Re: Heat pump tumble dryer regas
Assuming that the Freon is NOT contaminated by anything you could recover the Freon with a Freon recovery tank and a lot of ice in a bucket and you could recover most of the Freon
But this is crap shoot to do this with out testing it for acid at a minimum also if you have a Freon recovery tank you should only use the liquid side of the tank not the gas side just in case there is non condensable in the Freon tank from the system that you are taking the Freon out of when you get ready for adding more Freon to the system that you are repairing let me know and I will try to explain to you how to charge a system with liquid Freon this not recommended procedure by the way and if done wrong you can damage the compressor
If you want to minimize the amount of contamination from using Freon from another system then get your self a central air conditioner filter dryer ( you could use two of them in series for more filtering if you want be more sure that you get as much as possible of any contamination in the Freon ) that is for a 5 ton unit and use the valve that I recommend that you should buy put one on each end of the filter dryer in front of the service hose going to the gauge to the system that you are repairing
You do have to prepare the recovery tank by vacuuming it out until you have 29 inch of vacuum and once you have reached this valve keep the vacuum pump for another 30 minutes and with valves on the Freon recovery tank closed watch the gauges for 15 minutes to see if it’s value changes then you might still mosture in the tank run the vacuum pump for another half hour until you do not see any changes in the value of the gauge reading
Once you have completed this procedure then put the recovery tank in a bucket full of ice and let the tank get very cold before you open the valves on your garage and if you can heat up the compressor on the doner system and leave it in status for at least an hour so you will recover most of Freon out of the donor system
You need to make sure that you purge the gauges service line before you start add or putting Freon in the tank or to system that you are repairing
Then you would charge the system that you are trying to repair you do not want your system suction side pressure to be lower than ( 40*F or 35 psi or slightly higher value would be fine as well ) so you do not have an evaporator freezing issue
One note if you do not follow the procedures to not contaminate the system systems you are asking for trouble down the road and may even shorten the life of the compressor and contaminate the system as well and at worst you would not be able to get the system pressure to be correct and changed it still will not work correctly
This is assuming that it just low on Freon now if it is a compressor issue or a cap tube restriction then you will have a lot more work to do but some of the procedures are the same for recovery of the Freon out of the system
I still would highly recommend that you use new Freon out of cans that are for automotive air conditioning systems just make sure that it does NOT have oil add for compressor the reason that most Freon for automotive air conditioning is because when you have a leak in the system because the compressor has so little oil in them and you have a Freon leak you would lose some oil but the amount of oil that is in these cans is too much oil in most cases and if you have to much oil in a system then you can some serious issues to possibility of compressor failure or very low cooling efficiency at a minimum
I hope this helps you with this repair
Try our *UPDATED* boardview, bios, & schematic search. Over 2.3 million files for download!
Heat pump tumble dryer regas
Collapse
X
-
Re: Heat pump tumble dryer regas
It was more of a theoretical question rather than practical.
Assuming the donor refrigerant and system are ok would the process be the same?Leave a comment:
-
Re: Heat pump tumble dryer regas
I highly recommend that you do NOT do this type of procedure because you do not know if this system is contaminated ( with acid or something else like non condensable ) or not and if it is it just contaminates your system and you would have a lot more work to clean the system after that happensLeave a comment:
-
Re: Heat pump tumble dryer regas
Thanks again.
As soon as I get some equipment I shall update.
Looking to obtain gauges, hoses, vacuum pump, refrigerant leak detector, vacuum gauge and k-type thermometer.
Question - is it possible to refill refrigerant from another system rather than from a cylinder or can?Last edited by notallbad; 07-30-2023, 02:20 PM.Leave a comment:
-
Re: Heat pump tumble dryer regas
The part you are referring to is known as the “ accumulator ” ( where the RED arrow is located at ) this is used so that it you still have some liquid refrigerant still in the suction line still has a chance to turn into a gas and not damage the compressor
To answer your second question I have answered it with where the low side and where the high side of the system and where the filter dryer and where the accumulator is located at and that is where you would want to put your value at
I caution you that not knowing weather or not it is that the system is low on refrigerant or is restricted or you have a compressor issue you need to know what the high side and low side pressures are in the system when the compressor is running ( you can not assume that it is low on refrigerant without knowing what the system pressures are when adding refrigerant to the system because if it restricted you can easily add a lot of refrigerant in the system and not know it if you are not careful it has happened to me before I have been doing air conditioning and refrigeration for many years and depending on how much it is restricted sometimes it can fool you and it being that the metering device is a cap-tube this is more likely to happen )
When you have gauges hooked up to the system if you would please take a picture of gauges when the compressor running and before you add refrigerant unless you loose the hole charge of the system because of not having the right equipment to just check the system pressure correctly then this another story
Because if you loose the hole charge of the system then your next step would be to add some refrigerant and some nitrogen to the system to have a pressure of around 350 psi ( no higher 400 psi ) and then use a leak detector and very slowly go around all of the brazing joints and coils and the compressor terminals and check for leaks no matter how small you should have NO leaks whatsoever if you do where are they and take a picture of where it is leaking if you have a leak in the system
Under No circumstances should you run the compressor when you have refrigerant and nitrogen in the system you will probably ruin the compressor if you were to do this also when you have the system vacuum out also do not run the compressor then either because the same thing could happen
I hope this helps you with this repairLast edited by sam_sam_sam; 07-29-2023, 02:37 AM.Leave a comment:
-
Re: Heat pump tumble dryer regas
You can do a vacuum test but let be clear it not as good as a pressure test with nitrogen as the boost the system pressure but if this dryer is 4 or 5 years old there is a good possibility that it might be a restriction in the cap tube or the filter dryer if you do not any leaks but your system pressures will verify if it is a restriction issue because you will not be able to get the pressure correctLeave a comment:
-
Leave a comment:
-
Re: Heat pump tumble dryer regas
Did it stop drying gradually or was it quick ?Leave a comment:
-
Re: Heat pump tumble dryer regas
How does this system differ to that of a cars/automobiles air con system? These generally require topping up or replacing every 2 years or so and not due to system failures but just part of a maintenance procedure.
What I'm really getting at I guess is that this dryer is 4/5 years old so would it not just likely be a case of needing similar maintenance/top-up as an aircon on a car?
Of course, doing a pressure test would eliminate any leak faults and save on the cost of wasting refrigerant but the nitrogen for a ptessure test would probably be far more expensive if even available to joe bloggs and a vacuum test would highlight any major leaks of concern.Last edited by notallbad; 07-27-2023, 06:00 AM.Leave a comment:
-
Re: Heat pump tumble dryer regas
Something like this would be preferable because it has the pressure temperature chart on the garages for 134A
https://www.amazon.com/Diagnostic-Ma...1zcF9tdGY&th=1
You would also need some of these as well ( but make sure that you remove the value before you braze them in place )
https://www.amazon.com/gohantee-10PC...a-815245751459
You would also need someone that knows how braze copper tubing as well
You would also need access to a vacuum pump for refrigeration would be preferable as well
You need access to some type of leak detector to know where the leak is
You will need access to nitrogen to boost the system pressure to around 350 psi this is to aid in the leak detection with the use of a leak detector
Your evaporator temperature should not be lower than 40*F otherwise you will ice up the evaporator coil
I hope this helps you with getting this device repaired
One note ( if you want to quote something please use the quote button and just delete what you do not want to quote ) it makes it much easier to read the section that you are commenting about thanks
Thanks.
Would I be correct in saying that the refrigerant would need recovering first with a bullet piercing valve on the low side, then remove the bullet piercing valve and replace with a brazed valve whilst also brazing a valve on the high side, to then hold vacuum on the low side for 30 mins or so before then replenishing the refrigerant at the correct pressure/temperature.Leave a comment:
-
Re: Heat pump tumble dryer regas
But we are a family of 7 and having clothes lying around drying would be like living in a clothes shop.
Why let someone else have all the fun!
