Looking for resistor
  • Almighty1
    • Apr 2014
    • 222
    Greetings everyone:
    I have a ring.com doorbell and it seems like to hardwire the doorbell so I don't have to take it off the wall to charge it weekly, I need a transformer and a resistor as seen here:
    https://support.ring.com/hc/en-us/ar...a-doorbell-kit
    So basically I need a 25 to 33 Ohm/20 to 50 Watt wirewound resistor, does anyone have any recommendations on what brands/parts are suitable for this and also for the doorbell wire, can I just use 18 or 20 guage speaker wire? Also, is there a reason to use a wirewound resistor instead of a film resistor? Since this will be outside, what can I use to cover up the wires?
    Thanks!
    • 31214
    Re: Looking for resistor
    http://www.digikey.com/product-detai...5R0-ND/1646203
    where is cheapest for delivery though?
      20~50W Resistor? How much power does this unit require? You should worry about dissipating the 20~50W of power in tight space.
      So you are not going to use a new door chime? https://www.badcaps.net/forum/showthread.php?t=52762
      https://cdn.badcaps-static.com/pdfs/...ad85f6e9e4.pdf
      • eccerr0r
        Solder Sloth
        • Nov 2012
        • 8701
        Looking at the docs a bit, the resistor isn't there for dropping, it's there in lieu of the doorbell chime... must be some other indication that the system was activated.
        I suppose if you have a 24V relay you could use that instead of the chime/resistor too. However I suspect the circuitry is assuming an inductive load and hence the wirewound. Without knowing what the actual circuitry is in the device, who knows...
          It is power through the door chime, so for them to use 25 ~ Ohms 20 ~50W resistor it must have quite AC drops on the resistor to dissipate that much power, you can calculate V drops on that resistor.
          So just assume safety margin so they double up on the Wattage of the resistor, so it will be 10W or 25W of power dissipation on the resistor.
          • Almighty1
            • Apr 2014
            • 222
            No idea how much power the unit really needs because normally it can be powered by the battery which is charged using MicroUSB so the power requirement is not high. It's just that if I'm traveling, I can't be there physically to charge the doorbell weekly due to the motion detection of 600-700 events weekly. The door chime is a option without the resistor except I do not know if the existing wiring even works or not as the only thing left is the wires where both the door bell button and door chime is supposed to be.
            I can see that it doesn't matter which wire is the transformer and which one is the chime for the door bell button but I still haven't figured out how to figure out which is the transformer wire where the chime is.
            I need to make sure the wires actually has voltage first before doing it without the resistor which would make it a whole lot easier. The house will be remodeled and everything will be torn down in a year or so, so anything is really only going to be a temporary solution. I can easily get a door chime kit which includes the transformer and the chime and even 2 doorbell buttons but ofcourse like I said, it's figuring out the transformer wire for the
            chime itself that seems to be hard as I tried a Digital MultiMeter on both wires with one on red and one on black and not seeing any voltage because only one wire is supposed to be connected to the transformer at where the chime is and where the doorbell button is. The other thing is rewiring the doorbell and chime is not easy as the wires all go straight inside the wall and you can't pull or push the wires either because they patched up the entire wall where the wires are as the house was being remodeled when the former owner got foreclosed on.
            • Almighty1
              • Apr 2014
              • 222
              Per this link, I don't think it can really use that much power as the power seems to be more for the doorbell's chime itself as the power is more for charging the battery...
              https://support.ring.com/hc/en-us/ar...attery-Powered
                They are using the resistor when you are not going to use the chime, if you have the chime then you do not need the resistor, if the chime come with the step down transformer then you do not need to use the new transformer if the old one is good and has the correct AC Voltage to match the new chime and wire it up as shown for single switch location.
                • Almighty1
                  • Apr 2014
                  • 222
                  Only problem is I hope the wires are still connected because the wiring in the house is messed up. The telephone termination for example is somewhere inside the wall so AT&T basically cut the wire outside and just mounted a new box outside and the only phone jack inside the house is dead. All I can do is run CAT6 cable from the box on the outside wall to where I need a phone jack using a existing hole from outside the wall. It just seems like a higher voltage would be better because it would charge the battery faster. I guess if all else fails, then I will need to use the transformer with doorbell wire and plug it into a AC Outlet. My concern if I go that route is what can I use to house the transformer so no one gets shocked should they touch it accidentally as I know there are plug-in transformers that are 24VAC 40-50VA from places like Parts Express but then I can pickup a Heath-Zenith 24VAC 20VA Transformer from a local hardware store for $5.00.
