    CyberPower 2200E not switching to AC power (0V output)

    Hi to all,

    I have CyberPower Value 2200E-B UPS which is not bypassing AC input to load.
    When connected and turned on to AC 230V it does not show any error, it passes self test and on display it's shown input & output voltage, batt capacity and load - everything as it should be. Problem is that there is no output voltage (0V!) on any socket (only when connected to AC 220V!) However, when switched to battery power (eg power failure) UPS works normally, it switches to battery and output voltage is stable 220V.

    I've tested all relays and they are OK, (voltage on their coils are 0V when UPS is on AC power). Charging of the battery works.

    Any ideas or schematic would be appreciated.
    Attached Files
  • budm
    Badcaps Legend
    • Feb 2010
    • 40746
    • USA

    #2
    Re: Cyber Power 2200E not switching to AC power (0V output)

    Since the relay are DPDT, are the contacts switching when the relay coil is activated?
    Never stop learning
    Basic LCD TV and Monitor troubleshooting guides.
    http://www.badcaps.net/forum/showthr...956#post305956

    Voltage Regulator (LDO) testing:
    http://www.badcaps.net/forum/showthr...999#post300999

    Inverter testing using old CFL:
    http://www.badcaps.net/forum/showthr...er+testing+cfl

    Tear down pictures : Hit the ">" Show Albums and stories" on the left side
    http://s807.photobucket.com/user/budm/library/

    TV Factory reset codes listing:
    http://www.badcaps.net/forum/showthread.php?t=24809

    Comment

    • emilije
      Senior Member
      • Aug 2010
      • 60

      #3
      Re: Cyber Power 2200E not switching to AC power (0V output)

      @budm

      Sorry for confusing you. UPS is not activating relays when on AC power.

      I've tested relays separately, by giving them known +12V from lab power supply and measuring resistance over contacts. They are tested good.

      Any other hints except relays?

      Comment

      • budm
        Badcaps Legend
        • Feb 2010
        • 40746
        • USA

        #4
        Re: Cyber Power 2200E not switching to AC power (0V output)

        Have to trace the wires from the outlets back to board to see which relays are used for bypassing the UPS when not in batteries mode, the complicate part will be that I believe that this UPS also has AVR (Automatic Voltage regulator using transformer tap switching) to maintain the AC output and will kick into UPS mode when it is out of regulation range or when it detects the lost of the incoming AC.

        Is this the one you have?
        Last edited by budm; 06-21-2013, 12:34 PM.
        Never stop learning
        Basic LCD TV and Monitor troubleshooting guides.
        http://www.badcaps.net/forum/showthr...956#post305956

        Voltage Regulator (LDO) testing:
        http://www.badcaps.net/forum/showthr...999#post300999

        Inverter testing using old CFL:
        http://www.badcaps.net/forum/showthr...er+testing+cfl

        Tear down pictures : Hit the ">" Show Albums and stories" on the left side
        http://s807.photobucket.com/user/budm/library/

        TV Factory reset codes listing:
        http://www.badcaps.net/forum/showthread.php?t=24809

        Comment

        • Elysarian
          Badcaps Veteran
          • Mar 2013
          • 200
          • United Kingdom

          #5
          Re: Cyber Power 2200E not switching to AC power (0V output)

          Is it just me or does there appear to be some scorch marks around the components between transistor Q5 and the buzzer? (BZ1)

          I'd guess that transistor is used to switch the relay next to it - might be somewhere to start?

          Comment

          • budm
            Badcaps Legend
            • Feb 2010
            • 40746
            • USA

            #6
            Re: Cyber Power 2200E not switching to AC power (0V output)

            I cannot tell from the pictures.
            Never stop learning
            Basic LCD TV and Monitor troubleshooting guides.
            http://www.badcaps.net/forum/showthr...956#post305956

            Voltage Regulator (LDO) testing:
            http://www.badcaps.net/forum/showthr...999#post300999

            Inverter testing using old CFL:
            http://www.badcaps.net/forum/showthr...er+testing+cfl

            Tear down pictures : Hit the ">" Show Albums and stories" on the left side
            http://s807.photobucket.com/user/budm/library/

            TV Factory reset codes listing:
            http://www.badcaps.net/forum/showthread.php?t=24809

            Comment

            • emilije
              Senior Member
              • Aug 2010
              • 60

              #7
              Re: Cyber Power 2200E not switching to AC power (0V output)

              Thank you for helping me guys.

              @budm
              yes that's the correct UPS and it has AVR function. Relays you were looking are lower two (NOT the two around the buzzer).

              @Elysarian
              There is no scorch, but some solder flux traces -that part was repaired i can see it how two resistors and diode nearby are soldered together (note that ups was repaired earlier, before i got it. Don't have any info why and was it working after)

              I think that relays are driven by transistors MPSA42 (to-90) which are near relays

              If needed, tomorrow i can provide you better pics of wiring with AVR transformer

              Comment

              • cheapie
                null
                • Jul 2010
                • 849
                • USA

                #8
                Re: Cyber Power 2200E not switching to AC power (0V output)

                Are all the connectors inside making good contact? I had an APC UPS do this once. The cause was a connector inside that had caught fire and burned up.

                Comment

                • emilije
                  Senior Member
                  • Aug 2010
                  • 60

                  #9
                  Re: Cyber Power 2200E not switching to AC power (0V output)

                  @cheapie

                  that was checked first Yes, all contacts are good!

                  Other suggestions?

                  Comment

                  • emilije
                    Senior Member
                    • Aug 2010
                    • 60

                    #10
                    Re: Cyber Power 2200E not switching to AC power (0V output)

                    Hi,

                    So here are pics of transformer and wiring:

                    Wiring goes like this;

                    1 - blue, from the AC input
                    2 - brown, from AC input
                    3 - blue, (thin) from transformer primary
                    4 - white, to output sockets
                    5 - black, from transformer primary
                    6 - yellow, from transformer primary
                    7 - black, to output sockets (for soldering on the board)
                    8 - blue/white wires (on conn) from transformer secondary
                    9 - fan
                    10 - red, (thick) from transformer secondary
                    11 - brown (thick), from transformer secondary
                    12 - blue (thick), from transformer secondary
                    13 - those two thick wires from board goes to the battery

                    Does anyone have a better clue now what could be wrong here and where to start?
                    Attached Files

                    Comment

                    • budm
                      Badcaps Legend
                      • Feb 2010
                      • 40746
                      • USA

                      #11
                      Re: Cyber Power 2200E not switching to AC power (0V output)

                      OK, this is what I come up with:
                      When you apply the AC to the unit, the relay A and B should turn on, relay B and C can be off if the AVR does not kick in, the out will either get the power directly from the L through normally closed contacts of relay C and D or it may select the output form the transformer Black wire if C is ON, or from Yellow wire of the transformer if D is ON. I do not know which one of the transformer wires are for Buck and Boost winding. But as you can see how the L (HOT) get connected to he outlet L.
                      Attached Files
                      Last edited by budm; 06-27-2013, 12:54 PM.
                      Never stop learning
                      Basic LCD TV and Monitor troubleshooting guides.
                      http://www.badcaps.net/forum/showthr...956#post305956

                      Voltage Regulator (LDO) testing:
                      http://www.badcaps.net/forum/showthr...999#post300999

                      Inverter testing using old CFL:
                      http://www.badcaps.net/forum/showthr...er+testing+cfl

                      Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                      http://s807.photobucket.com/user/budm/library/

                      TV Factory reset codes listing:
                      http://www.badcaps.net/forum/showthread.php?t=24809

                      Comment

                      • budm
                        Badcaps Legend
                        • Feb 2010
                        • 40746
                        • USA

                        #12
                        Re: Cyber Power 2200E not switching to AC power (0V output)

                        Here is the relay's switching diagram.
                        Attached Files
                        Never stop learning
                        Basic LCD TV and Monitor troubleshooting guides.
                        http://www.badcaps.net/forum/showthr...956#post305956

                        Voltage Regulator (LDO) testing:
                        http://www.badcaps.net/forum/showthr...999#post300999

                        Inverter testing using old CFL:
                        http://www.badcaps.net/forum/showthr...er+testing+cfl

                        Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                        http://s807.photobucket.com/user/budm/library/

                        TV Factory reset codes listing:
                        http://www.badcaps.net/forum/showthread.php?t=24809

                        Comment

                        • SusiBiker
                          New Member
                          • Jan 2012
                          • 1

                          #13
                          Re: Cyber Power 2200E not switching to AC power (0V output)

                          Hi.
                          Sorry to leap on this thread, but I have one of these Value 2200E beasties too.
                          My problem is that the AVR thinks the mains voltage is wandering between 196VAC and 225VAC. This is causing the thing to do the opposite and energise the inverter.
                          I suspect it may be a dodgy cap somewhere, BUT, if the board is pressed gently with a plastic rod, I can make the inverter switch on and off. This points to a possibility of a dodgy joint as well, er, or just the Cap.
                          It would really help to be able to locate a circuit diagram (schematic). If you do not have one available, could you possibly advise where to buy/get one?
                          I've tried to by one from CPS Europe, but they were not interested in selling one.

                          Any ideas where to look for the fault, or to get hold of a circuit?
                          Thanks,
                          Susi.

                          Comment

                          • mladen82
                            Member
                            • Mar 2009
                            • 39
                            • Montenegro

                            #14
                            Re: Cyber Power 2200E not switching to AC power (0V output)

                            I have identical problem with this UPS.
                            I found near all 22uF/50V caps are bad, and one 47uF/63V.
                            But still problem is exist, no voltage from mains 220V.

                            Comment

                            • mladen82
                              Member
                              • Mar 2009
                              • 39
                              • Montenegro

                              #15
                              Re: Cyber Power 2200E not switching to AC power (0V output)

                              Problem solved!
                              Re-soldered solder joints for all relays on pcb (there are 4 of them). Seems that were cracks in solder. First remove them completely then rework by new soldering.
                              Also replaced all 22uF/50V and 47uF/63V capacitors.
                              Last edited by mladen82; 08-30-2013, 03:37 AM.

                              Comment

                              • mladen82
                                Member
                                • Mar 2009
                                • 39
                                • Montenegro

                                #16
                                Re: Cyber Power 2200E not switching to AC power (0V output)

                                Unfortunately, UPS come back for repair.
                                Same problem.

                                I found that -15V voltage is actually -10.5V. Checked all components in circuit for generating -15V but all seems ok.
                                I can't find out why this voltage is not good, its not voltage regulated, no regulator, delivered by LM324 op amp probably some pwm configuration.

                                I doubt that PCB maybe since is double-side have some bad via connections.

                                ps. i have schematic and service manual so anyone if need, contact by pm.
                                Last edited by mladen82; 09-10-2013, 05:34 AM.

                                Comment

                                • budm
                                  Badcaps Legend
                                  • Feb 2010
                                  • 40746
                                  • USA

                                  #17
                                  Re: Cyber Power 2200E not switching to AC power (0V output)

                                  Up loading the service manual will be better so any one here needs it can just download it.
                                  Never stop learning
                                  Basic LCD TV and Monitor troubleshooting guides.
                                  http://www.badcaps.net/forum/showthr...956#post305956

                                  Voltage Regulator (LDO) testing:
                                  http://www.badcaps.net/forum/showthr...999#post300999

                                  Inverter testing using old CFL:
                                  http://www.badcaps.net/forum/showthr...er+testing+cfl

                                  Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                                  http://s807.photobucket.com/user/budm/library/

                                  TV Factory reset codes listing:
                                  http://www.badcaps.net/forum/showthread.php?t=24809

                                  Comment

                                  • mladen82
                                    Member
                                    • Mar 2009
                                    • 39
                                    • Montenegro

                                    #18
                                    Re: Cyber Power 2200E not switching to AC power (0V output)

                                    I think that finally find root cause of problem.
                                    It is a NPN transistor MPSA42 in TO-92 package (Q9) that drive main relay, precisely there are two of them but only one was bad (diode test-open circuit both base-emiter, base-colector).
                                    I change both MPSA42.
                                    UPS works for now, will test couple of days.

                                    Comment

                                    • larrymoencurly
                                      Badcaps Veteran
                                      • Oct 2004
                                      • 960
                                      • USA

                                      #19
                                      Re: Cyber Power 2200E not switching to AC power (0V output)

                                      Originally posted by mladen82
                                      I think that finally find root cause of problem.
                                      It is a NPN transistor MPSA42 in TO-92 package (Q9) that drive main relay, precisely there are two of them but only one was bad (diode test-open circuit both base-emiter, base-colector).
                                      Does it have a protection diode across it or the coil? My brother had a car with a relay controlled by a 555, and every few months it would blow its driver transistor rated for 300-400V. No more failures after a 600V diode was soldered across the relay coil.

                                      Comment

                                      • Brandi008
                                        New Member
                                        • Jan 2018
                                        • 5
                                        • Switzerland

                                        #20
                                        Re: Cyber Power 2200E not switching to AC power (0V output)

                                        Hello everyone,
                                        I have a CyberPower Value 2200E that have the problem of charging the battery. Checking the electrolytic caps and find the same as Mladen82 : most of the 22uF/50V were defect, especially C3, C37, C39 and C41 that have about 13uF instead of 22 , ESR of 150 ohms and a Vloss of 30% ! As I was on the way, I've changed all the electrolytic caps. Then the unit work again.
                                        I was wondering why this 4 caps were so bad. Except C3,they physically are located near the L7815CV (+15Vdc) regulator. It has a heat sink. I found this become quite very hot. I've put a temp probe and measure near 80°C ! I've then tried to put a little fan to cool and get max 40°C at normal work, much better. It is right the cooling is not the strong point of UPS's, but with a little modification (I'm on to build), I'm sure this will extend the life of my UPS.
                                        The +15V is mainly use to drive the relays. Current is about 67mA each. At minimum 2 relays are active (up to 4 in boost mode).

                                        @mladen82 : thanks for the service manual.

                                        I've also notice that -15Vdc is around -10Vdc. Do not know if this is right or not. Like Mladen82 explains, there is no regulator for this -15Vdc.

                                        @Larrymoencurly
                                        There is no diode on the relay's coil, but a 10k resistor.

                                        Regards,
                                        Brandi008

                                        Comment

                                        Related Topics

                                        Collapse

                                        • sam_sam_sam
                                          Modification to a ZD-987 desoldering/soldering station using a external switching power supply
                                          by sam_sam_sam
                                          I have been working on this concept for quite some time now with limited success but recently I found a switching power supply that is setup for the voltage that this soldering station needs to operate at however it also needs part of the secondary circuit from the original switching power because you need several voltage rails

                                          I once tried to get a ZD-915 desoldering station to work on a 18 volt battery power supply but unfortunately things did not go well but I did find a work around but I might try this idea again but going at a little differently more about this another time...
                                          07-01-2024, 06:34 AM
                                        • Tynan Dill
                                          Vizio e601i-A3 - Has Sound and Display, But No Backlight - Bad Power Supply Board or Bad LED Bulbs ?
                                          by Tynan Dill
                                          I was given this TV from my great uncle. He said it just wouldn't turn on one day out of nowhere, replaced the TV, and gave it to me to possibly fix and use for myself.

                                          Upon bringing it home and plugging it up, it showed a standby light.

                                          I powered it on and without a flashlight, the display showed the "V" but the lighting is very dim, but visible.

                                          The screen seems to blackout and stay black, but with a flashlight I can see the display.

                                          With my Playstation 4 connected via HDMI, and running a game I can hear sound.

                                          Assuming...
                                          11-22-2024, 01:46 PM
                                        • PantherDave
                                          Microsoft Surface Pro (5th gen) model 1796 - no power
                                          by PantherDave
                                          Hi all!

                                          I'm trying to troubleshoot a Microsoft Surface Pro (5th gen) model 1796 that won't power on. Motherboard model is M1007506-015. My priority is retrieving data, but the SSD is integrated so it looks like if I can't repair it it'll need to go to a data recovery company. I've done a little basic board repair before, but nothing this advanced until now. So please forgive my ignorance in advance. 😅

                                          I found the boardview for this laptop in the forums here, and am able to open it on my PC with FlexBV.
                                          https://www.badcaps.net/forum/troubl...-hardware-devi...
                                          05-29-2024, 02:01 PM
                                        • sam_sam_sam
                                          Desoldering gun station modified to use a 18 volt @ 20 amp switching power supply
                                          by sam_sam_sam
                                          I have wanting to do this project for quite sometime now and I finally found a switching power supply that will work on this desoldering gun station ZD-915 that the original switching power supply took a shit and just was not worth trying to fix it because this switching power is not quite big enough to handle the heater element and the vacuum pump

                                          One note when I tested the switching power supply and the voltage control board I noticed that this desoldering gun heat up much faster than the original switching power supply which I was really surprised by to the point that I might buy...
                                          03-31-2024, 02:12 PM
                                        • sam_sam_sam
                                          DVR camera recorder switching power supply capacitor failure really
                                          by sam_sam_sam
                                          These cheap non brand capacitors at it again

                                          Last night we had a power outage [ long drawn out trying three to come back up before going out completely ] and when I went to turn the DVR camera recorder back today no go 3 bad capacitors ( one capacitor no ESR reading on DVR board the other 3 capacitor on the power supply board over 40 ohm this is not a misprint ) on the external switching power supply and one capacitor on the DVR camera recorder board where the power supply that goes to the hard drive disk is

                                          Well at least I have the cameras back on line I to try the...
                                          01-22-2022, 06:28 PM
                                        • Loading...
                                        • No more items.
                                        Working...