    Re: Possible ground loop

    Originally posted by stj
    yes, i was wondering why there is a wire-twist instead of putting the incoming and box earths into the socket terminal.
    Do you mean wrap the incoming gnd or earth around the screw on the receptacle, leaving a long enough end to also screw it to the box? If so, I thought about doing that, but personally felt the way I did it looked a little nicer.

    I wanted to buy some of those splicer box things you showed me that one time. I just haven't gotten around to ordering them. They looked interesting.
    -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

    Comment

    • petehall347
      Badcaps Legend
      • Jan 2015
      • 4448
      • United Kingdom

      #22
      Re: Possible ground loop

      can you not get earth wire sleeving ?

      example

      Comment

      • Spork Schivago
        Badcaps Legend
        • Mar 2012
        • 4734
        • United States of America

        #23
        Re: Possible ground loop

        Originally posted by stj
        unshiethed earth wires - yuk.
        what's the gray paste-shit on the incoming N wire?
        That N wire looks like aluminum. It's on the other two hot legs as well. My guess is some sort of conductive material that might prevent oxidation, especially being in a basement. We run a dehumidifier down there 24x7, that drains directly into the city sewage. Perhaps the electrician thought it was necessary?
        -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

        Comment

        • Spork Schivago
          Badcaps Legend
          • Mar 2012
          • 4734
          • United States of America

          #24
          Re: Possible ground loop

          Originally posted by petehall347
          can you not get earth wire sleeving ?

          example
          In this area, I've only ever seen the bare copper wire being used. Various companies all carry these blocks that attach directly to the bare wire, so it might be a local code or something?
          Attached Files

          if you find these attachements useful please consider making a small donation to the site

          Last edited by Spork Schivago; 10-10-2018, 05:28 PM.
          -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

          Comment

          • petehall347
            Badcaps Legend
            • Jan 2015
            • 4448
            • United Kingdom

            #25
            Re: Possible ground loop

            some electricians here use bare earth wire . i follow them round and add sleeving . not really necessary unless close to live wires to cause arcs or dead short like we had here . the earth rod was smoking

            Comment

            • stj
              Great Sage 齊天大聖
              • Dec 2009
              • 31285
              • Albion

              #26
              Re: Possible ground loop

              wrong, sleeving is mandated by the 17th edition of the codes.
              it's strict on the colours too.

              Comment

              • delaware74b
                Badcaps Veteran
                • Apr 2009
                • 628
                • USA

                #27
                Re: Possible ground loop

                The gray paste on the neutral is Noalox and is required on outdoor aluminum connections. It is optional for indoor connections. Personally, I use it on all stranded connections, regardless of location. The 2 hot feeds under those yellow safety covers should also have the Noalox like the service neutral.
                Last edited by delaware74b; 10-10-2018, 08:26 PM.
                Stupidity should be a crime, especially for drivers. I have NO patience for them.

                Comment

                • Spork Schivago
                  Badcaps Legend
                  • Mar 2012
                  • 4734
                  • United States of America

                  #28
                  Re: Possible ground loop

                  The two hot feeds do contain it as well. Is that the same stuff they give you at auto supply stores when you buy a new car battery? Looks the same.

                  For the ground wire for the rack... What's the reason for running a dedicated wire from the rack to the ground buss bar in the panel? Is it in case the water, gas, or cable accidently get struck by lightning or something, there's no chance of it going to the rack on its way to earth?

                  I used 4 gauge bare stranded wire. I will use insulated for this new wire but should I use 4 gauge? Can someone suggest a link to a good source? I noticed the stuff in the house vs the stuff I bought at Corning Building has different twists and probably different number of individual strands...
                  -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                  Comment

                  • Spork Schivago
                    Badcaps Legend
                    • Mar 2012
                    • 4734
                    • United States of America

                    #29
                    Re: Possible ground loop

                    I might not have a ground loop here at all. I have two dual pole breakers, one on each side of the panel. Each breaker is using both incoming lines. The two buss bars, GND and Neutral, are connected together. I measure voltage on both receptacle metal boxes and don't see any voltage, at least as fine as my meter can measure.

                    I'm now grounding the various equipment. The splitter doesn't have a spot for me to hook up a ground wire. I believe the case just grounds directly to the rack through the case nuts. However, the local cable company is insisting it be bonded per their requirements, which includes running a cable from the splitter to that bare cable running throughout the basement's ceiling, or directly to the panel, if it's 20 feet or closer away.

                    I think I'll take a screw out and just put a D-ring terminal on 10-gauge THHN stranded green wire, bond it the way they want, call them to come verify it's to their satisfaction, have them hook the new hard line up at the pole, and then start running the coax and ethernet lines to the new system.

                    I still need to ground the router and install the wireless APs. Then I can start working on making money. I was sick for a long time and it really put me behind schedule, but I'm starting to feel a lot better and it's good to get back to work!!!!!!
                    -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                    Comment

                    • petehall347
                      Badcaps Legend
                      • Jan 2015
                      • 4448
                      • United Kingdom

                      #30
                      Re: Possible ground loop

                      can you explain the incoming supply ? or draw a diagram . trying to get a handle on this .
                      for example we have high voltage transformer up a pole that supplies single phase 240v . terra terra system .. dead easy if working from same main panel . only ground loops caused from more than one unit unit connected to supply earth .

                      Comment

                      • delaware74b
                        Badcaps Veteran
                        • Apr 2009
                        • 628
                        • USA

                        #31
                        Re: Possible ground loop

                        It's different than the stuff at the auto parts stores. Here is a link to it at Big Orange:

                        https://www.homedepot.com/p/Ideal-NO...-202276208-_-N
                        Stupidity should be a crime, especially for drivers. I have NO patience for them.

                        Comment

                        • Spork Schivago
                          Badcaps Legend
                          • Mar 2012
                          • 4734
                          • United States of America

                          #32
                          Re: Possible ground loop

                          Originally posted by petehall347
                          can you explain the incoming supply ? or draw a diagram . trying to get a handle on this .
                          for example we have high voltage transformer up a pole that supplies single phase 240v . terra terra system .. dead easy if working from same main panel . only ground loops caused from more than one unit unit connected to supply earth .
                          Yes sir, to the best of my ability. I believe we have a transformer at that pole that receives 240VAC and supplies two 120VAC lines plus a neutral to the house breaker. I believe it's called centre tapped.

                          On the panel, every other breaker is on one of the 120VAC lines. So we install a dual pole breaker, we're getting 120VAC from one incoming line, another 120VAC from the other incoming line, 180 degrees apart, giving us 240VAC.

                          On the panel is two bare copper lines, 4 gauge, stranded. One them runs throughout the basement and the various utilities get bonded to this line. It ties in right next to where the neutral from the pole ties into. One the GND buss bar is where the other 4 gauge stranded wire hooks up. It's a shorter run and goes out to my side yard, where it's buried and attached to a rod (I believe).

                          This is now why I don't think I have a ground loop at all. Even though both receptacles are ran seperately to the breaker panel, they're still sharing the same earth connection.

                          Originally, I thought the electrician ran two earth connections to the panel, because of the two bare copper 4 gauge stranded wires coming out of the panel.

                          Does this help you at all?
                          -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                          Comment

                          • petehall347
                            Badcaps Legend
                            • Jan 2015
                            • 4448
                            • United Kingdom

                            #33
                            Re: Possible ground loop

                            ground and neutrals bonded at same place says you should be fine so far as i understand it .

                            Comment

                            • Spork Schivago
                              Badcaps Legend
                              • Mar 2012
                              • 4734
                              • United States of America

                              #34
                              Re: Possible ground loop

                              Originally posted by petehall347
                              ground and neutrals bonded at same place says you should be fine so far as i understand it .
                              Yes, that's the way I understand the ground loops. I believe I misunderstood the electrician when he said he was running a seperate grounding wire throughout the basement. I saw the two bare copper lines and thought there were two rods in the ground. I am not sure if there's any benefit to the way he ran those wires, but I guess it looks a little nicer.

                              I have 4 gauge lugs or whatever they're called. I crimped one on the bare wire for the rack, that bonds to the ground wire above it. I want to replace that with the (insulated?) green with yellow stripe wire and run it directly to the panel. Just need to find a place that sells it in 4 gauge.
                              -- Law of Expanding Memory: Applications Will Also Expand Until RAM Is Full

                              Comment

                              • petehall347
                                Badcaps Legend
                                • Jan 2015
                                • 4448
                                • United Kingdom

                                #35
                                Re: Possible ground loop

                                way i understand ground loops is with audio equipment .. only one unit should have an earth wire connected to the outlet .

                                Comment

                                • redwire
                                  Badcaps Legend
                                  • Dec 2010
                                  • 3912
                                  • Canada

                                  #36
                                  Re: Possible ground loop

                                  I'm not sure about picking off ground from the panel neutral bus. It would have to have the current rating including all the neutral currents. Square-D might have made a mistake there- does it make sense, the feeder bus bar and neutral (return) buss bar carry the same currents for 120VAC loads. Example: take two 40A loads on one side (120VAC), you have 80A flowing on the little neutral buss bar. It's much smaller than the feeder buss bar.

                                  What I've done (for sub-panels) is use a split-bolt to bond the ground-rod wire to the ground wire running out to the sub-panel.

                                  I would not worry about PDU ground loops. It can be an issue between some crappy RS-232 serial systems or audio gear where a few V is a problem, so I've used orange duplex receptacles which have an isolated ground to prevent ground loops.
                                  Your PDU's are grounded together in the rack, and back at the junction box. So there is a loop but not a prob.

                                  Comment

                                  Related Topics

                                  Collapse

                                  • Takeatry
                                    Yet another Samsung QLED Boot Loop
                                    by Takeatry
                                    Samsung QLED QN50Q — purchased 2022 started experiencing a delay in the picture coming on in the morning less than 2 years later. Did not know the term boot loop at that time. As the loop delay ran into a few minutes did all the recommended troubleshooting, soft and hard reset, changing cables and outlet locations, no help. As the delay increased contacted Samsung tech group and allow them remote access the tv. Tech was moving too fast to see exactly what he was doing but this ultimately it was also no help. Lived with the delay until it stretched out over 6 hours. Pulled of off the back cover...
                                    10-04-2024, 02:57 PM
                                  • blaster_
                                    Samsung UE49MU6105K - boot loop, horizontal lines
                                    by blaster_
                                    Less than a year out of warranty, samsung UE49MU6105K craps out, they've got this designed obsolescence down to an exact science of self destruct when out of warranty...

                                    Screen started to show horizontal lines and ghosted image at the bottom, then turned off by itself. Did software update, to no avail of the line problem, and got a boot loop after some minutes of watching TV. This boot loop will turn on the backlights for some seconds the sound comes on, the image will turn dark very fast and then it reboots again. Pressing power button will not put it on standby. Disconnecting...
                                    06-22-2022, 05:19 PM
                                  • Stefano Crivellari
                                    Lenovo Legion 5 (15ITH6H) kind of boot loop but not sure
                                    by Stefano Crivellari
                                    Hi, I wonder if anyone can help me fix my Lenovo Legion 5 (15ITH6H) laptop. Basically, after a windows update the computer would not boot anymore. When powering on the laptop the screen has no backlight and nothing would show up, using an external monitor did not help. However, the laptop would still spin up the fans and turn on the keyboard backlight. The keyboard backlight intensity function key would work and the power button led and the charging led are also working. I've tried every possible combination of key press and power button hold down time but did not change anything. At this point...
                                    01-14-2025, 03:49 PM
                                  • ferah831208
                                    HP gaming 15-0013dx quanta G3HA no video, screen polarize on and off loop
                                    by ferah831208
                                    I have an HP gaming 15-0013dx laptop , motherboard quanta G3HA with AMD Ryzen 5 cpu and Nvidia discrete grsphics card. The laptop turns on and u can see the screen polarizing on and off in a loop but no video signal. All voltages are ok measured and stable (I checked all with oscilloscope). This schematics don't have power sequence but I'm using a similar sequence from another laptop with AMD CPU and I get all to the point CPU must release apu_pwrok and apu_rst#, this signal comes valid only for the period of time the screen is polarized and they disappear and same loop behaviour (active/inactive)....
                                    12-07-2024, 04:02 PM
                                  • NolesFan
                                    Samsung un82ru88000f - Boot loop sort of but can correct with taping of LVDS ribbon
                                    by NolesFan
                                    Hello all... TV started boot looping. Opened the back panel and tried to isolate the problem. Just PSB no boot loop. PSB and MB no boot loop. Plug in the LVDS from panel to MB and boot looping starts up. It doesnt matter of order that I plug the LVDS ribbons back in, only 1 and no boot loop but as soon as 2nd one plugs in boot looping. I then noticed a flicker on the screen when I was closing the clip on the harness to the LVDS. Shut the lights off so I can see better, and I noticed as i slowly close it, I will get a picture, but as soon as it clips in, I lose picture and booting happens. So I...
                                    10-24-2024, 06:36 PM
                                  • Loading...
                                  • No more items.
                                  Working...