    Using a 240vac to 12vac transformer to test for shorts?

    Shorting devices I want to test
    1. Heat Gun
    2. AC Electric Motor (not sure if it is the motor so just want to test that directly)

    Hi There

    The two above devices trip a circuit breaker when I plug them into a wall.

    I was wondering if it would be feasible to use a 240vac to 12vac transformer to power the devices to do a bit of testing etc, making it safer and to keep the circuit breaker from stopping the power getting cut off?

  • eccerr0r
    Solder Sloth
    • Nov 2012
    • 8701
    • USA

    #2
    Re: Using a 240vac to 12vac transformer to test for shorts?

    How many watt heat gun is it? Typically they're around 1500W so they should draw 6.25A and resistance should be around 38Ω which should be easily readable with a 200.0Ω Full Scale 3½ digit DMM where in 120V land like in the USA, you'd need a 4½ digit DMM 200.00Ω FS or 3½ digit 20.00Ω FS to get reasonable data without needing to power it as resistances are less than 10Ω and the number of significant digits becomes more critical to measure precisely.

    How many watt breaker is it anyway, could that breaker be bad or will the devices trip different breakers?

    Comment

    • petehall347
      Badcaps Legend
      • Jan 2015
      • 4429
      • United Kingdom

      #3
      Re: Using a 240vac to 12vac transformer to test for shorts?

      not much to go wrong in either that you cant find with your dmm . if the trip is suspect try a new one or plug in to a different circuit . i dont see any need for any more than that . a regular series light bulb will let you test things safer than a transformer if you want to go that deep into it .

      Comment

      • budm
        Badcaps Legend
        • Feb 2010
        • 40746
        • USA

        #4
        Re: Using a 240vac to 12vac transformer to test for shorts?

        Is the breaker tripped due to over current or due to leakage current?
        Never stop learning
        Basic LCD TV and Monitor troubleshooting guides.
        http://www.badcaps.net/forum/showthr...956#post305956

        Voltage Regulator (LDO) testing:
        http://www.badcaps.net/forum/showthr...999#post300999

        Inverter testing using old CFL:
        http://www.badcaps.net/forum/showthr...er+testing+cfl

        Tear down pictures : Hit the ">" Show Albums and stories" on the left side
        http://s807.photobucket.com/user/budm/library/

        TV Factory reset codes listing:
        http://www.badcaps.net/forum/showthread.php?t=24809

        Comment

        • i-didnt-start-the-fire
          New Member
          • Aug 2018
          • 9
          • Australia

          #5
          Re: Using a 240vac to 12vac transformer to test for shorts?

          OK, Well done all.

          Took the motor into the garage and it didn't trip the circuit breaker so will sort that.

          Opening the heat gun further to measure resistance as I couldn't figure out the wiring. There is 5 going into to where the element is, for the different temperatures I guess. One of those had broken at the connector. That is working fine now I've reconnected it. Although 1 out of four settings is not working so will look further.

          I have a 75 watt flood light bulb for a load protection device but that lights up with most things so I was to try more in series. I'm not sure if they are the right bulbs to use. I think it is incandescent.

          My Transformer idea came from an isolation transformer. I connected two of the same transformers... 240v->12v to 12v->240v, to in theory make my own.
          It worked from a voltage perspective but I was worried if something tried to draw too much current that something scary might happen.

          So thought I might be able to test with 12v ac going through the motor and heat gun without causing too many issues????

          Comment

          • i-didnt-start-the-fire
            New Member
            • Aug 2018
            • 9
            • Australia

            #6
            Re: Using a 240vac to 12vac transformer to test for shorts?

            Originally posted by budm
            Is the breaker tripped due to over current or due to leakage current?
            That I don't know sorry. But my new answer I just posted may answer that?
            i.e. The motor works on another separate power board without tripping.
            I think the heat gun had a wire shorting but I just fixed that.

            Comment

            • eccerr0r
              Solder Sloth
              • Nov 2012
              • 8701
              • USA

              #7
              Re: Using a 240vac to 12vac transformer to test for shorts?

              Isolation transformer will not help as once you connect the load, the load will be presented to the primary and you're back into step 1.

              These loads appear to be fairly substantial, meaning the DBT won't work unless you had a bulb of even higher wattage than you heat gun; and the isolation transformer would need to be really hefty to deal with the wattage transferred from input to output.

              If you have an RCD/GFCI breaker, yes, make sure you're not tripping due to leakage current to GND or something. Usually you won't see a huge spark if you trip GFCI - you'd probably see a large spark if you trip a breaker with a 'short' type overload.

              Comment

              Related Topics

              Collapse

              • sansonet
                Converting 12VDC transformer to 12VAC
                by sansonet
                I need an AC transformer because the one I used is burned. Since I have some unused DC transformers, I wonder if it is possible to just remove the bridge rectifier from it to convert it to an AC transformer. I measured voltage before the rectifier on this one - it shows 13 VAC, and 16 VDC at connector without load. Rated 12VDC 1000mA....
                06-29-2023, 03:20 PM
              • ohren
                Original Xbox 1.0 PSU: Foxlink FTPS-0002 Rev. B. — 12 V low, 5 V high — transformer?
                by ohren
                Hello!

                I'm looking at an original Xbox PSU: Foxlink ftps-0002 rev. B. The 12 V output is too low, and the 5 V output is too (?) high. Unfortunately I don't have an oscilloscope but only a DMM for diagnosis.

                Measured voltages with no load:

                After rectifier diodes
                12V: 6.17 V
                5V: 5.67 V

                Secondary transformer pins AC measurement (really don't know if this says anything)
                12V: 2-2.5 V
                5V: 1.04 V


                I also have another (working) Xbox psu from Delta. The same measures there, in order, being: 10.79,...
                03-18-2023, 10:33 AM
              • khelane
                test active pfc power with lamp test
                by khelane
                Hello
                I have a big problem and that is that in some cases when repairing active pfc power supplies I cannot work with a test lamp. I can only get help with 5 volts standby and for starting and starting I have to work without a lamp and this way there is a possibility of parts exploding and other parts being added.
                Sometimes with a multimeter test the problems can be reduced to some extent, but I had several cases that had to be tested on and online and recently two varistors exploded. They had terrible resistance because the power supplies were over 800 watts.
                Is there a way...
                06-03-2025, 01:00 AM
              • chronic519
                Mats / mods: detected and repaired GPU fault. Cant seem to test after!
                by chronic519
                Hello.

                GPU came in, green lines. Spent lots of time using to get the Mats / mods drive working (found on youtube).
                Found issue with a RAM block
                Replaced, green lines gone.
                Trying to test again, assuming getting the false positive. Originally had over 1K on a single bank. Now getting tosses low between banks.
                Used a good card to test and same results low errors 32+.

                I am just search for some form of command to do a full test on the GPU.
                I just ran the mats command with my good GPU and passed after roughly 40 min.
                The repaired one, ran...
                05-20-2025, 07:56 PM
              • DCJack
                B&K 707 tube tester. I need help.
                by DCJack
                Hi everyone!

                I managed to get my hands on a rough condition B&K 707 for "the best price" because it was not working. It's my first tube tester and I'm really wanting to get it up and running. I downloaded that manual that has the schematics and tested every resistor and capacitor and replaced the ones that failed. I replaced the missing 83 rectifier tube with a used but tested-good one. I also have a number 80 rectifier tube that I have used in tests before I found the 83 tube.

                Initially I noticed that I was not getting the red on-light to turn on, but it...
                03-05-2024, 05:05 PM
              • Loading...
              • No more items.
              Working...