Repair Success! Middle Atlantic UPS2200R-IP

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • valvashon
    Senior Member
    • Oct 2020
    • 90
    • USA

    #1

    Repair Success! Middle Atlantic UPS2200R-IP

    Yesterday I successfully repaired a Middle Atlantic UPS2200R-IP that had inadvertently been used as a surge suppressor at our transmitter site. It has already been replaced with an updated one but it's coming home with me now instead of being e-cycled. To be specific, this is the MA model that has the blue backlit display and has been discontinued, although this design may have been used in many UPS units including the smaller Middle Atlantic ones in this series.

    Click image for larger version  Name:	UPS-2200R-IP_main.webp Views:	0 Size:	6.7 KB ID:	3211577

    Here's what happened: We experienced a brownout/surge at the site, which damaged the UPS and took our broadcasting facility off the air. While it was not powering the transmitter, it was powering some signal delivery equipment and kept it on during the transfer to and from the generator. The engineer on duty had to hike in part of the way and found the UPS powered on but showing "E021" with no power to the rear outlets.

    Unit was removed from service. Bench testing revealed the following symptoms:

    When plugged and cold started the unit gave one relay click and then showed "E021" with no voltage at the rear. IIRC the battery charging circuit operated normally.

    When unplugged and cold started the unit powered up and delivered voltage from the batteries to the rear outlets as normal, like if the shore power went out.

    If plugged in while running the unit would constantly fire a relay as if to try to switch over to shore power. Power to rear outlets would be interrupted when this was happening.

    Middle Atlantic/Legrand was of little to no help saying that they do not offer repair service on these units as they are over 3 years old. They did drop a nugget, suggesting that the input relay may have failed.

    With that I pulled off the top cover to have a look at the unit. Removing the main circuit board looked to be a daunting affair and it was. There are a considerable number of connections to this main board, so take copious notes about what connections go where. All but one of the connector points on the board are labeled so use those markings when you are taking your notes.

    It goes without saying, unplug the unit and remove the battery pack. Discharge the two main capacitors by shorting across the big heat sink, otherwise you will get more than a tingle when you brush across this heat sink.

    Start by cutting any zip ties that look like they should be removed. Squeeze tabs on and push in circuit breaker at upper left rear of unit. Pull up black and white incoming power wires and undo ground screw near rear of unit. Uncoil wires from ferrite cores and pull power input cables over back of unit. This will give you more access to unit and the large strain relief does not need to be removed. Remove large wires going to transformer and pull back, then remove large wires going to UPS rear outlets and pull back. Remove housing for IP ethernet connection board and pull out. From there pull out board mounted plugs and large wires going to heat sink. Again, make notes and take pictures of where everything hooks up. Eventually you will get all the connections off and 5 screws hold board in place. Remove
    those and pull the board out.

    Click image for larger version  Name:	IMG_3982.jpg Views:	0 Size:	2.41 MB ID:	3211571 Click image for larger version  Name:	IMG_3951.jpg Views:	0 Size:	2.26 MB ID:	3211568 Click image for larger version  Name:	IMG_3980.jpg Views:	0 Size:	2.27 MB ID:	3211567 Click image for larger version  Name:	IMG_3956.jpg Views:	0 Size:	2.44 MB ID:	3211565 Click image for larger version  Name:	IMG_3955.jpg Views:	0 Size:	2.46 MB ID:	3211569

    While I had the board out I did open/shorted testing of all power handling devices such as MOSFET's and diodes. All checked OK. Input MOV's and capacitors were OK. At that point I recalled the hint given by MA Tech Support- the input relay. Here you can see my Sharpie notes on what wires go to the heatsink. The relay has been removed at this point.
    Click image for larger version  Name:	IMG_4071.jpg Views:	0 Size:	1.97 MB ID:	3211564

    I started checking relays and found that one along the input line checked backwards- the normally open contacts were closed and the normally closed contacts were opened. The surge must have fused the contacts this way causing the unit to go into an error mode when plugged in- it could not go to normal mode when the power input was applied.

    Discovered that these relays have been officially discontinued or are about to be but eBay was thick with them. 793-P-1C is the Song Chaun part number and Panasonic seems to have one that will work. I ordered two from eBay thinking i was getting two but it was two packs of two so now I have three extras. They are only a few dollars each. While the board is out I would check all of them. The failed relay was RL2 in this case.

