Re: Mechanical Relay Quality
i did not use a clamp meter this time, i used a meter that measures the current flowing through the meter with wires
"goosechase due to a cheap crappy Songle relay" is what i have been thinking
the only changes i did on the AC side was moving the wires for the tubes to the relays in the thermostat
https://www.badcaps.net/forum/newrep...eply&p=1105511
I do not think i have a way to measure that
the fan does have a delay as far as i know, the fan does turn on/off in auto mode
wonder what those relays cost and if i can source them...
as far as i am aware the only fans are in the outdoor unit
the defrost cycle is on a timer cause someone wanted to not pay extra
Mechanical Relay Quality
Collapse
X
-
Re: Mechanical Relay Quality
One thing that I always check on these boards are for bad soldering joints I have seen quite a few them with issues at terminals joints and at the relays joints as well and you are better off if the soldering joints looks questionable remove the solder and redo it you are better off in the long run
I have fixed a few them before when they either do not go into defrost or do not want to come out of defrost
Does this unit have a time delay for the fan to go off when the temperature hits the set point if does they quite often fail open which means they do not turn on the fan or the fan never turn off in auto fan control modeLast edited by sam_sam_sam; 02-02-2022, 04:15 PM.Leave a comment:
-
Re: Mechanical Relay Quality
Digital inputs to HVAC (furnace, A/C) control boards are typically a 820R-1k 3W resistor load. So 24-30mA AC typ. which is what I expect.
Like to "O" Heat/Cool, and "Y" Compressor (after loss of charge/pressure switch).
The control board already has 3-4 relays to deal with the higher power stuff. One large one for the outdoor fan, smaller ones for compressor contactor CC, reversing valve RV and what they call Defrost Heater W. What's funny is the control board relays are the same cube size as OP's: Goodsky RWH-SS-124DMF-U rated 15A.
There can be another (indoor) fan motor contactor we don't know about, and a timer board for the electric heater option as well. I suspect there's extra loads like these lurking somewhere that are responsible for the relay wear.Leave a comment:
-
Re: Mechanical Relay Quality
Post #6 says you measured "0.67A up to 1A then back down" and now you're saying 32mA ???
I looked at Heil ICP Tempstar PA5536AKA4/PYPA36GA4 heat pump, from your picture. It looks just like an air conditioner but has a reversing valve to pump heat into the home and there's some optional electric heater package.
Power transformer is 24VAC 40VA. Based on pictures, you can figure out the schematic of the Heil control board 1087562/Honeywell 1084-83-100A, if I'm right about the one in your outdoor unit.
The thermostat inputs are low current going to a PIC MCU. There is no usual 24VAC inductive loads the thermostat relays would be seeing, like contactors etc.
So either your wiring is wrong and you are crowbarring something or this is a massive goosechase due to a cheap crappy Songle relay.Last edited by redwire; 02-02-2022, 01:04 PM.Leave a comment:
-
Re: Mechanical Relay Quality
Using my meter it showed ~32ma at ~27v AC
if i were to use 3 SSRs i would have to redo the pcb layout, but if i can sick with 2 relays it i can just swap them out and garage some wires at the relay for a new pin out/location
maybe i could use this relay: https://www.digikey.com/en/products/...1Z-4-5V/648227Last edited by evilkitty; 02-02-2022, 01:02 PM.Leave a comment:
-
Re: Mechanical Relay Quality
Well, it seems a full amp can be passed through the circuit, so a 1A relay is pushing it.
