anyone recommend an earth leakage clamp meter ?
Collapse
X
-
had plenty of rain and its not tripped . i won't be convinced until after lots more rain . -
at least a year ago if not more like 2 years . it was soaking wet . i left it to dry out in the sun for a while and it felt dry before splicing it . its on a slope and the bad half of the cable is the higher side . but i suppose it could have soaked in more regardless . 9 hours of heavy rain forecast today so if its going to trip its very likely to do so today .Leave a comment:
-
This is probably a good way of seeing if’s a bad connection somewhere but you could still use a megger but here is how I would do where ever you have a spliced connection repair I would soak them one at a time and see if your resistance goes down or not if it does not go to the next spliced connection repair and do the whole cable that way if you do not find anything else at this point you are going to have very hard time figuring out what is still causing the breaker to trip but if it is been in service for a long time I might consider replacing it with a new one if you still have issues then I would recommend inspecting every inch of the cable for nicks and signs of corrosion or pitting of any kind check those areas as wellLeave a comment:
-
Leave a comment:
-
still some insulation leakage going on but that bit looks the worst from i can see , might be the old joiner letting damp in . its hard to tell .. thinking of getting a thermal imaging camera and putting a heavy load on it and looking for hot spots .Leave a comment:
-
Unfortunately you can do anything for someone who does not listen you when you tell them that are electrical wiring in a certain place or area and what is even worse is that they do not tell you that they damaged it so it could have been fixed properly the first time what kind-a contractors are these people anyway
The reason why you use plastic outside rated conduit is that when you are digging you will see the conduit and you know where the wiring is yes we have underground cable here but I still put it in outdoor conduit anyway
I would agree with you if it gets damaged it is harder to deal with but me personally I do not like making splices that are underground for any reason I would rather just have it come up three feet and go back underground for peace of mind and not have breakers tripping when it rains real heavy but that's just meLast edited by sam_sam_sam; 07-11-2024, 07:53 PM.Leave a comment:
-
Why do you not have this cable in a outdoor rated conduit in this country you are required to use outdoor conduit for running electrical wiring except for landscaping lighting 12 volts or under that voltage if I was running landscaping lighting and it was going to be permanent I would use conduit even for thisLeave a comment:
-
mystery solved when one of the lads was looking for the resin joint i did years ago after some idiot lit a fire on it . this is jcb damage from a year or two back . i did warn him about the cables . looks like he badly damaged it then attempted to do a quick tape up job . .. makes the mind boggle it does . now we have to get another resin kit and do a proper repair ..
Leave a comment:
-
Sweet! I figured it would fail that insulation test and there must be some trouble somewhere. Glad you found it.Leave a comment:
-
mystery solved when one of the lads was looking for the resin joint i did years ago after some idiot lit a fire on it . this is jcb damage from a year or two back . i did warn him about the cables . looks like he badly damaged it then attempted to do a quick tape up job . .. makes the mind boggle it does . now we have to get another resin kit and do a proper repair ..Leave a comment:
-
insulation test failed . especially live to ground and ground to armour 0.0 others at 0.3 .. they all should be better than 1.0 hardly any difference testing from both ends of the swa cable .Leave a comment:
-
Yes, with a Megger or equivalent. This should show leakage real fast. I use the Fluke 1587FC for all these leakage tests. I don’t use it every day, but every time I need it, it’s a freaking god send for me.Leave a comment:
-
if you mean with the megger not yet . will do once i have the new switch and wires disconnected both ends , i could also do a psc test but not sure if that will help here
this is same as my insulation tester .
Last edited by petehall347; 07-10-2024, 05:43 AM.Leave a comment:
-
Leave a comment:
-
yes i know it should only connect at supply end really in case of a fault that could make all grounds live . anyway both ends disconnected for testing at the moment . i cant see this causing a problem just when it rainsLeave a comment:
-
the armor is supposed to be earthed, the metal bits that mount the wire to a box see to that.
Leave a comment:
-
The 60k reading will move - the multimeter (Ohms) DC current causes electrolysis like charging a battery with the water and metals there. Try flip polarity and watch the reading.
Another approach is measure DCV to get an idea if it's wet. 3-wire? Or measure Ohms between all conductors and the armour, 4 possible readings to see if how much is leaking to what.
Line/Hot will make water boil and steam and make gurgling sounds if immersed, as a give away.
If many wet readings, I'd prepare to dig up the splice. The water will eventually corrode the conductors and the cable go open circuit.
Do you have frost and soil heaves? That moves cables around unless 1-2m below surface here.Leave a comment:
Related Topics
Collapse
-
by BaldbentleyI am repairing a Fluke 335 clamp meter. After contacting fluke it appears there is no service manual or circuit board/ component list available. I have determined that there us a faulty PNP bipolar junction transistors shown in the pictures. I am having trouble sourcing this transistor. I pulled a good one off of the board and tested it with my component analyzer but I cannot find anything that matches the specifications. Any help locating this part or a replacement would be greatly appreciated.
Thanks... -
by chth96I read EBOOK of Testing Electronic Component and found that
"In order to test the small blue resin coated ceramic disk capacitor which has 104 50v specification,it is possible to test this small ceramic capacitor by making use of analogue meter.
Set to times 10Kohm that has 12v output from the probe to check disorder of ceramic capacitor.
It is not uncommon that testing result of digital capacitance meter is okay,But It show shorted reading when you check it with analogue meter."
Is it really possible to test small ceramic disc capacitor with analogue...-
Channel: General Capacitor Questions & Issues
-
-
by budmUNI-T UT210D/210E Digital Clamp Meter AC/DC Current Voltage Multimeter Temp Tester.
Is it any good? Any body has one?
https://www.ebay.com/itm/UNI-T-UT210.../303564557647?
https://www.ebay.com/itm/UNI-T-UT210.../303570930240? -
by neuronThe factory / reseller ... don't know anything about the device (Schematic, Service manual, etc)
and I need to repair this DMM - Clamp Meter.
2TY - Transistor - Q5 (Diode mode ok)
CHX ??? 5 Pins - U3
C31 ??? Burn,
Tested - V, Ohm, Diode, ºC ... don't see any errors
Thanks in advance for all info
Ruy... -
by jorpecHi
I want to change the scale of an analog meter, to monitor the charge of an li-ion single cell, so the needle at the end would point 4.2 volts and the 0 on the meter would point 2.5 volts or so, i tried to add diodes or a zener in series with the meter but the changes of the ambient temperature also changes the voltage value on the meter
I wonder how i can accomplish this so the meter would be precise at any temperature ?
Thnaks - Loading...
- No more items.
Leave a comment: