Lenovo ideapad 5 windows 11 update disable charging circuit?
  • m1ch43lzm
    • Mar 2019
    • 1078
    • Peru
    #101
    bogart219 What SMDFlea meant, is 1) the firmware is stored on another chip already installed on the board
    This is the case for the NM-E211 Board (Thinkpad E14/E15 gen 4) SMDFlea mentioned where there's indeed a 24c256 EEPROM onboard with the firmware, or "configuration bundle" as TI calls it
    Originally posted by TPS65994 datasheet
    9.1 Application Information
    The TPS65994AE firmware implements a host interface over I2C to allow for the configuration and control of all device options.Initial device configuration is configured through a configuration bundle loaded on to the device during boot.The bundle may be loaded through the I2C_EC port or it may be loaded over I2C3m from an external EEPROM.The TPS65994AE configuration bundle and host interface allow the device to be customized for each specific application. The configuration bundle can be generated through the Application Customization Tool.
    But in your board NM-E401 i don't see such EEPROM on the schematics/board view, so according to the datasheet, the EC supplies the "configuration bundle"
    Maybe Lenovo did something differently
    2), 3), 4) No need to do anything about it, it should work, according to TPS65994 datasheet and the schematics for your board
    • bogart219
      • May 2009
      • 200
      • usa
      #102
      Thanks for explaining that to me.
      Great, we can proceed then. I replaced the TPS chip, put the two mosfets back on and put the two inductors back on. I'm back to 5 volts and no amps on the usb tester. Will put the PC8309 back, hook the battery back on, and see what happens. The cap that was glowing I will leave off. will let you know.
      • bogart219
        • May 2009
        • 200
        • usa
        #103
        Well I'm back to where I started. Put that PC8309 cap back on and still got 5 volts and no amp draw. I put everything back together. hooking up the battery. connected all the cables and everything thinking the computer might need to sense something. Didn't make a difference. It wouldn't even turn on with the battery hooked up now. I measured 12 volts on the battery. I must of fuxed something up real good, probably with my soldering. I don't know what to do now. If anyone has any suggestions. I'm all ears.
        • bogart219
          • May 2009
          • 200
          • usa
          #104
          You know one thing I don't understand is the fact that I never remember seeing 20 volts anywhere. Mc1 you " The issue you have is that it's not negotiating 20v with the AC adapter / not charging". To me. I'm taking this as when certain conditions are met, the board is sending a signal to the power adapter to let 20 volts flow. Is this a right assumption? seems to me that if you plug in that power adapter to the USB-C port, that you should have all the voltages on the outlet of that port. When watching a bunch of Sorin;s repair videos it always seems even though a lot of his repairs are no charging problems (sort of like mine), he alwyas seems to read 19 volts on a power rail and then tracks down from there. Never seen 19 or 20 volts. Do you see what I mean? Thank you for your time.
          • m1ch43lzm
            • Mar 2019
            • 1078
            • Peru
            #105
            Let's start troubleshooting the basics
            Get a copy of FlexBV Free if you haven't already, use this software to open the boardview
            https://pldaniels.com/flexbv5/
            Unplug all power, measure resistance to GND on all power rails, post the values here
            Click image for larger version  Name:	power rails nm-e401.png Views:	0 Size:	39.2 KB ID:	3649789
            +3VL at RE4501, PR6219 or if not present/replaced with a trace, then across PC6205, near PU6219
            +3VALW at PJ6201
            +5VL at PC6204 (one side is GND, the other is +5VL)
            +5VALW at PJ6206
            +3VALW_PCH at J2
            +1.8VALW at PJ7912
            +3VS at J5
            +5VS at J4
            EDIT: Review US301, it's near PC5302 which you removed, hopefully you didn't damage it
            • bogart219
              • May 2009
              • 200
              • usa
              #106
              Hey M1, first off I'm not even sure I know where all the power rails are. I'm going to study on this and get back to you. I did get flexBV free , thanks
              This is with the power off.
              those vl's below the chart, are also with the power off, measuring to ground correct
              • m1ch43lzm
                • Mar 2019
                • 1078
                • Peru
                #107
                I marked the locations of the power rails below the chart, all resistance measurements with power off, battery and charger disconnected, and RTC battery/coin cell disconnected (i think it gets connected to the USB daughterboard), that's what i meant by "unplug all power"
                In flexbv, press Ctrl-F, then type PJ6201 for example)
                The chart is for reference which voltages should be present, do not apply power yet until after checking resistance values
                • bogart219
                  • May 2009
                  • 200
                  • usa
                  #108
                  Alrighty then, lets get back to business. I was just about to post my findings yesterday when the site went down.
