Power-One solar Inverter driving me NUTS!!!

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • sam_sam_sam
    Badcaps Legend
    • Jul 2011
    • 6025
    • USA

    #141
    Originally posted by mitsu2k
    I tested between the first and third legs in my photo. Here are the results.

    500vdc test

    #1
    175 mOhms

    #2
    205 mOhms

    #3
    215 mOhms

    #4
    239 mOhms
    Did you do the test procedure that is outlined in this maintenance manual
    Did you follow it exactly or did you deviate from what they have and if you did please explain how you did it differently
    Also if you did run the test as they outlined in the manual what were your results for each section of tests
    https://www.badcaps.net/filedata/fetch?id=3153508
    Last edited by sam_sam_sam; 11-25-2023, 05:53 AM.

    Comment

    • CapLeaker
      Leaking Member
      • Dec 2014
      • 8020
      • Canada

      #142
      Originally posted by mitsu2k
      I tested between the first and third legs in my photo. Here are the results.

      500vdc test

      #1
      175 mOhms

      #2
      205 mOhms

      #3
      215 mOhms

      #4
      239 mOhms

      I also tested the two blue ones on the AC side and those tested over 4000 mOhms. (full scale on megger)

      Not sure what these results mean. Could all 4 of them be bad?
      I hope you mean MOhm not mOhm. There is a huge difference between Mega and Milli

      See, MOVs degrade with time and how often the get zapped. The insulation layer will break down each time it gets hit, to a point of leaking or total failure (basically a short). A 175 Mega Ohms is not a failure, but it's getting time to change it out. All depends on what the rating of this MOV is and how much voltage you use with the Megger,
      Let's say you hit a 375V MOV with 500V from the Megger, it will hurt the MOV each time you press the test button.

      Comment

      • mitsu2k
        Senior Member
        • Aug 2013
        • 199
        • USA

        #143
        Originally posted by sam_sam_sam

        Did you do the test procedure that is outlined in this maintenance manual
        Did you follow it exactly or did you deviate from what they have and if you did please explain how you did it differently
        Also if you did run the test as they outlined in the manual what were your results for each section of tests
        https://www.badcaps.net/filedata/fetch?id=3153508
        I have not seen any test in any maintenance manual. Where are you seeing this?

        Comment

        • mitsu2k
          Senior Member
          • Aug 2013
          • 199
          • USA

          #144
          Originally posted by CapLeaker

          I hope you mean MOhm not mOhm. There is a huge difference between Mega and Milli
          Yes I meant MegaOhms

          Comment

          • petehall347
            Badcaps Legend
            • Jan 2015
            • 4424
            • United Kingdom

            #145
            troubleshooting is page 49 onwards

            Comment

            • mitsu2k
              Senior Member
              • Aug 2013
              • 199
              • USA

              #146
              Originally posted by petehall347
              troubleshooting is page 49 onwards
              OK I think I know what you are referring to now. Please see attached. This is the only test that I can see that would be relevant. And I did perform this test in the following manner:

              tested between positive and earth ground and got over 50 MegaOhms.

              got approximately the same results from negative to earth ground.

              I did not short the positive and negative together because it was daytime and I didn't think that would be a good idea being that there's about 256 V there. However, I wouldn't expect to see any different results if I shorted them being that they were both over 50 mega anyway. I suppose I can do this test at night, but I am just afraid of blowing the diodes on the panels and I don't really want to go up on the roof being that I am afraid of heights
              Attached Files
              Last edited by mitsu2k; 11-25-2023, 03:47 PM.

              Comment

              • mitsu2k
                Senior Member
                • Aug 2013
                • 199
                • USA

                #147
                Originally posted by petehall347
                from what i can make out its behaving correctly its only the "A" models that dont halt at this fault . unless yours is an "A" model

                HI Pete, I now know what you are talking about "A" models. Mine is not an "A" model. I found the manual that you must have been looking at. It appears that these have a built in Arc detection feature as well as some other features. For example, the "Autotest" feature is non existent in my inverter. I even looked under the service menu. I was able to find a key generator in order to access this menu.

                Comment

                • mitsu2k
                  Senior Member
                  • Aug 2013
                  • 199
                  • USA

                  #148
                  Ok I did the test outlined in the manual. (Positive shorted to Negative) at 250v on the megger to earth ground.

                  result= >4000 MegaOhms on the megger (full scale). All good here.

                  Comment

                  • CapLeaker
                    Leaking Member
                    • Dec 2014
                    • 8020
                    • Canada

                    #149
                    Yours isn't an A model. It doesn't have that fat ass clamp contraption. When you hook that inverter back up to test, you put one or both strings to it? Are you using both DC ports? The solar panels face all in the same direction?

                    Comment

                    • mitsu2k
                      Senior Member
                      • Aug 2013
                      • 199
                      • USA

                      #150
                      Originally posted by CapLeaker
                      Yours isn't an A model. It doesn't have that fat ass clamp contraption. When you hook that inverter back up to test, you put one or both strings to it? Are you using both DC ports? The solar panels face all in the same direction?
                      I only have one string. All panels face the same direction. I am using only one DC port but I have tried connecting to the second one as well, and got the same results

                      Comment

                      • sam_sam_sam
                        Badcaps Legend
                        • Jul 2011
                        • 6025
                        • USA

                        #151
                        I would mega ohm the cables from the solar panels to the inverter with out the cable being attached to the solar panels or the inverter especially if the positive and negative cables are connected to together as one cable run and or are in conduit because I ran into a situation where water had introduced into the installation of wires and were shorting out in the conduit so do not rule this one out I use a mega ohm tester to figure out why this device was blowing fuses ( how you test for this is you have one meter lead on positive wire and the other meter lead on the negative wire )

                        On the same note are you using outside rated cable that you are using for the wiring from the solar panels to the inverter if not you should be and should be outside rated conduit or if I was doing this I would be doing it this way

                        Your results should be the highest mega ohm reading that the meter ohm meter has and any thing else would be suspicious at least to me it would be or you have something wrong with inverter showing a voltage leaking situation
                        Last edited by sam_sam_sam; 11-26-2023, 04:28 AM.

                        Comment

                        • CapLeaker
                          Leaking Member
                          • Dec 2014
                          • 8020
                          • Canada

                          #152
                          I did notice that there is a switch on your inverter, next to the AC connection. That is to pair or not to pair them DC inputs. I think the switch isn't set for them 2 DC ports as paired. Also there support to be a jumper between the 2 DC ports going from positive to positive and negative to negative. Putting the inverter on the DC port into paired, supposed to handle more current or something. Can't remember. Got to read that manual again.
                          Last edited by CapLeaker; 11-26-2023, 05:59 AM.

                          Comment

                          • petehall347
                            Badcaps Legend
                            • Jan 2015
                            • 4424
                            • United Kingdom

                            #153
                            what is the history of this thing ? like did it work then suddenly this fault ? any other factors that may have happened just prior to this particular fault ?

                            Comment

                            • mitsu2k
                              Senior Member
                              • Aug 2013
                              • 199
                              • USA

                              #154
                              Originally posted by sam_sam_sam
                              I would mega ohm the cables from the solar panels to the inverter with out the cable being attached to the solar panels or the inverter especially if the positive and negative cables are connected to together as one cable run and or are in conduit because I ran into a situation where water had introduced into the installation of wires and were shorting out in the conduit so do not rule this one out I use a mega ohm tester to figure out why this device was blowing fuses ( how you test for this is you have one meter lead on positive wire and the other meter lead on the negative wire )

                              On the same note are you using outside rated cable that you are using for the wiring from the solar panels to the inverter if not you should be and should be outside rated conduit or if I was doing this I would be doing it this way

                              Your results should be the highest mega ohm reading that the meter ohm meter has and any thing else would be suspicious at least to me it would be or you have something wrong with inverter showing a voltage leaking situation
                              SAM, this is good thinking about wires shorting out inside the conduit. I do not think this will be the case but I will check it at night. It may shed light on that small transient voltage either way.. They are coming through my attic in a flex conduit. 12awg I believe. I have not seen any signs of water or moisture when I went up in the attic. The panels were installed by the builder or builder's contractor when the house was built so the wiring should all be the proper type there..

