Controlling heater with rheostat and fotek ssr
  • xboxhaxorz
    • Jan 2011
    • 196
    I have a 220v 500w heater that i want to be able to control with a 25 amp DA fotek relay along with a 5 amp fuse. I have a potentiometer that i was using, but the ssr light would not come on when i wired it and i am not quite sure if i actually need to get a rheostat, the fuse is bypassed during this test.
    source: http://www.auberins.com/index.php?ma...roducts_id=332
    Re: Controlling heater with rheostat and fotek ssr
    Show us how you wire up your circuit.
    • Longbow
      • Jun 2011
      • 623
      You are on the right path with a SSR, although this term is too general. Heater control is a huge subject in most industrial manufacturing settings. The 2 possible methods of controlling a high wattage heating element are phase angle control and zero cross firing. Usually a phase angle fired SCR is chosen for small load applications but it creates lots of RFI. Most large scale heating control is done using zero cross firing of back-to-back SCR's. Separate control circuits are used to drive a dual SCR block, which must have a heat sink. The controls need not be complicated if they are open loop. Industry standard is called a 20 mA control loop and all heating control SCR blocks will accept that control signal. Going up in expense, a closed loop controller can be plugged right in to the same SCR block. You will want a much more robust fuse in these cases along with MOV protection for the SCR's.
      Is it plugged in?
        The question is, are you trying to just turn the heater on and off or you are trying to be able to adjust the amount of heat from the heater?
        • xboxhaxorz
          • Jan 2011
          • 196
          I will provide circuit information when i get back to my equipment
          Initially i purchased this item http://www.ebay.com/itm/161166795326...84.m1439.l2649
          I felt though the quality of this was not too high and may be the culprit if failure arises so i looked into the SSR option
          The heater being used is a 60 x 60 ceramic heater, its actually 230v, 500W and 750c
          I went with a ceramic fuse at 5 amps, when i tested another heater which is 250w using a kill o watt at 120v it was using less than an amp but due to voltage worked at 70w
          My end goal is to have a controllable analog heater to raise and lower the temperature
          I have a PID that i used, but for this particular product i dont want it digital
            "230v, 500W" If the heater is made for 230V, the current draw will be 500W/230V = 2.17A.
            "which is 250w using a kill o watt at 120v it was using less than an amp" If this 250W heater is made for 230V then heater resistance will be 211 Ohms so the current draw with 230v applied = 1.09A, but the same heater (211 Ohms) at 120V then current draw will be 0.57A. So you need to know if the heater is made for 120 or 230V operation.
            If the resistance remains the same, double the voltage applied to the load will result in quadruple the Wattage.
            So basically you need to vary the power using TRIAC (or back to back SCR to get full wave) with controller to be able to adjust the firing angle to give you variable heat you need. It should also have good RFI/EMI fllter to reduce the generated noise.
            I would get the unit that have at least 50% higher capacity than the load requires.
            That $4.99 EBAY 2000W SCR module does not look like it can handle 2000W, no filter, no protection, etc.
            http://sound.westhost.com/lamps/dimmers.html
            • xboxhaxorz
              • Jan 2011
              • 196
              the heaters are definitely 230v i THOUGHT i could use them at 120v but was wrong so i got a transformer which is rated for 500 watts so now i am operating them at the proper voltage
              my issue now is that the SCR module i bought does not work, i figured it would not tolerate 2000w but at least 250w or 500w
              i have about 5 pcs SSR relays http://www.amazon.com/40A-SSR-Solid-.../dp/B004HZLMTW that were lying around so i figured i could just use those instead of the faulty SCR to make it analog using a potentiometer
                SSR is fully on or fully off (it done using SCR or TRIAC for switching instead of electro-mechanical relay with mechanical contacts) so if you try to adjust the output with POT is not going to work.
                SSR input control can be anything from 3-32VDC without burning up the Optoisolator inside is also isolated from the output circuit so it can be controlled by logic circuit.
                The amount of the SCR or TRAIAC conduction time is done with RC Phase angle firing control circuit.
                That one from EBAY, you can see the pot and R-C circuit for Phase angle firing control, as shown, it is a 2000W Dimmer.
                We also do not know if the load side has to be isolated from the control side for safety or not for your requirement.
                • xboxhaxorz
                  • Jan 2011
                  • 196
                  I understand. So this is a special SSR then basically an SSVR as it mentinos? http://www.auberins.com/index.php?ma...roducts_id=332
                  It would be great if you could point out a product that will allow me to control the heater via analog without use of PID controller.
                  I found some information on this forum as well http://www.homebrewtalk.com/f170/pid...s-ssvr-429498/
                    That SSVR is the high current dimmer module with Pot for adjusting the power applied to the load.
