anyone recommend an earth leakage clamp meter ?
  • petehall347
    • Jan 2015
    • 4447
    #81
    Originally posted by stj
    rcd test is just a resistor - i suppose a good tester could use a variable resistance somehow to ramp it till it trips in order to calculate the trip current.
    better ones do have automatic ramp test . trip current can be measured with clamp meter . trip time is displayed on rcd tester .
    • redwire
      • Dec 2010
      • 3912
      I got confused by the Megger LT6 Loop Tester - it looks like a vanilla ohmmeter but "The test current, up to 25 A, is dependent on the impedance of the phase-earth loop being measured and flows for two half cycles of the supply voltage."
      So I think it somehow imposes a signal on a conductor and looks at the resulting voltage blip? Maybe it uses a CT to inject current on a conductor. That would trip a RCD too.
        • 31264
        the high current is to detect loose connections or shit crimps etc.
        • petehall347
          • Jan 2015
          • 4447
          #84
          just bought another loop tester . another bargain .. this time its a robin KMP-4120 . it should not trip rcd.s .
          • redwire
            • Dec 2010
            • 3912
            It says the same thing - "25A test current (20Ω range) ... for 2 half cycles of AC (20msec)."
            Have to do a teardown of one to see how they are pumping so much current through for the impedance test, yet it can take a mains surprise.
            It looks really good. Don't use them in North America and we should.
            The impedance test pulse might be fast enough to not trip a RCD, not sure what the response time of them is.
            D-Lok for RCD's rated 10mA or less, might trip.
            • petehall347
              • Jan 2015
              • 4447
              #86
              i cant remember ever seeing a 10ma rcd so cant see it being a problem .
                • 31264
                you wont see a 10mA rcd on 240v - too easy to false-trip one.
                • redwire
                  • Dec 2010
                  • 3912
                  North American GFCI mainly for shock protection and GFCI duplex outlets are 4-6mA here. I have one powering my workbench.
                  I see British duplex outlet 10mA but you're kinda dead?
                  Whole house RCD I guess is 30mA.
                  I did read cable capacitance can also cause false tripping, long runs >50m.
                    • 31264
                    30mA is the common value for 240v
                    • petehall347
                      • Jan 2015
                      • 4447
                      #90
                      along with 100ma .
                      • petehall347
                        • Jan 2015
                        • 4447
                        #91
                        loop tester turned up today . seems to work ok but i suspect it needs calibrating . when i get chance i will check it against the first one i bought .
                        back to the rcd tripping issue it's fixed now and no more nuisance tripping even during heavy rain .
                        • petehall347
                          • Jan 2015
                          • 4447
                          #92
                          plot thickens 2 times tripping different days .. but getting close to the tripping issue ,, narrowed it down to one circuit when it rains . this is going to be fun . 10mm armoured cable approx 100 to 120 metres long . hoping its simply at one end or the other as pulling it up for visual inspection isnt going to be easy . if the ends appear good it will have to be cut somewhere near the middle to see which half is bad . or maybe use the megger and try and calculate where it might be . and of course i dont work in the rain so it might fix itself before i start . suppose i could connect a car battery to it and look for smoke coming out of the ground .
                            • 31264
                            you need a time domain reflectometer
                            BT used to have crude ones with crt's in a compact case, maybe you can find one on ebay.
                            or something more modern even.
                            https://www.youtube.com/watch?v=gw_JAc7l8CA
                            • petehall347
                              • Jan 2015
                              • 4447
                              #94
                              i have a seaward oscar 250 but think its no use for this problem . had it for years and not found a use for it yet . think its more fore for it shit .
                              • redwire
                                • Dec 2010
                                • 3912
                                Where does this cable run?
                                Outdoor armoured cable (TECK cable) is plastic coated over the armour, then you have the plastic-jacketed conductors.
                                So you need at least the inner conductor's insulation being breached to have a ground fault or leakage.
                                Or there is a splice, and that's what is getting wet.
                                One site, we injected compressed air to see if it could make it to the other side.
                                • petehall347
                                  • Jan 2015
                                  • 4447
                                  #96
                                  we call it swa . plastic coat outside the steel wire armoured . there is one splice that was done years ago that's underground .i did that with a proper potted connector .
                                  https://www.tlc-direct.co.uk/Main_In...SWA/index.html
Name:	shopping?q=tbn:ANd9GcTuUvZnt6Y7bdHEr2Zg8OJP1ReLq7daPvvpcIMQEN1GDeQJBDjjntm9QlKRZrEhfGKwCPPvPctQKE9sPQVGVn9OKDEYWt4VSnZeMfqDGXfV.webp
                                  • petehall347
                                    • Jan 2015
                                    • 4447
                                    #97
                                    today's findings with the swa cable .. disconnect both ends and checked resistance and getting 60k ohms between live and earth .this is same at both ends . disconnected the earth at supply end so now the earth wire is disconnected both ends .its ok because there is local earth rod as i made it terra terra anyway . funny thing is there is 9 volts showing between the disconnected earth and the ground rod . whether this is because of cable capacitance or leakage i do not know .. the trip hasn't tripped yet but its not raining .
                                      • 31264
                                      if you know where the splice is, try watering the ground and see if it trips!
                                      • petehall347
                                        • Jan 2015
                                        • 4447
                                        #99
                                        thought about this but if the wet problem is underground surely it will stay wet for lots longer .. this problem goes away not long after the rain stops . its the 60k ohms between live and earth that is a clue here but find it odd its same reading no matter which end of the long cable i measure from unless its bad right near the middle . am hoping the issue is now fixed for now by disconnecting the earth wire . maybe not though thinking about it .
                                        • petehall347
                                          • Jan 2015
                                          • 4447
                                          #100
                                          on another note it only has a 2 pole switch at supply end so going to swap that for a 40 amp mcb so the cable wont completely burn out if it hard shorts ..