Power-One solar Inverter driving me NUTS!!!

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • mitsu2k
    replied
    Originally posted by petehall347
    troubleshooting is page 49 onwards
    OK I think I know what you are referring to now. Please see attached. This is the only test that I can see that would be relevant. And I did perform this test in the following manner:

    tested between positive and earth ground and got over 50 MegaOhms.

    got approximately the same results from negative to earth ground.

    I did not short the positive and negative together because it was daytime and I didn't think that would be a good idea being that there's about 256 V there. However, I wouldn't expect to see any different results if I shorted them being that they were both over 50 mega anyway. I suppose I can do this test at night, but I am just afraid of blowing the diodes on the panels and I don't really want to go up on the roof being that I am afraid of heights
    Attached Files
    Last edited by mitsu2k; 11-25-2023, 03:47 PM.

    Leave a comment:


  • petehall347
    replied
    troubleshooting is page 49 onwards

    Leave a comment:


  • mitsu2k
    replied
    Originally posted by CapLeaker

    I hope you mean MOhm not mOhm. There is a huge difference between Mega and Milli
    Yes I meant MegaOhms

    Leave a comment:


  • mitsu2k
    replied
    Originally posted by sam_sam_sam

    Did you do the test procedure that is outlined in this maintenance manual
    Did you follow it exactly or did you deviate from what they have and if you did please explain how you did it differently
    Also if you did run the test as they outlined in the manual what were your results for each section of tests
    https://www.badcaps.net/filedata/fetch?id=3153508
    I have not seen any test in any maintenance manual. Where are you seeing this?

    Leave a comment:


  • CapLeaker
    replied
    Originally posted by mitsu2k
    I tested between the first and third legs in my photo. Here are the results.

    500vdc test

    #1
    175 mOhms

    #2
    205 mOhms

    #3
    215 mOhms

    #4
    239 mOhms

    I also tested the two blue ones on the AC side and those tested over 4000 mOhms. (full scale on megger)

    Not sure what these results mean. Could all 4 of them be bad?
    I hope you mean MOhm not mOhm. There is a huge difference between Mega and Milli

    See, MOVs degrade with time and how often the get zapped. The insulation layer will break down each time it gets hit, to a point of leaking or total failure (basically a short). A 175 Mega Ohms is not a failure, but it's getting time to change it out. All depends on what the rating of this MOV is and how much voltage you use with the Megger,
    Let's say you hit a 375V MOV with 500V from the Megger, it will hurt the MOV each time you press the test button.

    Leave a comment:


  • sam_sam_sam
    replied
    Originally posted by mitsu2k
    I tested between the first and third legs in my photo. Here are the results.

    500vdc test

    #1
    175 mOhms

    #2
    205 mOhms

    #3
    215 mOhms

    #4
    239 mOhms
    Did you do the test procedure that is outlined in this maintenance manual
    Did you follow it exactly or did you deviate from what they have and if you did please explain how you did it differently
    Also if you did run the test as they outlined in the manual what were your results for each section of tests
    https://www.badcaps.net/filedata/fetch?id=3153508
    Last edited by sam_sam_sam; 11-25-2023, 05:53 AM.

    Leave a comment:


  • mitsu2k
    replied
    I tested between the first and third legs in my photo. Here are the results.

    500vdc test

    #1
    175 mOhms

    #2
    205 mOhms

    #3
    215 mOhms

    #4
    239 mOhms

    I also tested the two blue ones on the AC side and those tested over 4000 mOhms. (full scale on megger)

    Not sure what these results mean. Could all 4 of them be bad?
    Last edited by mitsu2k; 11-24-2023, 09:43 PM.

    Leave a comment:


  • CapLeaker
    replied
    2 is the middle leg. Number 3 is the closest leg to 2. Number 1 is the furthest away from leg 2 (middle pin).

    leg 2 to leg 3 is the thermal fuse and should read a dead short.
    leg 1 to leg 3 is the MOV and it should be either OL or full scale resistance on the Megger.
    Attached Files
    Last edited by CapLeaker; 11-24-2023, 09:29 PM.