                  Are there any good brands of resistors available that is reliable since just like capacitors, I would prefer something like Panasonic, Nichicon, Chemi-con for example.
                  To be honest, I do want to go the chime route if possible since it seems easier and the chime will be louder than the Ring Chime that I'm using now which is only connected by WiFi that I can't hear it most of the time but if the existing wires don't work, then I'll have to do a run from the AC Outlet to the transformer with the resistor which is about a 25 feet or less run.
                    • 31214
                    now stop right there,
                    a increasing voltage wont charge a battery faster, it will heat it up till it bursts or burns.
                    the speed a battery charges is controlled by the current, not the voltage.
                    • Almighty1
                      • Apr 2014
                      • 222
                      Good point but usually the higher voltage has higher current, atleast on transformers. Since there are plug-in transformers sold by Parts Express that is 40VA in current at 24VAC except ofcourse the battery is DC and not AC so not sure what happens inside the ring.com doorbell internally as I know at the standard 500mAh 5vdc using MicroUSB, it will take 10 hours to charge but if the charger is a USB charger at 1700mAh, it will take roughly 3.5 hours or so to fully charge.
                      http://www.parts-express.com/parts-e...rmer--120-1175
                      • Almighty1
                        • Apr 2014
                        • 222
                        As can be seen in the other thread, doing it the doorbell chime route is very risky since I have to change out the transformer... So it seems like the resistor idea is still the better bet so would greatly appreciate anyone's help in picking out a resistor that will work.
                        • mxslick
                          Motocross Racer
                          • Oct 2010
                          • 19
                          First, as was already mentioned in the other thread, you need to get a licensed electrician in there to correct all of the serious wiring issues.
                          Second, I suggest you find an experienced LV/alarm installer. The conditions you have going on puts this task over your head..and the use of that resistor can create a safety hazard if not done correctly.
                          The time that will be saved and the reduction/elimination of the hazards present will be worth the extra cost.
                          • keeney123
                            Lauren
                            • Sep 2014
                            • 2536
                            So 40VA = 40 watts. or P= V*A therefore P/V=A Where P is power in Volt * Amps better known as Watts. 40Watts/24Volts= 1.67 Amps now we use the formula V=I*R where I is current and R is resistance We rearrange this formula to V/R=I that is 24volts/25ohms= 0.96 amps. Now we use another equation that may be derived from P=V*I with substitution to get P=I^2*R
                            Of course you will notice that A and I are the same "current". So the equation becomes P=0.96^2*25, this then gives you 23.04Watts or VA.
                            You should check the voltage on the wires to the transformer before you disconnect the wires to make sure the voltage side you are disconnecting is the 24 volt side and "not" the 120 Volts side. Make sure you take one side off at the time making sure not to short wires across transformer. Or you can have someone stay with a meter measuring the voltage on the transformer and another person can start flipping breakers until to find the one that cuts the power off to the transformer. Then do the below step.
                            To check your door bell wires. First detach wires on transformer. Undue the door bell and connect both wires go back to transformer using an OHM Meter measure the resistance between the two detached wires that go to the door bell. Your resistance will be low around 25 ohms which is the chime coil. This is a continuity check. Also, before you measure the Ohms switch to Voltage scale and make sure you have no DC volts or AC volts between the wires you are going to measure in OHMs.
                            • Almighty1
                              • Apr 2014
                              • 222
                              Not when the cost is over $10k as all the walls will need to be torn down. I will already be spending $650k+ in the remodeling process alone, licensed electricians and even contractors had looked at the issue as this was even part of the home inspection process before the home was purchased 7+ years ago. They basically all said that to fix the problem, all the walls need to be taken down and demolished as that will require a permit on it's own since everything is in sealed walls now which is why they all suggested to just have it done during the remodeling process since everything will be taken down at that point anyways. I am not planning to use the resistor on the existing wiring as I want to avoid that due to what was mentioned by you and others about the safety hazard. This is why I will just have a plug-in transformer to the wall directly to the doorbell which is about 10 feet away and the reason for the resistor.
                              • Almighty1
                                • Apr 2014
                                • 222
                                Thanks for the reply. So is 40VA really 40 Watts or 23 Watts? The transformer is actually a GE 10V 5VA, what would happen if I use a door chime that normally requires 16V 10VA, will it still work but just not be as loud since it seems like both the voltage and the VA is lower. I know which side is the 120VAC side as that is the one that goes into the AC wires while the other side usually in the black/white/green configuration while the lower voltage side is always the one that goes into the small screw terminals with the markings of the LOAD and the 10VAC 5VA.
                                If you see the other thread, my post https://www.badcaps.net/forum/showpo...80&postcount=7
                                I actually do not have a door bell button or a door bell so there is nothing connected on the other end of the wires which was the reason I asked how to check if the wires found where the door chime and door bell is supposed to be is actually connected to the transformer as all the wires are sealed inside the wall so I don't know if the wires are connected all the way. Normally in a circuit, it will require two wires that atleast are connected on the other end to something to make testing easier but since I do not have a door bell button and a door chime, my original question was how do I test the wire at the location where the door chime was supposed to be as I am trying to determine which wire goes to the transformer which would be connected while the other wire is not connected at the other end as that one is supposed to go back to the door bell.
                                • keeney123
                                  Lauren
                                  • Sep 2014
                                  • 2536
                                  Yes 40VA is 40 watts. 40 VA is 40 volts times amp. Volts times amps is watts. I think in another thread or even this thread I post where you can by a 16 volt 10VA at Home Depot for $8. I would not use a transformer that is the wrong rating for the door chime as it may not work at all. I would still check the wires with a meter as some people may of connected them wrong. Any good electrician would do this check. You always check voltages or current on the largest scale and then go to a smaller scale if you can not get a reading. I went to your link but there was no pictures.
                                  If you have no door bell or wires on the outside of the home then you will need to run wires to the outside of the home. You will need what they call a fish. This is a reel of solid very stiff wire with a loop at the end of it. It is contain in a plastic container than can be reeled out or up depending on what you need. You will fish this wire up from your basement or down from your attic. In the basement you may have to drill a hole in a stud to get to the interior wall. You will also have to drill another hole in the outside wall where you want the door bell. That is where the wires will come through. You fish this stiff wire to this hole. This will require two people. One looking for the wire and one doing the fishing. When you get the fish to the outside wall you then strip the end of the two wires your are going to use for the door chime. Then you twist the wire end and loop them them through stiff wire loop and twist them back on to themselves and lastly you tape them very tight and smooth so they do not slip off. The next thing is to pull the wire. you will then bring them to the chime and then to the transformer. Or you could get a wireless door bell. You will have a door bell on the outside of the door. This has a AA or AAA battery which can be replaced easy. It also last a long time. The chime you plug in to a wall outlet somewhere near the door on the inside of you house.
                                  Lastly if the wiring is screwed up in your house then make sure you have smoke and fire alarms in each room. When you can afford an electrician, get a "master" electrician first to come to your house to see what needs to be done and gives you a cost break down on doing it. Then do one thing at a time until you get is completed.
                                    VA vs WATTS:
                                    http://switchon.eaton.com/power-esse...FQqIfgodsG8JNw
                                    http://electronicdesign.com/energy/w...d-volt-amperes
                                    • Almighty1
                                      • Apr 2014
                                      • 222
                                      What I meant was in your previous example, the 40VA = 40 watts somehow became 23.04Watts.
                                      As for the link, it works fine when I just tried it as there are atleast 3 pictures but this is the main link for the thread:
                                      https://www.badcaps.net/forum/showpost.php?p=638380
                                      I replied in the other thread a few days ago that I can get a Heath Zenith Multi-purpose transformer locally at the hardware store for $5 which is the exact model as shown here:
                                      https://www.heath-zenith.com/product...125?taxon_id=3
                                      The only thing using one of those, I would need something to house the transformer as it will be on the floor in the living room even though it's underneath a table, sometimes I need to fix my computer and might accidentally touch it.
                                      That's why using something like this will probably work better:
                                      http://www.amazon.com/Honeywell-Powe.../dp/B004HN3OEK
                                      I'm in San Francisco, a anti-chain store city so the only thing here is Lowe's as the location was something HD negotiated for 10+ years that finally got approved but they decided not to open so Lowe's took over it.
                                      I think you misunderstood what I said. The wires are there where the doorbell and chime is supposed to be, there is just no chime and no doorbell button there if you are able to see the pictures. Basically at where the doorbell button is, there is two wires which from what I read, it doesn't matter which direction it goes so that part I am not concerned about. The part I am concerned about is the two wires where the doorchime is supposed to be but there is no doorchime there so I just need to figure out if one of the wires is connected to the transformer and how to actually do it since remember the other wire would connect to one side of the non-existent doorbell button so it is not a complete circuit that can be tested easily as at both locations, one wire is supposed to go to the transformer while the other is between the doorbell button and the doorbell chime. The entire basement is finished so it's not easy accessing wires except at the location where it is still exposed as all the wires are in finished walls including the telco demarc point which is the same reason AT&T would cut the outside line and just mount a new box and not even deal with inside wiring as I had to run a external CAT 6 cable on the exterior wall.
