Help With Reassembling Basic 110 VAC Motor
  • Sparkey55
    • Jan 2010
    • 1523
    Re: Help With Reassembling Basic 110 VAC Motor
    To Used Cars: How is it coming together with the shop vac yet?
    • Used_Cars
      • Oct 2015
      • 102
      Originally posted by budm
      BYW, based on this measurement you provided: https://www.badcaps.net/forum/attach...2&d=1521157574
      N1 to Not_ N1 did not show open circuit so that means the Thermal protection did not go open circuit.
      Once you put it all together to check to see if it shows open circuit or not between the AC plug's blades then we can go from there. Be careful on those brushes when putting them back together.
      I carefully reassembled the motor per your diagram, making sure to keep the thermal protection on the black, switched, "L" side of the motor. Plugged it in, turned and turned it on. It ran for about 3 seconds and then this happened:
      • eccerr0r
        Solder Sloth
        • Nov 2012
        • 8711
        That's weird, did it run as energetically as before it zapped the outlet? When it starts spinning it should pass some power back and not fry like that, or was that outlet there in bad shape to begin with?
          That to me looks like bad contact on the Line side socket of the AC outlet.
          BTW, is it the same out you used when the vacuum stopped working?
          • petehall347
            • Jan 2015
            • 4450
            • United Kingdom
            need to fit gcfi or something . that shouldn't happen these days ...
            • eccerr0r
              Solder Sloth
              • Nov 2012
              • 8711
              PSA: If you plug in something and it feels "loose" or the plug easily pushes in or pulls out, that outlet is in poor condition - WORN OUT - and should be REPLACED. If you can't replace it, you must derate it significantly - if it's nominally 15A, do not even think about attempt to power 13A, 10A, or even 5A through it, it will overheat and can cause a fire. If it's weak, best to stay below 1 or 2 amps tops, and you'll still be frustrated with it losing contact... REPLACE IT!
              • Sparkey55
                • Jan 2010
                • 1523
                The shop vac works. The AC outlet does not.
                show us what the cord prongs look like now.
                • eccerr0r
                  Solder Sloth
                  • Nov 2012
                  • 8711
                  I've seen a lot of "outlet fire" post-mortems and always wondered how the fire could have happened. A short should have triggered the circuit breaker so that couldn't be it. However if there was effectively a 900 watt heater pointed at the plastic of the outlet and plug... that would explain everything.
                  • Used_Cars
                    • Oct 2015
                    • 102
                    Yes. At first I thought it was going to "go", and then it died, looked over my shoulder and saw the outlet.
                    It's a brand-new switch/outlet. I replaced it less than a year ago because I wanted an outlet near the door that connects the house to the garage. I haven't tested the outlet yet to see if it's hot or not. I don't think a circuit breaker flipped, but it might have. Have not checked that yet either.
                    I don't know if by "bad contact" you mean the outlet is defective in some way, or something is wrong with the way the motor is wired.
                    No, it's not the same outlet I used when the vacuum quit working.
                    I haven't disassembled the motor again, yet, because I wanted to wait to see if taking pics of the wiring as it is right now might be useful, to see if I did something wrong or whatever.
                    There is one odd thing I noticed when reassembling it, and that is how the switch on the vacuum flips a toggle switch. There's a plastic "slide" which, on the outside of the vacuum housing allows your thumb to slide it left to right, and behind the plastic slide it mechanically pushes a standard toggle switch one way or the other. I noticed that the interface between the orange plastic slide and the toggle switch was odd in that the plastic slide did not seem to fully "flip" the toggle switch. It traveled about 3/4 of it's arc, but did not "click" all the way over, so (it appears) the toggle switch goes from a solid "OFF" (with a click), to 3/4 of the way towards "ON", but the toggle wouldn't go all the way to the point that it actually clicked.
                    I noticed this when the vacuum housing was still separated, and figured that when the other half was fastened the slide would actuate the toggle 100%, like it needed additional support in order to make that toggle go all the way to the point that it actually clicked.
                    Even if the toggle doesn't travel all the way over to the "ON" (click) position, I don't see how that causes this problem. But I wanted to through out the possibility that it's the cause of the problem, i.e. maybe the toggle switch is bad.
                    I can take a pic of this also, if useful.
                    Thanks for all the help.
                    • Used_Cars
                      • Oct 2015
                      • 102
                      The wiring in this house is completely f*****. Before we moved in, there was a house fire and this is the area of the house that burned. Afterwards, some kind of professional "flipping" company did the repairs and they did horrible terrible things with everything, such as painting over charred wood, and other things with the wiring too terrible to even mention. So defective wiring is on the list for possible suspects in every outlet in the entire house.
                      • Used_Cars
                        • Oct 2015
                        • 102
                        Travelling today. I'll get that posted later on this evening when I get back.
                        • goontron
                          5000!
                          • Dec 2011
                          • 4108
                          • US
                          #32
                          Looks like the plug is the issue, not the socket...
                          Follow the white rabbit.
                            There are ONLY two wires connected to the switch so it cannot be wired wrong. The whole connections of the motor and switch are in series.
                            You have bad contact problem between your AC plug and the outlet.
                            • Used_Cars
                              • Oct 2015
                              • 102
                              The outlet tests good with a standard household light bulb plugged in (a home-made "trouble light". It's also brand-new. I've used a household vacuum cleaner in that outlet within the week. It's one of the most-used outlets in the whole house. I converted a simple switch (for the lights in the garage) to a switch + outlet because an outlet in that location was necessary for lots and lots of things, and I've been using it for lots of things since I installed it.
                              Another thing I think I noticed but didn't mention is that the wire that connects the brush to the terminal that clips to the motor housing was discolored somewhat. You might see it in the photographs. One is dark and normal colored,the other is a lighter, dustier, more pale color than the other.
                              Could the one of the brushes (the whole assembly, brush, braided wire and terminal clip) be defecting in some way, and cause this? Maybe it opens under load so only one brush is doing all the work? Will the motor still spin if one brush is open? Is there a way to test a brush for continuity?
                              I don't know what kind of metal is in the brush. What if I do a continuity test from brush, through the braided wire, to the terminal and it's open? What if there is resistance? How else would you test a brush?
                              • Used_Cars
                                • Oct 2015
                                • 102
                                I did a continuity test on the cable, on both sides and they tested short, and they tested open from one cable to the next. The Plug appears to be in good condition. How would I verify the plug is good or bad beyond this?
                                  "Will the motor still spin if one brush is open? Is there a way to test a brush for continuity" No it not run since they whole things are connected in series so if one goes open circuit then there will be no current flow.
                                  Can we see the picture of the AC plug?
                                  If you think the outlet is OK then try plugging in hair dryer set to the max and see what happen. In my 40 years, that kind of failure at the AC outlet like that are due to poor contact.
                                  • eccerr0r
                                    Solder Sloth
                                    • Nov 2012
                                    • 8711
                                    for a commutated motor to work, both brushes must be working in order to give continuity as well as to spin. A poorly conducting brush would allow much less current to flow and would not allow the rotor to strongly turn.
                                    You mention "It's one of the most-used outlets in the whole house" which would imply it could take a lot of wear. The outlets, depending on how it's designed, is usually the wear point. Granted higher quality outlets would not wear out as fast but it's hard to tell the quality by looking at the outside. And even if it gives a tight fit when plugging and unplugging, it may not be the metal contacts that are providing the needed friction to allow a strong, low resistance connection.
                                    • Sparkey55
                                      • Jan 2010
                                      • 1523
                                      budm in post #33 is right. Lose or worn out plugs and or outlets usually do not show the results of such damage with low current devices plugged in. It take high current things like air conditioners, microwave ovens, space heaters and vacuume cleaners to see the effects of worn contacts. what current rating is the breaker? It should be a 20 amp. When you plug in vacuume cleaners do the lights dim?
                                      Put one probe of your ohm meter on one prong and the probe on the other prong. With the vacuum switch in the ON position you should see a LOW ohm reading ( it will vary in numbers because of the carbon brushes ).
                                      Do the same above but with the vacuum switch in the OFF position. You should see an open circuit reading.
                                      Is this a 2 wire cord or a 3 wire cord?
                                      • eccerr0r
                                        Solder Sloth
                                        • Nov 2012
                                        • 8711
                                        Usually wet/dry shop vacs use a 3-wire cord, and that outlet looks like a standard NEMA 5-15 - which is usually paired with a 15-amp fuse or breaker.
                                        Looking at the photo closer, oh nice, it's an even "newer" tamper resistant outlet ... not sure about the design tradeoffs they made to make these tamper resistant outlets...
                                        • Sparkey55
                                          • Jan 2010
                                          • 1523
                                          Another thing that could cause the outlet to fry is if you had the shop vac switch turned on before you inserted the power cord into the live outlet. instant sparks or fire.
                                          • juergenb
                                            Nescafe Aeroccino, still fails with new Motor (red flashes only once)
                                            by juergenb
                                            i am asking for some Help.
                                            I have one of these Nescafe Aeroccino (Milk Frother) things with a bad motor.
                                            The Motor didn´t start anymore and internet is full of users just swapping the motor for a Mabuchi RF-500TB-12560.
                                            So i got a few of these from Banggood.
                                            I swapped the motor and now i have a new fault condition.
                                            In a working Frother you would press the start button, it will light red and work for a few minutes.
                                            If you press longer it will light blue and just mixup the milk.
                                            With the new Motor it just starts...
                                            03-23-2021, 11:24 AM
                                          • d00m178
                                            Philips toothbrush 4100 (HX369BK) - motor getting hot
                                            by d00m178
                                            trying to fix Philips toothbrush 4100 (HX369BK)
                                            The battery started draining quickly.
                                            After disassembling it, I discovered that the motor gets very hot when brush is off, which is apparently causing the battery to lose charge.
                                            The motor is connected to contacts M1 and M2.
                                            When I turn on the brush, 0.4V appears on these contacts, and the motor starts running as expected.
                                            But when I turn off the brush, the voltage changes to 3.8V—exactly the same as the battery.
                                            The motor gets so hot you can't touch it. And after 5 minutes, the battery drains to 0V.
                                            (To...
                                            11-12-2025, 03:11 PM
                                          • wnlewis
                                            New wire for my RDE3340 Whirlpool electric range
                                            by wnlewis
                                            OK. I got the rocker switch figured out thanks to the good advice on this forum.
                                            Now I need to figure out the correct wire to go to the switch from the broiler element and from the oven element.
                                            This is a Whirlpool RDE3340 electric range.
                                            The common wire on the switch appears to have a high temperature insulating material. I am guessing that both the wire to the broiler and the wire to the oven elements also need relatively high temperature insulation. What do I need to look for? The broiler is rated at about 2400 watts.
                                            Where may I find parts...
                                            01-08-2025, 11:21 PM
                                          • emeskay
                                            Lenovo Yoga 710 15ISK, 80U00002US battery cable wire broken.
                                            by emeskay
                                            We have an Lenovo Yoga 710 15ISK that we use as a secondary laptop. To cut a long story short, around May 2023, while traveling, I connected the laptop into an electrical outlet that was already switched on. Something made a "pfft" sound and the laptop refused to turn on after that. After getting back home, I gave the the laptop for repair to an informal repair person. He replaced the adapter and an internal motherboard part, but after he returned it I noticed that the LCD did not look normal. Essentially, every alternate horizontal line on the screen had gone missing. The laptop was...
                                            08-06-2024, 07:13 AM
                                            Heater element wire type instead of a fuse when troubleshooting a short circuit DIY
                                            by sam_sam_sam
                                            I was Ollie today which is a close out / surplus outlet store I do not go in there to often because you find things that you should not be tempted by but that is a another story
                                            I saw a small space heater that used a wire type of heater element which I been looking for a while but not really hard mind you but when I saw this I grabbed it I going to go back tomorrow and buy the last one that is like the one I bought today because I need the heater element and the ceramic insulators and more of heat element wire because this one has two different wattage settings one 1300 watts ( tap...
                                            12-16-2023, 08:39 PM