Hmm... have to see what my thermostat is using now... I'm surprised it's not using a SSR, it too uses 3V logic (uses two AA batteries and probably residual power from the 24V control line)...Leave a comment:
-
Re: Mechanical Relay Quality
Leave a comment:
-
-
Re: Mechanical Relay Quality
Those relays ( if they are 24 ac ones ) are cheaply made in the first place and if your thermostat cycle to many times will wear them out in 3 to 5 years of use any way unless you get the heavy duty ones ( cost a lot more money ) which are hard to find only some Air Conditioning Supply House carry them and most of them require a journeymen license to buy from in the first place
These relays are mostly used to control fan speed between heating and cooling and sometimes used for heating element relays that are made for switching the heating element on and off if there is more than one heating element bankLast edited by sam_sam_sam; 02-02-2022, 11:43 AM.Leave a comment:
-
Re: Mechanical Relay Quality
What about using this relay, it calls for 4.5v and says it will work as low as 3.2v
https://www.mouser.com/ProductDetail/817-SY-4.5-K
If this issue is the TIP120 would you expect both sides to wear like this? the NC (coil on state) wouldn't that one not look like this assuming the spring was not worn out, this contact does not look good, but it was not dead
i do not know for sure how much voltage the contacts are dealing with, i just know it is low amps based on wire gaugeLeave a comment:
-
Re: Mechanical Relay Quality
The NO contacts get a weak make but the break works fine due to the spring.
The NC contacts get a weak break but the make works fine due to the spring.
Well it's something to consider in any case. You could use 2/6 of a 74HCT04 to make a buffer so the RPi output isn't as loaded to drive something you can use as a saturated switch. Or even drive a logic level MOSFET,... Would be nice to direct drive a MOSFET but a 3.3V signal limits the number of MOSFETs available without some sort of buffer.
I really think that TIP120 is a bad idea for this situation, if you were using a 12V relay and supply then the TIP120 may do much better.Leave a comment:
-
Re: Mechanical Relay Quality
The old relay contacts are not pitted from arcing, but the plating has vanished and gone somewhere. There is no black soot so I'm puzzled what is going on. It might be chinesium plating.
Songle SRD-05VDC-SL-C coil is 70R or 71mA and they offer three different contact platings and current ratings 7,10,15A 250VAC as well as basic 10,000 cycle lifetime into resistive loads.
UL/CSA rate them only 3A 125VAC inductive loads, and there is a secret long life 100,000 cycle model. Thne specs are a bit deceptive and I've seen plenty of Songle knockoffs too.
Driving the relay with a TIP120, the base resistor is large 6k8 so the TIP120 sees about 0.2mA drive with hFE 500 so it is on a bit weak.
Changing to 2k gives 1mA drive from the RPi. The TIP120 loses at least a volt so the relay at best will see 4V.
If you drive the relay "weak" it pulls in slow and wimpy which would wear the N.O. contact only. The N.C. relies on the spring for force.
This is why I think the software might extra pulse the relay, or the snubber is simply too small for whatever the load is, or the relay quality is poor.
I have some 2N2222A NPN and 2N3906 PNP transistors on hand and a wide assortment of 1% 0.25W metal film resistors
rpi gpio is specked at 16ma max, however there is also a shared total max as well, i think that is 50ma, not sure if sinking and outputting both count towards this total
my LCD panel uses alot of pins, but the total ma should be silly low as i was trying to make the led a bit dim
front panel:
edit: i checked the voltage across the coil and got 4.14v on the bottom relay and 4.13 on the top relay
EDIT: took some pictures of the labels on the outdoor unit: https://imgur.com/a/809clTp they are not in great shape, but here they areLast edited by evilkitty; 02-01-2022, 10:42 PM.Leave a comment:
-
-
Re: Mechanical Relay Quality
you dont need a transistor for an ssr, they use an optoisolator and take under 5mA usually.Leave a comment:
-
Re: Mechanical Relay Quality
The old relay contacts are not pitted from arcing, but the plating has vanished and gone somewhere. There is no black soot so I'm puzzled what is going on. It might be chinesium plating.
Songle SRD-05VDC-SL-C coil is 70R or 71mA and they offer three different contact platings and current ratings 7,10,15A 250VAC as well as basic 10,000 cycle lifetime into resistive loads.
UL/CSA rate them only 3A 125VAC inductive loads, and there is a secret long life 100,000 cycle model. Thne specs are a bit deceptive and I've seen plenty of Songle knockoffs too.
