Tankless hot water heater controller board not powering up when power is applied
    • Jul 2011
    • 6033
    I recently bought a used tankless hot water heater and the controller board is completely dead no power up when power is applied the display board works however the main controller board does not work correctly at all the fuse is good
    I bought a used replacement controller board that also had issues that I was able to fix and now the tankless water heater works correctly now
    However I would like to know if I could figure what happened to this controller board if possible
    Tomorrow I will take some better pictures of both side of both boards
    The transformer has resistance on the primary and secondary sides the rectifier diodes test good with a meter I have not checked with power connected to the controller board because I would have to make a jig to be able to check if I am getting secondary power from the transformer
    The power inputs are the white connector red wire ( L1 ) and a red connector the left pin which is black is
    ( L2 ) is the power pins for the controller board the right pin which yellow goes to the triac gate pin then other two pins on the triac go the power in and to the temperature limit switch and then to the heater element the other side of the goes to the other side of the power supply
    • 30979
    Re: Tankless hot water heater controller board not powering up when power is applied
    pictures are shit.
    but you have a microcontroller - so you have a voltage regulator.
    find it and check it's input and output pins
      • Jul 2011
      • 6033
      Well now the replacement controller board has an issue with the flow sensor it is not seeing it and it does not see the replacement one either and it is supposedly a new one
      The error message is “E4” flow sensor issue
      But what is weird is that even power cycling the controller board does not clear it which it should
      If I can find the right controller board for the flow sensor that is in this device I will try to figure out what happened to this controller board and the original controller board that does not power on at all which I have not had time to troubleshoot it more what I had done in post #1
      Because the newer controller board have a 4 pin flow sensor not a 3 pin flow sensor
      • CapLeaker
        Leaking Member
        • 8112
        What sensor is this? A hall sensor? Maybe check it and see if it works?
          • Jul 2011
          • 6033
          It is a 3 wire hall flow sensor
          If I leave the power off for about 5 minutes it resets it self it seem like I have to have flow restrictors in both tankless water heater because ———>
          I have 18kw and a 27kw and I will explain why below
          The turn on rates are different from 18kw to the 27kw
          So if my wife is doing the dishes in the kitchen sink the 27kw does not turn on but 18kw one does but the shower heads are the opposite way the 18kw goes into an over flow or not staying on because depending on what water temperature you try to get and if you have two shower heads going it goes into a overflow on the 27kw
          Now you might ask why I have two well because I started using the 18kw first and found out that I can not run two shower heads at the same time I can with 27kw but depending on what each person temperature preferences are because my wife and son want to take the hottest shower possible this causes a really big problem with flow rate on both tankless water heater so what I going end up doing is put a flow restrictors in both tankless water heater to keep them from going into a overflow condition is only thing that I can think of and the instructions point out that depending on your situation might need to install flow restrictors
          These tankless water heaters also have another issue and that is the following
          If your flow rate is not at a certain point it never activates another heater element which is also an issue depending on what water temperature you are trying to achieve so I have only one heater element hooked up on each tankless water heater and I use two different electrical wiring circuits and 2 set of breakers for each tankless water heater
            • 30979
            i'm confused.
            why does it have a flow sensor?
            i have tankless heaters and they have a pressure sensor on the input to detect a tap turning on, and a temp sensor on the output.
            • CapLeaker
              Leaking Member
              • 8112
              Originally posted by stj
              i'm confused.
              I am not a pro with this, but a friend of mine has infloor heating with one of these tankless heaters. They all had a regulator board, a temperature sensor and a pressure sensor on the input too.
              Now I am confused Sam, did you defeat the pressure sensor? Because I don’t think that it is a good idea.
              Huh? Your hookup is a bit complicated. I need my coffee to work first. Lol
                • Jul 2011
                • 6033
                i'm confused.
                This is a flow Hall effect sensor that is used to detect the amount flowing through the heating elements
                Can you please post a picture of the type of sensor that you are talking about
                  • Jul 2011
                  • 6033
                  No the only modification that I did is instead of using the two inputs for each heater element I only use one on each tankless water heater because of what I described in a previous post
                  I would like to see the type of pressure switch that they are using in this type of tankless water heater
                  But I would like to modify the algorithm because I do not like the way that it is designed to work
                  This is the way the 18kw is setup
                  The way that this algorithm should work is that if you have at least 0.500 to 0.750 gallons pre minute ( instead of 1.5 gallon per minute which is the way that it is set up in order to activate the heater element you have to have a 1.5 gallon per minute and then you back it down to 1.0 gallon per minute )
                  Another issue with this algorithm is that when it detects a no flow situation it stay on for several seconds before it turns off the heater element why this does not need to be this way
                  The 27kw flow rate is different and off the top of my head I can not remember exactly what the flow rate needs to be for it to activate but it is different from the 18kw
                    • 30979
                    i cant get a picture but they are also used on central heating systems - they use a rubber diaphram that presses against a microswitch to indicate pressure on the input - when water flows the pressure drops and switches the switch - turning it on
                      • 30979
                      do your flow sensors actually work?
                      if they have a spinning bit with a magnet - do they spin?
                      i'v seen similar magnetic coupled devices get scaled or gunked up
                      • redwire
                        • 3906
                        EcoSmart, Eemax, Rheem tankless hot water heater controller SMT18-36A
                        It's got jumpers to config the heater power kW. So that means no EEPROM I guess for special settings. This is proportional (phase) control using the triac? Or only ON/OFF? 4-pin connector is for the remote control.
                        You might have a difference in the flow sensors - the pulses per rev. but I can't see one ever giving a fault code because the impeller (magnet) stops on the Hall sensor or not. So the signal stuck high or low does not mean there is trouble. It's something else. The restrictors are at the shower head?
                        I would guess 4-wire sensor has flow plus a thermistor in it for incoming water temp possibly.
                        someone figured out the EcoSmart tankless hot water heater remote control protocol:
                        https://github.com/ryangriggs/EcoSmartLib
                        https://github.com/PhilRW/ecosmart-remote
                        It's pretty dumb, you can't get diagnostics or setting info.
                        P.S> - it's been 10 months, when are we getting good pictures of the controller board that went dead lol
                          • Jul 2011
                          • 6033
                          If you ever find a part number or a website link you can please if for me because i would be interested in buying some
                            • Jul 2011
                            • 6033
                            The first question I can answer for you the range is from 20 to about 36 amp
                            The second question is there is supposedly a use for the restrictors if you get an “E4” error message according to the troubleshooting manual that tech support provided when I was getting this error message when I first installed it ( yes you can reach an over flow condition this the reason there is troubleshooting mode on the controller so you can easily see the flow rate however you can not leave it in this mode without issues more than a couple of minutes before it errors out )
                            As far as the better picture I will take them tomorrow afternoon when the sun is up high in the sky for the best possible pictures of each of the two sides of each of the two board
                            The reason I did not post the better pictures is because I first of all I was not having any issues for several months then just recently it started giving me this error message again more often ( I had put a water valve to prevent it from overflowing the flow sensor but this not the best way to control the flow to each tankless water heater )
                            The reason there is an neutral wire is this panel is because it goes to another sub breaker panel box because the other breaker panel has a neutral wire in it for some light demand devices like a freezer which does not run all the time and nether does the tankless hot water heater so I can use this breaker can do both functions without any issues so far
                            The second reason is that I forgot about saying that I going to post better pictures of the controller board was this repair on the board that this post was about had low priority I was working on higher priority projects
                            To answer your second question yes the shower heads do have a restrictors however if you have more than one device going at the same time you might exceed the flow rate of the tankless water heater which what I do not understand is why the restrictors are not included in the box just in case need to use them and they are not cheap 4 different flow rate 2 , 3 , 4 , 5 gallon pre minute $35.00 plus shipping for $7.00
                            I ordered two sets of them in case I need two of the same size restrictors I will post a picture of them when I get in the mail
                            I also ordered a another controller board just in case the issue is with the controller board itself plus I want to easily clean the flow paddle wheel which the one that comes with it is very hard to remove it to clean it
                            The 27kw is a used one that had the bad controller board and some scale on the heater element that I cleaned before I installed it
                            The 18kw is the new one that I had bought first which is how I found out that it was not big enough for the demand of of our house hold
                            But I would not go back to a tank type water heater again
                            Here is some pictures of how I have it installed in my garage
                            The second picture is where I checking the installation of the tankless hot water heaters
                            The breaker that has the black and white wires are the ones that were use on the tank hot water heater that I had originally when I moved into the house
                            And yes this breaker box was modified for this project
                            One note the red and black and white wires are a #6 wire good for about 100 amps
                              • 30979
                              just search "water pressure switch" and maybe include words like boiler or heater
                                • Jul 2011
                                • 6033
                                I miss spoke about what “E4” is a temperature over 140*F
                                “E5” is the over flow rate but in the beginning I did get the “E5” error message
                                Here is the troubleshooting manual
                                https://cdn.badcaps-static.com/pdfs/...4dc5d0e9e5.pdf
                                • petehall347
                                  • Jan 2015
                                  • 4426
                                  • United Kingdom
                                  maybe you need a pressure vessel i know my gas one does . and a pump fed from a tank as mains pressure is not reliable .
                                  • CapLeaker
                                    Leaking Member
                                    • 8112
                                    This tankless heater is waaay different than the one I dealt with a while back. A friend of mine is using this for infloor heating.
                                      • Jul 2011
                                      • 6033
                                      I have done a little research and found out that I might have to put a pressure regulator on the cold water to the tankless heater to control the pressure because I have noticed that the pressure goes up and down sometimes while taking a shower so this might be a reason why I am having issues with the temperature getting to hot or I might have a bad temperature sensor or something is wrong with the temperature section of the controller board which I have a supposedly a new controller board ( because the first replacement controller board was supposed to be new it turns out that it was a return *** yes I got a some of my money back because of it ) so let see if this is issue or not
                                      Electrical service and water service is owed by the city of Jacksonville and I can tell you that because I live in out shirt of the downtown Jacksonville and we have voltage sagging and running higher voltage other times
                                      Water pressure is lower in the morning and at night and higher in the afternoon or at least on the weekends so I like living in the boondocks where there are less house or it used to be that way not so much now
                                      We can not even get fiber optic cable in this area and who knows when that going to happen
                                      They need to upgrade the electrical system in this area you can not get 3 phase service down this street if you want it because you only have one high tension power line that service a lot of houses and churches and what ever else in the summer time when everyone is running their air conditioning you can actually see the lights dimming every so often and when it is really bad that the battery backup goes off letting you had a voltage drop of course it does not last long but that is not the point it is the fact that it does
                                      Not to mention that the roads around here need to be repaved which do not get done until it is almost not drivable anymore or the road sinks pretty bad
                                      And do not get me started with internet service and cable service and phone service all from the same company when it goes down you play hell getting back working again to make matters worse is that they tried to charge me for coming out to supposedly fix it and the very next night it went out again I did get charged reversed but I had to go to their service center to get it resolved forget doing this on the phone you will not get any where
                                      I am done ranting and raving about all this stuff
                                      • redwire
                                        • 3906
                                        Seeing the pics - I would check for a ground fault. If anything is shorted to the metal, it could make a lot of electrical noise on the sensors. Like a triac or heating element. Just check with an ohmmeter.
                                        Or ground the backpan like it's supposed to be...
                                        The sensor wiring is best away from mains wiring, not on top of it.
                                        Noise on the flowmeter wiring could make it look like too high a flow rate.
                                        edit: also noticed the 4-wire flow sensor has a second sensor inside, it appears to be optical... the wheel has 6 holes. So that I would think gets silt and dirt on it, then the optical signal doesn't jive with the Hall sensor.
                                        • edugimeno
                                          Vaillant 242 Gas Water heater. Shortcut in board anc compatibility with model 282
                                          by edugimeno
                                          Hi!!
                                          Yesterday I was installing a new Wifi thermostat for my domestic gas water heater model Vaillant 242/2-3, and accidentlly one wire from mains touched one wire from the thermostat output contacts. This shut off the heater so I finished installing the thermostat and then went out to check the heater
                                          I found one fuse blown (T2 250V). Replaced it with another equivalent fuse and it blew right away. I measured L-N in mains input and I sometimes got 4K but sometimes, not sure why, I got 100 Ohm...
                                          At a certain point, moving stuff around, I put all wires back in place and...
                                          03-24-2024, 02:31 PM
                                        • nop
                                          Busted tankless electric water heater control board
                                          by nop
                                          Hi. I have an old Bosch/Powerstar AE125 water heater in my cabin whose control board died for the nth time. This time around, I figured I'd try to diagnose and repair it. At the end of the board's life its power indicator LED will quickly cycle on and off as water passes through the heater, rather than remaining steadily on as it normally would, and water at the tap remains cold. Slightly increasing pressure in the system by closing the outlet valve seems to delay the inevitable for a little while.
                                          Here's all the info I found from Bosch regarding troubleshooting the board:
                                          04-27-2022, 09:57 AM
                                          20 year old Kenmore refrigerator ice maker bad water valve coil took a crap
                                          by sam_sam_sam
                                          I got lucky that when I got home and was about to get some ice out of the ice dispenser I hear and see water running down the outside of the ice dispenser what the heck is going on here
                                          At first I thought that the ice dispenser mold was cracked so I brought a new ice maker because this one has been in there for about 10 years now
                                          Well I put the new one in and wait and I wait for the water valve to open and let water in no such luck well there is a way to check the function of the motor and the water valve on this ice maker just need a jumper wire “L” to...
                                          04-09-2023, 08:04 PM
                                        • master3112
                                          ASUS ROG Strix- G513IH-HN008, G513-6050A3249301- MB-A04 (A4) damaged Embedded Controller
                                          by master3112
                                          I have an ASUS ROG Strix- G513IH-HN008, motherboard G513-6050A3249301- MB-A04 (A4)
                                          When I received the device, the device has no function. After an investigation, I found that the PWM CONTROLLER RT6575B (U6100) is getting warm and there is a short circuit at the 3V3 output. This normally supplies 3V3 for the embedded controller IT5571E-128 (U301). When measuring and analyzing with a thermal imaging camera, I found that some components are damaged: SLG4E42553VTR (U8500), IT5571E-128 (U301), LAN RTL8111H (U450), LOGIC 74LVC1G08GW (U1900), RT6575B (U6100) All these components are on...
                                          10-29-2024, 09:32 PM
                                        • madan1
                                          Diesel heater emergency power supply / poor man's UPS
                                          by madan1
                                          Hello everyone.
                                          Some background - I have one of those chinese diesel heaters, which I'm using to heat a garage. Probably most of you are familiar with that units, but here is some basic info - the main heater body is enclosed with the motherboard+sensors unit inside a plastic case. The heater has a glow plug, that works only when the unit is starting (start the fire in the burner) and stopping (make sure to completely burn the fuel inside the burner) and two fans on a single motor. One fan is used to push fresh air in the burner, the other is used to push cold air in the case and...
                                          12-18-2022, 08:05 PM
