Wine and Beverage Cooler Control Board Repair Attempt
  • KYBOSH
    • Oct 2011
    • 581
    • Unknown
    I started taking a look at the big transformer. I measured 162v going into the primary windings but nothing coming out. Grabbed my blue ring tester and checked it. Primary side looks very good. Green lights/ Hi Q. Primary side gives me 2 red lights which is meant to mean bad or low Q. The marking in this transformer is EF20. Not sure what its specifications are...couud be 24v?
    • KYBOSH
      • Oct 2011
      • 581
      • Unknown
      Originally posted by KYBOSH
      Thanks for the tip! I studied up on decoupling capacitors last night.
      You are correct by the way: 105 is code for 1uF. I think i change out C8 and C10 for fresh ones.
      The other ones seem to be rated for 100 nF so I will swap out C2 and C15 for fresh ones as well.
      I'll check for voltage after I get those sorted.
      Correction: C15 is labelled 102 (1nF) and not 100 nF as i previously mentioned above.
      • KYBOSH
        • Oct 2011
        • 581
        • Unknown
        Thinking this over I realized that the transformer was good as it was the one supplying the lower voltages to the board and a secondary with fewer winding will give a low-Q reading on the Ring Tester.
        The next thing I did last night was check the octocoupler to ensure that it was good.
        When I tested leads 1 and 2 with my multimeter in diode mode it tested good.
        I checked leads 3 and 4 and it was giving a strange reading. Its a Sharp PC817.
        I pulled it out of circuit and tested it again but it read good. The readings I was getting was from the lines it was connected to.
        I put the OC back in circuit and decided decided to check if the connectors had any voltages across them and I was pleasantly surprised to see I was getting voltages to all of them.
        Click image for larger version  Name:	Screenshot 2024-08-15 at 6.02.42 PM.png Views:	0 Size:	7.10 MB ID:	3330130
        So apparently the board is working for the most part. The 120VAC goes inside the fridge and not directly to the compressor. I am not sure where it goes or what its supposed to be powering though.
        The next thing I am going to test is the Start Relay for the compressor. It maybe bad and it may act as a switch that will shut the whole system down if it its.
        Im now working off the assumption that something off the board is bad and causing it to shout down. I tried pulling connectors off 1x1 in hopes that disconnecting the offending component would let the rest of the system start up but that didnt seem to add any clues.
        Again the issue i am currently having now is the system never powers on. It makes a short beep (solid beep rather than a fading one) when plugged in but no sign of life at all.
        Edit to add: The resistance of the starter relay is 5.3Ω which is said to be GOOD so its not the relay.
        • KYBOSH
          • Oct 2011
          • 581
          • Unknown
          Gotta a question...
          The scheme here shows a "transformer" being connected to the Control PCB .... Does this mean there is an external transformer somewhere on this fridge? Not the little transformer (T1) in the board....
Name:	Screenshot 2024-08-15 at 7.14.58 PM.png
          • KYBOSH
            • Oct 2011
            • 581
            • Unknown
            I went back to track what the wires were for the AC connectors. The one with 120VAC and 1.8VAC on when the PCB is on my bench seem to be the heaters. Makes sense since they lead into the fridge unit.
            This is wrong. The heater should not be on by default but rather the compressor. I tested the relay labelled JK2 out of circuit and it tested good. I will check JK3 tonight to see how it fares.
            Looks like my issue is indeed with the board as its not powering what it should be powering in its default state (off the appliance).
Name:	Screenshot 2024-08-15 at 8.09.13 PM.png
            • redwire
              • 3912
              You might be on a goose chase - I can see two (snubber) capacitors that are likely across the relay contacts, to suppress arcing on them.
              So a multimeter will read ACV from the leakage current.
              These boards usually collapse due to the electrolytic capacitors failing. They are cheap to begin with and run 24/7. I would test on the primary side, some in the pic look like rounded tops? Like EC6. Carefully discharge them if needed.
              The rails might look ok but fizzle out with say the LED loading.
              • KYBOSH
                • Oct 2011
                • 581
                • Unknown
                #27
                Thanks for the guidance RW. I thought I was all alone on an island for a second!
                I followed your lead and tested the caps on the primary side for capacitance and ESR (for the electrolytics).
                This is what I found out (ratings on top/measured readings on bottom):
Name:	Screenshot 2024-08-16 at 11.17.08 PM.png
                The electrolytic caps are manufactured by LSCON. The datasheet (which was a little hard to find) says that they have a tolerance of ±20% so we are well within spec on these plus the ESRs are pretty low at these capacitances.
                I dont have a pair of replacement 10uf/400V caps on hand (just 1) but I will likely replace them with a better brand just to rule them out as the problem. As you say they may look good but underload they are failing.
                The "snubber" capacitors are also looking really good too. I see no reason to replace them unless you advise otherwise.
                • redwire
                  • 3912
                  Those values look OK but EC6 is a bit rounded top looking. You have +5V and +12V power but the board still acts dead? Did you test the secondary caps as well? The two large ones.
                  I found it as Zephyr Wine Cooler Control Circuit Board GB-KB3100-MAIN-V3.1
                  Main Power Control Board 11010114 ripoff pricing
                  • KYBOSH
                    • Oct 2011
                    • 581
                    • Unknown
                    #29
                    Yes! The board is very expensive for what it is.
                    This is the reason why these appliances are discarded rather than repaired and that's a pure shame.
                    But the going price of these models are over $1000US (new) locally so it's worth repairing in my opinion.
                    At the VERY least its worth the effort to rectify the defective board if possible.
                    The cap that you say is bulging really isn't bulging much, if at all, and the appearance is really more a product of the camera angle and lighting but to make you happy RW I am replacing it with one that has a completely flat top and a capacitance of 9.76µF and an ESR or 2.1Ω.
                    I tested the secondary electrolytic caps and this is what I got:
Name:	Screenshot 2024-08-17 at 1.43.19 PM.png
                    Yes, EC11 was very bad. I changed all 4 of these caps in the group with caps that averaged 105µF and 0.61Ω ESR.
                    I made EC13 a 100µF 50V bcos i didnt have a stock replacement with long enough legs to bend.
                    I also checked the last relay JK3 and it tested good.
                    When I plugged up board it STILL DIDNT fire-up.
                    Same behavior.
                    • KYBOSH
                      • Oct 2011
                      • 581
                      • Unknown
                      #30
                      I'm turning my attention back to the D7 diode next to the transformer.
                      It caught my eye today bcos it looked like it had a small crack on the surface.
                      It was always giving weird readings when i tested it with the multimeter but I attribute that to the caps right next door.
                      When I test it out of circuit I recall it read okay.
                      Click image for larger version  Name:	Screenshot 2024-08-17 at 2.56.43 PM.png Views:	0 Size:	1.96 MB ID:	3331280
                      Hard to make out the markings but i think its a STPS 3150 which is a 150 V, 3 A power Schottky rectifier.
                      I dont have a direct replacement so I'm researching which one of the diodes i have maybe a good substitute for it.
                      • R_J
                        • 9629
                        I checked for voltage going to the relays.
                        JK1 has 11.5v going to it, while the others (JK2 and JK3) have none.
                        This is from post 20, if this is true then you have a broken trace between the +12v on JK1 and where it connects to JK2 then on to JK3. Look at the circuit traces, all 3 relays have one pin connected to +12 volts and the other pin is connected to IC3 which controls the relays. Plug X6 should have +12dc on pin1
                        Why keep checking the power supply? it is working! The diodes capacitors etc. are all working there is no need to replace them, you will just end up destroying the power supply section.
                        The so called crack you see is just a plastic molding mark
                        • KYBOSH
                          • Oct 2011
                          • 581
                          • Unknown
                          #32
                          Wow.. Thank you very much R_J.
                          Your diagram of my PCB is better than what I am doing.
                          I have to step my game up!
                          Regarding checking and rechecking components on the board I wanted to ensure that I am thorough as possible this 2nd time around (recording readings, etc) and that i did not miss anything.
                          My cursory checks are often with components in circuit. Or if i ddi take them out i dont write down my findings.
                          Redwire also mentioned that everything can look good on the bench but when the board is put underload it fails.
                          I have already found a bad cap which i have overlooked today.
                          But there is truth in what you advice... constant soldering and desoldering runs the risk of ruining the board.
                          Once measurements are recorded i will not have to take them out of circuit again if they are found to be good.
                          Regarding the +12V traces and positive leads on the board all have continuity as I just ran down to the bench and checked.
                          When i checked whether they had voltage or not I checked the + and - leads of each of relay.
                          The UN2001D driver (IC3), for some reason, is not providing ground for JK2 and JK3. I believe this signal to provide ground should be on by default or come from the main IC (IC1).
                          If not on by default it must be waiting for a signal/trigger from one of the connected accessories.
                          But as I mentioned there is 120V going to the internal heater coil as soon as the board is connected to the mains (this is connected to the JK1 relay which is powered on as automatically).
                          That seems wrong to me...
                          At no time during my testing have i seen JK2 or JK3 cut on.
                          • R_J
                            • 9629
                            Check U3 pins 1,2 & 3 using pin4 ground, that will tell you the state of the outputs from the micro ic1 It may be that when ic3 shorted it damage ic1 port
                            • KYBOSH
                              • Oct 2011
                              • 581
                              • Unknown
                              #34
                              when i measure the resistance as you instructed i get ~14.8 kohms on pins 1. 2 and 3 (against pin4 ground)
                              • R_J
                                • 9629
                                Resistance does not turn on the ic, you need to check the Voltage on those pins, I suspect pin 3 will be high indicating that driver is turned ON causing JK1 to be activated
                                • KYBOSH
                                  • Oct 2011
                                  • 581
                                  • Unknown
                                  #36
                                  Sorry about that... i thought we were looking for an internal short of some sort in IC1.
                                  So when the board is not plugged into mains there is no continuity on any of the 4 pins as I mentioned before.
                                  But when the board is plugged in and activated you get 0V (actually shorted to ground) on pins 1 and 2 then 1.75V on pin3.
                                  • R_J
                                    • 9629
                                    The microprocessor is outputting 1.75 volts which turns on the ic3 driver pin3.so either the micro output for that pin is bad or the program is turning on that pin to turn on the heater, maybe a bad sensor is causing the problem.
                                    This fridge has two zones correct, a left zone and a right zone, It should then have two separate sensors, so I would find a way to switch the sensors on the board and if one of the sensors is causing the problem it should turn off JK1 and turn ON JK2. Or maybe try unplugging both sensors and see what the relays do.
                                    Which plug do the sensors connect to?
                                    • KYBOSH
                                      • Oct 2011
                                      • 581
                                      • Unknown
                                      #38
                                      Im a complete laymen when it comes to microprocessors Im affraid.
                                      Micro output is internal to the microprocessor?
                                      Also which sensor would you referring to?
                                      Remember the PCB is sitting on my bench and the only thing that is connected to it is the mains power line.
                                      So there would be no input from any sensor it would normally be connected to when hooked up to the fridge.
                                      What would be the next step to rectify or at least verify your ideas here?
                                      • R_J
                                        • 9629
                                        Well without a sensor connected to tell it the temperature, it may think it needs to turn on the heater? I guess at this point you may need to install it back into the fridge to see what it does.
                                        here is a similar fridge controller wireing diagram
                                        • KYBOSH
                                          • Oct 2011
                                          • 581
                                          • Unknown
                                          #40
                                          So when I connect the board to the fridge and power it up I get a short beep from the surface mounted speaker and that's it. No sign of life after that. But I will connect everything up and take voltage readings this time.
                                          Will let you know how it goes in the morning.
                                          Thanks for the assist and brainstorming session (mostly your brains!)
                                          • edugimeno
                                            Wine cooler flickers at startup and doesn't cool enough
                                            by edugimeno
                                            Hi there!
                                            I have an old wine bottle cooler, it's a basic peltier cell system with a power supply built in with the controller board, with a simple display at the front door and 2 push buttons to select the desired temperatura.
                                            Symptoms are it doesn't barely cool down, and makes a chirping noise at the board.
                                            Both fans on each side of the peltier are (now, after much cleaning) running smooth and silent
                                            When you turn it on, the front 7-segment display flickers for a variable time, usually like 1 minute but sometimes nothing or 3 minutes... Then turn on solid (but still some...
                                            03-01-2025, 04:51 AM
                                          • watergremlin0
                                            Wine Cooler CD-110-B
                                            by watergremlin0
                                            Anyone have an experience with this board? Ive actaully replaced 2 caps on it before. Worked for a few years. However this time around they all seem good. Ive pulled a few and tested they all test in range. Checked a few of the diodes they all seem good. dont see any popped resistors or anything. The light and screen power on however the fans never kick on. Havent found a skematic for this board however my guess would be a component in line with the fan.
                                            06-18-2024, 08:03 PM
                                          • Yanleb
                                            LG 60PK550 Logic Control Board EBR63450301
                                            by Yanleb
                                            Hi all, I just want to share the repair of my 60PK550-UA TV set.
                                            The TV set was powering on, just no image. After verification, nothing wrong on the YSus or ZSus boards. Nothing wrong on the main board either.
                                            But I noticed that the LED was not flashing on the Logic Control Board. This is an EBR63450301. The LED is supposed to flash even with all the flat cables disconnected, with only the power cable attached.
                                            All the voltages measured at the electrolytic capacitors on the board were good. From top left to bottom right:
                                            C57: 3.30V
                                            C61:...
                                            07-20-2023, 12:38 AM
                                          • BleedCap
                                            OLD Socket 478 custom bracket + NEW generic cooler
                                            by BleedCap
                                            I already posted this on vogons.
                                            Its a 3d printed custom bracket for socket 478.
                                            I used this AM4 bracket as a base design.
                                            Its to be use with cheap generic clip based cpu cooler.
                                            Reason for doing this is:
                                            - Its hard to get/find a good copper base cooler. Even if you find one, the price is ....
                                            - New generic cooler is cheaper and can use bigger fan (less noise)
                                            I tested the bracket with cheap chinese horizontal cooler + fan taken from CM hyper 212 evo.
                                            The processor that I was using is P4 2.4Ghz prescott....
                                            11-05-2023, 08:09 PM
                                          • harp
                                            triac phase control 0-100%
                                            by harp
                                            Trying to understand which properties of circuit affect triac phase range, is it possible to control near whole period, or it have some limitations - on net found a couple circuit, that claims almost full control, but in the past I build some simple circuit and remember that it do only half of control over triac?...
                                            06-02-2024, 09:00 AM
