    UPS beeping continuously

    Good day folks. This is going to be a general discussion, since it's a rather particular issue with a rather particular device that not many people are going to have around, but the basics may still apply.

    I've got an UPS (called "SPS Pro", whatever) which won't turn on but beeps continuously when you connect its batteries or plug it into the mains. When you apply mains, the display does come on with all the segments illuminated like it's initializing something, but then begins beeping and the display goes out (sometimes, but not always, accompanied by an "overload" indicator). The weirdest thing about this is that I replaced the batteries in it yesterday (takes 2 of them in series for 24v) and it worked perfectly on the bench with nothing plugged it. My colleague then took it to the customer where it was to be installed and on its way there it somehow broke down and when he arrived and tried plugging stuff in, the thing went crazy and he had to come back with it....heavy thing BTW

    I'm suspecting bad caps (pun intended) This thing likes to get hot....VERY hot...in fact when I first got it to replace the batteries, it was SO hot inside of it that the transformer inside was impossible to touch, despite having spent around half an hour in transit turned off, from the client's site to our shop, so I can imagine those caps don't like that, especially 24h a day for the past year or so ! The batteries were completely cracked, bulged and leaky...it was a freak show. Still, it appeared to work immediately after replacing the batteries, and I may have a theory: it was still warm when I replaced the batteries, so the faulty cap(s) might have still been semi-functional, you know how you heat them up slightly and that SOMETIMES tricks devices like TVs and main boards and other stuff to turn on ? After a while sitting on the bench, it cooled down, the caps failed for real this time and here we are...I might try heating it up again gently just to see what happens. Batteries are full, at around 25v in series, so no issues there.

    Point is: what are some of the common failures in UPSs (upsS...is there such a word ? ) that would cause them to behave like this, as if the battery is low or it's being overloaded ? Nothing's blown, of course, at least not visibly. Certainly none of the 8 transistors - I checked those, plus I doubt it would've looked so pristine if one of those went Could it be considered a "software" issue ? Is it really that smart ? I see a micro on there, but that could be for the display for all I know.
    Attached Files
    Wattevah...
  • Curious.George
    Badcaps Legend
    • Nov 2011
    • 2305
    • Unknown

    #2
    Re: UPS beeping continuously

    Originally posted by Dannyx
    Point is: what are some of the common failures in UPSs that would cause them to behave like this, as if the battery is low or it's being overloaded ?
    APC units will squeal incessantly if the battery is dead. Have you checked to see if there is a blown battery fuse?

    Note that the UPS shouldn't be "hot" with no load if on mains power.

    Comment

    • Dannyx
      CertifiedAxhole
      • Aug 2016
      • 3912
      • Romania

      #3
      Re: UPS beeping continuously

      Originally posted by Curious.George
      Have you checked to see if there is a blown battery fuse?
      It does react to the battery being connected to the terminals, so there is power going into it. Having a look at the underside of the board also shows us that there's no other way for current from the battery to get into the board but through the fuses. For a second I thought there might be some hope in what you suggested, like current flowing into a sense line but not to the main FETs, but no...

      I imagine it got hot when he brought it in because those busted batteries were drawing a lot of current, since otherwise the transformer is not doing any (major) work when on mains beside trickle-charging...unless, from what my brief knowledge is telling me, we're talking about a line interactive UPS which this clearly isn't.
      Last edited by Dannyx; 08-10-2018, 02:14 PM.
      Wattevah...

      Comment

      • petehall347
        Badcaps Legend
        • Jan 2015
        • 4434
        • United Kingdom

        #4
        Re: UPS beeping continuously

        as far as know line interactive will raise or lower mains voltage accordingly . and if gets too low it will switch to batteries .. ones i have had have a dip switch for parameters .or is software controlled ..
        warm up the caps see what happens ...

        Comment

        • Dannyx
          CertifiedAxhole
          • Aug 2016
          • 3912
          • Romania

          #5
          Re: UPS beeping continuously

          Tried hitting the board with some hot air but didn't change anything. Strangely, today the problem is consistent: a continuous beep with FAULT shown on the display...
          Wattevah...

          Comment

          • stj
            Great Sage 齊天大聖
            • Dec 2009
            • 31163
            • Albion

            #6
            Re: UPS beeping continuously

            it's taken some knocks, there are a lot of micro-cracks in the soldering.

            Comment

            • stj
              Great Sage 齊天大聖
              • Dec 2009
              • 31163
              • Albion

              #7
              Re: UPS beeping continuously

              btw, after caps, micro-cracks around pins of large or heavy parts or connectors is the most common fault on stuff.

              Comment

              • Dannyx
                CertifiedAxhole
                • Aug 2016
                • 3912
                • Romania

                #8
                Re: UPS beeping continuously

                Not too many large components on this thing...just those FETs. Guess it's worth a reflow nonetheless. Normally, it should fire right up in battery mode when it detects no AC. It could be that it's not detecting the transformer (no AC output), but I don't hear any relay clicking, so that power couldn't make it to that sense resistor network on the right (third photo) even if it DID work...something else is interrupting the "startup" sequence, whatever that might be....
                Wattevah...

                Comment

                • stj
                  Great Sage 齊天大聖
                  • Dec 2009
                  • 31163
                  • Albion

                  #9
                  Re: UPS beeping continuously

                  when you have bad connections to connectors and relays it could be anything.

                  Comment

                  • CapLeaker
                    Leaking Member
                    • Dec 2014
                    • 8297
                    • Canada

                    #10
                    Re: UPS beeping continuously

                    did you check them relays yet?

                    Comment

                    • kc8adu
                      Super Moderator
                      • Nov 2003
                      • 8832
                      • U.S.A!

                      #11
                      Re: UPS beeping continuously

                      replace the caps near the heatsink in the center.
                      it runs hot and probably baked the caps dry.

                      Comment

                      • Dannyx
                        CertifiedAxhole
                        • Aug 2016
                        • 3912
                        • Romania

                        #12
                        Re: UPS beeping continuously

                        That heatsink holds a 12v regulator whose input is in series with that large ceramic resistor....I wonder why a regulator needs such a large resistor on its input. I'll try replacing them - not like I have anything to lose.

                        Relays are good - I tried each of them and they work.
                        Wattevah...

                        Comment

                        • stj
                          Great Sage 齊天大聖
                          • Dec 2009
                          • 31163
                          • Albion

                          #13
                          Re: UPS beeping continuously

                          Originally posted by Dannyx
                          Relays are good - I tried each of them and they work.
                          how did you test??
                          you have to check contact resistance both open and closed.

                          Comment

                          • Dannyx
                            CertifiedAxhole
                            • Aug 2016
                            • 3912
                            • Romania

                            #14
                            Re: UPS beeping continuously

                            I didn't go that in-depth (though it would've been easy), because I couldn't hear them coming on at all, so I checked the coils first: 12v from bench supply on either coil contact, paying attention to the polarity of the freewheel zener diodes so as not to short the power supply. I heard them clicking, the were good I reckon contact resistance would come into play once I hear a relay turning on but stuff not going through, so I didn't do that just yet.
                            Wattevah...

                            Comment

                            • CapLeaker
                              Leaking Member
                              • Dec 2014
                              • 8297
                              • Canada

                              #15
                              Re: UPS beeping continuously

                              Only because a relay clicks, it doesn't mean it is good. You have to check the contacts to see if they make a good contact too. The overload LED can come on also if the UPS doesn't output correct voltage. Measure the current consumption of the UPS with whatever it is doing at this point.
                              Last edited by CapLeaker; 08-15-2018, 03:03 PM.

                              Comment

                              • Dannyx
                                CertifiedAxhole
                                • Aug 2016
                                • 3912
                                • Romania

                                #16
                                Re: UPS beeping continuously

                                Originally posted by CapLeaker
                                Only because a relay clicks, it doesn't mean it is good. You have to check the contacts to see if they make a good contact too.
                                Agreed, but only after the system actually turns on that relay, otherwise contact resistance is irrelevant since the contacts don't touch anyway. The two relays that the AC input has to travel through (one for L and one for N) do no have a have an NC position to check. I got your idea otherwise.

                                Originally posted by CapLeaker
                                The overload LED can come on also if the UPS doesn't output correct voltage.
                                Which is not going to happen anyway with no transformer connected though I tried it with the transformer and same thing. I measured the continuity of the transformer and I got readings on both the primary and secondary. I'm fully aware that's not how you measure a transformer, but I wanted to check for thermal fuses or completely open windings. Just because I got continuity doesn't mean the transformer operates correctly. I was thinking of powering it straight off the mains to ensure I actually get output on the fat output leads, which I'm expecting to be somewhere around 26v, since it goes straight to the batteries using the body diodes of the FETs - no charge circuit as far as I can see, so it shouldn't exceed the charge voltage normally.

                                Originally posted by CapLeaker
                                Measure the current consumption of the UPS with whatever it is doing at this point.
                                Where would I measure this ? At the batteries ?
                                Wattevah...

                                Comment

                                • Dannyx
                                  CertifiedAxhole
                                  • Aug 2016
                                  • 3912
                                  • Romania

                                  #17
                                  Re: UPS beeping continuously

                                  I made another discovery: I did the transformer thing with a series lightbulb and I get 9.5v on the output. Without the bulb I get 12.5v with one pair of primary wires (black and yellow) and 15.5 with the other (black and blue), which makes me wonder how it charges the batteries with that little. Anyway, we can assume the transformer is working.
                                  Last edited by Dannyx; 08-16-2018, 02:55 AM.
                                  Wattevah...

                                  Comment

                                  • stj
                                    Great Sage 齊天大聖
                                    • Dec 2009
                                    • 31163
                                    • Albion

                                    #18
                                    Re: UPS beeping continuously

                                    did you fix the shit soldering yet?
                                    if not then your just wasting your time.

                                    Comment

                                    • Dannyx
                                      CertifiedAxhole
                                      • Aug 2016
                                      • 3912
                                      • Romania

                                      #19
                                      Re: UPS beeping continuously

                                      Originally posted by stj
                                      did you fix the shit soldering yet?
                                      if not then your just wasting your time.
                                      Pff that put a grin on my face, the way you called it "shit soldering"

                                      Anyway, I guess I did reflow most of the components. I believe I'm close to tracking down the issue: something's not right in the battery level monitoring - I have no idea ATM how it determines it, but when it DOES decide to turn on, the battery level indicator bars on the LCD display jump up and down randomly before the thing finally shuts down, so it's either a cold joint somewhere still, or a component (resistor?) became out of spec. Trying to track down how it senses the battery level now. Such a pain with these SMD resistors since you can't check them in circuit...
                                      Last edited by Dannyx; 08-16-2018, 06:17 AM.
                                      Wattevah...

                                      Comment

                                      • stj
                                        Great Sage 齊天大聖
                                        • Dec 2009
                                        • 31163
                                        • Albion

                                        #20
                                        Re: UPS beeping continuously

                                        i imagine it's centered around that LM324

                                        Comment

                                        Related Topics

                                        Collapse

                                        • carrzkiss
                                          Cyberpower cps1500avr not charging batteries
                                          by carrzkiss
                                          Hello, all.

                                          Cyberpower Battery Backup Unit.

                                          I bought two new ML18-12 batteries through Amazon (They have already refunded my money for the two batteries as we thought the batteries might have been bad.)
                                          When I got them in, they were not fully charged. I connected them to the UPS and waited 24 hours before connecting any networking equipment.
                                          In parallel, they read 24v, but within 24 hours, the meter on the front of the unit dropped from 4 to 3 bars on the battery charge indicator.
                                          Checking the voltage, it was down to 22v.
                                          I quickly removed everything...
                                          06-15-2024, 02:10 PM
                                        • ribcage
                                          UPS issue
                                          by ribcage
                                          A couple of years ago I got an UPS rated 1000VA 600W, with two 12V 7Ah SLA batteries in series. It ran 24/7 up until recently with a load of about 70 W. When it was new it could hold my setup for an hour or so. Not so long ago a power outage occurred and the UPS hardly lasted a few seconds. The UPS has only ever seen a handful of outages in it's life, and before this one, there probably weren't any for many months. So initially I thought the batteries must be dead, although I've read they typically last 3-5 years, so it's a little strange. I thought perhaps the batteries being at a voltage of...
                                          02-20-2022, 10:17 AM
                                        • howardc64
                                          Where do repair shops buy MB replacement batteries?
                                          by howardc64
                                          Order my parts from mobilesentrix.com and iPhone batteries have been excellent. Recently got 3x bad A1534 (2015) batteries. All would work until ~30-40+% and drop to < 10% instantly. Typical sign of cheap batteries.

                                          Perhaps the less popular A1534 model's aftermarket batteries are more source limited. Just find it surprising quality from mobilesentrix (usually fairly high quality aftermarket parts) have been so poor.

                                          BTW, this isn't the only defective parts I've had from mobilesentrix. Amongst others including iPad Air touch screen and A1989 touch bar (display was...
                                          07-25-2024, 10:42 AM
                                        • Astonished
                                          Fixing the Charge Circuit of the Batteries of the DC Motor
                                          by Astonished
                                          Hi friends of electronics

                                          What you see in the video and pictures attached is the circuit for charging the batteries of a DC motor.

                                          The problem is that this circuit cannot charge the batteries (3 1800mAH NiMH batteries) any more. When the circuit was OK, its green LEDs lit up one at a time to show that the batteries have charged more. But now that the circuit is flawed, LEDs light up as you see in the video and at the same time successive beeps are heard.

                                          Please help me fix this circuit.

                                          (the datasheet of the IC: https://pdf.datasheet.live/28...
                                          01-28-2025, 06:24 AM
                                        • dbuergi
                                          DIY: Modified smart charger for all types of batteries
                                          by dbuergi
                                          Hi all,

                                          sometimes i'm in need of a charger / tester for very small batteries and even if my multimeter doesn't show anything there is a chance that a smart charger helps to revieve. I'm happy with my Keenstone smartcharger and i made a small mod just to use it with smaller batteries like in smartwatches or even camera batteries with special contacts.

                                          Soldering wires on the charger contacts and using needles as probes. I covered both with a shrink hose with integrated solder.
                                          My first work was to bring my Samsung watch battery back to life with was not recognized...