    Re: Using higher amperage receptacles with lower amperage breakers

    Originally posted by Spork Schivago
    It'd be nice to be able to replace the switches / receptacles without having to flip the breaker.
    Thanks!
    i dont cut the power, i just use gloves and an insulated screwdriver - fuck it!

    Comment

    • televizora
      ghettomodmaster
      • Nov 2016
      • 957
      • Bulgaria

      #42
      Re: Using higher amperage receptacles with lower amperage breakers

      Originally posted by stj
      i dont cut the power, i just use gloves and an insulated screwdriver - fuck it!
      Nice. Do you know that you are absolutely, totally insane?
      Useful conversions. I don't "speak" imperial. Please use metric, if you want to address me.
      1km=1000m=100000cm, 1inch=2.54cm, 1mile=1609.344meters, 1ft=30.48cm 1gal(US)=3.785liters, 1lb=453grams, 1oz=28.34grams

      Comment

      • stj
        Great Sage 齊天大聖
        • Dec 2009
        • 30963
        • Albion

        #43
        Re: Using higher amperage receptacles with lower amperage breakers

        do you know that your whole house or street would be connected or cut live?

        pro's just isolate themselves, we dont need to cut power to something we wont touch.

        Comment

        • dmill89
          Badcaps Legend
          • Dec 2011
          • 2534
          • USA

          #44
          Re: Using higher amperage receptacles with lower amperage breakers

          Originally posted by Spork Schivago
          Isn't that called back stabbing and isn't that a bad idea? I planned on just using the screw terminals and wrapping it around and tightening them down. I heard some bad stuff about backstabbing and believe it should be avoided, unless things have changed. From the sounds of it, things have changed a bit, but does it actually make a difference? Is it a good idea to backstab now? Thanks!
          Originally posted by Spork Schivago
          Are you saying it's okay to back-stab with the GFCI outlets?
          It is ok if the "back stab" terminals use a clamp and screws to hold the wires in, as is common in GFCI and even higher-end standard outlets. The cheap spring loaded clamps that don't have much contact area to begin with and hold poorly on cheap outlets are what causes issues.

          Comment

          • delaware74b
            Badcaps Veteran
            • Apr 2009
            • 628
            • USA

            #45
            Re: Using higher amperage receptacles with lower amperage breakers

            Spork - the clamps on the GFCI's and spec grade devices are not the same as back-stabbing on the cheap devices.

            This is pig-tailing, although I don't use that brand of wire nut:
            https://s-media-cache-ak0.pinimg.com...d313d72737.jpg

            Live work? Sure I do it. With permission from the local power utility, my boss and I have permission to pull meters and reinstall for panel repairs and service replacement.
            Stupidity should be a crime, especially for drivers. I have NO patience for them.

            Comment

            • redwire
              Badcaps Legend
              • Dec 2010
              • 3900
              • Canada

              #46
              Re: Using higher amperage receptacles with lower amperage breakers

              Spring-clamp connectors can be good quality, they're the only thing allowed on locomotives due to vibration and temperature swings. Europe loves them for DIN-rail panel stuff.

              But on outlets they suck badly. I never use them because copper oxidizes with brass and crappola connection happens, with age and chinese drywall H2S gas.
              I can take 10 seconds and tighten the screws. Really.

              As far as live work goes, it's all fine until the day you disconnect a wire and it unexpectedly springs back and touches something grounded or the opposite phase. Poof! Had an arc happen doing that. You need eye/face protection!
              Attached Files

              Comment

              • keeney123
                Lauren
                • Sep 2014
                • 2536
                • United States

                #47
                Re: Using higher amperage receptacles with lower amperage breakers

                Originally posted by Spork Schivago
                Isn't that called back stabbing and isn't that a bad idea? I planned on just using the screw terminals and wrapping it around and tightening them down. I heard some bad stuff about backstabbing and believe it should be avoided, unless things have changed. From the sounds of it, things have changed a bit, but does it actually make a difference? Is it a good idea to backstab now? Thanks!
                I am trying to explain the new connector that the wire can be put in the back of. These are not spring loaded like the old connecters that were no good. The screw on the side of the connector is what causes the tightening down on the wire. It is much like how one puts a wire in a breaker terminal and tightens down on a screw. Look at the picture on the right hand side of redwire's post 46. The left one is the old connector. Noticed the screw is not tightened on the picture on the left.
                Last edited by keeney123; 01-03-2017, 09:48 PM.

                Comment

                • keeney123
                  Lauren
                  • Sep 2014
                  • 2536
                  • United States

                  #48
                  Re: Using higher amperage receptacles with lower amperage breakers

                  Originally posted by stj
                  i dont cut the power, i just use gloves and an insulated screwdriver - fuck it!
                  You can do this. One of my nephews works that way. I always like to turn it off if I can. My nephew says be does it because he is lazy.

                  Comment

                  • televizora
                    ghettomodmaster
                    • Nov 2016
                    • 957
                    • Bulgaria

                    #49
                    Re: Using higher amperage receptacles with lower amperage breakers

                    Originally posted by stj
                    do you know that your whole house or street would be connected or cut live?
                    I know some very special mystique equipment that can help you to solve this problem.

                    And yes - you MUST cut the power. Because if insulated screwdriver works for 220Volts, this definitely doesn't work for 220KILO Volts.
                    One gipsy nearby confirmed this by making example of himself. Tried to cut and steal 50Kilovolt wires. Fried to the degree of charcoal.
                    Professionals always cut the power. And if they don't - they understand the risks. Are you prepared for these?
                    Last edited by televizora; 01-04-2017, 03:00 AM.
                    Useful conversions. I don't "speak" imperial. Please use metric, if you want to address me.
                    1km=1000m=100000cm, 1inch=2.54cm, 1mile=1609.344meters, 1ft=30.48cm 1gal(US)=3.785liters, 1lb=453grams, 1oz=28.34grams

                    Comment

                    • joshnz
                      Badcaps Veteran
                      • Feb 2011
                      • 969
                      • New Zealand

                      #50
                      Re: Using higher amperage receptacles with lower amperage breakers

                      Originally posted by televizora
                      I know some very special mystique equipment that can help you to solve this problem.

                      And yes - you MUST cut the power. Because if insulated screwdriver works for 220Volts, this definitely doesn't work for 220KILO Volts.
                      One gipsy nearby confirmed this by making example of himself. Tried to cut and steal 50Kilovolt wires. Fried to the degree of charcoal.
                      Professionals always cut the power. And if they don't - they understand the risks. Are you prepared for these?
                      Meter installers love leaving the power on lol.
                      My pc
                      CPU : AMD PHENOM II x4 @ 3.5Ghz
                      MB : ASUS M4A89TD PRO USB3
                      RAM : Kingston ValueRAM 16gb DDR3
                      PSU : Cooler Master 850W Silent Pro
                      GPU : ATI Radeon HD 6850

                      Comment

                      • Spork Schivago
                        Badcaps Legend
                        • Mar 2012
                        • 4734
                        • United States of America

                        #51
                        Re: Using higher amperage receptacles with lower amperage breakers

                        Originally posted by stj
                        do you know that your whole house or street would be connected or cut live?

                        pro's just isolate themselves, we dont need to cut power to something we wont touch.
                        Here, they don't hook up the lines to the house live. They call the electric company who kills the power and they won't turn it on until it's been inspected.
                        -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                        Comment

                        • Spork Schivago
                          Badcaps Legend
                          • Mar 2012
                          • 4734
                          • United States of America

                          #52
                          Re: Using higher amperage receptacles with lower amperage breakers

                          Originally posted by delaware74b
                          Spork - the clamps on the GFCI's and spec grade devices are not the same as back-stabbing on the cheap devices.

                          This is pig-tailing, although I don't use that brand of wire nut:
                          https://s-media-cache-ak0.pinimg.com...d313d72737.jpg

                          Live work? Sure I do it. With permission from the local power utility, my boss and I have permission to pull meters and reinstall for panel repairs and service replacement.
                          So what are the benefits from using the pigtails? I've ordered my GFCI outlet. When it comes, should I wire it up using pigtails like what's in the picture?
                          -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                          Comment

                          • Spork Schivago
                            Badcaps Legend
                            • Mar 2012
                            • 4734
                            • United States of America

                            #53
                            Re: Using higher amperage receptacles with lower amperage breakers

                            Originally posted by redwire
                            Spring-clamp connectors can be good quality, they're the only thing allowed on locomotives due to vibration and temperature swings. Europe loves them for DIN-rail panel stuff.

                            But on outlets they suck badly. I never use them because copper oxidizes with brass and crappola connection happens, with age and chinese drywall H2S gas.
                            I can take 10 seconds and tighten the screws. Really.

                            As far as live work goes, it's all fine until the day you disconnect a wire and it unexpectedly springs back and touches something grounded or the opposite phase. Poof! Had an arc happen doing that. You need eye/face protection!
                            My old apartment up in Deposit had fuses but the lower neighbor had access to the fuse box. With permission from the land lord, I replaced all the two prong receptacles with three. I did all of them live with no problems, until I got to the last one. The screw driver caught on the white wire while I was unscrewing the black. There were sparks and then no power. The downstairs lady was pissed. I told her the landlord said I could do it though and just replaced the screw. I'm glad I didn't get hurt.
                            -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                            Comment

                            • stj
                              Great Sage 齊天大聖
                              • Dec 2009
                              • 30963
                              • Albion

                              #54
                              Re: Using higher amperage receptacles with lower amperage breakers

                              just one more joint to fail,

                              Comment

                              • stj
                                Great Sage 齊天大聖
                                • Dec 2009
                                • 30963
                                • Albion

                                #55
                                Re: Using higher amperage receptacles with lower amperage breakers

                                Originally posted by Spork Schivago
                                The screw driver caught on the white wire while I was unscrewing the black.
                                that's why electrician's screwdrivers are insulated down to the tip!!

                                Comment

                                • Spork Schivago
                                  Badcaps Legend
                                  • Mar 2012
                                  • 4734
                                  • United States of America

                                  #56
                                  Re: Using higher amperage receptacles with lower amperage breakers

                                  Originally posted by keeney123
                                  I am trying to explain the new connector that the wire can be put in the back of. These are not spring loaded like the old connecters that were no good. The screw on the side of the connector is what causes the tightening down on the wire. It is much like how one puts a wire in a breaker terminal and tightens down on a screw. Look at the picture on the right hand side of redwire's post 46. The left one is the old connector. Noticed the screw is not tightened on the picture on the left.
                                  Is there a way to tell without tearing apart the device? Also, are there any benefits to backstabbing? If not, I'll probably just do the screw connection.

                                  I know in our old house, my dad hired a "master electrician". When I say master electrician, I really mean a scam artist.

                                  Anyway, half the outlets didn't work. We tore them apart and where he screwed the wire down, it had come off on a ton of outlets and switches! Even at the breaker box, there were white wires that weren't connected. Whenever we flipped the switch in the bathroom, we'd see a spark. I tore off the wall plate and the connections there looked good. It took me a while to figure out what was causing it. It was the white wire in the breaker, it wasn't connected at all! Every time we flipped the switch, at the breaker box, you could actually see the spark arcing from the white neutral wire to the neutral busbar.

                                  With the good connections in the back, are they less likely to come off? Personally, I always try to bend the wires into a circle or almost a circle, around the screw, and then tighten the screw down. I have them bent in such away where they grab when the screw is tightened.

                                  The "master electrician" had his wires going every which way. Some grabbed when the screw was tightened, some were bent the wrong way and wanted to slip out. He didn't know any codes at all. We had a scuttle and you couldn't even get into the attic, there were wires going over the freaking scuttle! That's not up to code at all. We had to slip the scuttle thingamajig out of the way and slide up through one of the wires. What a rip off! My dad went for the cheapest guy he could find, 10$ an hour. I told him a master electrician isn't no 10$ an hour! But his "friend" recommended him. Such a freaking scam! He also had my dad do most of the work! He just supervised! I spoke my mind, right in front of him, and the guy got really pissed and asked why I don't do the job if I don't like his work. And I said because we're freaking paying you!!!!
                                  -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                                  Comment

                                  • Spork Schivago
                                    Badcaps Legend
                                    • Mar 2012
                                    • 4734
                                    • United States of America

                                    #57
                                    Re: Using higher amperage receptacles with lower amperage breakers

                                    Originally posted by stj
                                    that's why electrician's screwdrivers are insulated down to the tip!!
                                    Yeah, this was just a normal screw driver, not something that was designed for the type of work I was doing. I still don't have one of those electrician screwdrivers. I should invest in one.

                                    My Uncle told me this story before he tied. There was this guy he used to know that used to like to show off for the ladies. They'd party down by the river and there was this tower with all these electrical lines on them. This guy would climb up there and jump from the tower to one of the wires and climb around on it. One night, he climbed up and went to jump to the wire but made contact with the wire while his feet were still on the tower. My Uncle said he lit right up. He smelled really bad and I guess he was somehow stuck to the wires. Like he melted to it or something. I was maybe 13 when he told me this so I don't remember all the details.

                                    When I was even younger, up at my parents house, there were these two big white birds on the telephone pole. They did something that made them light up and die. I ran inside and told my dad, he came out and looked at them. They were on the ground smoking. My dad said they probably pecked the wire or something. I don't know if they were seagulls or what. It was the only time I seen birds die like that.
                                    -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                                    Comment

                                    • stj
                                      Great Sage 齊天大聖
                                      • Dec 2009
                                      • 30963
                                      • Albion

                                      #58
                                      Re: Using higher amperage receptacles with lower amperage breakers

                                      about the screwdriver,
                                      in a pinch you can fit a couple of layers of heatshrink tubing over the shaft of a regular driver.

                                      i have done that with one of those drivers that takes the hex-ended bits.

                                      Comment

                                      • keeney123
                                        Lauren
                                        • Sep 2014
                                        • 2536
                                        • United States

                                        #59
                                        Re: Using higher amperage receptacles with lower amperage breakers

                                        Originally posted by Spork Schivago
                                        Is there a way to tell without tearing apart the device? Also, are there any benefits to backstabbing? If not, I'll probably just do the screw connection.

                                        I know in our old house, my dad hired a "master electrician". When I say master electrician, I really mean a scam artist.

                                        Anyway, half the outlets didn't work. We tore them apart and where he screwed the wire down, it had come off on a ton of outlets and switches! Even at the breaker box, there were white wires that weren't connected. Whenever we flipped the switch in the bathroom, we'd see a spark. I tore off the wall plate and the connections there looked good. It took me a while to figure out what was causing it. It was the white wire in the breaker, it wasn't connected at all! Every time we flipped the switch, at the breaker box, you could actually see the spark arcing from the white neutral wire to the neutral busbar.

                                        With the good connections in the back, are they less likely to come off? Personally, I always try to bend the wires into a circle or almost a circle, around the screw, and then tighten the screw down. I have them bent in such away where they grab when the screw is tightened.

                                        The "master electrician" had his wires going every which way. Some grabbed when the screw was tightened, some were bent the wrong way and wanted to slip out. He didn't know any codes at all. We had a scuttle and you couldn't even get into the attic, there were wires going over the freaking scuttle! That's not up to code at all. We had to slip the scuttle thingamajig out of the way and slide up through one of the wires. What a rip off! My dad went for the cheapest guy he could find, 10$ an hour. I told him a master electrician isn't no 10$ an hour! But his "friend" recommended him. Such a freaking scam! He also had my dad do most of the work! He just supervised! I spoke my mind, right in front of him, and the guy got really pissed and asked why I don't do the job if I don't like his work. And I said because we're freaking paying you!!!!
                                        The benefit I would say is that the wires in the box can be shorter, will fit in the box better, less exposed surface to short out to the box and it takes less time. Do what makes you comfortable.
                                        The easy way to tell is put a wire in the back, if it can not be pulled out without resistance then it is the wrong type. The ones that work correctly you need to tighten the screw down for the wire "not" to move. You can then loosen the screw and the wire will again be able to come out. You will need to strip the end of the wire to a certain length. You can figure this out by simply stripping one wire a 1.5 inches and measure the amount inserted into the receptacle. You will then know approximately how far to strip a wire You can also ask the person you buy the product from and to verify they are telling you the truth carry a number twelve wire with you and verify it in front of the sales person.

                                        Comment

                                        • keeney123
                                          Lauren
                                          • Sep 2014
                                          • 2536
                                          • United States

                                          #60
                                          Re: Using higher amperage receptacles with lower amperage breakers

                                          Originally posted by stj
                                          about the screwdriver,
                                          in a pinch you can fit a couple of layers of heatshrink tubing over the shaft of a regular driver.

                                          i have done that with one of those drivers that takes the hex-ended bits.
                                          You can also bring a dried piece of wood to stand on.

                                          Comment

                                          Related Topics

                                          Collapse

                                          • BigTroll
                                            help with home a/c and circuit breaker
                                            by BigTroll
                                            while I was gone today the women called me and said the a/c isn't working and the breaker is buzzing so she turned off the breaker. The a/c is a old 1993 model York so its nearing the end of its days, on really hot days the a/c will trip the breaker.

                                            I visually checked the cap and contactor and they looked okay, I also pulled the 250v ac fuses and switched the main ac breaker on and got no buzz. I did get buzz when I put the ac 250v fuses back in and flipped on the breaker nothing but buzzing. could it be a shorted wire or did the circuit breaker just finally give up the ghost?...
                                            09-05-2020, 07:53 PM
                                          • notallbad
                                            Rockworth breaker burning out motor
                                            by notallbad
                                            Got given this breaker to fix, armature had failed so replaced and the same thing happened.

                                            Its a 240v heavy duty breaker as opposed to site 110v.

                                            The 1st armature was bought from aliexpress and advertised as 240v but burnt out within 2 minutes light use taking the 13amp fuse with it and the 2nd bought from ebay (german seller) started to get very hot and begin to smoke so hopefully saved it by shutting it off quick at the first sign of smoke but have now tested the x2 safety cap and its not reading 0.22uf, much lower.

                                            Theres very little to it really on the...
                                            08-16-2024, 04:46 AM
                                          • petehall347
                                            correct way to wire this breaker
                                            by petehall347
                                            ok i have this new mcb 40 amp breaker but its not marked which is line in and load and live and neutral .everywhere i look they are wired differently . i know single ones its line in at the bottom and load at the top . the data sheet doesn't say .it only has a diagram on it ....
                                            07-10-2024, 01:37 PM
                                          • beetle1303
                                            Electric oven tripping circuit breaker after turned on for 3-5 minutes
                                            by beetle1303
                                            My electric oven was working fine all the while from purchased 2 years ago. I have been using it weekly for about a year, but stopped using for a year now since then.
                                            When I turn it on again yesterday, the tripped the circuit breaker and whole house no power supply. I reset the circuit breaker, and retried. Same thing happened.

                                            This is what happened:
                                            - Turned on the oven power supply, set temperature to 200c, everything worked for a few minutes, then the power tripped. Oven was warmed/hot.
                                            - Reset circuit breaker, retried, same thing happened.
                                            ...
                                            05-03-2020, 09:18 AM
                                          • sew333
                                            monitor AORUS AD27QD - short circuit and tripped breaker.
                                            by sew333
                                            Hello. I had a good monitor AORUS AD27QD. Yesterday when i was sleep i left monitor on like always. When i woke in morning there was not power in house. Something tripped breaker/fuse.
                                            When i turn up breaker and power back in,monitor just refused to turn on. So monitor i guess tripped breaker somehow and make short circuit.

                                            PC starting normally. Only monitor get damaged.
                                            During night only pc was running and monitor. Other devices was off.

                                            Is this possible that monitor can trip breaker?
                                            02-24-2020, 07:46 AM