Delta TDPS-138AF Avaya no output repair

Collapse
This topic has been answered.
X
X
 
  • Time
  • Show
Clear All
new posts
  • CapLeaker
    Leaking Member
    • Dec 2014
    • 8352
    • Canada

    #21
    Re: Delta TDPS-138AF Avaya no output repair

    No, I did change the 1207A PWM and the comperator on the primary side on the little daughter board. Same result. The PWM isn't getting hot. It doesn't make any sense to me. There is another comperator on the backside of the main board, it also is on the primary. Haven't checked around there yet.

    Comment

    • R_J
      Badcaps Legend
      • Jun 2012
      • 9633
      • Canada

      #22
      Re: Delta TDPS-138AF Avaya no output repair

      Trace that line connected to the 51K resistor, something is drawing way too much current. If it was'nt the ncp1207a then it could be the DAP6A, it is a similar pwm ic.
      Last edited by R_J; 03-06-2020, 11:17 AM.

      Comment

      • CapLeaker
        Leaking Member
        • Dec 2014
        • 8352
        • Canada

        #23
        Re: Delta TDPS-138AF Avaya no output repair

        the DAP6A has its own resistor same size, different value. Haven't gotten around to swap the DAP6A out yet, as I have to take the little daughter board out again. Its like something telling both PWM's to shut down. They don't even try to turn on.

        Comment

        • R_J
          Badcaps Legend
          • Jun 2012
          • 9633
          • Canada

          #24
          Re: Delta TDPS-138AF Avaya no output repair

          They both need to have the HV voltage at least around 50vdc so the startup cell can produce the vcc voltage.
          For the 1207a PWM, I get 1.5V on Vcc and 17.5V on the HV pin.
          On the DAP6A are 1.3V on the Vcc and 6.5V the HV pin.
          The voltage on the HV pins are being loaded down by something, if it's not the ic it must be something else.
          Last edited by R_J; 03-06-2020, 03:09 PM.

          Comment

          • CapLeaker
            Leaking Member
            • Dec 2014
            • 8352
            • Canada

            #25
            Re: Delta TDPS-138AF Avaya no output repair

            Yesteraday I went for why these big resistors heat up. Went to the 1207A PWM, checked again the path between it and the Mosfet it drives and nothing to be found. So I took the Mosfet out, no change. Took the new 1207A out and there was no more current draw on that 51k resistor. So removing the PWM does stop the current draw on the resistor. Put that 1207A back in circuit and voila, the resistor gets hot again. Haven't checked the DAP6A side yet, it functions the same way.

            O.k. so lets say there is a problem with one of these PWM's, something is telling them both to not power up. An error on one side, should affect the other side of the PSU. I don't think that only a 2/3rds of that PSU runs, while the other 3rd doesn't on this PSU.

            Comment

            • R_J
              Badcaps Legend
              • Jun 2012
              • 9633
              • Canada

              #26
              Re: Delta TDPS-138AF Avaya no output repair

              The datasheet say's the ic will not operate with a vcc below 9 volts
              Last edited by R_J; 03-07-2020, 11:13 AM.

              Comment

              • CapLeaker
                Leaking Member
                • Dec 2014
                • 8352
                • Canada

                #27
                Re: Delta TDPS-138AF Avaya no output repair

                I measured that 51k three different times and each time it measured 51k. Correct me if I am wrong, but lets say the resistor changes resistance under load (value going higher) it just would drop the output voltage but should not getting hot to the touch.

                Earlier I had the 1207A out and before I replaced it with a new one, I had full power on both sides of the 51k resistor. I proceeded to check the DAP6A and it still loaded it's 240kOhm resistor down to 6.5V! Now why would that be, unless something is telling BOTH pwm's to shut down.

                To recap: the 380v goes through the 51k resistor to the 1207A. The 380V go through a different 240kOhm resistor to the DAP6A.
                Last edited by CapLeaker; 03-07-2020, 11:13 AM.

                Comment

                • R_J
                  Badcaps Legend
                  • Jun 2012
                  • 9633
                  • Canada

                  #28
                  Re: Delta TDPS-138AF Avaya no output repair

                  The ic's must be getting told to be turned off.
                  I re-check the math and 7ma through a 51k would result in a 357 volt drop (2.64 watts).
                  The dap6 must also be turned off and drawing about 1.5ma

                  It looks like both ic's can be turned off via pin2 (FB pin) So I guess pin 2 must be low on both ic's and could be controlled by a transistor somewhere, and something else could be telling that transistor to turn both ic's off
                  Last edited by R_J; 03-07-2020, 11:39 AM.

                  Comment

                  • CapLeaker
                    Leaking Member
                    • Dec 2014
                    • 8352
                    • Canada

                    #29
                    Re: Delta TDPS-138AF Avaya no output repair

                    Yeah, that's what I am thinking, it's a feedback problem and the FB pins are low on both. I have to trace these FB pins where they go next. I was going to do that in my post 21, but anyway... gonna do it in a bit.
                    Last edited by CapLeaker; 03-07-2020, 12:19 PM.

                    Comment

                    • CapLeaker
                      Leaking Member
                      • Dec 2014
                      • 8352
                      • Canada

                      #30
                      Re: Delta TDPS-138AF Avaya no output repair

                      no dice. the fb pins go to these rectangular opto couplers on the back.

                      Comment

                      • R_J
                        Badcaps Legend
                        • Jun 2012
                        • 9633
                        • Canada

                        #31
                        Re: Delta TDPS-138AF Avaya no output repair

                        That makes sense, but could there also be a transistor connected to them? the only way the optocouplers would shut down the two pwm ic's is if their leds were turned on and the photocel part would then be low resistance. If the led side has no voltage, the photocel side should read open.
                        What is the number on the optocoupler? Are they EL1018?
                        Which opto connects to which pwm ic?

                        It does look like the opto, ic602 could control the opto, IC603
                        Last edited by R_J; 03-07-2020, 03:54 PM.

                        Comment

                        • sam_sam_sam
                          Badcaps Legend
                          • Jul 2011
                          • 6070
                          • USA

                          #32
                          Re: Delta TDPS-138AF Avaya no output repair

                          Originally posted by R_J
                          if their leds were turned on and the photocel part would then be low resistance. If the led side has no voltage, the photocel side should read open.
                          This is in reference to his comment earlier


                          This might be a real stupid question but what is the voltage at the optic sensors on the input side
                          Last edited by sam_sam_sam; 03-08-2020, 07:30 AM.

                          Comment

                          • R_J
                            Badcaps Legend
                            • Jun 2012
                            • 9633
                            • Canada

                            #33
                            Re: Delta TDPS-138AF Avaya no output repair

                            Originally posted by sam_sam_sam
                            This is in reference to his comment earlier


                            This might be a real stupid question but what is the voltage at the optic sensors on the input side
                            Not really, I would have likely asked it next. It is a hard power supply to work on and even harder to try and trace the double sided circuit only with a couple pictures.

                            Comment

                            • sam_sam_sam
                              Badcaps Legend
                              • Jul 2011
                              • 6070
                              • USA

                              #34
                              Re: Delta TDPS-138AF Avaya no output repair

                              Yes I know I have work on some switch power supply board that I have wanted to pull my hair out not that I have much hair left

                              Comment

                              • CapLeaker
                                Leaking Member
                                • Dec 2014
                                • 8352
                                • Canada

                                #35
                                Re: Delta TDPS-138AF Avaya no output repair

                                the PSU is apart at this moment. the 1207a is out and the daughter board too. i've had a few hard to work on power supplies, but i always got them going again. this one has me beat without any schematic to go by. I was thinking on fooling the PSU in a manner where i can turn individual power rails on, even without regulation, like i've done before.

                                Comment

                                • CapLeaker
                                  Leaking Member
                                  • Dec 2014
                                  • 8352
                                  • Canada

                                  #36
                                  Re: Delta TDPS-138AF Avaya no output repair

                                  well, I put that PSU on the "fix later" pile for now. Thanks for everything RJ!

                                  Comment

                                  • CapLeaker
                                    Leaking Member
                                    • Dec 2014
                                    • 8352
                                    • Canada

                                    #37
                                    Re: Delta TDPS-138AF Avaya no output repair

                                    I guess our Province declared a state of emergency. Being bored, I put that PSU back on the bench for further investigation. I've got lots of stuff off the PSU, trying to eliminate a short I found going to the little daughter board. Dousing the board in IPA and feeding power from my lab PSU, I did find a shorted SMD cap in a parallel group of four C912 on the back of the PSU main board. Now I have to find a replacement for that shorted SMD cap put it back together and test again.
                                    Last edited by CapLeaker; 03-22-2020, 10:33 AM.

                                    Comment

                                    • CapLeaker
                                      Leaking Member
                                      • Dec 2014
                                      • 8352
                                      • Canada

                                      #38
                                      Re: Delta TDPS-138AF Avaya no output repair

                                      All in a nutshell, the Delta TDPS-138AF power supply for the Avaya IP500 is fixed!

                                      It's a pretty complicated power supply with 3 negative and 2 positive voltage rails. After a while of poking at it, something was dragging the Vin to the PWMs down. I had to remove quite a few things that were on that voltage line, but the short never went away. After removing all the more sensitive IC's and the little daughter board, I fed that voltage trace power with my lab PSU, cranked it to 12V and 1A, put some IPA on the board and watched, but no bubbles? Came to find out that the problem is on the back side of the board, in 4 parallel SMD 11uF caps (the C912 group). One of them had an almost short. Put a used 12uF SMD cap in from a junker board, reassembled the PSU and Bingo! Works like a charm! :-D Frustrating little thing, but it was a doable repair without a schematic again.
                                      Using this 91% IPA and feeding power trick, never gets old.
                                      Case closed.

                                      Dang, now I am bored again... gotta find something else to put on the bench.
                                      Last edited by CapLeaker; 03-23-2020, 05:56 AM.

                                      Comment

                                      • sam_sam_sam
                                        Badcaps Legend
                                        • Jul 2011
                                        • 6070
                                        • USA

                                        #39
                                        Re: Delta TDPS-138AF Avaya no output repair

                                        Originally posted by CapLeaker
                                        Came to find out that the problem is on the back side of the board, in 4 parallel SMD 11uF caps (the C912 group). One of them had an almost short. Put a used 12uF SMD cap in from a junker board, reassembled the PSU and Bingo! Works like a charm! :-D Frustrating little thing, but it was a doable repair without a schematic again.
                                        Using this 91% IPA and feeding power trick, never gets old.
                                        Case closed.
                                        Could I trouble you to show on the board where the problem was

                                        Thanks

                                        Comment

                                        • CapLeaker
                                          Leaking Member
                                          • Dec 2014
                                          • 8352
                                          • Canada

                                          #40
                                          Re: Delta TDPS-138AF Avaya no output repair

                                          Lucky you, the owner didn't pick it up yet. Here ya go!
                                          Attached Files

                                          if you find these attachements useful please consider making a small donation to the site

                                          Comment

                                          Related Topics

                                          Collapse

                                          • Document Archive
                                            MSI Delta DELTA 15 A5EFK-008 Notebook 15 Specification for Upgrade or Repair
                                            by Document Archive
                                            This specification for the MSI Delta DELTA 15 A5EFK-008 Notebook can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the DELTA 15 A5EFK-008 boardview and DELTA 15 A5EFK-008 schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet,...
                                            09-07-2024, 03:40 AM
                                          • FrancescoV
                                            Onkyo HT-R390 no sound output, video output ok
                                            by FrancescoV
                                            Good morning everyone,
                                            I'm trying to repair an onkyo ht-r390 that has no sound output, despite the volume being at maximum, the rest seems to work; the video output signal (coming from an hdmi input) is present, but the audio is absent. Similar situation if I send an audio signal from any input I have no output.

                                            The firmware reported is the following:
                                            M:1.00/11107BLP
                                            D:?.??/????????
                                            O:1.00/11107AL

                                            The DSP firmware given the question marks seems corrupt.

                                            On the BCHDM-0678 - 25140678 - QPWBCHDM0678A0 board the chip that usually seems...
                                            05-11-2025, 02:59 AM
                                          • corrize
                                            A funny fuse story – Lumix LX100 II
                                            by corrize
                                            Hello, I disassembled this dead camera, and found this WTF… Two fuses soldered one above the other !
                                            I was pretty sure nobody touched it before, but that can't be from factory. There is flux, and capacitor is probably missing.
                                            The other weird thing : the fuses are « G » fuse : (0.75A – 8V), seems very low. The original fuse should be « O » : (32V 2,5A).
                                            There is « O » mark beside. All fuses have the same mark letter on main board. So, I can deduce it's a « O » fuse.
                                            And this correspond to the issus I saw : when I plug the battery, I measure the voltage dropping...
                                            10-19-2023, 09:58 AM
                                          • Document Archive
                                            Surface Mount Fuses Fundamentals Datasheet
                                            by Document Archive
                                            TE Circuit Protection offers the widest selection of surface-mount fuses available for addressing a broad range of overcurrent protection applications. Helping to prevent costly damage and promote a safe environment for electronic and electrical equipment, our single-use chip fuses provide performance stability to support applications with current ratings from .5A up to 20A.

                                            TE Circuit Protection also offers the telecom FT600 fuse for telecommunications applications. This telecom fuse helps comply with North American overcurrent protection requirements, including Telcordia, GR-1089,...
                                            10-07-2024, 06:07 AM
                                          • Junkrepair
                                            Calculating ESR from tan delta -- tan delta's dependence on capacitance
                                            by Junkrepair
                                            I'm finally recapping my Soyo K7VX6 motherboard (aka KT600 Dragon Ultra) and replacing Sacon SZ-series caps. The Sacon SZ datasheet provides a spec for tan delta, but not for ESR, while the candidate replacement caps are specified in terms of ESR.

                                            I found this nice little description of the conversion:

                                            Calculating capacitor ESR from Tan(delta)
                                            https://forum.digikey.com/t/calculat...-from-tan/2633

                                            It mentions that a general spec for tan delta has to be adjusted for the specific capacitance before plugging tan delta into the formula...
                                            06-12-2023, 02:45 PM