Power-One solar Inverter driving me NUTS!!!
  • mitsu2k
    • Aug 2013
    • 219
    Yes you are probably correct. I will try and test all components in that area to the best of my ability. So far I did not see anything that was shorted. That silicone type coating all over the board makes it difficult.
    • petehall347
      • Jan 2015
      • 4426
      • United Kingdom
      #122
      the lamp circuit will be fine i guess . what i am trying to see is what turns it on and then see what tells it to come on . there must be something that measures the resistance to earth ground from panel outputs and i suspect something there is amiss . datasheet for the mcu might help a bit .
      • mitsu2k
        • Aug 2013
        • 219
        Not sure which one is the MCU for this circuit. I do know the alarm relay is on this corner of the board. Do you think this might be the MCU? Sorry for the upside down pic. it’s the only way I can get it under my microscope.
        edit: looks like that one is a USB to serial
        • CapLeaker
          CapLeaker commented
          Editing a comment
          You are on the wrong board.
      • petehall347
        • Jan 2015
        • 4426
        • United Kingdom
        #124
        TUSB34101 USB
        to Serial Port Controller
        • mitsu2k
          • Aug 2013
          • 219
          The strange part is that the GFI LED comes on instantly before the unit has time to go through its checks. I have seen videos online where the LED did not come on until after the checks.
          • petehall347
            • Jan 2015
            • 4426
            • United Kingdom
            #126
            from what i can make out its behaving correctly its only the "A" models that dont halt at this fault . unless yours is an "A" model
            • mitsu2k
              • Aug 2013
              • 219
              Not sure what the “A” model is but here is the labels
              • mitsu2k
                • Aug 2013
                • 219
                OK now I’m thinking there is really a ground fault. When I connected it back up to the array and turned it on, I tried to measure current from positive, DC, negative DC, to earth ground. I was not able to measure any current, but when on the positive and touching the earth ground with my probe, I noticed very slight arching. I don’t get this arcing on the negative side.
                I don’t think that should be the case. When I measured for voltage between the positive terminal and earth ground, I get approximately 149 V. Between the negative and earth ground I get approximately 87 V. The array itself positive to negative measures approximately 256 V. When I disconnect the array from the inverter and just measure the positive and negative coming from the array to earth ground I get very low transient voltage, like 5 to 10 V.
                but the question is, where could this leakage be?
                edit: when I remove the 4 red MOVs and perform the above test again, I get practically no voltage from negative to earth ground but the voltage from positive to earth ground jumps up to about 191v
                • petehall347
                  • Jan 2015
                  • 4426
                  • United Kingdom
                  #129
                  leakage is on the negative if indeed there is any leakage .. the measurements suggest there is . maybe a cable is damaged or got water inside it .
                  • mitsu2k
                    • Aug 2013
                    • 219
                    Are you referring to the cables coming from the array? I tested those disconnected from the inverter and they seem to test fine. I tested them with a mega and the resistance was in the high mega ohms on both the positive and the negative to earth ground. The inverter itself measures them above 20 mega Ohms when it performs it start up test.
                    • CapLeaker
                      Leaking Member
                      • 8155
                      That sounds like a real ground fault all right. I would start again bare ass from square one. This time take as sheet of paper and make nots want you did, how you did it and what the result was.
                      i do have a document that comes with a different inverter that deals with this on the solar side.
                      • petehall347
                        • Jan 2015
                        • 4426
                        • United Kingdom
                        #132
                        this post does not exist . honest .
                        • mitsu2k
                          • Aug 2013
                          • 219
                          I have a question about the MOVs. None of them look discolored or show any signs of heat. They test open with DMM. I know this is not a proper test but should I just not worry about these?
                          • CapLeaker
                            Leaking Member
                            • 8155
                            best way to test MOVs is with the Megger, Put 250V or whatever their max rating is on there and if the Megger ranges out, they are good to go.
                            • petehall347
                              • Jan 2015
                              • 4426
                              • United Kingdom
                              #135
                              i would expect the A to be part of the model number . maybe the manual has clues about it .
                              • mitsu2k
                                • Aug 2013
                                • 219
                                These are 3 legged MOVs. The middle leg on the positive terminals seems to be connected directly to earth ground.
                                • CapLeaker
                                  Leaking Member
                                  • 8155
                                  The third leg is a thermal fuse.
                                  • mitsu2k
                                    • Aug 2013
                                    • 219
                                    so which legs do I test across with the megger?
                                    Legs 1 and 2 from left to right test short.
                                    • CapLeaker
                                      Leaking Member
                                      • 8155
                                      2 is the middle leg. Number 3 is the closest leg to 2. Number 1 is the furthest away from leg 2 (middle pin).
                                      leg 2 to leg 3 is the thermal fuse and should read a dead short.
                                      leg 1 to leg 3 is the MOV and it should be either OL or full scale resistance on the Megger.
                                      • mitsu2k
                                        • Aug 2013
                                        • 219
                                        I tested between the first and third legs in my photo. Here are the results.
                                        500vdc test
                                        175 mOhms
                                        205 mOhms
                                        215 mOhms
                                        239 mOhms
                                        I also tested the two blue ones on the AC side and those tested over 4000 mOhms. (full scale on megger)
                                        Not sure what these results mean. Could all 4 of them be bad?
                                        • Francesc V.
                                          Trying to repair a MPI5.5kW solar inverter
                                          by Francesc V.
                                          My parent's solar inverter died after 5 years of good service.
                                          It's a called hybrid inverter:
                                          - It can go with or without batteries
                                          - It has 2 MPPT (8 330W panels in 2 strings) -> 5280Wp
                                          - A 20kWh lithium battery previously used in a Nissan leaf (14S at 4.1V max) -> 57.4V
                                          Panel is showing error 17 and the battery connection has disappeared. On the other hand, is delivering load, MPPTs are working and it's exporting energy to the GRID. Not that "bad".
                                          Let's open it......
                                          I see that 150A fuse is gone and the...
                                          03-07-2023, 06:17 AM
                                        • x_orange90_x
                                          by x_orange90_x
                                          01-29-2025, 09:24 PM
                                        • Gentian
                                          APSINT3636VR 3600W APS INT Series 36V DC 230V AC Inverter/Charger schematic
                                          by Gentian
                                          I have a tripp-lite aspint 3636vr inverter charger which blow some of mosfet transistors. I replaced them repaired also the driver circuit and tested but the mosfets burn again.
                                          It work very well as inverter and also as charger if I let the rear switch in auto mode (inverter) and charger only(charging) but in auto when I connect the feed line 220V AC first time it pass ok to line and start charging the batteries but when I remove the feed line it pass to inverter mode and if I do it again the second time when passing from charging to inverter the Main transformer start making a...
                                          03-06-2023, 07:07 AM
                                        • valvashon
                                          Insignia NS-LCD19-09 (PS OK, Inverter problem?)
                                          by valvashon
                                          For some reason I'm just not going to let this 19" TV defeat me. I guess because I have a schematic to work from I feel like I'm oh so close.
                                          History- while adding a turn-on circuit I let a small screw roll under the power board. Worked through all of that circuitry, probably replacing a MOSFET and PWM controller that were not bad but I was following the service manual. Finally figured out that the power supply is in working order when the inverter section (for the backlights) is disconnected. When the +12 supply to the inverter is disconnected the +12 and +5 will come up...
                                          01-04-2024, 01:44 PM
                                        • caseyjay_48
                                          Sony KDL-46BX450 Inverter Troubleshoot Logic
                                          by caseyjay_48
                                          I am currently on a troubleshoot of 46” Sony KDL-46BX450 tv. I came back from Washington to Texas on medical emergency and had to leave all my tools up there. All I have is a couple of screwdrivers and a dvm. I wish to ask the community a troubleshooting question. Please forgive stupid questions as meds I am taking produce brain fog.
                                          I have well maintained Sony KDL-46BX450. It went black one day. After turn-on, I get solid green light and Sony logo in screen center for about 1-2 seconds, then black. No blinking LEDs, no hissing. Flashlight test shows screen characters dimly viewable,...
                                          09-23-2022, 08:08 PM
