APC Back-ups RS 1500 Dead
Collapse
X
-
Re: APC Back-ups RS 1500 Dead
Components were burned in my APC RS-1500, but I can not read their values . There is a board diagram of the board?
The components are D35, Q41, R73, R37 (I can't read)
ThanksComment
-
Re: APC Back-ups RS 1500 Dead
arielleon305,
Photo attached...
D35 = "A7W"
Q41 = "1AM"
R73 = "2000"
R37 = "2000"
My board is labeled 640-0253E in the bottom right corner (when the big transformer is in the upper right).
My RS 1500 (tall, narrow, beige) is not dead but has started constantly cycling between on-battery and on-AC. None of my other UPS's are unhappy with the incoming AC, which seems to be steady at 122V. There are no expanded caps or burn spots on the board or components. The two 40A fuses are OK. I'm debating my next steps.
Anyway I had it open and thought that you might still be able to use the info.Comment
-
Re: APC Back-ups RS 1500 Dead
arielleon305,
Photo attached...
D35 = "A7W"
Q41 = "1AM"
R73 = "2000"
R37 = "2000"
My board is labeled 640-0253E in the bottom right corner (when the big transformer is in the upper right).
My RS 1500 (tall, narrow, beige) is not dead but has started constantly cycling between on-battery and on-AC. None of my other UPS's are unhappy with the incoming AC, which seems to be steady at 122V. There are no expanded caps or burn spots on the board or components. The two 40A fuses are OK. I'm debating my next steps.
Anyway I had it open and thought that you might still be able to use the info.
have you found out why is this happening?
- I have also APC 1500 RS 220V - without display.
- The thing that happens is when I power it up it stays on battery and does not detect current from wall.
- It's plugged into wall. I pusshed circuit breaker several times. Set UPS sensitivity to low.
- Actually it happes the same as on this YouTube video
http://www.youtube.com/watch?v=lioxJe0UdxY
Any ideas?Comment
-
Re: APC Back-ups RS 1500 Dead
No ideas. I was unable to locate a service manual or even a schematic. And because none of the caps were bulged/discolored the solution was not clear in the case of my board.
I replaced the unit with an APC SMC1500. BTW, I wasted time exploring APC's swap program (I've forgotten APC's name for that program) but it was less expensive (and less hassle) to buy a new unit from a retailer rather than dealing directly with APC. (USA. I don't know if that holds true for other countries.)Comment
-
Re: APC Back-ups RS 1500 Dead
Not wanting to appear stupid ( which I can easily manage ) ..
In troubleshooting these APC Ups .. what voltage should I be seeing across the charging leads /battery terminals with zero load if its healthy .. ?
( 2 x 12volt 20amp batterys , 1250VA Ups )Comment
-
Re: APC Back-ups RS 1500 Dead
Hmmm That sort of confirms my suspicions ..
Its definitely not supplying a charging voltage..
I've had people tell me to just buy another set of batterys , but it seems to have killed the last set of new ones and buying more seems like a waste of money ..
Whats the most likely thing to fail in the charge circuit ..?
I'm getting to the sad conclusion it may be an "ex-Ups"Comment
-
Re: APC Back-ups RS 1500 Dead
Hmmm That sort of confirms my suspicions ..
Its definitely not supplying a charging voltage..
I've had people tell me to just buy another set of batterys , but it seems to have killed the last set of new ones and buying more seems like a waste of money ..
Whats the most likely thing to fail in the charge circuit ..?
I'm getting to the sad conclusion it may be an "ex-Ups"Never stop learning
Basic LCD TV and Monitor troubleshooting guides.
http://www.badcaps.net/forum/showthr...956#post305956
Voltage Regulator (LDO) testing:
http://www.badcaps.net/forum/showthr...999#post300999
Inverter testing using old CFL:
http://www.badcaps.net/forum/showthr...er+testing+cfl
Tear down pictures : Hit the ">" Show Albums and stories" on the left side
http://s807.photobucket.com/user/budm/library/
TV Factory reset codes listing:
http://www.badcaps.net/forum/showthread.php?t=24809Comment
-
Re: APC Back-ups RS 1500 Dead
I know this topic is a little bit old but I think this could help. A common problem in the BR1500 model is that two surface mount aluminium electrolytic capacitors (C40 and C41) responsible for the -8v supply to the line sense circuit is marginal or failed. On mine, they read correct 22uF value but fail on ESR test. Replacing either or both of these should fix the on battery always or constant switching to battery.
I also have a PDF of the schematic for the board model 640-0253E. I don't know about this forum's policy though. APC has shut down sites providing schematics in the past.Comment
-
Re: APC Back-ups RS 1500 Dead
Back-UPS XS 1500 was repaired by replacing all 22uF SMD electrolytic caps. There are five of them and they were reading anywhere from tens of ohms to infinite ESR. Symptom was failure to charge battery and eventually failure to power on at all emitting only a chirp on attempt.Comment
-
-
I know this topic is a little bit old but I think this could help. A common problem in the BR1500 model is that two surface mount aluminium electrolytic capacitors (C40 and C41) responsible for the -8v supply to the line sense circuit is marginal or failed. On mine, they read correct 22uF value but fail on ESR test. Replacing either or both of these should fix the on battery always or constant switching to battery.
I also have a PDF of the schematic for the board model 640-0253E. I don't know about this forum's policy though. APC has shut down sites providing schematics in the past.
For the last six months i had noticed any time my RS 1000 was powered off it took multiple attempts to start up before it would switch to AC power. Over the last few weeks it had started rapidly switching to battery and back very quickly. Always in the middle of the night you would hear a clickity clack, clickity clack, clickity clack from the next room and i would have to get up and power it off. Then power cycle it multiple times the next day before it would switch to AC.