I was offered £20 for it and that wouldnt go far towards a new replacement, a secondhand unit possibly but then theres the possibility it wont last long unless you can find an honest seller. So many crooks about selling rubbish.Leave a comment:
-
Re: Heat pump tumble dryer regas
been following this post and it makes me happy that i have a washing line . or rather hang up inside and put the dehumidifier on .
i dont know your area but some people buy broken clothes driers and that money could go towards a new one .Leave a comment:
-
Re: Heat pump tumble dryer regas
Something like this would be preferable because it has the pressure temperature chart on the garages for 134A
https://www.amazon.com/Diagnostic-Ma...1zcF9tdGY&th=1
You would also need some of these as well ( but make sure that you remove the value before you braze them in place )
https://www.amazon.com/gohantee-10PC...a-815245751459
You would also need someone that knows how braze copper tubing as well
You would also need access to a vacuum pump for refrigeration would be preferable as well
You need access to some type of leak detector to know where the leak is
You will need access to nitrogen to boost the system pressure to around 350 psi this is to aid in the leak detection with the use of a leak detector
Your evaporator temperature should not be lower than 40*F otherwise you will ice up the evaporator coil
I hope this helps you with getting this device repaired
One note ( if you want to quote something please use the quote button and just delete what you do not want to quote ) it makes it much easier to read the section that you are commenting about thanksLast edited by sam_sam_sam; 07-26-2023, 07:06 PM.Leave a comment:
-
Re: Heat pump tumble dryer regas
quote"Now if the compressor restart right after you turn it off and right back on then either it is very low on Freon or the compressor has an issue with pumping the Freon and bring the system pressure where it should be in this situation you will need to use gauges to determine what the issue is"
Ok so this test with the compressor standalone, i.e disconnected from the control board and directly connected to 230v ac via the start cap it does indeed start right back up after running for 2 minutes.
What gauges/setup would you recommend getting?Leave a comment:
-
Re: Heat pump tumble dryer regas
quote"
The other thing I would like you to do is when the compressor is running after a couple of minutes turn off the compressor and then turn it right back on dose the compressor start right back up or dose it hum and dose not start up if it does not restart then do the same test again but this time leave it off for at least a minute and see if it will restart if not wait another minute and see if it restart ( one note do not leave it until the temperature over load trips the purpose of this test is a way to determine if the system is very low on Freon or if the system is a little bit restricted or not )"
With it reassembled if I pause it then restart it the compressor takes 1 minute to start up again. This may be to do with the control board so think this test with the control board connected/controlling the compressor is inconclusive at the moment.Last edited by notallbad; 07-24-2023, 06:12 AM.Leave a comment:
-
Re: Heat pump tumble dryer regas
quote "
There might be a problem with the system but it going be a little bit difficult to determine with this said the the next time you run the system put the amp probe on the compressor wire that has over one amp reading but this time run it with the fan running and see if there is a difference in the amount of amperage"
with the machine re-assembled the amps on the black wire (common) reads around 0.98a.
Being reassembled there is air flow across the evaporator/condenser.
The fan that blows air across the compressor doesnt come on even after being on for an hour.Leave a comment:
-
Re: Heat pump tumble dryer regas
quote "One other thing you can try is when you first turn the unit on when it has been off for many hours when you turn it on feel the bottom of compressor does the compressor feel very cold or does it get warm to hot very quickly and never get cold if so it might be very low on Freon feel the bottom of the compressor until the compressor gets warm until you can not leave your hand on it but time how long this takes because this will tell more of what is going with the system"
Wouldnt say it feels very cold after being sat for several hours.
