UPS Wiring
  • PlainBill
    • Feb 2009
    • 7034
    Re: UPS Wiring
    Originally posted by pentium
    Well I'm going to have a heck of a time finding tha manual at the Sola website.
    So follow the link I gave you and ask the nice person for the pdf of the manual. :roll:
    Okay, so assuming the abtteries are dead, is there any way I can jumpstart the unit?
    Why are you assuming the batteries are dead? Take a DMM and measure their voltage. Have you looked at the batteries and determined their voltage?
    I know trying to recharge the batteries now might be useless but a wise man once told me that if you beat a dead horse long enough it will eventually make movements that resemble life.
    If they are dead, hook up a battery charger and see if they take a charge. Miracles do happen. Last night Congress passed Health Care Reform legislation.
    If the miracle doesn't come to pass, you can hook up any batteries of equivalent chemistry (probably lead-acid) and the proper voltage as a TEMPORARY measure.
    Also the white going to green is the fault of whoever wired up the UPS in the first place. There are no other wires for the neutral to run along.
    Either we have a failure to communicate, you don't understand wiring principles, you have gremlins at your house, or you are trying to bullshit me. Take a look at the picture. The Green wire from the UPS is ground. SOMEONE hooked the white wire from the dryer cord to it. You don't need a neutral wire, you need a ground wire for safety.
    PlainBill
    • Krankshaft
      • Jan 2007
      • 2328
      Re: UPS Wiring
      The green wire from the UPS should go to the bare copper wire as PB said. The neutral is not needed since unlike your dryer the UPS has no need for 120.
      • pentium
        • Mar 2006
        • 2778
        Re: UPS Wiring
        But both wires go to the same place. Is it not wise to use the lower guage wires instead of the flimsy thin ground wire?
        Okay, I'll try emailing that guy but I am doubtful I'll get a response and a 6mb PDF is too big for Gmail to handle.
        As stated also, my DMM will be useless until I buy a new one or replace the probes on my current one.
        Hmm, any specific battery charger? I got one for the car someplace here.
        Find Nedry!
        Check the Vending machines!!
        <----Computer says I need more beer.
        • PlainBill
          • Feb 2009
          • 7034
          Re: UPS Wiring
          That is a valid point. Again, that is not what is causing the dead UPS; it is something that raises a red flag to an electrical inspector. Double flag, actually. Here in the USA under size ground wires have been banned for over 40 years.
          Be charming. Don't remind him that Canada won the Olympic Hockey title. There are many free sites that allow transferring large files. uousendit.com is one.
          So borrow, buy, or steal a pair of probes. If Spock could make a computer from bear skins and stone knives, a pentium should be able to make some probles from tin foil and newspaper.
          What is the voltage rating of the batteries?
          PlainBill
          • pentium
            • Mar 2006
            • 2778
            Re: UPS Wiring
            The batteries are rated for 6V. They come in modules of ten (wired in series so you get 60V DC per module) and two modules fit into a box. (so each battery box I got outputs 120V DC)
            Find Nedry!
            • pentium
              • Mar 2006
              • 2778
              Re: UPS Wiring
              Nothing?
              I can't leave this thing sitting in the laundry room much longer. Either I get help now or else it goes back into storage where the batteries will certainly become useless.
              Find Nedry!
              • PlainBill
                • Feb 2009
                • 7034
                Re: UPS Wiring
                Nothing?
                Hey, some people have a life!! (I'm not one of them, but we'll ignore that).
                So dig out your battery charger. If it's a 12 volt charger, hook it across two batteries in a module and plug the charger in. (Don't forget to observe polarity.) If the charger has an ammeter, does it show the batteries are charging? If it DOES show it is charging, leave it hooked up for at least 4 hours (ideally until the charge rate tapers off), then move to the next pair of batteries in the string until you get all of them charged. Then go to the the next string in the module.
                By the way, once you get the battery pack charged, you might want to avoid touching the leads. 120 VDC packs a pretty good punch.
                PlainBill
                • PlainBill
                  • Feb 2009
                  • 7034
                  Re: UPS Wiring
                  Note that I wouldn't do it that way. I'd take my Kill A Watt, Variac, isolation transformer, and a rectifier bridge from a power supply. I'd plug the Kill A Watt into the outlet, the variac into the Kill A Watt, use the variac to adjust the voltage to the isolation transformer; the isolation transformer would feed the rectifier bridge, and the DC output of the bridge would be hooked across the battery pack. Then using the Kill A Watt to monitor current, I'd slowly increase the voltage until the battery pack was charging. If I maxed out the variac before the current started rising, I'd stick a light bulb in series with the feed to the battery pack (to limit current surge), and try charging only one module at a time.
                  PlainBill
                  • pentium
                    • Mar 2006
                    • 2778
                    Re: UPS Wiring
                    Hmm. Something is wrong.
                    When my charger is connected to a very, very dead battery the needle stays at the bottom of the guage and does not rise up to the apporpriately scaled part of the chart (I can charge at 2 and 6 amp rates so I got two "dead" and "charged" points). Right now it is doing that to every cell set that I have tried.
                    This is not promising. You think there is any way to trick the UPS into powering up so the integrated charging system can give it a shot at charging? It must all be controlled by a relay or something, right?
                    Find Nedry!
                    • PlainBill
                      • Feb 2009
                      • 7034
                      Re: UPS Wiring
                      That is the symptom of a dead gel-cell.
                      One infamous experiment I tried involved hooking a light bulb in series with the input of a bridge rectifier, then hooking the DC output of the bridge across a 6 volt gel-cell. This was plugged into my variac and I cranked the output up to roughly 140 volts. This means the peak voltage across the cell was about 200 volts DC!!! The bulb didn't even glow. Eventually it broke down the insulating layer on the electrodes of the battery and I was finally able to get it to take a charge at approximately the recommended charging rate. I then switched to a conventional charger, then put the battery into a 350 VA UPS, let it charge overnight, then plugged in a small load and unplugged it from the wall. The 'rejuvenated' battery lasted less than a minute. Not an auspicious sign.
                      The easiest way to 'trick' the UPS into starting up is to hook 10 ea 12 volt car batteries in series to the battery terminals.
                      PlainBill
                        • 31265
                        Re: UPS Wiring
                        would one of those "desulfer" circuits designed to regenerate liquid battery's do any good on a gel cell?
                        • PlainBill
                          • Feb 2009
                          • 7034
                          Re: UPS Wiring
                          I don't know. It depends on the mechanism that destroyed the battery. Gel cells have an additional layer of complexity (the gelling agent) that may affect this. Given the cost and life of UPS batteries I would say this is certainly worth investigating.
                          The only thing that discourages me from trying is the thought that if the circuit truly works, a UPS would be the ideal environment for it. I would be expecting Sola, APC, Triplite, etc to be touting their new, improved design which offers extended battery life.
                          PlainBill
                          • pentium
                            • Mar 2006
                            • 2778
                            Re: UPS Wiring
                            Okay then. I guess I can write this iff as an irrepairable unit as there's no way I'll ever find a set of 40 new 6V cells for a dime a dozen.
                            Find Nedry!
                              • 31265
                              Re: UPS Wiring
                              PlainBill
                              i wouldnt, any more that car company's offering petrol vaporizers or hydrogen-seperation tanks.
                              i think the big ups company's make a lot of money from battery sets & service-contracts.
                              i know a guy working for a semi-government unit that has a lot of computer gear.
                              they pay 10x the true value for all there stuff (ram, battery's etc) because a clause in the service contracts say's EVERYTHING DOWN TO REPLACING A FUSE must use approved components.
                              • PlainBill
                                • Feb 2009
                                • 7034
                                Re: UPS Wiring
                                Marketing. "Buy the New improved APC Genius-UPS with our exclusive Eterna-Cells. We guarantee 5 years of service between battery replacements. Note: Eterna-cells are not compatible with older UPS." Managment would go for it because of the improved sales this year. They don't give a hoot about sales in 5 years - they will be retired by then.
                                When additional UPS' are needed, instead of staying with the old technology, customers will be buying the new ones because of lower maintenance and greater reliability. Geeks will do the same. Some won't- they're the ones that think a UPS is the guy in the brown truck.
                                PlainBill
                                • Krankshaft
                                  • Jan 2007
                                  • 2328
                                  Re: UPS Wiring
                                  Sure keep junking your UPSs I'll be scooping them up for practically nothing.
                                  I love getting 170 dollar UPSs for 20 bucks when all they need is a new set of batts. Their not powering on dead as a doornail failure mode makes most users think they're broken I love it .
                                  I'm surprised they're junking the bigger UPS units I would think the larger units purchase cost would exceed the cost of replacement batteries. Unless your stupid enough to buy from the original manufacturer of course then I can see that.
                                  • pentium
                                    • Mar 2006
                                    • 2778
                                    Re: UPS Wiring
                                    I understand this IS a seven year old thread, but in the end (jesus christ I never throw anything out) I got it running.
                                    Lmao, in reality they were all 12V cells. Each battery tray has 10 cells (120v DC). Two trays run in series. Two sets of two in parallel. Roughly 240V DC with a scary amount of amps.
                                    http://i11.photobucket.com/albums/a1...d/IMG_6676.jpg
                                    http://i11.photobucket.com/albums/a1...d/IMG_6675.jpg
                                    http://i11.photobucket.com/albums/a1...d/IMG_6678.jpg
                                    With new connections in the recycling industry I was able to find used but still good cells in bulk and was able to rebuild all four trays. Having used other UPS systems in the meantime I learned that most UPS units will not come up if the battery side is no good.
                                    With the batteries replaced it was reassembled and the breaker thrown.
                                    https://www.youtube.com/watch?v=DI1EJmD3IJQ
                                    The harmony of the fans alone was bittersweet music to my ears.
                                    So there we have it. MY original problem was simply all the batteries had to be replaced...
                                    Find Nedry!
                                    • eccerr0r
                                      Solder Sloth
                                      • Nov 2012
                                      • 8704
                                      Re: UPS Wiring
                                      All my UPS need new batteries, and battery packs aren't cheap
                                      I need 3x6V12A and 12V7A packs...
                                      I was annoyed that the first set of 6V12A packs I used in my UPS had problems in a year, and completely dead and gone by 2... *sigh* but the UPS actually works...
                                      • Shagreobe
                                        Puzzling Electrical problem
                                        by Shagreobe
                                        OK, At work (I'm a maintenance mechanic/technician), we have a 120v (USA) twist-lock receptacle that is 1. split into 2 separate circuits, and 2. Showing 120v between hot to neutral, and 12-v hot to Ground.0v N-G, so far so good. The motor that plugs into it does not work, but works elsewhere. There is not much of a circuit, just a breaker, on/off switch, fuse, outlet, and wiring ran maybe 10 feet or so.
                                        And yes, I used my fluke clamp-on to check everything. Can someone explain why I have voltage but nothing runs when plugged in???...
                                        03-14-2024, 02:48 PM
                                      • t4796
                                        Fender Mustang non valve guitar amp - owner connected 110v amp to 220v.
                                        by t4796
                                        I recently picked up this amp as not working. I took it as is. Didn't notice until I got home it had foreign power plug and was marked 110v and our local voltage is 220v so then I knew what had happened to it.
                                        Opened it up and was able to find the schematic online. In the schematic I have uploaded I have erased the parts for 220v operation to make it easier for me to visualise however I have since added the two additional diodes and remove the wire link from the power supply so I can test it easier on 220v
                                        From the FAQ I learnt that for 110v the power...
                                        10-25-2024, 06:59 PM
                                      • sew333
                                        Can i plug pc on this apartment with older fuse box?
                                        by sew333
                                        Hello. I will be buying new apartment to live. But fuse box is older. Not the newest.
                                        And my question. It will be fine to plug pc in this new apartment with that fuse box,i think it is aluminium,right?
                                        PC WILL BE: Rtx 4090,14900K,1600W PSU
                                        It looks like this ( screen from internet ). Looks like this,not sure i dont take a pic from there. Can i plug pc with that one?
                                        screen of this:
                                        room:
                                        Someone said this to me.
                                        1
                                        "I would get advice from a local electrician...
                                        03-29-2024, 05:37 PM
                                      • Zonzi
                                        Neptune mixer model 611 - Works for a few minutes then fades out and distorts
                                        by Zonzi
                                        Hi there !
                                        This is my first post out there, glad to be part of the community.
                                        I was gifted an old analog mixing unit (from the 70s) by a good friend. It's a Neptune Audio Mixer model 611, 6 channel mixer with :
                                        -6 XLR inputs wired hot to 3, and 1&2 to ground (which is already a weird start. You can see this in Picture 3, and all sockets are what I understand to be common ground, as there's a long wire connecting all XLR grounds together. Besides, all Hot are connected to the other pins via a cap with the marking 24 102k)
                                        -6 unbalanced...
                                        02-16-2023, 06:28 AM
                                      • mkdj
                                        Acer TravelMate P214 - N19Q7 main power rail shorted to ground
                                        by mkdj
                                        Dear all,
                                        I have taken out the motherboard of a Acer TravelMate P214. There is a short to ground on the main power rail (19V). I don't have the schematics or boardview for this board (DAZ8IMB1AA0 REVA). But I have found 4 MOSFETS close to the main power rail : 2 N-Channel and 2 P-Channel.
                                        I have checked resistance across each of the 4 MOSFETS. I have the following readings:
                                        Both N-Channel Mosfets: nothing odd
                                        P-Channel MOSFET number 1:
                                        source - drain : 117 kOhm
                                        source - gate: 96 Ohm
                                        gate - drain: 117 kOhm
                                        P-Channel MOSFET...
                                        08-20-2025, 06:08 AM
