What is telephony? where does the VCC come from?
    Re: What is telephony? where does the VCC come from?
    That bridge rectifier is on the main unit so more than likely that the two ~ pins are connected to the transformer winding.
    What ACV do you get between those two ~ pins?
    • keeney123
      Lauren
      • Sep 2014
      • 2536
      What would be good at this point is to determine on the remote board where the voltage is being generated. We know that the main board it want is generating the voltage on remote board. What we don't know is the link between the voltage on the main board and the remote. By ohming out the trace on the remote board with the R11 connector disconnected you will find out where it is coming from on the remote board. Once you find that then you will be able to find out the link from the main board. So you can physical look at the trace and follow it with the ohm meter. If the other people's input is that it is coming from a particular place that can be ohmed out to verify that is correct. Again the problem is the voltage on the chip on the remote board has to get 5volt min. 4.75 volts DC to work. Following this line of thinking will lead you to why there is no 5 volts DC on that chip. Sometimes, not always, engineers and physic professors know to much about the circuitry. They then think they can skip sets in troubleshooting. The problem happens when they make an error. Instead of a typical error it is complicated because steps have been skipped, so what I would do for your own benefit is when they tell you a particular thing verify that it is the case. I approach a problem like Archimedes. First we do not know anything about a problem, but we must make a decision. Once we make a decision we observe the outcome. Based on that outcome we then make another decision and so forth and so on. We end up getting better and better at dealing with a problem, but we are never perfect at the problem.
        • 31061
        damn, i thought i was looking at the slave panel!
        • fzabkar
          • Mar 2009
          • 772
          The remote PCB is powered from the main board, not vice versa.
          • fzabkar
            • Mar 2009
            • 772
            AISI, the incoming supply at the remote PCB is regulated as follows:
            Code:
                  "15H"
                .---------. +1.875V .--------. +2.36V .-----------.
            RJ11-B |     |  Cin  |    |  Cout  |      |
              o------>|--+-------+----|in  out|----+-----|      |
             -1.1V |   | |  |  |    |  |   |  MCU  |
                |   z |  |+  |    |  |+  |  RS485  |
                |   A |  ===  | LP2951 |  ===  | display |
                |   | |  ---  | reg  |  ---  |      |
            RJ11-C     |    | 100uF |     | 100uF   |
              o----------+-------+--------+---------+-----------'
             0V               |
                            GND
            The RJ11-B input appears to be an AC waveform sitting on a -1.1V DC bias.
            I'm guessing that the "15H" component provides reverse polarity protection and voltage clamping.
            The rectified input is filtered by Cin, but the voltage subsequently decays during the negative AC cycles. It appears that Cin could be leaky or low in capacitance, or perhaps "15H" is leaky.
            Cout is charged during the peak of the AC input and appears to retain its charge during the negative AC cycles.
            That's the only scenario that I can come up with to explain the observed measurements. It would REALLY help to see what is happening on a scope.
            • keeney123
              Lauren
              • Sep 2014
              • 2536
              Yes, I know this, but I do not know if there is a voltage step down to get 5 volts on the remote board. He verified this when he unplug the R11 connector and got o volt across the transmitter IC on the remote bd. There could still be some type of weird grounding that the designer created or it is just that the voltage is coming from the main board. The voltage could be of a higher amount and a DC to DC converter could be stepping it down on the remote board. The problem still exist on the remote board as not having at least 4.75 volts DC on the transmit IC. The IC will not function with less then this so no communication will occur between the two boards.
              • scampo77
                • 233
                #47
                cant I just put a NPN transistor in place of the 15H and see what happens? should I order new communication ICs for each end?
                it makes sense that something in the remote side is causing the 4.5v to drop, when I unplug the remote the output voltage bounces back up to 4.5-5 and when I plug the remote back in, the voltage drops again to 3v
                • fzabkar
                  • Mar 2009
                  • 772
                  I wouldn't touch the remote board. The problem is with the RJ11-B voltage on the logic board. Trace it back to its source, probably near the bridge rectifier. Test for continuity with the + terminal of the bridge, or each of the PCB interconnect pins.