I tried replacing all the regular electrolytics which made no difference, but it was probably no harm in doing them anyway. Then i found your post and changed the C40 and C41 SMD's as per your recommendation and it worked perfectly. Just to future proof it i replaced the other SMD's, so thank you, a combination of your wisdom and my stubborness it should serve me well for another decade or so.
P.S. Would love a copy of the schematic if you could PM me a copy?Comment
-
Re: APC Back-ups RS 1500 Dead
A common problem in the BR1500 model is that two surface mount aluminium electrolytic capacitors (C40 and C41) responsible for the -8v supply to the line sense circuit is marginal or failed . . . Replacing either or both of these should fix the on battery always or constant switching to battery.Comment
-
Re: APC Back-ups RS 1500 Dead
Also another thanks to you all, I used my Ungar heat gut to locate the caps last week, and Just wanted to confirm that you were right, when I heated the caps with the gun It works fine, cooling them off with the Freeze mist = Fail, So we are in agreement, thanks again. PeaceComment
-
Re: APC Back-ups RS 1500 Dead
I just joined the board to thank everyone who contributed the information on the failed C40 & C41 capacitor issue. After replacing them, I can report that three more APC Back-UPS RS 1500 units are back in operation!
Now I have to plan on replacing those sickly capacitors on three more APC Back-UPS RS 1500 units I have deployed and still working that haven't failed yet--but undoubtedly will soon.
Thanks again to everyone for saving us TONS of time finding the cause.Comment
-
Re: APC Back-ups RS 1500 Dead
I also joined this board just to say "thank you"!
My RS 1500 is great and integrates perfectly with NUT on Linux. I bough over the years many other products from other manufacturers but none pleased me like this old APC.
Until one day... when is stopped to go online. I tried everything (circuit break, hardware reset the unit, software reset the front panel with NUT, set the tolerance to low, replaced batteries). Nothing worked. Even if plugged on AC power (230V) it wouldn't go online but on batteries. Sometimes was charging batteries (even if not going online), other times will discharge the batteries in the same conditions (plugged to AC). Some times it went online, but if AC power was lost and come back it will not go online again.
I monitored the parameters (with NUT) and saw that parameter "input.voltage" was erratically changing from 184V to 92V, 144V... etc. I mounted a meter and saw that the AC voltage was constantly 228V, so the UPS was a complete mess.
A nightmare. That is why I bought several other products... but not being satisfied I decided this Sunday to play with my old buddy.
And I found this thread! I opened the unit and saw that C41 was already manually replaced (with a higher voltage one). I bough the unit as new and nobody opened it ever.I replaced C40 and yupppyyyy! now everything works! I used a 50V one to prevent it from burning again too soon... maybe it helps.
I noticed that the marks for the polarity on motherboard are reverse to the ones on the capacitor (check attached). That is the "+" sign on the motherboard goes with "-" sign on the capacitor. I am not a specialist but I noticed this on the replaced one and I did the same.
I didn't had a hot air tube to heat the old damaged capacitor in order to remove it so I just cut it off with a clipper.
Thank you again for this common effort!Comment
Related Topics
Collapse
-
by carrzkissHello, all.
Cyberpower Battery Backup Unit.
I bought two new ML18-12 batteries through Amazon (They have already refunded my money for the two batteries as we thought the batteries might have been bad.)
When I got them in, they were not fully charged. I connected them to the UPS and waited 24 hours before connecting any networking equipment.
In parallel, they read 24v, but within 24 hours, the meter on the front of the unit dropped from 4 to 3 bars on the battery charge indicator.
Checking the voltage, it was down to 22v.
I quickly removed everything... -
by howardc64Order my parts from mobilesentrix.com and iPhone batteries have been excellent. Recently got 3x bad A1534 (2015) batteries. All would work until ~30-40+% and drop to < 10% instantly. Typical sign of cheap batteries.
Perhaps the less popular A1534 model's aftermarket batteries are more source limited. Just find it surprising quality from mobilesentrix (usually fairly high quality aftermarket parts) have been so poor.
BTW, this isn't the only defective parts I've had from mobilesentrix. Amongst others including iPad Air touch screen and A1989 touch bar (display was... -
by double_DDHi all,
As the title suggests, how can I be sure that my EC chip is really dead?
I've recently gotten into this hobby of laptop repairs, and have successfully brought back to life a couple with some easy fixes, mostly shorted caps.
Now I'm working on HP Probook 455 G8, that had some "devil" run around on 3V line, burning a bunch of stuff. Luckily I have a dead 455G7 (for spare parts) so I managed to fix it (swapped burned parts) to a point that it will charge (both on barrel jack and usb-c), but it doesn't want to turn on. There is a 3V3 on a keyboard... -
by AstonishedHi friends of electronics
What you see in the video and pictures attached is the circuit for charging the batteries of a DC motor.
The problem is that this circuit cannot charge the batteries (3 1800mAH NiMH batteries) any more. When the circuit was OK, its green LEDs lit up one at a time to show that the batteries have charged more. But now that the circuit is flawed, LEDs light up as you see in the video and at the same time successive beeps are heard.
Please help me fix this circuit.
(the datasheet of the IC: https://pdf.datasheet.live/28... -
Problem description:
My UPS requires new batteries every ~3 months; in this time frame, an average of about 5 to 10 power flickers or short power interruptions (< 2 minutes) occur. After an average of 3 months, a new pair of batteries begins to fail to keep the UPS up during any flicker or power interruption. The load it powers is a single computer/workstation running 24/7 with a continuous consumption between 200W to 300W.
UPS model:
The Atlantis 1001 is a non-inexpensive (~120€ back then) home/office offline UPS, rated 1000VA, 600W, designed for two 7Ah... - Loading...
- No more items.
Comment