EuropAce EWC 3108 Wine Chiller - Seems like no temperature sensor input
  • beetle1303
    • Jul 2019
    • 279
    • Singapore
    Re: EuropAce EWC 3108 Wine Chiller - Seems like no temperature sensor input
    you could monitor 2sc1815 base or just change it ..
    on another note i wouldn't use that transistor for a relay driver . i would choose a better one .
    What would be a better replacement if I were to change them?
    • beetle1303
      • Jul 2019
      • 279
      • Singapore
      If I were doing this I would recommend removing the relay from the board and checking its function off the board if working correctly off the board then I would try to figure out what is wrong with the board circuit and why it is not working correctly
      I would not trust just using only a ohm meter to check the relay contacts I would hook a light bulb ( if you have a bench power supply and some automotive light bulb to test the relay output pins ) to test weather or not the relay output pins are capable of carrying current
      Or another option is if you can [ isolate ] ( make sure that the pins do not have any connection to the controller board ) the relay coil pins from the circuit board and attach two wires to relay coil them yes you could inject the 4.5 to 5 volts to activate the relay just make sure that you are correct about what the relay coil voltage is for the coil
      I have done some tests and learnt something new today:
      1) I took the relay off circuit, tested with 12Vdc and it clicked on/off correctly when applied power is applied/off. Tested with 5Vdc it does not click actually...
      2) I wired the relay output pins to the circuit and wired the replay input pins to the external 12Vdc.
      3) Powered up the chiller, and the same click-on click-off sounds every 5 seconds interval.
      4) Same scenario - when relay is off, the bottom compartment get chilled as usual; when relay is on, the bottom compartment continue to get chilled, and the top compartment get barely chilled..
      Something new I found was - this click-on click-off sound is not from the relay but from the solenoid!! Seems like the solenoid is toggling between the 2 output valves every 5 seconds, but somehow it cannot hold it at the toggled position.
      This could be the reason always one compartment get chilled?
      • petehall347
        • Jan 2015
        • 4440
        • United Kingdom
        i would check out bc337
          • Jul 2011
          • 6069
          You have to figure out what or if there is another relay that switching back and forth
          • beetle1303
            • Jul 2019
            • 279
            • Singapore
            There are only 2 relays - 1 for compressor and 1 for solenoid. I am convinced that the clicking noise came from solenoid itself as I can feel the clicking-vibration when I put my finger on it.
            I disassembled the solenoid, took out the tiny PCB on top, and did some check on some of the components. Nothing obviously read bad, except I do not know how the read the C106M transistor. I also not able to trace the current flow as I don't quite understand the circuit.. I attached the photos of it with various angles to see if you're or anyone are able to see what might be wrong with it.
              • Jul 2011
              • 6069
              I would recommend checking the following
              Diode for shorted for open
              if you have a ESR capacitor tester check the capacitors
              Check the transistor or mosfet or what ever the three pin device that you put the part number
              • beetle1303
                • Jul 2019
                • 279
                • Singapore
                #27
                I have checked most of the components, and nothing seems obviously faulty.. So I wired the relay to a 12Vdc supply, and the solenoid PCB with external 240Vac. The output is stable 280+ Vdc.
                I then put this setup onto the solenoid, and got the same 5 seconds click-on click off sound. I am assuming this the the sound of the plunger being energized and moved, but de-energized immediately and sprung back to original position.
                But if this is the case, what makes it repeating itself every 5 seconds?? Could it the 280+ Vdc is too high causing the solenoid coil to over heat and cut-off, and re-energized after cooling down after 5 seconds??
                  • Jul 2011
                  • 6069
                  Put a couple of 100 watt or a 200 watt bulb on the output of this board and see if it can handle this load with out switching on and off if can and it does not cycle on and off
                  Then I would conclude that the solenoid coil has some issues
                  • beetle1303
                    • Jul 2019
                    • 279
                    • Singapore
                    #29
                    Under zero load, the output is ~280Vdc. So the 100W AC incandescent bulb won't lit...
                    I happened to have a 220Vdc motor around, connected it the the output. It spin for a split second, then gone into a start-stop-start-stop every second or so... I measured the voltage under this load, and it reads zero, then ~2-3Vdc, then repeat this as the motor in start-stop start-stop state.
                    There is a 400v 10uF capacitor - could this be the issue if it is bad not charging or not holding charge? It measured good in circuit ~10uF, but I don't have an ESR meter to confirm if truly good.
                    Worthwhile to replace this to see if it work?
                      • Jul 2011
                      • 6069
                      Do you have any capacitor from a switching power supply that might have a capacitor that is close to this value what is the value of the other capacitor and where do the pins of that capacitor goes to
                      • beetle1303
                        • Jul 2019
                        • 279
                        • Singapore
                        #31
                        The other capacitor is a 50V 1uF, see attached pic on how they are mounted. And yes, I found a 50V 1uF and a 450V 10uF capacitors from some power PCBs. Will find time to replace them and test it later.
                        • beetle1303
                          • Jul 2019
                          • 279
                          • Singapore
                          #32
                          Update:
                          I have replaced the 2 capacitors, tested but same outcome - clicked on/off every 5 seconds. In fact in inserted my DMM on the 2 output connectors during the tests, and the reading is 0Vdc for about 5 seconds, then sudden jumped to 7-25Vdc then back to 0. This is co-inside with the 5 seconds internal between clicking on/off cycle.
                          It is possible that the circuit if cut off if this PTC is overheated and reconnected after cooling for 5 seconds?
                            • Jul 2011
                            • 6069
                            Test this board with an in-condensed light bulb 100 watt because the issue might be the solenoid but we to know for sure which one is the real problem
                            • beetle1303
                              • Jul 2019
                              • 279
                              • Singapore
                              #34
                              I think you meant incandescent (not in-condensed) light bulb. Yes, I have done that not it's not lighting up at all, see post #29.
                              I suspect there is a short circuit somewhere and the PTC is shut off due to overcurrent. And this the repeating itself when it cooled and enabled every 5 seconds. Possible?
                                • Jul 2011
                                • 6069
                                Do you have a spare bc337 to if this part might be bad
                                • beetle1303
                                  • Jul 2019
                                  • 279
                                  • Singapore
                                  #36
                                  No, I don't have this part yet but will go buy some later.
                                  I am focusing on the solenoid PCB to determine if this is good or bad. I found someone's description of this solenoid, SDF0.8 3/2:
                                  Product Type Description SDF ---- pulsed electromagnetic valve code
                                  0.8 ---- solenoid valve diameters: 0.8mm
                                  3/2 ---- Feature code: Indicates a two state, three connecting pipe
                                  Power supply voltage: 220V
                                  Frequency: 50 / 60Hz
                                  Rated operating voltage: 165 ~ 253V
                                  Insulation resistance: 500M
                                  Electrical strength: 1500V, 50HZ sinusoidal AC 1min
                                  (From the state of the solenoid valve air 400mm) Noise: 55dB (A)
                                  Solenoid valve control power: solenoid valve driver needs at least four sinusoidal 50 / 60Hz positive or negative half-wave pulse (drive pulse waveform of FIG. See in particular), a state of the switch into another state of the time interval is not less than 30s.
                                  I don't understand this solenoid PCB and not able to trace the current flow. I have replaced the 2 capacitors, and checked the C106M SCR off-circuit. Still getting the same result..
                                  I finally managed to get my video posted online: https://www.flickr.com/photos/145334.../shares/3689ME
                                  From this video, you can see that when the solenoid first powered up, the 280Vdc motor spin briefly for 1 second or so, then gone into start-stop repeatedly.
                                  • petehall347
                                    • Jan 2015
                                    • 4440
                                    • United Kingdom
                                    #37
                                    if you use bc337 be aware the pin out is reversed from the 2sc1815
                                    • beetle1303
                                      • Jul 2019
                                      • 279
                                      • Singapore
                                      #38
                                      *** Merry Christmas everyone ***
                                      I was ignorant about incandescent light bulb, thinking it only works with AC voltage in my previous post. I retested connecting the output to a 100W incandescent bulb. There is no light at all and I think it's because it only lit for a split second then stopped for 5 seconds, and the bulb has not time to heat up..
                                      To confirm the short-circuit in the solenoid PCB, I connect the 100W incandescent bulb in series with the incoming Live cable. The bulb flickered for first 1-2 seconds, then off. I believe this is due to a short circuit when the varistor heated up opened, and took few seconds to cool and opened again due to the short circuit.
                                      See this video: https://flic.kr/p/2kkh6yg
                                      * the clicking sound is from the solenoid plunger.
                                      But I just don't understand the circuit to trace the short..
                                        • Jul 2011
                                        • 6069
                                        Like had above I am being to think that the bc337 is bad or the inrush device is bad or both of them together
                                        Because it starts off pulling current but then there is no current being pulled
                                        • beetle1303
                                          • Jul 2019
                                          • 279
                                          • Singapore
                                          #40
                                          I am powering up the solenoid directly for the test, so bc337 is not in scope.
                                          I am thinking the inrush device cut off the power supply when too much current is drawn.. But I will replace it to see what happen.
                                          • CapLeaker
                                            AcuRite 5 in 1 temperature sensor replacement repair
                                            by CapLeaker
                                            Got a new victim:
                                            AcuRite 5 in 1 Iris outdoor weather station not updating the temperature / humidity anymore. The original sensor is a SHT21. Also there are identical other sensor manufacturers. I chose the HTU21D to replace the original SHT21. Both have identical specs. I've had two failure modes with these sensors.
                                            A: outside temp stuck at -40? It's cold here at times in Canada, but not that cold!
                                            B: stuck at some temperature and maybe updating once in 12 hrs or so.
                                            Easy solution is to go to AcuRite website and purchase the sensor. Right?...
                                            04-15-2025, 01:32 PM
                                          • beetle1303
                                            Wine Chiller - SMPS issue - fluctuating voltages
                                            by beetle1303
                                            My wine chiller, TECNO SW-126LCD, is semi-functional - it powers up, can set temperature, and chilled to the set temperature, and cuts off compressor, etc. It however runs very hot.
                                            Upon taken out the PSU and did some basic check - 5V output to LCD panel buttons and display is stable, but there is no 12V output to LED lights, and fans.
                                            Further checks found the secondary side voltage is fluctuating around 8-15V range, but the 7805 regulator seems ok and producing the stable 5V output.
                                            Checking further on the primary side: Incoming line input to bridge...
                                            09-04-2023, 10:33 AM
                                          • asdas09
                                            Temperature to remove chips from motherboard
                                            by asdas09
                                            What temperature with the heat gun should be use to remove large and small chips from the laptop and mobilephones motherboard? My problem is that the chips not easily remove from the motherboard, example 380°C degrees. I don't know if there is a difference with the devices that the temperature is not stable with them even it shows the right temperature, what should it be? I don't know if I should use higher temperature but the risk of destroying other components?
                                            I have device Sugon 202. I'm used also normal flux and rosin flux.
                                            09-12-2023, 12:44 AM
                                          • beetle1303
                                            Vintec V160SGB wine chiller - thermostat replacement
                                            by beetle1303
                                            My vintage wine chiller, Vintec model# S160SGB, mechanical thermostat failed (not cutting off compressor at set temperature anymore).
                                            After some initial research, this is a Dasfoss 25T65 EN 60730-2 part number.
                                            While this part is generally still available in some online portal, it is fairly expensive. There are many digital thermostat available with some simple rewiring, but I am hoping to preserve it with a with a less expensive mechanical equivalent part.
                                            Anyone familiar can recommend some less expensive equivalent?...
                                            11-06-2023, 06:57 AM
                                          • Dreigas
                                            ISL95880HRTZ desoldering temperature
                                            by Dreigas
                                            I bought from China ISL95880HRTZ (3+1+1 Voltage Regulator with Expanded ICCMAX Register Range Supporting IMVP8 CFL/CNL CPUs) chip, which I think is not the original one, but anyway, I tried to resoldering it with a 380C hot air station. Seems soldering is pretty good, but the laptop doesn't work (it worked before, but still had some problems with power delivery).
                                            Is there any big chance, that they sent me two fake ISL95880HRTZ chips or did I just use too big temperature for desoldering? I will try with another chip, but I can't find any info about the maximum desoldering...
                                            09-13-2024, 10:59 PM