    Leave a comment:


  • mitsu2k
    replied
    Originally posted by CapLeaker
    The third leg is a thermal fuse.
    so which legs do I test across with the megger?

    Legs 1 and 2 from left to right test short.
    Attached Files
    Last edited by mitsu2k; 11-24-2023, 08:58 PM.

    Leave a comment:


  • CapLeaker
    replied
    The third leg is a thermal fuse.

    Leave a comment:


  • mitsu2k
    replied
    Originally posted by CapLeaker

    best way to test MOVs is with the Megger, Put 250V or whatever their max rating is on there and if the Megger ranges out, they are good to go.
    These are 3 legged MOVs. The middle leg on the positive terminals seems to be connected directly to earth ground.
    Attached Files

    Leave a comment:


  • petehall347
    replied
    Originally posted by mitsu2k
    Not sure what the “A” model is but here is the labels
    i would expect the A to be part of the model number . maybe the manual has clues about it .

    Leave a comment:


  • CapLeaker
    replied
    Originally posted by mitsu2k
    I have a question about the MOVs. None of them look discolored or show any signs of heat. They test open with DMM. I know this is not a proper test but should I just not worry about these?
    best way to test MOVs is with the Megger, Put 250V or whatever their max rating is on there and if the Megger ranges out, they are good to go.

    Leave a comment:


  • mitsu2k
    replied
    I have a question about the MOVs. None of them look discolored or show any signs of heat. They test open with DMM. I know this is not a proper test but should I just not worry about these?

    Leave a comment:


  • petehall347
    replied
    this post does not exist . honest .
    Last edited by petehall347; 11-24-2023, 07:37 PM.

    Leave a comment:


  • CapLeaker
    replied
    Originally posted by mitsu2k
    OK now I’m thinking there is really a ground fault. When I connected it back up to the array and turned it on, I tried to measure current from positive, DC, negative DC, to earth ground. I was not able to measure any current, but when on the positive and touching the earth ground with my probe, I noticed very slight arching. I don’t get this arcing on the negative side.

    I don’t think that should be the case. When I measured for voltage between the positive terminal and earth ground, I get approximately 149 V. Between the negative and earth ground I get approximately 87 V. The array itself positive to negative measures approximately 256 V. When I disconnect the array from the inverter and just measure the positive and negative coming from the array to earth ground I get very low transient voltage, like 5 to 10 V.

    but the question is, where could this leakage be?

    edit: when I remove the 4 red MOVs and perform the above test again, I get practically no voltage from negative to earth ground but the voltage from positive to earth ground jumps up to about 191v
    That sounds like a real ground fault all right. I would start again bare ass from square one. This time take as sheet of paper and make nots want you did, how you did it and what the result was.
    i do have a document that comes with a different inverter that deals with this on the solar side.
    Attached Files

    Leave a comment:


  • mitsu2k
    replied
    Originally posted by petehall347
    leakage is on the negative if indeed there is any leakage .. the measurements suggest there is . maybe a cable is damaged or got water inside it .
    Are you referring to the cables coming from the array? I tested those disconnected from the inverter and they seem to test fine. I tested them with a mega and the resistance was in the high mega ohms on both the positive and the negative to earth ground. The inverter itself measures them above 20 mega Ohms when it performs it start up test.

    Leave a comment:


  • petehall347
    replied
    leakage is on the negative if indeed there is any leakage .. the measurements suggest there is . maybe a cable is damaged or got water inside it .

    Leave a comment:


  • mitsu2k
    replied
    OK now I’m thinking there is really a ground fault. When I connected it back up to the array and turned it on, I tried to measure current from positive, DC, negative DC, to earth ground. I was not able to measure any current, but when on the positive and touching the earth ground with my probe, I noticed very slight arching. I don’t get this arcing on the negative side.

