  • Spork Schivago
    Badcaps Legend
    • Mar 2012
    • 4734
    • United States of America

    #1

    Possible ground loop

    I have two seperate PDUs in a rack. I have two seperate 240VAC receptacles running to seperate dual pole breakers. I have the rack attached to the bonding wire that the gas lines, coax spilters, water pipes, etc are bonded to.

    By having each PDU on a seperate circuit like I have it, did I create a ground loop?
    -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full
  • petehall347
    Badcaps Legend
    • Jan 2015
    • 4425
    • United Kingdom

    #2
    Re: Possible ground loop

    yes most likely

    Comment

    • Spork Schivago
      Badcaps Legend
      • Mar 2012
      • 4734
      • United States of America

      #3
      Re: Possible ground loop

      Would I test by plugging on each PDU and running a voltmeter across the two PDUs? Any suggestions on how to keep the two separate receptacles but do away with the ground loop?

      **edit:

      The two receptacles have a pigtail running from the ground to the metal workmans box. If I used metal conduit to connect to the two metallic boxes together, that should tie to the two grounds together, and prevent the grounding loop, correct? They'd share the same potential voltage difference than.
      Last edited by Spork Schivago; 10-09-2018, 12:19 PM.
      -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

      Comment

      • kaboom
        "Oh, Grouchy!"
        • Jan 2011
        • 2507
        • USA

        #4
        Re: Possible ground loop

        240V as in the two 120V outside legs of a single-phase distribution transformer?
        If so, and they're straight-240V (not using the neutral or no neutral current) ground on the supply side isn't involved.



        They're already bonded to each other in the rack- just run a #6CU bonding jumper from rack to the GND bar in the panel. Don't run the rack jumper to the grounding electrode conductor(s) going to the waterpipe or ground rod(s).

        Take the rack back to its source.

        Your metal boxes still need to an EGC per NEC.
        "pokemon go... to hell!"

        EOL it...
        Originally posted by shango066
        All style and no substance.
        Originally posted by smashstuff30
        guilty,guilty,guilty,guilty!
        guilty of being cheap-made!

        Comment

        • Spork Schivago
          Badcaps Legend
          • Mar 2012
          • 4734
          • United States of America

          #5
          Re: Possible ground loop

          Originally posted by kaboom
          240V as in the two 120V outside legs of a single-phase distribution transformer?
          Could you go a bit more in detail about what you mean by outside leg? I believe the answer to your question is yes. Two 120VACs coming in, centre-tapped. Each of the 120VACs are 180 degrees out of phase with the other. Are these the legs you speak of?

          Originally posted by kaboom
          If so, and they're straight-240V (not using the neutral or no neutral current) ground on the supply side isn't involved.



          They're already bonded to each other in the rack- just run a #6CU bonding jumper from rack to the GND bar in the panel. Don't run the rack jumper to the grounding electrode conductor(s) going to the waterpipe or ground rod(s).

          Take the rack back to its source.
          We currently have the rack bonded to a wire that runs to the earth electrodes buried in the ground, that the panel also uses, that the splitter uses, the gas line, the water pipes, etc.

          Are you saying unhook that wire from the rack that goes to that bare stranded wire, and instead run a wire from the rack directly to the ground bar in the panel? That (I think it's 8 gauge, but might be larger, like 6) runs to the panel as well and connects to the ground and neutral buss bars. There's one on each side, but the electrician who installed it didn't seem to run the bare copper to one side, the neutrals to the other, like I probably would have done. I can show pics if you'd like.

          Originally posted by kaboom
          Your metal boxes still need to an EGC per NEC.
          I ran a continuity meter between the receptacles and saw 0 ohm resistance, because they're sharing the same ground. Code enforcer checked everything out and passed us. Could you please elaborate how this EGC should be done with the metal boxes? These boxes had a raised spot, and that's where I installed my pig tail, grounding the receptacles metal boxes. Is that not correct?