                              Comment

                              • mitsu2k
                                Senior Member
                                • Aug 2013
                                • 199
                                • USA

                                #155
                                Originally posted by CapLeaker
                                I did notice that there is a switch on your inverter, next to the AC connection. That is to pair or not to pair them DC inputs. I think the switch isn't set for them 2 DC ports as paired. Also there support to be a jumper between the 2 DC ports going from positive to positive and negative to negative. Putting the inverter on the DC port into paired, supposed to handle more current or something. Can't remember. Got to read that manual again.
                                CapLeaker, The "PAR' switch according to my understanding of the manual is used to parallel more inverters together.

                                Comment

                                • mitsu2k
                                  Senior Member
                                  • Aug 2013
                                  • 199
                                  • USA

                                  #156
                                  Originally posted by petehall347
                                  what is the history of this thing ? like did it work then suddenly this fault ? any other factors that may have happened just prior to this particular fault ?
                                  Pete, the history of this unit is as follows. The inverter was probably installed around 2014 based on the date code. About 3 years ago it got the E031 error which is where the relay contacts on the PCB arc and burn out. At that time I repaired it by reflowing the solder joints on the relay in question. about a year later same thing happened but on a different relay. I repaired it same way. Several months later, it happened a third time and again on a different relay. This time I decided to reinforce the traces using some copper wire to allow more current to flow so the contacts would not arc and burn out. This seemed to work very well however I neglected to add the copper wire on one of the relay contacts. a couple months after that, I noticed that the inverter was not working and the red GFI light was on. So again I opened it up and found that the one relay contact that I did not reinforce with wire had burned out. However, this time that relay was melted pretty good and was not functional. I replaced all 4 relays at that time and reinforced all the pads/contacts with wire. Reinstalled it and the GFI light did not go away. So here we are today.

                                  I would like to add that the very last time I mentioned above, there were no error messages on the display. The 3 previous times I had the E031 error on the display and the alarm led was lit but no GFI light.
                                  Last edited by mitsu2k; 11-26-2023, 10:19 AM.

                                  Comment

                                  • petehall347
                                    Badcaps Legend
                                    • Jan 2015
                                    • 4424
                                    • United Kingdom

                                    #157
                                    so it looks like gfi coincides with the 4th relay then . what is that relay for ?
                                    maybe set your meter on megohms and check between the ground and around that 4th relay looking for leakage on the board . it does look as if the inverter is seeing leakage from somewhere .

                                    Comment

                                    • mitsu2k
                                      Senior Member
                                      • Aug 2013
                                      • 199
                                      • USA

                                      #158
                                      Originally posted by petehall347
                                      so it looks like gfi coincides with the 4th relay then . what is that relay for ?
                                      maybe set your meter on megohms and check between the ground and around that 4th relay looking for leakage on the board . it does look as if the inverter is seeing leakage from somewhere .
                                      the 4 relays are on the AC side. During normal operation, you can hear the relays cycling on/off.

                                      Comment

                                      • mitsu2k
                                        Senior Member
                                        • Aug 2013
                                        • 199
                                        • USA

                                        #159
                                        I have a question about those 4 MOVs. When I measure voltage between positive and earth ground, I get about 145V. When I remove the MOVs and measure without them, the voltage increases to around 194V. So the MOVs are suppressing some voltage. I am wondering if these MOVs are getting weak and they should be suppressing more. I did find that the middle leg of the MOVs of the positive input is connected directly to earth ground. On the negative the middle leg is connected directly to the GRP terminals that goes to that second board. I have went ahead and ordered some new MOVs and I should have them tomorrow. So I guess time will tell if this is the problem. The thing that strikes me odd is the blue MOVs on the AC side both test greater than 4000 MegaOhms with my megger. But these red ones are far below that. I know this is not a proper test but the specs of these MOVs are similar, at least close enough so I would think the results shouldn't be that far off. Just my crazy brain thinking without the proper expertise and experience. What if these MOVs are actually there for GFCI purposes rather than surge? Any thoughts?
                                        Last edited by mitsu2k; 11-28-2023, 01:25 PM.

                                        Comment

                                        • ssrkh
                                          Member
                                          • Jul 2023
                                          • 12
                                          • Malaysia

                                          #160
                                          listen you guys most of the times Ground fault comes with the CT what u need to do is just bypass CT by jumpering ground to Output of the CT so u will know where the fault is comming from and after that if u have again same fault of not performing initialization completely then watchdog is getting the bit High from the EC embedded controller so replace the controller fault will gone thanks me later bye

                                          Comment

                                          Related Topics

                                          Collapse

                                          • Francesc V.
                                            Trying to repair a MPI5.5kW solar inverter
                                            by Francesc V.
                                            My parent's solar inverter died after 5 years of good service.

                                            It's a called hybrid inverter:
                                            - It can go with or without batteries
                                            - It has 2 MPPT (8 330W panels in 2 strings) -> 5280Wp
                                            - A 20kWh lithium battery previously used in a Nissan leaf (14S at 4.1V max) -> 57.4V

                                            Panel is showing error 17 and the battery connection has disappeared. On the other hand, is delivering load, MPPTs are working and it's exporting energy to the GRID. Not that "bad".

                                            Let's open it......
                                            I see that 150A fuse is gone and the...
                                            03-07-2023, 06:17 AM
                                          • x_orange90_x
                                            Vizio E55-E1 bad backlights or bad inverter?
                                            by x_orange90_x
                                            I just got this tv today and it appeared to have no backlight on. After taking off the rear cover and checking again in the dark I can see that MAYBE one quadrant is lit.. But still it's quite dim. I was going to check the LEDs with my tester, and I found LED 1 and LED 2 + pins on the wire from the inverter, but I couldn't identify a ground. Nonetheless I tried using a mounting screw on the inverter board and also the chassis as ground but regardless my tester reads 300 which is what it reads when there is no voltage draw.

                                            I don't know how exactly to test the inverter itself. Is it...
                                            01-29-2025, 09:24 PM
                                          • Gentian
                                            APSINT3636VR 3600W APS INT Series 36V DC 230V AC Inverter/Charger schematic
                                            by Gentian
                                            I have a tripp-lite aspint 3636vr inverter charger which blow some of mosfet transistors. I replaced them repaired also the driver circuit and tested but the mosfets burn again.

                                            It work very well as inverter and also as charger if I let the rear switch in auto mode (inverter) and charger only(charging) but in auto when I connect the feed line 220V AC first time it pass ok to line and start charging the batteries but when I remove the feed line it pass to inverter mode and if I do it again the second time when passing from charging to inverter the Main transformer start making a...
                                            03-06-2023, 07:07 AM
                                          • valvashon
                                            Insignia NS-LCD19-09 (PS OK, Inverter problem?)
                                            by valvashon
                                            For some reason I'm just not going to let this 19" TV defeat me. I guess because I have a schematic to work from I feel like I'm oh so close.

                                            History- while adding a turn-on circuit I let a small screw roll under the power board. Worked through all of that circuitry, probably replacing a MOSFET and PWM controller that were not bad but I was following the service manual. Finally figured out that the power supply is in working order when the inverter section (for the backlights) is disconnected. When the +12 supply to the inverter is disconnected the +12 and +5 will come up...
                                            01-04-2024, 01:44 PM
                                          • caseyjay_48
                                            Sony KDL-46BX450 Inverter Troubleshoot Logic
                                            by caseyjay_48
                                            I am currently on a troubleshoot of 46” Sony KDL-46BX450 tv. I came back from Washington to Texas on medical emergency and had to leave all my tools up there. All I have is a couple of screwdrivers and a dvm. I wish to ask the community a troubleshooting question. Please forgive stupid questions as meds I am taking produce brain fog.
                                            I have well maintained Sony KDL-46BX450. It went black one day. After turn-on, I get solid green light and Sony logo in screen center for about 1-2 seconds, then black. No blinking LEDs, no hissing. Flashlight test shows screen characters dimly viewable,...