    I don’t think that should be the case. When I measured for voltage between the positive terminal and earth ground, I get approximately 149 V. Between the negative and earth ground I get approximately 87 V. The array itself positive to negative measures approximately 256 V. When I disconnect the array from the inverter and just measure the positive and negative coming from the array to earth ground I get very low transient voltage, like 5 to 10 V.

    but the question is, where could this leakage be?

    edit: when I remove the 4 red MOVs and perform the above test again, I get practically no voltage from negative to earth ground but the voltage from positive to earth ground jumps up to about 191v
    Last edited by mitsu2k; 11-24-2023, 03:25 PM.

    Leave a comment:


  • mitsu2k
    replied
    Not sure what the “A” model is but here is the labels
    Attached Files

    Leave a comment:

Related Topics

Collapse

  • Francesc V.
    Trying to repair a MPI5.5kW solar inverter
    by Francesc V.
    My parent's solar inverter died after 5 years of good service.

    It's a called hybrid inverter:
    - It can go with or without batteries
    - It has 2 MPPT (8 330W panels in 2 strings) -> 5280Wp
    - A 20kWh lithium battery previously used in a Nissan leaf (14S at 4.1V max) -> 57.4V

    Panel is showing error 17 and the battery connection has disappeared. On the other hand, is delivering load, MPPTs are working and it's exporting energy to the GRID. Not that "bad".

    Let's open it......
    I see that 150A fuse is gone and the...
    03-07-2023, 06:17 AM
  • x_orange90_x
    Vizio E55-E1 bad backlights or bad inverter?
    by x_orange90_x
    I just got this tv today and it appeared to have no backlight on. After taking off the rear cover and checking again in the dark I can see that MAYBE one quadrant is lit.. But still it's quite dim. I was going to check the LEDs with my tester, and I found LED 1 and LED 2 + pins on the wire from the inverter, but I couldn't identify a ground. Nonetheless I tried using a mounting screw on the inverter board and also the chassis as ground but regardless my tester reads 300 which is what it reads when there is no voltage draw.

    I don't know how exactly to test the inverter itself. Is it...
    01-29-2025, 09:24 PM
  • Gentian
    APSINT3636VR 3600W APS INT Series 36V DC 230V AC Inverter/Charger schematic
    by Gentian
    I have a tripp-lite aspint 3636vr inverter charger which blow some of mosfet transistors. I replaced them repaired also the driver circuit and tested but the mosfets burn again.

    It work very well as inverter and also as charger if I let the rear switch in auto mode (inverter) and charger only(charging) but in auto when I connect the feed line 220V AC first time it pass ok to line and start charging the batteries but when I remove the feed line it pass to inverter mode and if I do it again the second time when passing from charging to inverter the Main transformer start making a...
    03-06-2023, 07:07 AM
  • valvashon
    Insignia NS-LCD19-09 (PS OK, Inverter problem?)
    by valvashon
    For some reason I'm just not going to let this 19" TV defeat me. I guess because I have a schematic to work from I feel like I'm oh so close.

    History- while adding a turn-on circuit I let a small screw roll under the power board. Worked through all of that circuitry, probably replacing a MOSFET and PWM controller that were not bad but I was following the service manual. Finally figured out that the power supply is in working order when the inverter section (for the backlights) is disconnected. When the +12 supply to the inverter is disconnected the +12 and +5 will come up...
    01-04-2024, 01:44 PM
  • caseyjay_48
    Sony KDL-46BX450 Inverter Troubleshoot Logic
    by caseyjay_48
    I am currently on a troubleshoot of 46” Sony KDL-46BX450 tv. I came back from Washington to Texas on medical emergency and had to leave all my tools up there. All I have is a couple of screwdrivers and a dvm. I wish to ask the community a troubleshooting question. Please forgive stupid questions as meds I am taking produce brain fog.
    I have well maintained Sony KDL-46BX450. It went black one day. After turn-on, I get solid green light and Sony logo in screen center for about 1-2 seconds, then black. No blinking LEDs, no hissing. Flashlight test shows screen characters dimly viewable,...
    09-23-2022, 08:08 PM
  • Loading...
  • No more items.
Working...