Approx after around 15 minutes of running it becomes uncomfortable to touch for more than 5 secs, it continues to be like this until up to around an hour when its more like 3 secs.Last edited by notallbad; 07-24-2023, 05:27 AM.Leave a comment:
-
Re: Heat pump tumble dryer regas
This looks about right for this size compressor and considering that it is being used as a dehumidifier setup the idea is to remove the humidity from the air and the air coming from the condenser is going to be a little warm and this should be normal but the humidity in the air coming out of condenser should be a lot dryer than what was going in
Depending on how much humidity is in the air where you live might determine weather or you condensation coming from the evaporator coil
This is how this dryer works if it is designed correctly the moisture in the cloth that goes in the dryer should become dry now with it take longer than a gas dryer possibly but do not compare the two on how fast they dry cloths
The correct way to measure the temperature of the condenser and evaporator coil is use a electronic thermometer with temperature sensors that you actually put on the copper pipe line and measure the temperature
There might be a problem with the system but it going be a little bit difficult to determine with this said the the next time you run the system put the amp probe on the compressor wire that has over one amp reading but this time run it with the fan running and see if there is a difference in the amount of amperage
The other thing I would like you to do is when the compressor is running after a couple of minutes turn off the compressor and then turn it right back on dose the compressor start right back up or dose it hum and dose not start up if it does not restart then do the same test again but this time leave it off for at least a minute and see if it will restart if not wait another minute and see if it restart ( one note do not leave it until the temperature over load trips the purpose of this test is a way to determine if the system is very low on Freon or if the system is a little bit restricted or not )
Now if the compressor restart right after you turn it off and right back on then either it is very low on Freon or the compressor has an issue with pumping the Freon and bring the system pressure where it should be in this situation you will need to use gauges to determine what the issue is
One other thing you can try is when you first turn the unit on when it has been off for many hours when you turn it on feel the bottom of compressor does the compressor feel very cold or does it get warm to hot very quickly and never get cold if so it might be very low on Freon feel the bottom of the compressor until the compressor gets warm until you can not leave your hand on it but time how long this takes because this will tell more of what is going with the systemLast edited by sam_sam_sam; 07-21-2023, 11:46 PM.Leave a comment:
Related Topics
Collapse
-
by flat-eartherThe auxiliary coolant pump, AKA turbo after run electric coolant pump, parking heater, on a 1.8 TSI VW VAG engine did not work.
part number 1K0965561J
I removed the pump and applied 12V to it but nothing happened.
The contact on flat side of the plastic molding is the positive.
I opened the pump by prying and pulling out the bottom piece where the electric plug is, it needs to be pulled out, it can not be twisted.
I discovered a PCB inside and it was wet and full of corrosion, I cleaned it with alcohol and toothbrush and tried 12V again and the motor... -
by Petros_ZHello. I have a board of a candy tumble dryer (evoc 981 at-s).
It does not give an error but it keeps drying even without load. It has 3 ntc. Two are for the clothes and one for the compressor. I measure them and they look ok. I went to the board to measure the voltage given to them. It gives about 4v and it is going down as the ntc value going down.
Because I wanted to measure more easily I tried to solder wires on the board. Probably I manage to destroy the component of the title. It looks like as a smd resistor. Hopefully there were other two same components. I disorder them and... -
This dryer is several years old and has previously had a new motor cap. Currently it's behaving erratically - sometimes it finishes the cycle fine, other times it cuts out after a random period of time (just stops with no LEDs as if it has finished normally), and occasionally it trips the RCD. There's always steam coming off the clothes at the time it cuts out.
Going to pull it apart tomorrow, before I lob a new heating element at it is there anything else worth checking? It's £70 for a new heating element and the whole machine only cost £180 to begin with...
Cheers -
by tmcwI was looking for a replacement capacitor for a tumble dryer, and I found one on eBay that has the correct values, and even looked similar, but of course, when the capacitor arrived, it didn't look like the cap in the listing picture.
I've attached the old (left) and the replacement (right) caps in a picture. The new one has plastic housing, the old one has a metal housing and is bigger. Am I likely to have any issues with this replacement?
Thanks....-
Channel: General Capacitor Questions & Issues
-
-
by notallbadAnyone able to help diagnose the fault with this board please.
Hopefully photos are clear enough to give me direction on what readings to take and where.
All ancillary components of the dryer have been tested and work i.e heating element, thermostats, sensors, motor, door switch, wiring harness.
So theres 230v at the control board but no life whatsoever with or without the ancillaries connected.
The on/off/timer dial contacts are clean and make good contact. All the through hole mounted components appear to be good i.e diodes, resistors,... - Loading...
- No more items.
Leave a comment: