Power-One solar Inverter driving me NUTS!!!
    • Jul 2011
    • 6037
    Originally posted by mitsu2k
    I tested between the first and third legs in my photo. Here are the results.
    500vdc test
    175 mOhms
    205 mOhms
    215 mOhms
    239 mOhms
    Did you do the test procedure that is outlined in this maintenance manual
    Did you follow it exactly or did you deviate from what they have and if you did please explain how you did it differently
    Also if you did run the test as they outlined in the manual what were your results for each section of tests
    https://www.badcaps.net/filedata/fetch?id=3153508
    • CapLeaker
      Leaking Member
      • 8135
      500vdc test
      175 mOhms
      205 mOhms
      215 mOhms
      239 mOhms
      I also tested the two blue ones on the AC side and those tested over 4000 mOhms. (full scale on megger)
      Not sure what these results mean. Could all 4 of them be bad?
      I hope you mean MOhm not mOhm. There is a huge difference between Mega and Milli
      See, MOVs degrade with time and how often the get zapped. The insulation layer will break down each time it gets hit, to a point of leaking or total failure (basically a short). A 175 Mega Ohms is not a failure, but it's getting time to change it out. All depends on what the rating of this MOV is and how much voltage you use with the Megger,
      Let's say you hit a 375V MOV with 500V from the Megger, it will hurt the MOV each time you press the test button.
      • mitsu2k
        • Aug 2013
        • 219
        I have not seen any test in any maintenance manual. Where are you seeing this?
        • mitsu2k
          • Aug 2013
          • 219
          Yes I meant MegaOhms
          • petehall347
            • Jan 2015
            • 4426
            • United Kingdom
            #145
            troubleshooting is page 49 onwards
            • mitsu2k
              • Aug 2013
              • 219
              OK I think I know what you are referring to now. Please see attached. This is the only test that I can see that would be relevant. And I did perform this test in the following manner:
              tested between positive and earth ground and got over 50 MegaOhms.
              got approximately the same results from negative to earth ground.
              I did not short the positive and negative together because it was daytime and I didn't think that would be a good idea being that there's about 256 V there. However, I wouldn't expect to see any different results if I shorted them being that they were both over 50 mega anyway. I suppose I can do this test at night, but I am just afraid of blowing the diodes on the panels and I don't really want to go up on the roof being that I am afraid of heights
              • mitsu2k
                • Aug 2013
                • 219
                from what i can make out its behaving correctly its only the "A" models that dont halt at this fault . unless yours is an "A" model
                HI Pete, I now know what you are talking about "A" models. Mine is not an "A" model. I found the manual that you must have been looking at. It appears that these have a built in Arc detection feature as well as some other features. For example, the "Autotest" feature is non existent in my inverter. I even looked under the service menu. I was able to find a key generator in order to access this menu.
                • mitsu2k
                  • Aug 2013
                  • 219
                  Ok I did the test outlined in the manual. (Positive shorted to Negative) at 250v on the megger to earth ground.
                  result= >4000 MegaOhms on the megger (full scale). All good here.
                  • CapLeaker
                    Leaking Member
                    • 8135
                    Yours isn't an A model. It doesn't have that fat ass clamp contraption. When you hook that inverter back up to test, you put one or both strings to it? Are you using both DC ports? The solar panels face all in the same direction?
                    • mitsu2k
                      • Aug 2013
                      • 219
                      I only have one string. All panels face the same direction. I am using only one DC port but I have tried connecting to the second one as well, and got the same results
                        • Jul 2011
                        • 6037
                        I would mega ohm the cables from the solar panels to the inverter with out the cable being attached to the solar panels or the inverter especially if the positive and negative cables are connected to together as one cable run and or are in conduit because I ran into a situation where water had introduced into the installation of wires and were shorting out in the conduit so do not rule this one out I use a mega ohm tester to figure out why this device was blowing fuses ( how you test for this is you have one meter lead on positive wire and the other meter lead on the negative wire )
                        On the same note are you using outside rated cable that you are using for the wiring from the solar panels to the inverter if not you should be and should be outside rated conduit or if I was doing this I would be doing it this way
                        Your results should be the highest mega ohm reading that the meter ohm meter has and any thing else would be suspicious at least to me it would be or you have something wrong with inverter showing a voltage leaking situation
                        • CapLeaker
                          Leaking Member
                          • 8135
                          I did notice that there is a switch on your inverter, next to the AC connection. That is to pair or not to pair them DC inputs. I think the switch isn't set for them 2 DC ports as paired. Also there support to be a jumper between the 2 DC ports going from positive to positive and negative to negative. Putting the inverter on the DC port into paired, supposed to handle more current or something. Can't remember. Got to read that manual again.
                          • petehall347
                            • Jan 2015
                            • 4426
                            • United Kingdom
                            #153
                            what is the history of this thing ? like did it work then suddenly this fault ? any other factors that may have happened just prior to this particular fault ?
                            • mitsu2k
                              • Aug 2013
                              • 219
                              SAM, this is good thinking about wires shorting out inside the conduit. I do not think this will be the case but I will check it at night. It may shed light on that small transient voltage either way.. They are coming through my attic in a flex conduit. 12awg I believe. I have not seen any signs of water or moisture when I went up in the attic. The panels were installed by the builder or builder's contractor when the house was built so the wiring should all be the proper type there..
                              • mitsu2k
                                • Aug 2013
                                • 219
                                CapLeaker, The "PAR' switch according to my understanding of the manual is used to parallel more inverters together.
                                • mitsu2k
                                  • Aug 2013
                                  • 219
                                  Pete, the history of this unit is as follows. The inverter was probably installed around 2014 based on the date code. About 3 years ago it got the E031 error which is where the relay contacts on the PCB arc and burn out. At that time I repaired it by reflowing the solder joints on the relay in question. about a year later same thing happened but on a different relay. I repaired it same way. Several months later, it happened a third time and again on a different relay. This time I decided to reinforce the traces using some copper wire to allow more current to flow so the contacts would not arc and burn out. This seemed to work very well however I neglected to add the copper wire on one of the relay contacts. a couple months after that, I noticed that the inverter was not working and the red GFI light was on. So again I opened it up and found that the one relay contact that I did not reinforce with wire had burned out. However, this time that relay was melted pretty good and was not functional. I replaced all 4 relays at that time and reinforced all the pads/contacts with wire. Reinstalled it and the GFI light did not go away. So here we are today.
                                  I would like to add that the very last time I mentioned above, there were no error messages on the display. The 3 previous times I had the E031 error on the display and the alarm led was lit but no GFI light.
                                  • petehall347
                                    • Jan 2015
                                    • 4426
                                    • United Kingdom
                                    #157
                                    so it looks like gfi coincides with the 4th relay then . what is that relay for ?
                                    maybe set your meter on megohms and check between the ground and around that 4th relay looking for leakage on the board . it does look as if the inverter is seeing leakage from somewhere .
                                    • mitsu2k
                                      • Aug 2013
                                      • 219
                                      the 4 relays are on the AC side. During normal operation, you can hear the relays cycling on/off.
                                      • mitsu2k
                                        • Aug 2013
                                        • 219
                                        I have a question about those 4 MOVs. When I measure voltage between positive and earth ground, I get about 145V. When I remove the MOVs and measure without them, the voltage increases to around 194V. So the MOVs are suppressing some voltage. I am wondering if these MOVs are getting weak and they should be suppressing more. I did find that the middle leg of the MOVs of the positive input is connected directly to earth ground. On the negative the middle leg is connected directly to the GRP terminals that goes to that second board. I have went ahead and ordered some new MOVs and I should have them tomorrow. So I guess time will tell if this is the problem. The thing that strikes me odd is the blue MOVs on the AC side both test greater than 4000 MegaOhms with my megger. But these red ones are far below that. I know this is not a proper test but the specs of these MOVs are similar, at least close enough so I would think the results shouldn't be that far off. Just my crazy brain thinking without the proper expertise and experience. What if these MOVs are actually there for GFCI purposes rather than surge? Any thoughts?
                                        • ssrkh
                                          • Jul 2023
                                          • 12
                                          • Malaysia
                                          #160
                                          listen you guys most of the times Ground fault comes with the CT what u need to do is just bypass CT by jumpering ground to Output of the CT so u will know where the fault is comming from and after that if u have again same fault of not performing initialization completely then watchdog is getting the bit High from the EC embedded controller so replace the controller fault will gone thanks me later bye
                                          • Francesc V.
                                            Trying to repair a MPI5.5kW solar inverter
                                            by Francesc V.
                                            My parent's solar inverter died after 5 years of good service.
                                            It's a called hybrid inverter:
                                            - It can go with or without batteries
                                            - It has 2 MPPT (8 330W panels in 2 strings) -> 5280Wp
                                            - A 20kWh lithium battery previously used in a Nissan leaf (14S at 4.1V max) -> 57.4V
                                            Panel is showing error 17 and the battery connection has disappeared. On the other hand, is delivering load, MPPTs are working and it's exporting energy to the GRID. Not that "bad".
                                            Let's open it......
                                            I see that 150A fuse is gone and the...
                                            03-07-2023, 06:17 AM
                                          • x_orange90_x
                                            by x_orange90_x
                                            01-29-2025, 09:24 PM
                                          • Gentian
                                            APSINT3636VR 3600W APS INT Series 36V DC 230V AC Inverter/Charger schematic
                                            by Gentian
                                            I have a tripp-lite aspint 3636vr inverter charger which blow some of mosfet transistors. I replaced them repaired also the driver circuit and tested but the mosfets burn again.
                                            It work very well as inverter and also as charger if I let the rear switch in auto mode (inverter) and charger only(charging) but in auto when I connect the feed line 220V AC first time it pass ok to line and start charging the batteries but when I remove the feed line it pass to inverter mode and if I do it again the second time when passing from charging to inverter the Main transformer start making a...
                                            03-06-2023, 07:07 AM
                                          • valvashon
                                            Insignia NS-LCD19-09 (PS OK, Inverter problem?)
                                            by valvashon
                                            For some reason I'm just not going to let this 19" TV defeat me. I guess because I have a schematic to work from I feel like I'm oh so close.
                                            History- while adding a turn-on circuit I let a small screw roll under the power board. Worked through all of that circuitry, probably replacing a MOSFET and PWM controller that were not bad but I was following the service manual. Finally figured out that the power supply is in working order when the inverter section (for the backlights) is disconnected. When the +12 supply to the inverter is disconnected the +12 and +5 will come up...
                                            01-04-2024, 01:44 PM
                                          • caseyjay_48
                                            Sony KDL-46BX450 Inverter Troubleshoot Logic
                                            by caseyjay_48
                                            I am currently on a troubleshoot of 46” Sony KDL-46BX450 tv. I came back from Washington to Texas on medical emergency and had to leave all my tools up there. All I have is a couple of screwdrivers and a dvm. I wish to ask the community a troubleshooting question. Please forgive stupid questions as meds I am taking produce brain fog.
                                            I have well maintained Sony KDL-46BX450. It went black one day. After turn-on, I get solid green light and Sony logo in screen center for about 1-2 seconds, then black. No blinking LEDs, no hissing. Flashlight test shows screen characters dimly viewable,...
                                            09-23-2022, 08:08 PM
