors in the condenser area.
                                            The attached French service manuals is incorrect, TH11 is gray and is a 95k thermistor and TH12 is black and is a 35k thermistor.
                                            In my case TH12 was bad. I was able to get a 35k thermistor on AliExpress. It's 6mm in diameter.
                                            Unfortunately the whole machine has to come apart to fix it.
                                            I have...
                                            11-01-2025, 06:40 PM
                                          • tmcw
                                            Tumble Dryer - motor start capacitor
                                            by tmcw
                                            I was looking for a replacement capacitor for a tumble dryer, and I found one on eBay that has the correct values, and even looked similar, but of course, when the capacitor arrived, it didn't look like the cap in the listing picture.
                                            I've attached the old (left) and the replacement (right) caps in a picture. The new one has plastic housing, the old one has a metal housing and is bigger. Am I likely to have any issues with this replacement?
                                            Thanks....
                                            05-09-2022, 09:11 AM