                    What do mean by via ANALOG, the pot is the analog which will control the output of the module. Are you talking analog output of the black box that put out variable DC voltage from 0~5VDC, 5VDC= MAX output of the module, 0V = no output? Clarify the word analog and what is it that you will use to control the module instead of using the Pot that comes with the module.
                    The pictures as shown for the connection and function is very simple:
                    • xboxhaxorz
                      • Jan 2011
                      • 196
                      When i mean analog i mean using a dial knob versus using a digital PID
                      • redwire
                        • 3912
                        Check the Fotek SSR part number you are using.
                        Fotek have some (VA=adjustable series) that have a potentiometer input which does phase control.
                        Their (DA=on/off series) is for only switching loads on or off (zero cross).
                        I think you have the two mixed up.
                        • Longbow
                          • Jun 2011
                          • 623
                          Seems like the OP is confused about what that product is and how it is used. The product detail indicates that it is a phase fired device, similar to a light dimmer and is capable of handling a load current of 25 amperes. You can use it to control either 120v mains or 240 volt mains.
                          The SSR device has a built it phase controller. In other words, it has the controller circuit built into the device and requires only the external pot. Very simple. Heater control IS done using "on-off" devices due to the high currents. Just mount the SSR on a heat sink and fuse it. My numbers indicate that the heater you desicribed will draw just over 2 amps @ 240v. So a 5 amp fuse would be sufficient. Use an industrial fuse like this:
                          http://www.littelfuse.com/products/f...lc/slc005.aspx
                          Most high power SSR devices can be used with a standard 20 mA open-loop controller available at the manufacturer's web site. PID controllers are closed-loop industrial devices and not needed for simple home projects. PID = proportional, integrative, derivative for those desiring extra credit.
                          Is it plugged in?
                            Heater element wire type instead of a fuse when troubleshooting a short circuit DIY
                            by sam_sam_sam
                            I was Ollie today which is a close out / surplus outlet store I do not go in there to often because you find things that you should not be tempted by but that is a another story
                            I saw a small space heater that used a wire type of heater element which I been looking for a while but not really hard mind you but when I saw this I grabbed it I going to go back tomorrow and buy the last one that is like the one I bought today because I need the heater element and the ceramic insulators and more of heat element wire because this one has two different wattage settings one 1300 watts ( tap...
                            12-16-2023, 08:39 PM
                          • corrize
                            A funny fuse story – Lumix LX100 II
                            by corrize
                            Hello, I disassembled this dead camera, and found this WTF… Two fuses soldered one above the other !
                            I was pretty sure nobody touched it before, but that can't be from factory. There is flux, and capacitor is probably missing.
                            The other weird thing : the fuses are « G » fuse : (0.75A – 8V), seems very low. The original fuse should be « O » : (32V 2,5A).
                            There is « O » mark beside. All fuses have the same mark letter on main board. So, I can deduce it's a « O » fuse.
                            And this correspond to the issus I saw : when I plug the battery, I measure the voltage dropping...
                            10-19-2023, 09:58 AM
                          • nop
                            Busted tankless electric water heater control board
                            by nop
                            Hi. I have an old Bosch/Powerstar AE125 water heater in my cabin whose control board died for the nth time. This time around, I figured I'd try to diagnose and repair it. At the end of the board's life its power indicator LED will quickly cycle on and off as water passes through the heater, rather than remaining steadily on as it normally would, and water at the tap remains cold. Slightly increasing pressure in the system by closing the outlet valve seems to delay the inevitable for a little while.
                            Here's all the info I found from Bosch regarding troubleshooting the board:
                            04-27-2022, 09:57 AM
                          • madan1
                            Diesel heater emergency power supply / poor man's UPS
                            by madan1
                            Hello everyone.
                            Some background - I have one of those chinese diesel heaters, which I'm using to heat a garage. Probably most of you are familiar with that units, but here is some basic info - the main heater body is enclosed with the motherboard+sensors unit inside a plastic case. The heater has a glow plug, that works only when the unit is starting (start the fire in the burner) and stopping (make sure to completely burn the fuel inside the burner) and two fans on a single motor. One fan is used to push fresh air in the burner, the other is used to push cold air in the case and...
                            12-18-2022, 08:05 PM
                          • jesterace
                            Samsung UE46ES8000 Blown fuse but no other signs of short
                            by jesterace
                            Hi I wonder if anyone might be able to steer me in the right direction. I have this Samsung UE46ES8000 TV and it went bang during use. The main fuse on the PSU board is open. I've checked every diode/mosfet/transistor I can see and nothing appears to be short to cause the fuse to go. The DC output of the bridge rectifier is not short either. I've seen online that some of these models are known for having their PFC mosfet or other mosfets shorting and blowing the fuse but i'm not seeing that here. If anyone aware of these models having any issues to cause this? I'm reluctant to just replace the...
                            09-11-2024, 03:14 PM