    Click image for larger version  Name:	IMG_4074.jpg Views:	0 Size:	1.84 MB ID:	3211566

    I'm a desolder braid kind of guy. That usually works well but removing this relay was a bear. I did remove C22 to allow better access when pulling up on the relay as I was heating up the pins. This is at minimum a two sided board so perhaps a solder sucker would have given better results. Eventually I was able to work the relay free. The heat involved did cause the relay contacts to un-fuse but I did not, of course, re-use this relay.

    Click image for larger version  Name:	IMG_4073.jpg Views:	0 Size:	1.82 MB ID:	3211562

    Soldering in the new relay was easy along with re-installing C22. I slowly and carefully re-installed the board and all connections. I powered the unit up and success! Here is the new relay in place. You can see that the "12VDC" marking is slightly different. The part number I used has an "F" as a suffix; they are electrically identical. The "F" denotes how well the relay is sealed at the bottom. Ignore the "X" on the adjacent relay; it's OK.

    Click image for larger version  Name:	IMG_4089.jpg Views:	0 Size:	2.50 MB ID:	3211576

    Would love to know if this helps or if you have any questions.

    Val

    Attached Files
  • CapLeaker
    Leaking Member
    • Dec 2014
    • 8000
    • Canada

    #2
    Nice fix! Yes... these UPS's have a real problem with the relay weld issue... not the first one and wont be the last either!

    Comment

    • sam_sam_sam
      Badcaps Legend
      • Jul 2011
      • 6024
      • USA

      #3
      Nice work on repairing this device one more item that did not end up in a landfill

      Comment

      • schmidtparty
        New Member
        • Jun 2025
        • 2
        • USA

        #4
        I have the same UPS. Great fix!

        I am posting here hoping someone can help me diagnose a problem with an identical unit.

        My unit was turning off immediately after power-on so I replaced the batteries, but things aren't quite right.

        In particular, using the network card (IPCARD), it shows "normal" and I can do a battery test and load test and all is good.

        However, when I try to use Network UPS Tools (NUT) through usbhid-ups driver, it always reports LB or Low Battery which makes it want to shut down. I also tried configuring SNMP and reports a status of 3 which means low battery. Finally, when I use the Middle Atlantic Power Manager ("MAP Power Manager") on Windows and connect via USB, it shows status ok, but when I go to diagnostics and try either Battery Test or Runtime Calibration, the fans turn on loud and after a very short while, I get an error popup: "Middle Atlantic Power Manager: Event - [Utility power failure] has occurred at 6/22/25 11;04 AM....". So, all is not good.

        Finally, if I just unplug the power, the battery seems to keep things running ok even with a load plugged in (tested with ~125 Watt load). I didn't time how long the battery will last, but it seems like it is about right.

        So ... seems like the unit kind of works, but is kind of broken. I tried a "full reset" but not sure it actually reset anything (unplug from wall, unplug battery, wait 10 seconds, push power button 5 seconds, then reconnect power). This reset does seem strange because is it really reading the power button with no battery or wall power? And after rebooting it doesn't seem like anything different.

        I am comfortable soldering and replacing components, but I'm not even sure anything is broken given the inconsistent result seen.

        Not sure it helps, but here is output of upsc command from NUT:

        battery.charge: 100
        battery.charge.low: 20
        battery.charge.warning: 20
        battery.mfr.date: Middle Atlantic Pro
        battery.runtime: 14381
        battery.runtime.low: 300
        battery.type: PbAcid
        battery.voltage: 53.8
        battery.voltage.nominal: 48
        device.mfr: Middle Atlantic Products
        device.model: UPS-2200Rl
        device.type: ups
        driver.name: usbhid-ups
        driver.parameter.pollfreq: 30
        driver.parameter.pollinterval: 2
        driver.parameter.port: auto
        driver.parameter.synchronous: auto
        driver.version: 2.8.0
        driver.version.data: CyberPower HID 0.6
        driver.version.internal: 0.47
        driver.version.usb: libusb-1.0.26 (API: 0x1000109)
        input.transfer.high: 145
        input.transfer.low: 80
        input.voltage: 118.0
        input.voltage.nominal: 120
        ups.beeper.status: disabled
        ups.delay.shutdown: 20
        ups.delay.start: 30
        ups.load: 0
        ups.mfr: Middle Atlantic Products
        ups.model: UPS-2200Rl
        ups.productid: 0601
        ups.realpower.nominal: 1650
        ups.status: OL CHRG LB BOOST
        ups.timer.shutdown: 0
        ups.timer.start: 0
        ups.vendorid: 0764

        Comment

        • valvashon
          Senior Member
          • Oct 2020
          • 90
          • USA

          #5
          I'm a Mac user so it's going to be kind of rough for me but I will attempt to run those diagnostic tools on mine and see what I get. I probably have the Middle Atlantic Power Manager on a disc somewhere and have an old Toshiba laptop that I can use for this. Honest question- what's Network UPS tools and usbhid-ups driver and where do I get them? Sounds like software or a driver that needs to be installed, not a physical USB connection device, correct?