                                      Unlike typical houses where the garage is on the lower level just below the front door, my garage where the transformer is at the rear of the house on the lower 1st floor while the front door doorbell wall hole with existing wires is on the upper level of the house on the 2nd floor so the fishing part might or might not work as it all depends on if the walls are still hollow or if it's completely solid. In any case, I think we should really get back to the original topic about the resistor. I have no problems finding transformers, wiring or anything else, it's the resistor I need help finding.
                                      If you read the thread on why I need a resistor, you will know my object is not to have a working chime or a regular doorbell whether conventional or wireless. I just need a working transformer with either a resistor or a working transformer with a working chime so that I can connect the existing wires where the doorbell is supposed to be to my Ring.com Doorbell so it is hardwired so that I do not have to remove it once a week to recharge the battery by MicroUSB which will not be possible when I am going to be on a trip in Asia for a month in May and June 2016. The doorbell captures all motion whenever it is detected that is 600-700 events a week.
                                      I have smoke/carbon monoxide detectors that is connected to my security system so if anything goes wrong, the security monitoring company will be calling the fire department.
                                      • keeney123
                                        Lauren
                                        • Sep 2014
                                        • 2536
                                        I never learned that in school. Although I did not download the PDF file, because one has to register, this explanation is a little convoluted. It says it is apparent power which can very according to your capacitance and inductive load. When it says VA is RMS power which is different than apparent power that is confusing. As RMS is 0.707 of peak voltage. DC is average voltage .6 something . Depending on the lead or lag of the current and voltage the apparent power will change, there is also a frequency component tied with apparent power. When I see VA I take it for VA Which is Volt*Amps there is no specifications as to RMS power or apparent power which are two very different things. Apparent power is not figured by RMS V and RMS A. It is figured from how the capacitance and inductive and frequency is effects the voltage and current in a sinusoidal wave. So if they are using VA as something other then want it is then I am totally confused.
                                        • jinu_j
                                          by jinu_j
                                          Hi
                                          05-03-2025, 10:51 PM
                                        • mikey5791
                                          by mikey5791
                                          Hi to all forum members,
                                          12-26-2024, 04:55 AM
                                        • MidnightRoller
                                          Can a resistor lose resistance after hot air?
                                          by MidnightRoller
                                          I am curious if a 0402 resistor could go from 43 ohm to 0. In electronics class and my experience a resistor can degrade and gain resistance all the way up to not being able to conduct at all. I have never heard of a resistor decreasing in resistance and becoming 0 ohm or a dead short… that's not the direction they fail… or so I thought.
                                          I was attempting to remove a wson8 chip on an iMac motherboard and it required a lot of heat, on one side of the chip were 3 0402 resistors that were very close. I popped the chip out unintentionally out of the tweezers and sent those resistors...
                                          02-02-2022, 11:46 PM
                                        • artvandalai
                                          What resistor ohm will work better to repair this waterpik?
                                          by artvandalai
                                          The resistor on this waterpik blew. I changed it with the a similar spec 47ohm 2 watt yageo resistor but it still keeps blowing the resistor. Checking with the multimeter the motor, capacitor, diodes, and thermal fuse all checked normal. Will a higher ohm resistor work better? What ohm resistor will work better to repair this waterpik? This video is showing the repair with a 56 ohm resistor https://www.youtube.com/watch?v=_J7_rV7ui1Y
                                          01-05-2025, 04:10 PM
                                        • chth96
                                          Is it okay to replace 1/2 watt resistor with 1 watt resistor in AC/DC adapter?
                                          by chth96
                                          I have purchased an 100-240v AC/5v 2a DC adaptor from aliexpress,and a month ago It smelled burning when I plugin it powerstrip.
                                          Since then, This AC/DC adaptor have been out of order.
                                          But A few days ago,I replace 0.5 watt resistor with 1 watt resistor(1ohm) in this adapter.
                                          After replacing resistor,It succeed to recharge all of android phone.And When I measure voltage on the two pins of USB port,It shows 5.5v
                                          And Is there any possibility that it will suddenly explode as well as to be out...
                                          12-03-2023, 04:40 AM