                  • keeney123
                    Lauren
                    • Sep 2014
                    • 2536
                    It is difficult of working without schematics. For fzabkar theory you could leave the RJ11 connectors unconnected and follow the voltage as he said to find out if there is indeed a voltage problem on the main board. You did say every thing on the main board was working and only the remote was not working? This is how you trouble shoot a board. You follow one train of thought to see if it is correct and if it is not then you modify you train of thought.
                    • keeney123
                      Lauren
                      • Sep 2014
                      • 2536
                      Just one more thing. While your troubleshooting this circuit keep in mind that why the two boards are not talking to each other is because the voltage on the communication chip on the remote is not getting at least 4.75 volts. Right now it has nothing to do with the communication lines between the two boards. A good procedure to follow is check voltages first. Then check the control lines. Lastly check the data and address lines. At all possible have a schematic in hand.
                      • scampo77
                        • 233
                        #51
                        I have found a second non functioning logic board, I have something I can poke and remove parts from to see traces better. please don't comment that the caps are corroded or the solder traces are bad. I am dissecting this one with the intention of throwing it away when I am done with it.
                        I have removed all of the RJ11 jacks on this donor board to better see the traces. this "B" port seems to go to the neighboring RJ11 port for the auto start module which I do not have hooked up. then it goes to a capacitor then to me it looks like ground, it takes off and goes all over the place on both sides of the board.
                        I am now getting 0vdc at the "B" terminal that I am chasing around. And I am getting 4.5VDC on terminal "D" with or without the remote board attached
                        I have tried calling multiple repair centers and Magnum directly with all of the power of my charm and non of them have access to diagrams or schematics or any engineering side of these repairs. These have been designed to be replaced like computer video cards, the only downside is that the logic board is $400 and the remote board is about $300 and the entire inverter is about $2000. All of these options are way out of my budget.
                        • keeney123
                          Lauren
                          • Sep 2014
                          • 2536
                          So on the main logic board the regulator 295151ACS is a 5 volt regulator because it has no XX numbers after it. The XX numbers would be like -2.5, -3.0. This is the data sheet for that chip.
                          If this is what is generating your 5 volts regulated to the remote board Then it has very tight tolerances. It you are reading 4.5 volts that would be out of spec. I also noticed that there is way too much solder on these components on the main logic board. I know if a capacitor gets to much heat near its plate you can damage to connection in a way that the cap will appear to work, but it will not perform correctly.
                          • scampo77
                            • 233
                            #53
                            GOOD NEWS!!
                            I found a damaged trace under one of the RJ11 jacks. (photo enclosed) this connected "B" terminal to the fuse. the huge trace I was chasing around turned out to be B+. It is de coupled by a cap and protected by a fuse (look on the previous post photos) I repaired the trace and now I have MUCH better voltages to work with.
                            Now the "B" terminal is B+ and I have much better voltages on the remote board (photo enclosed).
                            The inverter is still going into some kind of protect mode. As soon as I apply battery voltage I throw a big relay and it will not power up like it was before. I am hoping this burnt trace is a step in the right direction.
                            I have enclosed measurements from my suspect 5v regulator and I have rock solid 5.00 VDC.
                              That is good progress, so the remote is fed by 5VDC not AC which makes a lot more sense.
                              • fzabkar
                                • Mar 2009
                                • 772
                                The remote is fed by 14.7V, not 5V.
                                • keeney123
                                  Lauren
                                  • Sep 2014
                                  • 2536
                                  Originally posted by scampo77
                                  GOOD NEWS!!
                                  So now that problem is fixed. We need to concentrate on this new problem. We need to know where the battery voltage is going too on the inverter. It is possible that the relay is held in by another circuit.
                                    I am confused:
                                    Per Post 45 : AISI, the incoming supply at the remote PCB is regulated as follows: per diagram: So RJ-1B is fed by 14.7V? Feeding 14V to drop down to feed LP2951 3V? That is lots of Vdrops on this LDO.
                                    Post 52: So on the main logic board the regulator 295151ACS is a 5 volt regulator because it has no XX numbers after it. The XX numbers would be like -2.5, -3.0. This is the data sheet for that chip.
                                    Post 53 'I have enclosed measurements from my suspect 5v regulator and I have rock solid 5.00 VDC.'
                                    So what is the Voltage feeding the Remote Module for sure?
                                      Double posted.
                                      • fzabkar
                                        • Mar 2009
                                        • 772
                                        budm, look at the 4th photo in post #53. The reading of 4.5V appears to be for one of the data pins of the RS485 transceiver IC, not the power supply.
                                        BTW, I agree that the 14V-5V in-out voltage differential is absurdly high, but that's the way it appears to be designed. If we knew the identity of the "15H" part, then perhaps we could determine the allowable input range.
                                          • 31061
                                          volt-drop over that crappy cable must be taken into account by the designers.
                                          • SluggerB
                                            Help with trying to fix phone that is not charging (Pics inside)
                                            by SluggerB
                                            I have two TCL A30 phones.
                                            Old Phone: This phone worked fine for years, then stopped charging If you plugged a charger into it, the phone would make the charging sound, the phone would tell you it is charging, but the battery icon would not have the charging symbol in it and the battery would not charge.I tried new battery, same behavior.
                                            New Phone: Works fine, bought as a donor board to try and repair Old Phone
                                            My interest here is to repair Old Phone, using components parts off New Phone if needed. I am not interested in replacing Old Phone with New Phone....
                                            08-12-2024, 08:11 AM
                                          • keeney123
                                            new OS on a Sonim XP5s phone
                                            by keeney123
                                            To you programmers out there I want to know if it is possible to put a new OS on the Sonim XP5s phone? I only need this phone to make calls, receive calls, have a list of contacts and be able to call voice mail.
                                            I bought this phone new Sep.2021 as an unlock phone from a third-party seller. The phone worked fine until Jan 2022. I then had intermittent problems with the sound setting resetting itself. One of the settings, outdoor, would go to silent all by itself. When in silent mode it does not indicate a call has come in. I missed very important phone calls. All the other setting in sound...
                                            05-13-2022, 07:19 PM
                                          • mikey5791
                                            Help with Samsung Galaxy J7 Prime phone
                                            by mikey5791
                                            Got this smart phone free from a guy who dropped it hard until the lcd display cracked with no seen display.
                                            Opened it and found the display ribbon cable partly damaged. I charged the phone full in 2 hours time, the led red light turns to green indicate full charge.
                                            Then i use a usb cable connect the phone to laptop but it only showed as media player with firmware version. Too bad there is no option to check folder.
                                            Does anyone know any method to check if the phone is working good? Looking forward for any advice and help possible.
                                            If tested the...
                                            09-15-2021, 07:54 PM
                                          • Dannyx
                                            Cisco IP phone F-up
                                            by Dannyx
                                            Good day folks. I had a little f-up over at my new shop today and it made me pretty angry, but at the same time it determined me to try and figure out what could've happened there. This is only going to be a speculative discussion since I don't know the exact layout of our network, hence I don't know what's going on past our room. So:
                                            The repair shop where I sit is situated in a remote building down the street from the main building. There's a Cisco IP phone in this room, a 7911, like the rest of the company uses. There's obviously some sort of networking going on between the two...
                                            11-27-2018, 12:39 PM
                                            Nokia C2-01 RM-721 RM-722 Phone Schematic
                                            The Nokia C2-01 RM-721 RM-722 was a mobile phone produced by Nokia. The Nokia C2-01 supported 3G and had a 3.2 megapixel back camera. It had a single SIM card. The handset was introduced to the markets in 2011. It replaced its predecessor, the Nokia 2700 classic and Nokia 2730 classic and has improved specifications....
                                            11-05-2024, 07:40 AM