          I'm also suspicious of the fact that it seems to run normally when the shore power is disconnected, like mine did. The relay switching in these things is complex given the large number of relays in there and you could also have a bad relay, just a different one than I had. Have you done the Power Manager and NUT tests with the shore power disconnected and the unit just running on the battery?

          Val
          Last edited by valvashon; 06-25-2025, 10:07 AM. Reason: Added second idea.

          Comment

          Related Topics

          Collapse

          • CuriousJohn
            Burco boiler power problem
            by CuriousJohn
            Burco BCPLSAFWM5L 5 Litre Wall Mounted Automatic Water Boiler With Filtration UK 240v

            Does anybody have any experience with these Burco units at all there is no record of them on the forum lol and a proper service manual would be nice. I invite you all to pesuade me not to botch repair it with a 5v relay, read on.

            This unit was rescued from a skip 3 years ago, the only fault it had then was no backight display (plus it wanted a new probe set and top seal) but the screen was never an issue you can still see the screen as is and I just use it to get 5 Litres of very hot...
            12-22-2024, 10:25 AM
          • momaka
            Seasonic B12 BC-550 – barely 2 years old and with BAD CAPS already!
            by momaka
            I know I've been a little scarce lately (like the last 2-3 years), but I'm still here and still doing my thing with fixing PSUs.

            For today's considerations, I have a Seasonic B12 BC-550 [A551bcafh] 550 Watt ATX power supply for you (click on links for full size images).

            https://www.badcaps.net/filedata/fetch?id=3591771


            https://www.badcaps.net/filedata/fetch?id=3591772

            It's a modern ATX unit with fixed (non-modular) cables and an 80-plus bronze certificate. Here's the label:

            https://www.badcaps.net/filedata/fetch?id=359177...
            03-12-2025, 03:42 PM
          • jm1234
            9V relay temperature 40C
            by jm1234
            Hi, I'm seeing one 9V relay having temperature 40C on its 9V (primary) side. Does that seem right? I switched 2 relays on that board and the temperature was the same (on the same position), so I'm sure it's not a faulty relay. I measured voltage on that relay and it was 9.5V DC, so that looks good. I don't see any other relay on that board having that kind of temperature and they have 9V on them too.
            I thought maybe the transistor that is switching this relay keeps switching on/off, so I also checked for AC and there was almost none: 0.3V using mV range. No steady frequency was shown, but...
            05-09-2024, 03:03 AM
          • edugimeno
            Biomass Boiler not driving cleaner motor relay. ENERTRES BIOMASA BI-650
            by edugimeno
            Hi everyone!
            I have this board that suddenly stopped supplying power to an output that drives an interchanger cleaner motor.
            I checked while the board was in place with all wires attached and there's no AC voltage on the corresponding plug X5
            This X5 is driven by fuse F8 (tested OK) which comes from the second orange relay
            To make sure there are no charcoaled contacts inside the relay, I got a 24VDC power supply and got it ready to manually power up the coil side of these relays.
            I respected the polarity, positive to cathode of protecting diode
            So provided all...
            04-18-2024, 01:15 PM
          • ngml
            Repair of an LG split AC system indoor unit PCB
            by ngml
            I am trying to repair an LG split AC indoor unit, which does not start and gives a CH05 error code.
            This indicates an error in the communication between the outdoor and the indoor unit.
            The outdoor unit is fine, so the problem is the indoor PCB.
            The indoor unit is an LG PC09SQ NSJ (3SNM09JA2FA), and the PCB has the following type number: EAX35907219-1.2 (see photo1)
            I changed optocouplers ICO1X & ICO2X and the NPN transistor S9013 which drives optocoupler ICO2X (see photo2), but this did not remedy the fault.

            Does anybody have the schematics of this board,...