          Thanks!
          -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

          Comment

          • petehall347
            Badcaps Legend
            • Jan 2015
            • 4425
            • United Kingdom

            #6
            Re: Possible ground loop

            sounds like a proper headache with split 240v . its normal here on single phase . although we do have 2 supplies here and when i done a party here we had to split the supplies . told everyone where to plug in lights and audio . they never listened and i had to find what they had done .. lights in audio supply and audio in lights supply caused the problem .

            Comment

            • kaboom
              "Oh, Grouchy!"
              • Jan 2011
              • 2507
              • USA

              #7
              Re: Possible ground loop

              Originally posted by Spork Schivago
              Could you go a bit more in detail about what you mean by outside leg? I believe the answer to your question is yes. Two 120VACs coming in, centre-tapped. Each of the 120VACs are 180 degrees out of phase with the other. Are these the legs you speak of?
              Yes.

              Originally posted by Spork Schivago
              Are you saying unhook that wire from the rack that goes to that bare stranded wire, and instead run a wire from the rack directly to the ground bar in the panel?
              Also, yes.
              For fun, put an AC ammeter in series with this jumper- you should read no current. Well, maybe a few milliamps from the line-GND Y-caps in any noise filters...

              Originally posted by Spork Schivago
              That (I think it's 8 gauge, but might be larger, like 6) runs to the panel as well and connects to the ground and neutral buss bars. There's one on each side, but the electrician who installed it didn't seem to run the bare copper to one side, the neutrals to the other, like I probably would have done. I can show pics if you'd like.
              If that's a service panel (not a subpanel), neutrals and grounds can be landed on the same bars. There should be some kind of jumper from both bars, and from the GND bar to the panel enclosure as well. Depending on the particular panel, the "bond" from the neutral bar to enclosure can be a green screw that's turned in completely, engaging threads in the enclosure.. since the GND bar is always tied to the panel, this effects the neutral-GND bond, by way of the neutral bar->bonding screw->enclosure->GND bus.

              Sometimes, there's a jumper. Or a little of both; sometimes there's a #6 solid between the two bars in addition to a green screw bonding the can.

              Originally posted by Spork Schivago
              I ran a continuity meter between the receptacles and saw 0 ohm resistance, because they're sharing the same ground. Code enforcer checked everything out and passed us. Could you please elaborate how this EGC should be done with the metal boxes? These boxes had a raised spot, and that's where I installed my pig tail, grounding the receptacles metal boxes. Is that not correct?
              Should be, you've got conduit or MC from the panel to each box, with one of those green pigtails jumping up to the receptacles. Or NM with ground to each box instead.

              If I may ask, these units do not power any 120V loads? Only 240V loads?

              Also, lose the bond to the gas line, unless you have CSST, which is another story.

              Iron/steel gas pipes are typically bonded thru the EGC of any electrically-operated device connected to such pipes. Eg- via the EGC of a gas dryer, furnace, range/oven/cooktop, etc...

              Originally posted by Spork Schivago
              Thanks!
              'Welcome.
              "pokemon go... to hell!"

              EOL it...
              Originally posted by shango066
              All style and no substance.
              Originally posted by smashstuff30
              guilty,guilty,guilty,guilty!
              guilty of being cheap-made!

              Comment

              • stj
                Great Sage 齊天大聖
                • Dec 2009
                • 30952
                • Albion

                #8
                Re: Possible ground loop

                draw a wiring schematic, i cant follow this.

                Comment

                • budm
                  Badcaps Legend
                  • Feb 2010
                  • 40746
                  • USA

                  #9
                  Re: Possible ground loop

                  Is ground loop causing problem in your setup right now?
                  Never stop learning
                  Basic LCD TV and Monitor troubleshooting guides.
                  http://www.badcaps.net/forum/showthr...956#post305956

                  Voltage Regulator (LDO) testing:
                  http://www.badcaps.net/forum/showthr...999#post300999

                  Inverter testing using old CFL:
                  http://www.badcaps.net/forum/showthr...er+testing+cfl

                  Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                  http://s807.photobucket.com/user/budm/library/

                  TV Factory reset codes listing:
                  http://www.badcaps.net/forum/showthread.php?t=24809

                  Comment

                  • Spork Schivago
                    Badcaps Legend
                    • Mar 2012
                    • 4734
                    • United States of America

                    #10
                    Re: Possible ground loop

                    Originally posted by kaboom
                    Yes.



                    Also, yes.
                    For fun, put an AC ammeter in series with this jumper- you should read no current. Well, maybe a few milliamps from the line-GND Y-caps in any noise filters...



                    If that's a service panel (not a subpanel), neutrals and grounds can be landed on the same bars. There should be some kind of jumper from both bars, and from the GND bar to the panel enclosure as well. Depending on the particular panel, the "bond" from the neutral bar to enclosure can be a green screw that's turned in completely, engaging threads in the enclosure.. since the GND bar is always tied to the panel, this effects the neutral-GND bond, by way of the neutral bar->bonding screw->enclosure->GND bus.

                    Sometimes, there's a jumper. Or a little of both; sometimes there's a #6 solid between the two bars in addition to a green screw bonding the can.



                    Should be, you've got conduit or MC from the panel to each box, with one of those green pigtails jumping up to the receptacles. Or NM with ground to each box instead.

                    If I may ask, these units do not power any 120V loads? Only 240V loads?

                    Also, lose the bond to the gas line, unless you have CSST, which is another story.

                    Iron/steel gas pipes are typically bonded thru the EGC of any electrically-operated device connected to such pipes. Eg- via the EGC of a gas dryer, furnace, range/oven/cooktop, etc...



                    'Welcome.
                    Thank you. We do have CSST, but the main supply run is black iron or black pipe, what ever its called. I wanted CSST the hole way, but the installer fibbed a bit and said you couldn't build up a supply with CSST. I want to say his reason was because they didn't make it large enough diameter, but I guess that was wrong. He just really really likes black iron. It's okay though, just a straight run of black pipe, then we branch off that straight run with CSST.

                    I will send a picture of the panel. It is not a sub panel. There is a green screw, but I believe it's not being used. The bare copper comes in where next to where the Neutral from the pole comes in. Both the gnd and neutral bars are connected.
                    -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                    Comment

                    • Spork Schivago
                      Badcaps Legend
                      • Mar 2012
                      • 4734
                      • United States of America

                      #11
                      Re: Possible ground loop

                      Originally posted by budm
                      Is ground loop causing problem in your setup right now?
                      No. But I fear if something goes wrong (not because of me), perhaps company's will not warrant my hardware because of it. Do you think I'd be fine if I just left it?
                      -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                      Comment

                      • Spork Schivago
                        Badcaps Legend
                        • Mar 2012
                        • 4734
                        • United States of America

                        #12
                        Re: Possible ground loop

                        Here's some pics of the panel.

                        Phone took the pics sideways for some reason. The first shows how the Neutral and gnd are hooked up to the panel. Second shows how the electrician ran the earth gnd to another point on the panel. The bare copper that's buried goes into the panel at the top, where the Neutral is hooked. The bare gnd that runs through the basement that everything is bonded to goes to the bottom the gnd buss bar. The gnd and neutral buss bars are connected at the top with a bar. The bar came with the panel. The conduit I ran is the cantex schedule 40 rigid PVC.
                        Attached Files
                        Last edited by Spork Schivago; 10-10-2018, 11:16 AM.
                        -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                        Comment

                        • Spork Schivago
                          Badcaps Legend
                          • Mar 2012
                          • 4734
                          • United States of America

                          #13
                          Re: Possible ground loop

                          Here's a pic of the two 240VAC receptacles that I installed myself. They run to dual pole breakers installed on opposite sides of the panel.

                          There's also a pic of one of the boxes with the cover removed, so you guys can see how I did the pigtail. I did this so if one of the supply lines ever came free, God forbid, and touched the metal box, it should trip the breaker, rather than energizing it so if someone touched it, they shouldn't get shocked.

                          What really surprised me, my neighbor who works for a company that installs junction boxes all the time, never heard of grounding those boxes like that, and doesn't understand why it needs to be grounded.
                          Attached Files
                          -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                          Comment

                          • Spork Schivago
                            Badcaps Legend
                            • Mar 2012
                            • 4734
                            • United States of America

                            #14
                            Re: Possible ground loop

                            Here's a pic of the two 240VAC receptacles that I installed myself. They run to dual pole breakers installed on opposite sides of the panel.

                            There's also a pic of one of the boxes with the cover removed, so you guys can see how I did the pigtail. I did this so if one of the supply lines ever came free, God forbid, and touched the metal box, it should trip the breaker, rather than energizing it so if someone touched it, they shouldn't get shocked.

                            What really surprised me, my neighbor who works for a company that installs junction boxes all the time, never heard of grounding those boxes like that, and doesn't understand why it needs to be grounded.
                            -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                            Comment

                            • stj
                              Great Sage 齊天大聖
                              • Dec 2009
                              • 30952
                              • Albion

                              #15
                              Re: Possible ground loop

                              unshiethed earth wires - yuk.
                              what's the gray paste-shit on the incoming N wire?

                              Comment

                              • budm
                                Badcaps Legend
                                • Feb 2010
                                • 40746
                                • USA

                                #16
                                Re: Possible ground loop

                                That electrical box is grounded when the face plate is bolted to the box since the outlet GND makes contact with the face plate via the brass strap on the back of the outlet.
                                https://www.ecmweb.com/qampa/code-qa...-conductor-box
                                Last edited by budm; 10-10-2018, 01:09 PM.
                                Never stop learning
                                Basic LCD TV and Monitor troubleshooting guides.
                                http://www.badcaps.net/forum/showthr...956#post305956

                                Voltage Regulator (LDO) testing:
                                http://www.badcaps.net/forum/showthr...999#post300999

                                Inverter testing using old CFL:
                                http://www.badcaps.net/forum/showthr...er+testing+cfl

                                Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                                http://s807.photobucket.com/user/budm/library/

                                TV Factory reset codes listing:
                                http://www.badcaps.net/forum/showthread.php?t=24809

                                Comment

                                • stj
                                  Great Sage 齊天大聖
                                  • Dec 2009
                                  • 30952
                                  • Albion

                                  #17
                                  Re: Possible ground loop

                                  as long as the screws are all good, but if the center ones fail the assembly will be floating inside.

                                  Comment

                                  • budm
                                    Badcaps Legend
                                    • Feb 2010
                                    • 40746
                                    • USA

                                    #18
                                    Re: Possible ground loop

                                    Originally posted by stj
                                    as long as the screws are all good, but if the center ones fail the assembly will be floating inside.
                                    Yep, this why it is better to ground the box instead of relying on the contact between the outlet GND and the face plate to the metal box. I always GND my outlet box with GND wire just in case.
                                    Last edited by budm; 10-10-2018, 03:17 PM.
                                    Never stop learning
                                    Basic LCD TV and Monitor troubleshooting guides.
                                    http://www.badcaps.net/forum/showthr...956#post305956

                                    Voltage Regulator (LDO) testing:
                                    http://www.badcaps.net/forum/showthr...999#post300999

                                    Inverter testing using old CFL:
                                    http://www.badcaps.net/forum/showthr...er+testing+cfl

                                    Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                                    http://s807.photobucket.com/user/budm/library/

                                    TV Factory reset codes listing:
                                    http://www.badcaps.net/forum/showthread.php?t=24809

                                    Comment

                                    • stj
                                      Great Sage 齊天大聖
                                      • Dec 2009
                                      • 30952
                                      • Albion

                                      #19
                                      Re: Possible ground loop

                                      yes, i was wondering why there is a wire-twist instead of putting the incoming and box earths into the socket terminal.

                                      Comment

                                      • Spork Schivago
                                        Badcaps Legend
                                        • Mar 2012
                                        • 4734
                                        • United States of America

                                        #20
                                        Re: Possible ground loop

                                        Originally posted by budm
                                        Yep, this why it is better to ground the box instead of relying on the contact between the outlet GND and the face plate to the metal box. I always GND my outlet box with GND wire just in case.
                                        That's what I did. It wasn't too long ago that we found a light switch that failed. It literally was broken in half.

                                        I do not mind spending the extra couple mins to run a pig tail for extra safety. I don't know if it's required by code, but it always feels like it's the right way to do it...
                                        -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                                        Comment

                                        Related Topics

                                        Collapse

                                        • Takeatry
                                          Yet another Samsung QLED Boot Loop
                                          by Takeatry
                                          Samsung QLED QN50Q — purchased 2022 started experiencing a delay in the picture coming on in the morning less than 2 years later. Did not know the term boot loop at that time. As the loop delay ran into a few minutes did all the recommended troubleshooting, soft and hard reset, changing cables and outlet locations, no help. As the delay increased contacted Samsung tech group and allow them remote access the tv. Tech was moving too fast to see exactly what he was doing but this ultimately it was also no help. Lived with the delay until it stretched out over 6 hours. Pulled of off the back cover...
                                          10-04-2024, 02:57 PM
                                        • blaster_
                                          Samsung UE49MU6105K - boot loop, horizontal lines
                                          by blaster_
                                          Less than a year out of warranty, samsung UE49MU6105K craps out, they've got this designed obsolescence down to an exact science of self destruct when out of warranty...

                                          Screen started to show horizontal lines and ghosted image at the bottom, then turned off by itself. Did software update, to no avail of the line problem, and got a boot loop after some minutes of watching TV. This boot loop will turn on the backlights for some seconds the sound comes on, the image will turn dark very fast and then it reboots again. Pressing power button will not put it on standby. Disconnecting...
                                          06-22-2022, 05:19 PM
                                        • Stefano Crivellari
                                          Lenovo Legion 5 (15ITH6H) kind of boot loop but not sure
                                          by Stefano Crivellari
                                          Hi, I wonder if anyone can help me fix my Lenovo Legion 5 (15ITH6H) laptop. Basically, after a windows update the computer would not boot anymore. When powering on the laptop the screen has no backlight and nothing would show up, using an external monitor did not help. However, the laptop would still spin up the fans and turn on the keyboard backlight. The keyboard backlight intensity function key would work and the power button led and the charging led are also working. I've tried every possible combination of key press and power button hold down time but did not change anything. At this point...
                                          01-14-2025, 03:49 PM
                                        • ferah831208
                                          HP gaming 15-0013dx quanta G3HA no video, screen polarize on and off loop
                                          by ferah831208
                                          I have an HP gaming 15-0013dx laptop , motherboard quanta G3HA with AMD Ryzen 5 cpu and Nvidia discrete grsphics card. The laptop turns on and u can see the screen polarizing on and off in a loop but no video signal. All voltages are ok measured and stable (I checked all with oscilloscope). This schematics don't have power sequence but I'm using a similar sequence from another laptop with AMD CPU and I get all to the point CPU must release apu_pwrok and apu_rst#, this signal comes valid only for the period of time the screen is polarized and they disappear and same loop behaviour (active/inactive)....
                                          12-07-2024, 04:02 PM
                                        • NolesFan
                                          Samsung un82ru88000f - Boot loop sort of but can correct with taping of LVDS ribbon
                                          by NolesFan
                                          Hello all... TV started boot looping. Opened the back panel and tried to isolate the problem. Just PSB no boot loop. PSB and MB no boot loop. Plug in the LVDS from panel to MB and boot looping starts up. It doesnt matter of order that I plug the LVDS ribbons back in, only 1 and no boot loop but as soon as 2nd one plugs in boot looping. I then noticed a flicker on the screen when I was closing the clip on the harness to the LVDS. Shut the lights off so I can see better, and I noticed as i slowly close it, I will get a picture, but as soon as it clips in, I lose picture and booting happens. So I...
                                          10-24-2024, 06:36 PM
                                        • Loading...
                                        • No more items.
                                        Working...