                  Question Mic, how can you tell where or what the power rails are? This does along with the question I posed in post 104.
                  Here are my findings: Thanks
                  Click image for larger version  Name:	lappyjune1.png Views:	0 Size:	328.7 KB ID:	3650269
                  • m1ch43lzm
                    • Mar 2019
                    • 1078
                    • Peru
                    #109
                    Looks fine to me
                    With only battery connected, before pressing power button you should have
                    +3VL
                    +5VL
                    +3VALW
                    +5VALW
                    You can measure those voltages, on the caps I listed, the board view shows which side is + (no need to measure voltage from GND to GND 😀, of course the side of the cap you measured 0.1ohms to GND is GND)
                    That's S5 state (power off)
                    S0 is power on, After pressing power button you get all voltages
                    S0Ix is the "modern standby" state after power on, when you close the lid/after some time when the laptop sleeps
                    Is the power button located on the keyboard? You can also power on the board with the "Novo" button, it's on the USB daughterboard, looks like this behind a pinhole, you can gently press it with a paperclip, or sim eject tool
                    Click image for larger version  Name:	84b104dd07114ac8859591dbe9b7ef85.jpg Views:	0 Size:	2.1 KB ID:	3650519
                    • bogart219
                      • May 2009
                      • 200
                      • usa
                      #110
                      Looks fine to me
                      +3VL
                      +5VL
                      +3VALW
                      +5VALW
                      With just the battery hooked up, I get 3.2 volts on PC6205 and 5 volts on PC6204. do you want me now to put the MB back in the lappy and hit the novo button? Don't hook up the adapter yet?
                      I'm confused on what your talking about with the S5,S0 & S0lx states, not sure what you want me to do next.
                      When we started troubleshooting this MB, I was getting 20 volts with the battery and charger hooked up, now I just get 5 volts. What do you Think happened?
                      • m1ch43lzm
                        • Mar 2019
                        • 1078
                        • Peru
                        #111
                        It's fine, you can remove the daughterboard from the chassis to test
                        Connect the daughterboard, battery, and try powering on with the Novo button, it should power on (fan spin)
                        The S5, S0 are the power states
                        S5 means "power off", S0 is "power on" that's what the chart means, on each power state there's the expected voltages
                        So when the laptop is powered off, it's in S5 state
                        When it's powered on, it's in S0 state
                        • bogart219
                          • May 2009
                          • 200
                          • usa
                          #112
                          Thanks for the info. I'll get that daughterboard off and get back with you. Thanks!
                          • bogart219
                            • May 2009
                            • 200
                            • usa
                            #113
                            Nothing happened. with or without the charger. Could you or someone please answer the question i asked in post 104, I'm trying to understand this better. please
                            • m1ch43lzm
                              • Mar 2019
                              • 1078
                              • Peru
                              #114
                              It only applies to laptops with regular DC input jack. you feed them 19v then it goes through 2 mosfets controlled by the charger IC
                              Or if it has a USB-C charger, then the USB-C PD controller managed to negotiate the 20V with the AC adapter
                              You have an extra step, that is the USB-C PD controller which negotiates the 20v, then that goes to the input of the charger IC
                              But it's strange that now your laptop doesn't react to the power button
                              With the charger plugged in you should get the voltages listed in "S5/S4 AC only"
                              With the daughterboard plugged in do you get 3VL, 3VALW, 5VL, 5VALW?
                              • bogart219
                                • May 2009
                                • 200
                                • usa
                                #115
                                Hello. OK, thanks for the explanation. so going by what you said, the " PD controller which negotiates the 20v" means I wouldn't see 20 volts anywhere until the PD controller tells the charger that " the right conditions have been met, its ok to provide 20 V now to the MB ". Is this correct?
                                " With the charger plugged in you should get the voltages listed in "S5/S4 AC only" = I don't get any of these voltages (3VL, 3VALW, 5VL, 5VALW) (just the charger plugged in and the daughterboard ).
                                • m1ch43lzm
                                  • Mar 2019
                                  • 1078
                                  • Peru
                                  #116
                                  Yes, charger when unplugged outputs nothing (0v); when plugged to something it starts at 5v, so it's safe to plug in to a device which expects only 5v (a phone or something else), after that the PD controller negotiates the 20v
                                  With only the battery+daughterboard you get those voltages?
                                  At that point you should even get 5v on PL8301-PL8302 with only charger plugged in, if nothing gets there, the MOSFETs are not turning on
                                  With charger plugged in, measure VCC3_LDO_PD1, you can check at the left side of RPU203, should be 3.3v
                                  At the D of PQ8302-PQ8303, or the D of PQ8304-PQ8301 depending on which port you connect the charger, you should get 5v, or 20v when everything works properly
                                  At this point the 5v only reach the S of PQ8302, or S of PQ8304, again depending on which port you connect the charger, that's straight from the USB-C ports
                                  • bogart219
                                    • May 2009
                                    • 200
                                    • usa
                                    #117
                                    I've been messing with this all day. In attempting to straighten out those two mosfets I replaced, I fuxed them up worse. when and If I get this shit straightened out, I'll get back to you. (disgusted and depressed about my fuxed up smd ability.
                                    • bogart219
                                      • May 2009
                                      • 200
                                      • usa
                                      #118
                                      Update: Right now when I plug in the usb tester with the charger it just flashes. Yesterday the usb tester wash flashing when plug in. I removed mosfet Pq8303 completely and the flashing stopped, went back to 5 volts again. OK, I thought i didn't have pq8303 done right, so I thought while I'm at it,I'll straighten out Pq8301 and the TPS (UU201) chip that I replaced. After putting the mosfets back down and straightening the TPS chip, I plugged the ubs tester back in and the dam thing was flashing, *uck. This morning I took back out both mosfets again and cap pc8309... tseter still flashing.
                                      I used my thermal camera and didn't see anything hot standing out. I'm lost at this point. Any suggestions or guidance would be greatly appreciated.
                                      PS: I know this is all my fault but I'm learning alot. All the equipment I bought in the last month or two to take this repair on, I could of bought another new laptop. However, the knowledge I'm gaining plus the interaction with you guys is priceless!
                                      • bogart219
                                        • May 2009
                                        • 200
                                        • usa
                                        #119
                                        Good morning. I'm trying to figure out why when I plug in my charger with the USB-C it just flashes (both usb-c ports). I'm thinking I have a short somewhere. At this point,I'm not sure where to start. I did find one of these fuses blown, I beleive but I don't think that would cause the tester to flash.
                                        How should I proceed from here?
                                        • m1ch43lzm
                                          • Mar 2019
                                          • 1078
                                          • Peru
                                          #120
                                          A fuse should read 0 ohms, so both fuses got blown if you're measuring resistance across them
                                          Measure resistance to GND after the fuses, if not shorted (tens of K upwards) then the fuses may have gotten damaged due to heat
                                          The flashing on the USB-C tester may indicate a fault with the TPS65994 or related circuit, sometimes ICs can get damaged when heat is applied for long time
                                          You can start by measuring resistance to GND on the power pins of TPS65994, VIN_3V3_PD1 at CU207, VCC3_LDO_PD1 at CU209, or at the left side of RPU203, VCC1V5_LDO_PD at CU208, and 5VALW
                                          mon2 what do you think?
                                            Lenovo IdeaPad IdeaPad 3 17ITL6 Notebook 3 Specification for Upgrade or Repair
                                            This specification for the Lenovo IdeaPad IdeaPad 3 17ITL6 Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the IdeaPad 3 17ITL6 boardview and IdeaPad 3 17ITL6 schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet,...
                                            09-07-2024, 05:20 AM
                                            Lenovo IdeaPad IdeaPad 3 15IGL05 Notebook 3 Specification for Upgrade or Repair
                                            This specification for the Lenovo IdeaPad IdeaPad 3 15IGL05 Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the IdeaPad 3 15IGL05 boardview and IdeaPad 3 15IGL05 schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet,...
                                            Lenovo IdeaPad IdeaPad Gaming 3 15IHU6 Ultrabook 3 Specification for Upgrade or Repair
                                            This specification for the Lenovo IdeaPad IdeaPad Gaming 3 15IHU6 Ultrabook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the IdeaPad Gaming 3 15IHU6 boardview and IdeaPad Gaming 3 15IHU6 schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any...
                                            Lenovo IdeaPad IdeaPad 3 15IML05 Notebook 3 Specification for Upgrade or Repair
                                            This specification for the Lenovo IdeaPad IdeaPad 3 15IML05 Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the IdeaPad 3 15IML05 boardview and IdeaPad 3 15IML05 schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet,...
                                            09-07-2024, 05:00 AM
                                            Lenovo IdeaPad IdeaPad Gaming 3 15ACH6 Notebook 3 Specification for Upgrade or Repair
                                            This specification for the Lenovo IdeaPad IdeaPad Gaming 3 15ACH6 Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the IdeaPad Gaming 3 15ACH6 boardview and IdeaPad Gaming 3 15ACH6 schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification,...
