Announcement
Collapse
No announcement yet.
anyone recommend an earth leakage clamp meter ?
Collapse
X
-
had plenty of rain and its not tripped . i won't be convinced until after lots more rain .
-
Originally posted by stj View Posthow long ago was it damaged?
could be water ingress up the cable
Leave a comment:
-
Originally posted by sam_sam_sam View Post
This is probably a good way of seeing if's a bad connection somewhere but you could still use a megger but here is how I would do where ever you have a spliced connection repair I would soak them one at a time and see if your resistance goes down or not if it does not go to the next spliced connection repair and do the whole cable that way if you do not find anything else at this point you are going to have very hard time figuring out what is still causing the breaker to trip but if it is been in service for a long time I might consider replacing it with a new one if you still have issues then I would recommend inspecting every inch of the cable for nicks and signs of corrosion or pitting of any kind check those areas as well
Leave a comment:
-
Originally posted by petehall347 View Postthinking of getting a thermal imaging camera and putting a heavy load on it and looking for hot spots .
Leave a comment:
-
still some insulation leakage going on but that bit looks the worst from i can see , might be the old joiner letting damp in . its hard to tell .. thinking of getting a thermal imaging camera and putting a heavy load on it and looking for hot spots .
Leave a comment:
-
Unfortunately you can do anything for someone who does not listen you when you tell them that are electrical wiring in a certain place or area and what is even worse is that they do not tell you that they damaged it so it could have been fixed properly the first time what kind-a contractors are these people anyway
The reason why you use plastic outside rated conduit is that when you are digging you will see the conduit and you know where the wiring is yes we have underground cable here but I still put it in outdoor conduit anyway
I would agree with you if it gets damaged it is harder to deal with but me personally I do not like making splices that are underground for any reason I would rather just have it come up three feet and go back underground for peace of mind and not have breakers tripping when it rains real heavy but that's just meLast edited by sam_sam_sam; 07-11-2024, 07:53 PM.
Leave a comment:
-
Originally posted by sam_sam_sam View Post
Why do you not have this cable in a outdoor rated conduit in this country you are required to use outdoor conduit for running electrical wiring except for landscaping lighting 12 volts or under that voltage if I was running landscaping lighting and it was going to be permanent I would use conduit even for this
Leave a comment:
-
Originally posted by petehall347 View Postmystery solved when one of the lads was looking for the resin joint i did years ago after some idiot lit a fire on it . this is jcb damage from a year or two back . i did warn him about the cables . looks like he badly damaged it then attempted to do a quick tape up job . .. makes the mind boggle it does . now we have to get another resin kit and do a proper repair ..
Leave a comment:
-
Sweet! I figured it would fail that insulation test and there must be some trouble somewhere. Glad you found it.
Leave a comment:
-
mystery solved when one of the lads was looking for the resin joint i did years ago after some idiot lit a fire on it . this is jcb damage from a year or two back . i did warn him about the cables . looks like he badly damaged it then attempted to do a quick tape up job . .. makes the mind boggle it does . now we have to get another resin kit and do a proper repair ..
Leave a comment:
-
insulation test failed . especially live to ground and ground to armour 0.0 others at 0.3 .. they all should be better than 1.0 hardly any difference testing from both ends of the swa cable .
Leave a comment:
-
Originally posted by petehall347 View Post
if you mean with the megger not yet . will do once i have the new switch and wires disconnected both ends , i could also do a psc test but not sure if that will help here
this is same as my insulation tester .
Leave a comment:
-
Originally posted by CapLeaker View Post
Did you do an insulation test yet?
this is same as my insulation tester .
Last edited by petehall347; 07-10-2024, 05:43 AM.
Leave a comment:
-
Originally posted by petehall347 View Post
yes i know it should only connect at supply end really in case of a fault that could make all grounds live . anyway both ends disconnected for testing at the moment . i cant see this causing a problem just when it rains
Leave a comment:
-
Originally posted by stj View Postthe armor is supposed to be earthed, the metal bits that mount the wire to a box see to that.
Leave a comment:
-
the armor is supposed to be earthed, the metal bits that mount the wire to a box see to that.
Leave a comment:
-
Originally posted by redwire View PostThe 60k reading will move - the multimeter (Ohms) DC current causes electrolysis like charging a battery with the water and metals there. Try flip polarity and watch the reading.
Another approach is measure DCV to get an idea if it's wet. 3-wire? Or measure Ohms between all conductors and the armour, 4 possible readings to see if how much is leaking to what.
Line/Hot will make water boil and steam and make gurgling sounds if immersed, as a give away.
If many wet readings, I'd prepare to dig up the splice. The water will eventually corrode the conductors and the cable go open circuit.
Do you have frost and soil heaves? That moves cables around unless 1-2m below surface here.
Leave a comment:
Leave a comment: