AC to Ground?
  • EasyGoing1
    Shock Therapist
    • Sep 2016
    • 977
    AC to Ground?
    OK, I'm not asking if this is a good idea ... cause I know it's not ... but I am curious ...
    IF you connect the supply side of an AC line to a circuit and the other side of the circuit to earth ground ... will it power up?
    sigpic
    • 31283
    Re: AC to Ground?
    it should, but it will trip any RCD or GFCI on the circuit.
    • dmill89
      • Dec 2011
      • 2534
      Re: AC to Ground?
      Yes, unless as stj stated the circuit has GFCI protection, however you will potentially make the entire ground circuit in the building "live" in the process (although current limited by the device, i.e. something like an LED lightbulb would only be a few mA, while something like an electric heater or toaster 10A+ which could give a nasty shock, anything that is metal and grounded could now potentially be "live", though current will take the path of least resistance so it depends on the distance the load is from the panel, and how conductive whoever touches it is if they would get a shock or not). In the US electrical system neutral and ground are bonded at the main panel, however ground is intended as a "safety" in the event of an electrical fault and should not be made used as a neutral and made "live" (even though a neutral isn't "hot" doesn't mean it does not have any current on it, if a device on the circuit is drawing current that current will be on the neutral (due to the "alternating" aspect of AC).
      • ReeceyBurger123
        Never Give Up !
        • May 2014
        • 7325
        • Britain
        Re: AC to Ground?
        I wouldn’t advise it tbh, keep all mains stuff as it should be.
          • Jul 2011
          • 6070
          Re: AC to Ground?
          The only reason why you would do this is if you are testing a grounding rod for a machine or if you are using a grounding rod at your house but make sure that you do not have a GFCI circuit or outlet while doing this test you will trip it if it is working correctly
          Use caution while doing this test if you have not done this test before
          This test is done with a 100 watt incandescent light bulb which should light up at full brightness if you have a good grounding rod connection
          • eccerr0r
            Solder Sloth
            • Nov 2012
            • 8706
            Re: AC to Ground?
            If you're thinking about a way to save a wire, no, likely getting an equivalent good ground is unlikely and you'll end up with lots of different voltages around, generating ground loops...but yes with a proper ground it should work as it's "theoretically" equivalent, hence the electrocution danger and the need for isolation transformers where there's a risk of accidentally grounding a live wire through a human.
            • EasyGoing1
              Shock Therapist
              • Sep 2016
              • 977
              Re: AC to Ground?
              My curiosity was purely academic.
              sigpic
                • 31283
                Re: AC to Ground?
                it can be used at very low current - i use it to power neons in lamp switches.
                (find the switch in the dark. )
                • EasyGoing1
                  Shock Therapist
                  • Sep 2016
                  • 977
                  Re: AC to Ground?
                  Have you ever stood under large high-power transmission lines with a fluorescent bulb tube (like what you often see in a garage) and held one end on the ground and watch it light up? It's ... interesting ...
                  sigpic
                    • Jul 2011
                    • 6070
                    Re: AC to Ground?
                    This does not sound like something you would want to do very long microwave oven do the same thing so really can not be good for you in the long run
                      • 31283
                      Re: AC to Ground?
                      seen it done - that's why you get cancer clusters under power lines and why the land is cheap.
                      https://www.youtube.com/watch?v=nXxQKUPB0vs
                      • EasyGoing1
                        Shock Therapist
                        • Sep 2016
                        • 977
                        Re: AC to Ground?
                        It was something I did once around 20 years ago.
                        sigpic
                        • EasyGoing1
                          Shock Therapist
                          • Sep 2016
                          • 977
                          Re: AC to Ground?
                          Originally posted by brethin
                          Your intresting things will get you or some killed. Asking questions when you should know better just shows how stupid you are. Go lick some 110v ac and tell us how it went for you, moron.
                          Never been electrocuted in the 50 years I've been on this planet.
                          Funny that you call me the idiot, yet I'm the one asking questions, and you're the one asserting that I do things I don't ever do ... Pretty hostile for someone who doesn't even know me ... your posts are VERY "Troll-ish" if you ask me.
                          sigpic
                            • 31283
                            Re: AC to Ground?
                            that's lame - your not trying hard enough.
                            my best yet - 16KV from a 14inch crt anode!!!
                            • eccerr0r
                              Solder Sloth
                              • Nov 2012
                              • 8706
                              Re: AC to Ground?
                              Not quite as good as a CRT anode, but I stuck my hand across a photoflash flash capacitor I thought was discharged... yow. "Test before touching" ...
                              • EasyGoing1
                                Shock Therapist
                                • Sep 2016
                                • 977
                                Re: AC to Ground?
                                That probably had a hell of a kick ... did you suffer any serious injuries?
                                sigpic
                                • redwire
                                  • 3912
                                  Re: AC to Ground?
                                  I was always careful around CRT's but car ignition coils on a 555 timer were such a blast.
                                  I connected one to a TV HV multiplier and was watching the arcs many inches, it must have been well over 150kV, full power lol, when the arc jumped to all the junk on my workbench. You know, nuts, bolts, tools, test leads, boards etc.
                                  It then arced onto a test lead that had one end dangling by my leg and through my jeans and nailed my leg. That hurt and was not at all expected. Keep your workbench clean lol.
                                  Running AC mains current to ground works but the safety is low.
                                  In North America, earth-ground and Neutral are bonded together in the electrical panel (service). So using Neutral as a GND, or GND as a Neutral can and does happen.
                                  There is of course a danger if that (panel) ground connection went high resistance or open-circuit, that all devices grounded to that would float up to shock levels, due to the leakage currents. This is why people flip out about it.
                                    • 31283
                                    Re: AC to Ground?
                                    i hurt my back when it threw me into a worktop.
                                    i'v said before, it's not the voltage or current that kills people - it's the thing you get thrown against!
                                    • EasyGoing1
                                      Shock Therapist
                                      • Sep 2016
                                      • 977
                                      Re: AC to Ground?
                                      So I remember back in school, we were told that if you see someone being electrocuted by standard home electricity, you were supposed to grab a piece of wood and knock them away from the source ... the wood part makes perfect sense, but what's the deal with someone holding on to the wire or whatever is feeding them current? Is it normal that people hold on when - for example, they accidentally grab a live wire with their bare hands? Why wouldn't it knock them back like what happened to you with the CRT? And is that a reflex that is more common with AC vs DC?
                                      sigpic
                                      • redwire
                                        • 3912
                                        Re: AC to Ground?
                                        Electricity affects the human body a few different ways. A sine-wave is different than DC or pulsed DC, to both the nerves and muscles.
                                        Nerves will get activated- a tingle, all the way leading up to pain receptors being activated, which triggers a reflex to pull away.
                                        At higher voltages, muscles will turn on to varying degrees depending on the voltage, frequency.
                                        High voltage mains 50/60Hz AC shocks, the muscles just turn on and you can't move or let go. This commonly kills people.
                                        For the physiotherapy electrical muscle stimulators, they are optimized pulsing waveforms that activate a muscle but not the pain receptors. A narrow few kHz DC pulse train but AC coupled through a capacitor, this turns on muscles.
                                        • Geeker007
                                          9th Gen Dell Optiplex Micro PC motherboard repair: Short Circuit?
                                          by Geeker007
                                          Hi All, I have a 9th Gen Dell Optiplex micro PC motherboard which doesn't power on. When I connect the motherboard with power adapter, it goes into safe mode and turns off. So from info I have gathered online, it looks like there is a short circuit on the motherboard. So can you guys help me with figuring out the issue?
                                          I am new to electronics repair, so my queries could be naive but I am ready to learn.
                                          So I have a multimeter and a solder with me. But I can try to get a variable voltage power supply with a thermal camera as well. From what I seen online, best way is...
                                          01-28-2025, 03:31 PM
                                        • Rolin
                                          Dell Laptop - over 14V between Chassis Ground and Circuit Ground?
                                          by Rolin
                                          Someone brought me a Dell laptop that had a loose power jack inside (power jack on a cable, not soldered to motherboard). Once disassembled found one of the wires was broken off the power jack. I replaced the jack and it won't turn on, but the metal shell of the jack inadvertently touched the metal hinge and suddenly it got power. I checked voltage from the metal chassis ground and the circuit ground and I get over 14V ? Has anyone seen this before? Typically is it some kind of filter cap that shorted? Very strange...
                                          10-30-2022, 10:18 PM
                                        • Per Hansson
                                          Repair of Sign WiFi Smart Plug PCB: SA-P302A v1.2 due to bad caps - with schematic
                                          by Per Hansson
                                          I have repaired a Sign WiFi Smart Plug with model number: SNSM-WASINGLE sold by Spares Nordic AB in Sweden.
                                          The fault condition was that the device gave no signs of life: pressing the push button did not cycle the internal relay and the blue LED did not come on and it was not seen on the WiFi network.
                                          The fault was very simple, capacitor C3 on the PCB with writing "KSJ" and "LOWESR" had literally blown its top off, after replacing it the device works fine again!
                                          As I find linear high voltage regulator designs interesting I drew up the attached schematic...
                                          12-23-2023, 06:20 AM
                                        • matk
                                          Question about electricity
                                          by matk
                                          Hello, I have a question about electricity. Suppose I'm well insulated from ground and neutral, and the live wire of mains comes in touch with a wound in my finger, will this potential interfere with body voltages, hearth for example, or it will only go to its circuit return path ?
                                          Thanks!
                                          05-23-2024, 02:12 PM
                                        • sew333
                                          Can i plug pc on this apartment with older fuse box?
                                          by sew333
                                          Hello. I will be buying new apartment to live. But fuse box is older. Not the newest.
                                          And my question. It will be fine to plug pc in this new apartment with that fuse box,i think it is aluminium,right?
                                          PC WILL BE: Rtx 4090,14900K,1600W PSU
                                          It looks like this ( screen from internet ). Looks like this,not sure i dont take a pic from there. Can i plug pc with that one?
                                          screen of this:
                                          room:
                                          Someone said this to me.
                                          1
                                          "I would get advice from a local electrician...
                                          03-29-2024, 05:37 PM
