Valliant boiler board

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • _ASH_
    Member
    • Dec 2011
    • 14

    #1

    Valliant boiler board

    Hi Guy's, ive got a valiant boiler & these are prone for the control boards failing, causing the boiler to go into a error state.

    When you run the hot tap, it goes into the error state but then when you reset, these work fine until next time.

    Im convinced that the problem with the boards are something simple like a relay which would cost considerable less than replacing the complete board at several hundred pounds.

    I was wondering if anyone had ever done any work or knows of anything to do with boiler boards?

    Many thanks in advance

    ASH
  • stj
    Great Sage 齊天大聖
    • Dec 2009
    • 31044
    • Albion

    #2
    Re: Valliant boiler board

    i ave fixed boiler boards.
    it's usually capacitors.
    fitting them in a box under a boiler probably doesnt help!

    Comment

    • _ASH_
      Member
      • Dec 2011
      • 14

      #3
      Re: Valliant boiler board

      Many thanks for the reply.

      Very true, you would have thought that there would be a better situation to put a board within a boiler.

      Could you give me any ideas to look at?

      Many thanks in advance

      Comment

      • stj
        Great Sage 齊天大聖
        • Dec 2009
        • 31044
        • Albion

        #4
        Re: Valliant boiler board

        your looking for any signs of yellow liquid or tops not perfectly flat.
        also check the soldering on the connectors - the cables put a lot of stress on the joints

        Comment

        • _ASH_
          Member
          • Dec 2011
          • 14

          #5
          Re: Valliant boiler board

          Many thanks for your reply, ive kept one of the old boards, so ill investigate on that & post any findings.

          ASH

          Comment

          • stj
            Great Sage 齊天大聖
            • Dec 2009
            • 31044
            • Albion

            #6
            Re: Valliant boiler board

            post a picture

            Comment

            • _ASH_
              Member
              • Dec 2011
              • 14

              #7
              Re: Valliant boiler board

              Please see below, although upon inspecting, the big black one seems to be slightly bulging, although no leakage, ive peeled the black wrap from the top and it seems to be a sealed (no the pressure cross, if you know what I mean, like on the others).. but I welcome and ideas or suggestions.




              Many thanks again

              ASH
              Attached Files
              Last edited by Per Hansson; 02-15-2021, 02:26 PM. Reason: Offsite images uploaded

              Comment

              • stj
                Great Sage 齊天大聖
                • Dec 2009
                • 31044
                • Albion

                #8
                Re: Valliant boiler board

                you forgot to upload the picture!

                Comment

                • _ASH_
                  Member
                  • Dec 2011
                  • 14

                  #9
                  Re: Valliant boiler board

                  I can see the picture..

                  Please see the links:

                  http://ash-group.co.uk/ashimages/2.jpg
                  http://ash-group.co.uk/ashimages/1.jpg

                  Comment

                  • redwire
                    Badcaps Legend
                    • Dec 2010
                    • 3910
                    • Canada

                    #10
                    Re: Valliant boiler board

                    The board shows water damage, rust on the pcb. Something leaked on it.
                    I would clean it up with isopropyl alcohol and an old toothbrush, gently.

                    Comment

                    • stj
                      Great Sage 齊天大聖
                      • Dec 2009
                      • 31044
                      • Albion

                      #11
                      Re: Valliant boiler board

                      sooo - you didnt notice the connector at x22 has burned all the pads off????
                      the oposing part on the wiring loom needs to be replaced or it will do that to any replacement boards.

                      Comment

                      • _ASH_
                        Member
                        • Dec 2011
                        • 14

                        #12
                        Re: Valliant boiler board

                        Nothing is plugged onto the board on the X22, so I didn't think that'd be the problem

                        Thanks

                        Ash
                        Last edited by _ASH_; 02-16-2021, 06:46 AM.

                        Comment

                        • _ASH_
                          Member
                          • Dec 2011
                          • 14

                          #13
                          Re: Valliant boiler board

                          This is a new board in situ, which has developed the exact same problem


                          http://ash-group.co.uk/ashimages/3.jpg

                          Ash

                          Comment

                          • stj
                            Great Sage 齊天大聖
                            • Dec 2009
                            • 31044
                            • Albion

                            #14
                            Re: Valliant boiler board

                            how old are these?
                            i know ignition coils have a lifespan.

                            Comment

                            • _ASH_
                              Member
                              • Dec 2011
                              • 14

                              #15
                              Re: Valliant boiler board

                              The newest board is about 12 months old

                              Thanks

                              Ash

                              Comment

                              • stj
                                Great Sage 齊天大聖
                                • Dec 2009
                                • 31044
                                • Albion

                                #16
                                Re: Valliant boiler board

                                well it's not the coil then.

                                i suppose if a pump or valve is drawing a lot of current then it could burn the relay contacts faster than usual.

                                Comment

                                • _ASH_
                                  Member
                                  • Dec 2011
                                  • 14

                                  #17
                                  Re: Valliant boiler board

                                  You could be onto something, after inspecting a little more of the old board I found this (I believe it to be a relay) which looks like its been warm in places.

                                  Whats everyones thoughts?


                                  https://ibb.co/gw45wJk


                                  https://ibb.co/dQ5WbH2

                                  Comment

                                  • sam_sam_sam
                                    Badcaps Legend
                                    • Jul 2011
                                    • 6040
                                    • USA

                                    #18
                                    Re: Valliant boiler board

                                    Originally posted by _ASH_
                                    You could be onto something, after inspecting a little more of the old board I found this (I believe it to be a relay) which looks like its been warm in places.

                                    Whats everyones thoughts?


                                    https://ibb.co/gw45wJk


                                    https://ibb.co/dQ5WbH2
                                    Yes they are relay

                                    I would highly recommend that you remove them and test them I would not recommend testing them on the board

                                    If the current is more than 5 amps I can see that it supposedly can handle 8 amps but I can tell you from experience with type of relays contacts are not very good for than about 2 amps if you are lucky

                                    You would have to reverse engineer what relay contacts have the high current on them and reroute them to a contactor that can the current of the heater element

                                    Use a contactor that is rated for at 40 amps yes it would be externally mounted but in the long run would be better

                                    Or

                                    Buy a box of these relays so when they fail to replace them

                                    Where I use to work at we had a CNC machine controller board relay bank that has a similar type of relay and they continually go bad and that what I did I bought them by the case if I remember correctly a case was 24 of them in a tube

                                    I never measured the current on the contacts because this relay had relay socket and it was very easy to replace them
                                    Last edited by sam_sam_sam; 02-16-2021, 09:55 AM.

                                    Comment

                                    • redwire
                                      Badcaps Legend
                                      • Dec 2010
                                      • 3910
                                      • Canada

                                      #19
                                      Re: Valliant boiler board

                                      On the second board I see capacitor C708 bent over, hopefully not mashed. It's by the big filter cap/relay at the edge.

                                      Did you clean the flame rod? Common problem here is boiler controller goes into lockout after either seeing an unexpected flame out or it's unable to light up. If the rod is dirty, the controller will see weak or no flame even though it's there.

                                      Another problem I have seen is the board's grounding, the igniter can cause the MCU to crash if the ground to the appliance or mains is not good. In the pic the two ground wires are cable-tied to the ignition cable- which is a bad idea. Keep everything away from it.

                                      I'm also seeing the high-limit switch trip, either due to low flow or the switch just getting old. I have not worked with Valliant but there should be an LED or something to read fault codes when the unit goes into lockout.

                                      Comment

                                      Related Topics

                                      Collapse

                                      • Hakuu
                                        LG OLED77G1PUA - No Video / Audio after a TCON Board change and Software Update
                                        by Hakuu
                                        Hi There,

                                        This TV was auto switching off after few seconds with some vertical lines on the screen, so got a new TCON board and replaced it.

                                        After replacing the TCON board it was working fine and i set it up with everything, used for few hours, then had the bright idea to update the software on it. During the update process, TV switched off and now no audio or video. No relay switch sound.

                                        More Details

                                        TV Model - LG OLED77G1PUA

                                        Got the same exact TCON board from TVPartsToday and replaced it. But didnt transfer the EPPROM data (didnt...
                                        07-12-2023, 02:37 PM
                                      • jb_Bak
                                        Sony xbr-65x900c main board issues?
                                        by jb_Bak
                                        Hey guys great forum glad to have found it. I bought a Sony XBR 65X900C cheaply because it didn't work. No signs of life at all not even a light/led. All I hear is a brief high voltage sound when I throw the power to it.

                                        Didn't see any obvious signs of damage so right away started checking voltages. This is what I see:
                                        Power Board Connector that goes to Main board
                                        CN6401
                                        Pin 01 NC
                                        Pin 02 NC
                                        Pin 03 "BL_ON": 0V
                                        Pin 04 "N/C"
                                        Pin 05 "STBY 3.3V": 3.5V
                                        Pin 06 "GND": N/C
                                        Pin 07 "AC_OFF"...
                                        09-27-2021, 04:52 PM
                                      • canadaboy25
                                        Panasonic TC-P54VT25 No image. A or D board?
                                        by canadaboy25
                                        I have a Panasonic TC-P54VT25 that will power on and prime the display but there is no image at all.

                                        The panel is primed as there is a slight glow from the entire panel. This means the problem should be logic related. The service manual also confirms this and recommends replacing the A or the D board.

                                        I have tried to get the TV to display the test sequence but I have been unable to and I don't even know if this TV has a test sequence or not. I tried following tom66's instructions in post #3 on this thread https://www.badcaps.net/forum/showthread.php?t=26790. There was...
                                        01-17-2021, 01:06 AM
                                      • sam_sam_sam
                                        Panasonic switching power supply daughter board has two 27uf @ 50 volt capacitors which I do not keep in stock
                                        by sam_sam_sam
                                        I did not have any 27uf @ 50 volt capacitors but one nice thing is that it has enough room for two capacitors in parallel a 22uf and a 4.7uf @ 50 volts 22 plus 4.7 equals 26.7uf which so very close to 27uf I will show some pictures of it sometime tomorrow

                                        This is one of the shit est boards I seen in a very long time and it was the daughter board the traces just lifting off the board I had to use the capacitor leads to repair the the traces and the main board is not any better because I had to repair several traces for the daughter board to the main board

                                        After all of...
                                        07-13-2024, 08:14 PM
                                      • fredtred
                                        Physically bending the T-Con board creates horizontal dotted lines on OLED55CXPUA
                                        by fredtred
                                        Hello!
                                        I have been trying to solve this issue the past 12 months to no avail. I have been a lurker here during that time but finally decided to post my problem and see if anybody knows a solution.

                                        Problem
                                        My tv (OLED55CXPUA) has an issue where it displays horizonal lines of dotted artifacts.

                                        (See Attachment 1)

                                        Self Diagnosing
                                        After a very long troubleshooting period I traced the issue to the T-Con board. If I gently flexed/bend the board I could make the display go from GOOD to BAD and vice versa. I have ruled out the connectors/wires...
                                        10-29-2023, 01:09 PM
                                      • Loading...
                                      • No more items.
                                      Working...