Originally posted by stj
View Post
Announcement
Collapse
No announcement yet.
anyone recommend an earth leakage clamp meter ?
Collapse
X
-
I got confused by the Megger LT6 Loop Tester - it looks like a vanilla ohmmeter but "The test current, up to 25 A, is dependent on the impedance of the phase-earth loop being measured and flows for two half cycles of the supply voltage."
So I think it somehow imposes a signal on a conductor and looks at the resulting voltage blip? Maybe it uses a CT to inject current on a conductor. That would trip a RCD too.
Comment
-
It says the same thing - "25A test current (20Ω range) ... for 2 half cycles of AC (20msec)."
Have to do a teardown of one to see how they are pumping so much current through for the impedance test, yet it can take a mains surprise.
It looks really good. Don't use them in North America and we should.
The impedance test pulse might be fast enough to not trip a RCD, not sure what the response time of them is.
D-Lok for RCD's rated 10mA or less, might trip.
Comment
-
North American GFCI mainly for shock protection and GFCI duplex outlets are 4-6mA here. I have one powering my workbench.
I see British duplex outlet 10mA but you're kinda dead?
Whole house RCD I guess is 30mA.
I did read cable capacitance can also cause false tripping, long runs >50m.
Comment
-
plot thickens 2 times tripping different days .. but getting close to the tripping issue ,, narrowed it down to one circuit when it rains . this is going to be fun . 10mm armoured cable approx 100 to 120 metres long . hoping its simply at one end or the other as pulling it up for visual inspection isnt going to be easy . if the ends appear good it will have to be cut somewhere near the middle to see which half is bad . or maybe use the megger and try and calculate where it might be . and of course i dont work in the rain so it might fix itself before i start . suppose i could connect a car battery to it and look for smoke coming out of the ground .
Comment
-
you need a time domain reflectometer
BT used to have crude ones with crt's in a compact case, maybe you can find one on ebay.
or something more modern even.
https://www.youtube.com/watch?v=gw_JAc7l8CALast edited by stj; 07-08-2024, 06:41 PM.
Comment
-
Originally posted by stj View Postyou need a time domain reflectometer
BT used to have crude ones with crt's in a compact case, maybe you can find one on ebay.
or something more modern even.
https://www.youtube.com/watch?v=gw_JAc7l8CA
Comment
-
Where does this cable run?
Outdoor armoured cable (TECK cable) is plastic coated over the armour, then you have the plastic-jacketed conductors.
So you need at least the inner conductor's insulation being breached to have a ground fault or leakage.
Or there is a splice, and that's what is getting wet.
One site, we injected compressed air to see if it could make it to the other side.
Comment
-
Originally posted by redwire View PostWhere does this cable run?
Outdoor armoured cable (TECK cable) is plastic coated over the armour, then you have the plastic-jacketed conductors.
So you need at least the inner conductor's insulation being breached to have a ground fault or leakage.
Or there is a splice, and that's what is getting wet.
One site, we injected compressed air to see if it could make it to the other side.
https://www.tlc-direct.co.uk/Main_In...SWA/index.html
Last edited by petehall347; 07-09-2024, 04:23 AM.
Comment
-
today's findings with the swa cable .. disconnect both ends and checked resistance and getting 60k ohms between live and earth .this is same at both ends . disconnected the earth at supply end so now the earth wire is disconnected both ends .its ok because there is local earth rod as i made it terra terra anyway . funny thing is there is 9 volts showing between the disconnected earth and the ground rod . whether this is because of cable capacitance or leakage i do not know .. the trip hasn't tripped yet but its not raining .
Comment
-
Originally posted by stj View Postif you know where the splice is, try watering the ground and see if it trips!
Comment
Comment