Driving the relay with a TIP120, the base resistor is large 6k8 so the TIP120 sees about 0.2mA drive with hFE 500 so it is on a bit weak.
Changing to 2k gives 1mA drive from the RPi. The TIP120 loses at least a volt so the relay at best will see 4V.
If you drive the relay "weak" it pulls in slow and wimpy which would wear the N.O. contact only. The N.C. relies on the spring for force.
This is why I think the software might extra pulse the relay, or the snubber is simply too small for whatever the load is, or the relay quality is poor.Leave a comment:
-
Re: Mechanical Relay Quality
Actually using a TIP120?! This might explain the failure.
How much drive current can a rpi source/sink? If it can drive more, you're better off not using a Darlington there, at least for 5V. Maybe a 2N4401 would be better.Leave a comment:
-
Re: Mechanical Relay Quality
i guess i could use a NPN and a PNP transistor and control them both with the same gpio pin each getting there own resistor, guess i should make use new pcb for this design, id need to take some parts off the old pcb, but they are easy ones to removeLeave a comment:
-
Re: Mechanical Relay Quality
no - atleast i dont think so.
using 2 and inverting the control signal on the second will work though.Leave a comment:
Related Topics
Collapse
-
by valvashonYesterday I successfully repaired a Middle Atlantic UPS2200R-IP that had inadvertently been used as a surge suppressor at our transmitter site. It has already been replaced with an updated one but it's coming home with me now instead of being e-cycled. To be specific, this is the MA model that has the blue backlit display and has been discontinued, although this design may have been used in many UPS units including the smaller Middle Atlantic ones in this series.
Here's what happened: We experienced a brownout/surge at the site, which damaged the UPS and took our broadcasting... -
by DXseekerMOHello everyone!
Recently I've noticed that some ShopJimmy backlight strips don't have double-sided tape installed upon them when an application calls for it, and I must purchase the tape separately. In a recent chat conversation with a customer service agent I told them if this tape wasn't applied when it was called for I would begin to consider ordering my backlight strips elsewhere. It looks like this time may have come.
I recently got a TCL 65S4 with bad backlights. After looking at the SJ listing here: https://www.shopjimmy.com/tcl-jl-d65...365as-m-led-ba...Yes0%1All backlight strips are the same quality0%1No0%0 -
by momakaI got this TV a little over a year ago from a coworker from my previous job. It’s a Samsung 46” TV, model number LN46b530p7f.
Problem:
Backlight cycles On and Off.
Basically, when the TV is turned On, there is a relay click heard from the TV PS board. The relay cycles On and Off 4 times in about 2-3 second intervals. Each of those 4 times, the backlights also cycle On and Off with the relay. The screen TFT isn’t cracked/damaged and appears to work - I can see a “no signal” image when the backlights turn On briefly – though the image is a bit dull/dark.... -
by CuriousJohnBurco BCPLSAFWM5L 5 Litre Wall Mounted Automatic Water Boiler With Filtration UK 240v
Does anybody have any experience with these Burco units at all there is no record of them on the forum lol and a proper service manual would be nice. I invite you all to pesuade me not to botch repair it with a 5v relay, read on.
This unit was rescued from a skip 3 years ago, the only fault it had then was no backight display (plus it wanted a new probe set and top seal) but the screen was never an issue you can still see the screen as is and I just use it to get 5 Litres of very hot... -
by SluggerBI have a very small float switch, I'm using in a very small tank. It only fits in one way. Link https://www.amazon.com/uxcell-Switch.../dp/B07DZ1J2GB
I want the switch to be open when the water is high, and closed when the water is low. Unfortunately it works the opposite. And since this switch is designed to be underwater, it's all sealed up, there is no taking it apart or hacking it up.
It will be driving a water pump, basic idea, when the water is low, switch closes, which turns on water pump, when enough water is in the tank, float switch floats,... - Loading...
- No more items.
Leave a comment: