Microwave Issue

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • momaka
    replied
    Re: Microwave Issue

    Isolation and MW transformers are quite different, though.
    Because MW traffos have to handle a lot of power while still trying to make them fairly compact, manufacturers usually keep the number of primary (and thus secondary) turns a bit small. This, however, lowers the inductance (and resistance) of the transformer's primary, which causes fairly large current to be drawn even at no load. For this reason, MW transformers also aren't usually rated for continuous duty cycle. On that note, most "long" MW cooking presets typically switch the MW to "medium" power - i.e. they cycle the transformer on and off periodically to allow it to cool. If you leave a MW transformer plugged into the wall continuously, even with no load, it will eventually overheat and burn itself out.
    Last edited by momaka; 03-03-2019, 03:36 PM.

    Leave a comment:


  • R_J
    replied
    Re: Microwave Issue

    If you are drawing 6 - 7 amps unloaded, Thats a bit high, unloaded it will draw a couple amps.

    I just went and check one that I have, it is for 110vac input, and it draws just under 2 amps unloaded.

    I also checked it with a lamp in series and it does light up quite a bit, so I was wrong in post 15

    Just for comparison I also check a regular isolation transformer I have and unloaded it was 300ma.
    Last edited by R_J; 03-03-2019, 01:17 PM.

    Leave a comment:


  • sam_sam_sam
    replied
    Re: Microwave Issue

    Originally posted by R_J
    If no current clamp try an incandescent lamp in series with the primary, if the lamp lights up and stays lit, you have a shorted transformer.
    Not exactly because this is high current transformer

    When you power the transformer up with no load your amperage might be around 6 or 7 amp and your transformer should be humming a little bit

    If when you use a incandescent light bulb in series with transformer it might start off being real bright and then reduce brightness a little bit

    This is only going to tell you that you do not have an open transformer and not much else
    Last edited by sam_sam_sam; 03-03-2019, 12:21 PM.

    Leave a comment:


  • Per Hansson
    replied
    Re: Microwave Issue

    Well, it's a step up transformer with roughly a 1:10 ratio I would assume.
    So 2.3kV output with 230v input.
    So if you feed it 24vac on the primary you should see around 240vac on the secondary...

    As for the magnetron heating element that is only ca 3v with 240vac on the primary.
    So that is safe to measure without a high voltage probe.
    (Well, safe as in if you make a mistake and measure the wrong secondary you blow up your meter but as you are working with a microwave I better hope you already understand the risks involved!)

    Leave a comment:


  • R_J
    replied
    Re: Microwave Issue

    If there is a short in the secondary it will show high current on the primary

    Leave a comment:


  • jamesmcuk
    replied
    Re: Microwave Issue

    I have a current clamp so will try that. However by the noise it's making I would suspect it's ok on the primary as it started to make the much louder buzzing having replaced the HV fuse. I would suspect if anything a broken secondary but I dont have a meter or other bits to test it properly. Thanks for the reply.

    Leave a comment:


  • R_J
    replied
    Re: Microwave Issue

    If you have a current clamp, disconnect the cap, diode, & magnatron and check the curent draw on the primary, it should be almost 0, If no current clamp try an incandescent lamp in series with the primary, if the lamp lights up and stays lit, you have a shorted transformer.

    Leave a comment:


  • jamesmcuk
    replied
    Re: Microwave Issue

    Once again thanks for all the replies and detailed responses. I have checked the magnatron for signs of arcing and there is none. I have tried shorting the cap after trying cook and noting happens, no spark. The cap tests out as working with my meter as I say. The only component I haven't tested is the transformer which is the bit that I think is making all the noise. I have looked at replacement caps and the diode is on the other terminal to mine does it make any difference? I guess I am going to try and test the secondary winding of the transformer.

    Leave a comment:


  • desert-rat
    replied
    Re: Microwave Issue

    You can check the pri and sec power trn. with the wires off. The ovens I have checked have had open pri. trn. Its cheeper to get a new oven than a power transformer .

    Leave a comment:


  • sam_sam_sam
    replied
    Re: Microwave Issue

    You can also check the Magnatron output with a small cfl tube inside the microwave oven
    You should only use one that is only about 2” long with the terminal end taped if the magnetron is working the cfl should glow if it does not then it is bad

    One note this should not be more than 30 seconds at time and the cfl should be in center of the turn table

    You need to use caution when doing this test
    Last edited by sam_sam_sam; 02-23-2019, 06:42 AM.

    Leave a comment:


  • momaka
    replied
    Re: Microwave Issue

    Thank you for the detailed info, redwire!
    Learning something new every day.

    Leave a comment:


  • redwire
    replied
    Re: Microwave Issue

    I would say that's not right because the circuit is a half-wave voltage doubler and it does not output pure DC.

    If you use a scope and HV probe, you will see 1/2 wave pulsating DC from +11V to -4,000V. If the magnetron is open-circuit, the no-load voltages go much higher than (loaded) 2kV out of the transformer. The portion of the sine-wave where the cap is charged is also not seen then.

    Really good information for microwave oven repair is here: https://repairfaq.org/sam/micfaq.htm#mictstmag

    snippet from Testing the Magnetron:

    A magnetron with an open filament will result in no heat but no other symptoms. The bad connection may be internal (in which case the magnetron will need to be replaced) or external at the filament terminals (which may be repairable).

    A magnetron with with a short between the filament/cathode and anode will likely result in a loud hum from the HV transformer and/or magnetron when the cook cycle is initiated but the main fuse will probably not blow. However, note that the actual wattage drawn from the power line will probably be much lower than under normal conditions. Although there will be a high current flowing in the HV transformer secondary through the HV capacitor (likely causing a loud hum or buzz), the real power consumed will be reduced since the current and voltage will be out of phase (due to the series capacitor) and the power factor will be low. A reading on an AC line wattmeter of 300 W compared to the normal 1,200 to 1,500 W would be reasonable.
    Attached Files
    Last edited by redwire; 02-20-2019, 09:44 PM.

    Leave a comment:


  • momaka
    replied
    Re: Microwave Issue

    You can check the high voltage with a regular multimeter if you build a proper resistor divider circuit.

    Assuming the output voltage should be around 2000V, ten 100 kOhm resistors in series will divide the voltage so that each has about 200V on it. So if you measure, let's say, 226V across a resistor, then the voltage is likely somewhere around 2260V (i.e. 10x that value, more or less, assuming all resistors have close to 100 kOhm resistance.)

    Now here is one important consideration when building such voltage divider circuits: power dissipation. With 200V across each resistor, the expected power dissipation, Pd, will be (200^2)/100000 = 40000/100000 = 0.4 Watts. So you will need resistors rated for at least 1/2 Watts each. And if the expected output voltage is double (i.e. 4000V), then the resistors power rating should be quadrupled - i.e. use 2W resistors.
    Last edited by momaka; 02-20-2019, 09:17 PM.

    Leave a comment:


  • R_J
    replied
    Re: Microwave Issue

    Check if you have high voltage, I doubt your meter can measure over 2000 volts so, you can dissconnect the magnatron high voltage lead, turn on the microwave for a few seconds, turn it off and see if the capacitor charged by checking if there is any voltage on it either with your meter or by shorting it with a screwdriver. or you can place the high voltage lead about a 1/4 inch or less from ground and see if it produces an arc when turned on.
    But I suspect the magnatron is bad. you can't check a magnatron, you can only check if the filament is open or shorted to case.
    wave guides don't go bad.
    Last edited by R_J; 02-17-2019, 11:41 AM.

    Leave a comment:


  • jamesmcuk
    replied
    Re: Microwave Issue

    Thanks for the replies guys. I have as you note Ruky checked all the items bar the secondary transformer winding on the HV circuit and they appear to test OK but thats not to say the cap which is reading correctly isn't breaking down under 2kv.

    Mag is giving me 0.19 to 0.2 on filament and open circuit filament to case but I haven't tried banging on it or removing it to check for damage so I will do that today.

    I have read people saying the waveguide could be faulty but I am not sure how, isn't that just a metal guide?

    Thanks again.

    Leave a comment:


  • RukyCon
    replied
    Re: Microwave Issue

    You should also check the capacitor as i've had many microwaves stop working because of it.

    Edit: realised you may have already have done that.
    Last edited by RukyCon; 02-16-2019, 07:28 PM.

    Leave a comment:


  • redwire
    replied
    Re: Microwave Issue

    +1

    The majority of magnetrons are 3.3VAC >10A filaments, so with the transformer disconnected expect under 0.33 ohms.
    I would check continuity from filament to housing and tap it, bang it a bit. What may have happened is the magnetron filament arced and later popped the HV fuse but now the filament short-circuit has cleared, vanished.

    Toshiba Magnetrons for Microwave Ovens has some datasheets etc. if you know the tube number.
    Attached Files

    Leave a comment:


  • Sparkey55
    replied
    Re: Microwave Issue

    Check for continuity of the tube filament; could be open.

    Leave a comment:


  • jamesmcuk
    replied
    Re: Microwave Issue

    Hi, Thanks for the reply. its a whirlpool jq280 which is not common here in the UK but I do have this link https://www.manualslib.com/manual/98...?page=5#manual


    I agree about replacing parts but I did the diode as its was cheap and as you say something difficult to test with a DMM. I do think the old one was probably good though looking at the DMM readings.

    The diode has crimped on tags that are different so its defo in correctly. I haven't yet removed the magatron so maybe thats the next step to see if there is any sign of arcing?

    Thanks again

    James

    Leave a comment:


  • redwire
    replied
    Re: Microwave Issue

    Can you give us a make and model number, that helps for the schematic.
    Some microwave ovens use both a rectifier and a protection (across capacitor) diode.

    If the new HV fuse is not blowing, then something has changed and gone open-circuit. So looking for shorts or breakdown is second on the list.

    A microwave oven rectifier diode is usually high voltage drop ~11V due to the stack of diodes inside. So you cannot test it for open with a multimeter unless you have a power supply or a couple 9V PP3's.

    When repairing things, it's best to track down and find the failed part instead of just replacing parts. One failed part can damage others and a person can get lost with what the original problem is.

    I would ensure the new diode is the right part and in correctly, was the old one good. Inspecting the magnetron for evidence of arcs, as that may be what originally popped the fuse.

    Leave a comment:

Related Topics

Collapse

  • drykid
    Matsui 175S microwave fuse replacement
    by drykid
    Hi,

    I recently picked up a used Matsui 175S microwave that was powering up (starts, turntable rotates) but not heating. From looking online the most likely culprit was the fuse, but unfortunately in this one the fuse had heated up and fused with the (badly designed) fuse holder and couldn't be removed. I guess this might indicate further issues beyond the fuse itself but at this stage I just want to replace the fuse and see how I go from there.

    Anyway since I couldn't get out the fuse itself the easiest fix was to replace the fuse holder assembly that runs between the...
    12-21-2020, 01:15 PM
  • corrize
    A funny fuse story – Lumix LX100 II
    by corrize
    Hello, I disassembled this dead camera, and found this WTF… Two fuses soldered one above the other !
    I was pretty sure nobody touched it before, but that can't be from factory. There is flux, and capacitor is probably missing.
    The other weird thing : the fuses are « G » fuse : (0.75A – 8V), seems very low. The original fuse should be « O » : (32V 2,5A).
    There is « O » mark beside. All fuses have the same mark letter on main board. So, I can deduce it's a « O » fuse.
    And this correspond to the issus I saw : when I plug the battery, I measure the voltage dropping...
    10-19-2023, 09:58 AM
  • ugamazing
    Three 820-01700 32GB Logic Boards Same Issue: Won't Wake From Hibernate
    by ugamazing
    I have three identical-spec 820-01700 boards (2.6/32/512), and ALL THREE boards came to us with the same fault, from different sources: The boards don't wake from hibernation with the keyboard or lid, they ONLY wake when you press the power button. I understand this is a very minor issue, but the boards must be fixed!

    We will of course begin with the obvious (checking lid signals), but I couldn't help but notice these three boards were all 32GB variants. Has anyone noticed an issue relating to these 32GB boards in particular? I of course don't think it's a RAM issue, but it's bizarre...
    12-17-2024, 07:05 PM
  • tvguy12012012120
    Zombie Samsung UN55NU6900F dead / no standby voltage - randomly came to life after hours of troubleshooting then died
    by tvguy12012012120
    This is my first attempt at troubleshooting a board like this, I know I could just buy a new board but I'm curious to figure out how this works. I've been testing different components in the evenings this week and I think the problem is with the IC failing to start up for some reason. When the board is plugged in there is no standby voltage.

    Then today it randomly sprung to life like a zombie but shortly died thereafter. I have no idea why it would have done that and its the first time I've seen it running. I discharged capacitors on the board last night, then it was sitting today....
    02-07-2025, 05:13 PM
  • asr
    Finding replacement diode iPad Pro 3rd gen A1701
    by asr
    Hello, I am looking for help to replace a damaged diode. The tristar was replaced and a diode was damaged in the process. I have a picture of the diode but dont have an exact donor. I mostly have macbooks for donors and only a few ipad and iphone boards. Diode part number: DSF01S30SCAP
    Im not sure where to find the ipad board number. Anybody have an idea where else this diode is used on other boards? Thanks....
    07-09-2024, 06:24 PM
  • Loading...
  • No more items.
Working...