UPS ruins batteries every three months
  • davidebaldini
    • Feb 2018
    • 37
    • Italy
    Problem description:
    My UPS requires new batteries every ~3 months; in this time frame, an average of about 5 to 10 power flickers or short power interruptions (< 2 minutes) occur. After an average of 3 months, a new pair of batteries begins to fail to keep the UPS up during any flicker or power interruption. The load it powers is a single computer/workstation running 24/7 with a continuous consumption between 200W to 300W.
    UPS model:
    The Atlantis 1001 is a non-inexpensive (~120€ back then) home/office offline UPS, rated 1000VA, 600W, designed for two 7Ah 12V SLA batteries in series, as per its user's manual. The UPS doesn't run periodic battery tests, and just keeps a float charge while on standby.
    Troubleshooting:
    I opened the UPS while plugged to the mains, powered on, and powering the computer. The float voltage is 26.99V across both batteries, partitioned in 12.85V on the left battery (2.14V per cell), and 14.14V on the right battery (2.35 per cell, see picture). While I took the measures the UPS was not recharging the batteries, these are the float voltages.
    The left battery has a corroded negative terminal.
    The temperature inside the UPS case feels about 30°C (86°F), approximately. The case has a fan, but it is normally off and spins only while on battery power, so the inside remains always warm.
    Interpretations:
    The UPS is designed for 600W, or 600W / 24V = 25A on the batteries (~3.5C). Even with half the load (300W, 12A, ~1.7C) the current on the batteries is quite high. I always bought cheap batteries from eBay, so I imagine this is an overload regime. However, very few power losses occur during the 3 months that a new pair of batteries endures, so I imagine this doesn't justify the short lifespan.
    AFAIK, the float voltage of 26.99V across both batteries is a good value per se, but badly partitioned across the batteries, so that 12.85V causes sulfation on one battery, and 14.14V causes electrolysis on the other.
    The warm temperature also doesn't justify the extremely short lifespan of the batteries.
    • 31051
    Re: UPS ruins batteries every three months
    i could be overcharging them,
    or they could be shit batteries.
    those batteries come in different types.
    you have ones designed to be trickle-charged forever and only discharge ocasionally at reasonable current - for ups/ backup lights etc,
    and you have ones designed to be constantly charged and dumped at high current for use in electric vehicles and such.
    i think if you use the type intended for golf carts, wheelchairs etc, they wont like the constant charging.
    • eccerr0r
      Solder Sloth
      • Nov 2012
      • 8701
      I also have a 1000W UPS that ate its batteries in a year.
      I didn't think to do battery tests when they were working, but need to make sure that the UPS does not charge the batteries past 20.7V, which would be 27.6V for your system. It is okay to go higher but only for a short period of time.
      But back to the reason why for doing battery tests - since you have more than one battery pack, the packs need to be identical and balanced. If one is weaker than the other, then the whole set is as weak as its weakest cell. Agreed that it's possible you have one poor quality pack that ruins it for both. Ideally there's a balancing circuit just like for lithium ion packs... but for lead acid, they don't explode as violently as lithium ion when they're abused...
      • davidebaldini
        • Feb 2018
        • 37
        • Italy
        Further tests:
        I unplugged the two batteries from the UPS; in open circuit, the corroded battery (float-charged at 12.85V) reads 2.5V across its terminals, the other battery (float-charged at 14.14V) reads 12.8V. No doubt, the corroded one is broken.
        I pried open the good battery; looking thru the cell caps, there's a white sponge inside each cell (fiberglass?) so these are non-flooded SLA batteries, which require a slightly higher float voltage than the flooded ones. The sponge looked dry so I added ~80ml of tap water across all cells, or 13ml per cell.
        Now I'm charging the battery with a bench PSU at 18V, 0.6A to gassify the liquid; I read that forcing gassification can clean the lead plates and increase conductivity.
        So, these batteries dried up too quickly in just three months, with an apparently correct float voltage and an acceptable temperature inside the UPS case.
        • eccerr0r
          Solder Sloth
          • Nov 2012
          • 8701
          I've had very poor luck dealing with these AGM/SLAs after they've failed. After watering them they last a little while longer but will fail again soon after, usually shorting out a cell.
          I gave up on my UPS for now after tossing the battery packs, and really need to think about
          a BMS for SLA packs as well...just for longevity.
          • eccerr0r
            Solder Sloth
            • Nov 2012
            • 8701
            I'd also have to add corrosion at a terminal of a SLA is a bad sign...
            • brethin
              • Dec 2008
              • 1907
              Id love to find a case that uses 18650 that allow cell replacement with bms etc same size to replace my 12v lead acid in most ups, i still have tons of 18650s i need to find a use for.
                • Jul 2011
                • 6040
                You can do it but you have to find the right BMS protection board for this to work right
                I have done this myself but I have not found the right BMS board but I did find a work around
                But here is the problem I was using 26650 batteries that the voltage is 3.5 volts fully charged which is only 7.75 ( which means that I used 7 batteries ) batteries this works however the cutoff the BMS protection causes a problem in that if battery runs down to BMS cutoff voltage when power comes back on the UPS dose not come back on you have to power up BMS board manually before it will work again
                You do not need a case for the 18650 batteries but I would recommend that if you can find cardboard battery sleeves you use this type because I do not really like the plastic sleeves because they tear very easily if you use hot glue on them
                If you do use a metal case for the 18650 battery cells make sure that the case fits into the UPS batteries case
                But yes you can use 18650 batteries but it is very important that you use the right BMS protection board and you do some bench testing to make sure that it functions correctly
                I would recommend that you run theses test many times to make sure that your batteries do not over charge / under charge that you are not over currenting the batteries when the UPS is at maximum current and when the UPS turns off because of low voltage at the batteries that when you turn power back on that the UPS turn back on and the batteries are charging
                One final comment but a very important one about this type of battery and BMS protection board
                You MUST make sure that you use batteries that have the same milliamperes testing results and the same run time if possible because if you do not do this step you are going to run into this problem
                Your run time is going to be not very long because ——>
                The battery that charge up first to the voltage cutoff will turn off the charging current to other batteries
                The battery that discharge first to the cut off voltage will turn off the BSM controller
                DO NOT BE TEMPTED to use this type of battery with out a BMS protection board
                This will become very dangerous to life and you could burn down your house
                • CapLeaker
                  Leaking Member
                  • 8186
                  maybe print a case with a 3d printer.
                    • Jul 2011
                    • 6040
                    This would be a good idea if you have access to one
                    Do you have someone or do you have one
                    • eccerr0r
                      Solder Sloth
                      • Nov 2012
                      • 8701
                      There's not really a good way to replace SLA packs with Li-ion (cobalt/manganese) directly without some circuit hacks. Likely you have to get the more expensive Li-ion iron phosphate cells.
                      I need to get more 18650s Li-ion cells to play with...
                        • 31051
                        why not use car batteries in a sealed box with a hydrogen vent hose?
                        • petehall347
                          • Jan 2015
                          • 4427
                          • United Kingdom
                          thats what i do .longer run times too so long as the ups isn't programmed to shut down after x amount of time . i find ones with fans seem to stay on ok .
                          • eccerr0r
                            Solder Sloth
                            • Nov 2012
                            • 8701
                            For the OP, two car or motor cycle batteries will do the job as replacements. For me, not acceptable as I want for cyclic use.
                            • eccerr0r
                              Solder Sloth
                              • Nov 2012
                              • 8701
                              BTW I wasn't thinking about replacing the batteries in my UPS. Mainly because my UPS uses an 18V battery system and that is rife with pitfalls if you don't do 3x6V, sorry if people were thinking that I should re-cell my UPS.
                              I was thinking of a different project
                              • petehall347
                                • Jan 2015
                                • 4427
                                • United Kingdom
                                have a 48v one the batteries died . still need to get 4x car batteries for it . handy thing it is as 2.8kw output
                                  • 31051
                                  it must be huge - is it a rack module?
                                  • petehall347
                                    • Jan 2015
                                    • 4427
                                    • United Kingdom
                                    similar to a large computer case
                                    • Curious.George
                                      • Nov 2011
                                      • 2305
                                      • Unknown
                                      I have a pair of rack-mountable 2200VA units each with an "expansion battery". This was the easiest way to address that load as I could use two 20A 110V branch circuits to power it (without having to go to 220V). It also makes them a lot easier to manage (physically) as each of the four "boxes" (2 UPS + 2 expansion) can be lifted by a single person (under the 70lb limit).
                                      I sited them in such a way that I can make a SHORT cable run through the wall and into the garage to install a larger battery pack, if I ever need longer up-times.
                                      And, by sticking with 48V batteries, I can charge/power them directly from the 300W solar panel I rescued. (I'm ever vigilant for other such panels so I can eventually power the UPSs directly without having the utility involved!)
                                      • carrzkiss
                                        Cyberpower cps1500avr not charging batteries
                                        by carrzkiss
                                        Hello, all.
                                        Cyberpower Battery Backup Unit.
                                        I bought two new ML18-12 batteries through Amazon (They have already refunded my money for the two batteries as we thought the batteries might have been bad.)
                                        When I got them in, they were not fully charged. I connected them to the UPS and waited 24 hours before connecting any networking equipment.
                                        In parallel, they read 24v, but within 24 hours, the meter on the front of the unit dropped from 4 to 3 bars on the battery charge indicator.
                                        Checking the voltage, it was down to 22v.
                                        I quickly removed everything...
                                        06-15-2024, 02:10 PM
                                      • howardc64
                                        Where do repair shops buy MB replacement batteries?
                                        by howardc64
                                        Order my parts from mobilesentrix.com and iPhone batteries have been excellent. Recently got 3x bad A1534 (2015) batteries. All would work until ~30-40+% and drop to < 10% instantly. Typical sign of cheap batteries.
                                        Perhaps the less popular A1534 model's aftermarket batteries are more source limited. Just find it surprising quality from mobilesentrix (usually fairly high quality aftermarket parts) have been so poor.
                                        BTW, this isn't the only defective parts I've had from mobilesentrix. Amongst others including iPad Air touch screen and A1989 touch bar (display was...
                                        07-25-2024, 10:42 AM
                                      • dicky96
                                        HP Laptop TPN-C125 replacement batteries will not charge after 12 months
                                        by dicky96
                                        I got four replacement batteries for these HP laptops about a year ago. The originals would not charge, and these replacements have now gone the same way.
                                        I'm not sure what the expected life of a laptop battery is but I woud have thought they would last longer than that
                                        I now need to order four more batteries. Possibly these replacement ones were now good? The owner does not mind paying a bit more for originals or good compatible batteries that last longer
                                        The top one is the original
                                        Any ideas?
                                        Cheers...
                                        05-19-2021, 07:53 AM
                                      • Astonished
                                        Fixing the Charge Circuit of the Batteries of the DC Motor
                                        by Astonished
                                        Hi friends of electronics
                                        What you see in the video and pictures attached is the circuit for charging the batteries of a DC motor.
                                        The problem is that this circuit cannot charge the batteries (3 1800mAH NiMH batteries) any more. When the circuit was OK, its green LEDs lit up one at a time to show that the batteries have charged more. But now that the circuit is flawed, LEDs light up as you see in the video and at the same time successive beeps are heard.
                                        Please help me fix this circuit.
                                        (the datasheet of the IC: https://pdf.datasheet.live/28...
                                        01-28-2025, 06:24 AM
                                      • dbuergi
                                        DIY: Modified smart charger for all types of batteries
                                        by dbuergi
                                        sometimes i'm in need of a charger / tester for very small batteries and even if my multimeter doesn't show anything there is a chance that a smart charger helps to revieve. I'm happy with my Keenstone smartcharger and i made a small mod just to use it with smaller batteries like in smartwatches or even camera batteries with special contacts.
                                        Soldering wires on the charger contacts and using needles as probes. I covered both with a shrink hose with integrated solder.
                                        My first work was to bring my Samsung watch battery back to life with was not recognized...
                                        07-18-2025, 03:17 AM
