Announcement

Collapse
No announcement yet.

anyone recommend an earth leakage clamp meter ?

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • petehall347
    replied
    had plenty of rain and its not tripped . i won't be convinced until after lots more rain .

    Leave a comment:


  • petehall347
    replied
    Originally posted by stj View Post
    how long ago was it damaged?
    could be water ingress up the cable
    at least a year ago if not more like 2 years . it was soaking wet . i left it to dry out in the sun for a while and it felt dry before splicing it . its on a slope and the bad half of the cable is the higher side . but i suppose it could have soaked in more regardless . 9 hours of heavy rain forecast today so if its going to trip its very likely to do so today .

    Leave a comment:


  • stj
    replied
    how long ago was it damaged?
    could be water ingress up the cable

    Leave a comment:


  • petehall347
    replied
    Originally posted by sam_sam_sam View Post

    This is probably a good way of seeing if's a bad connection somewhere but you could still use a megger but here is how I would do where ever you have a spliced connection repair I would soak them one at a time and see if your resistance goes down or not if it does not go to the next spliced connection repair and do the whole cable that way if you do not find anything else at this point you are going to have very hard time figuring out what is still causing the breaker to trip but if it is been in service for a long time I might consider replacing it with a new one if you still have issues then I would recommend inspecting every inch of the cable for nicks and signs of corrosion or pitting of any kind check those areas as well
    hoping the tripping has stopped now . will have an idea as heavy rain forecast tomorrow . we tried soaking the old splice and if anything the readings went better but that might have been the cable drying out with the megger . at least its narrowed down to the last 1/4 length of the cable . well the other 3/4 still has insulation breakdown between the earth core and the armour . other cores are fine . not too concerned about that as they should connect together anyway . the 3 cores are packed tightly together in this cable and not much space between them .

    Leave a comment:


  • sam_sam_sam
    replied
    Originally posted by petehall347 View Post
    thinking of getting a thermal imaging camera and putting a heavy load on it and looking for hot spots .
    This is probably a good way of seeing if's a bad connection somewhere but you could still use a megger but here is how I would do where ever you have a spliced connection repair I would soak them one at a time and see if your resistance goes down or not if it does not go to the next spliced connection repair and do the whole cable that way if you do not find anything else at this point you are going to have very hard time figuring out what is still causing the breaker to trip but if it is been in service for a long time I might consider replacing it with a new one if you still have issues then I would recommend inspecting every inch of the cable for nicks and signs of corrosion or pitting of any kind check those areas as well

    Leave a comment:


  • petehall347
    replied
    still some insulation leakage going on but that bit looks the worst from i can see , might be the old joiner letting damp in . its hard to tell .. thinking of getting a thermal imaging camera and putting a heavy load on it and looking for hot spots .

    Leave a comment:


  • petehall347
    replied
    that's better now .... Click image for larger version

Name:	20240713_154212.jpg
Views:	83
Size:	2.51 MB
ID:	3308532

    Leave a comment:


  • stj
    replied
    it's only 240v though - atleast it wasnt 3-phase

    Leave a comment:


  • sam_sam_sam
    replied
    Unfortunately you can do anything for someone who does not listen you when you tell them that are electrical wiring in a certain place or area and what is even worse is that they do not tell you that they damaged it so it could have been fixed properly the first time what kind-a contractors are these people anyway

    The reason why you use plastic outside rated conduit is that when you are digging you will see the conduit and you know where the wiring is yes we have underground cable here but I still put it in outdoor conduit anyway

    I would agree with you if it gets damaged it is harder to deal with but me personally I do not like making splices that are underground for any reason I would rather just have it come up three feet and go back underground for peace of mind and not have breakers tripping when it rains real heavy but that's just me
    Last edited by sam_sam_sam; 07-11-2024, 07:53 PM.

    Leave a comment:


  • petehall347
    replied
    Originally posted by sam_sam_sam View Post

    Why do you not have this cable in a outdoor rated conduit in this country you are required to use outdoor conduit for running electrical wiring except for landscaping lighting 12 volts or under that voltage if I was running landscaping lighting and it was going to be permanent I would use conduit even for this
    its swa steel wire armoured it can live outside for 50 years if some idiot doesn't damage it with a large machine then try and hide the fact after being told it was there . the repair wont take long but finding the damage has taken hours and money . if it was in conduit matters might have been much worse . cant even imagine pulling over 100 metres through conduit around bends and over uneven surfaces ,

    Leave a comment:


  • sam_sam_sam
    replied
    Originally posted by petehall347 View Post
    mystery solved when one of the lads was looking for the resin joint i did years ago after some idiot lit a fire on it . this is jcb damage from a year or two back . i did warn him about the cables . looks like he badly damaged it then attempted to do a quick tape up job . .. makes the mind boggle it does . now we have to get another resin kit and do a proper repair .. Click image for larger version Name:	20240711_191347.jpg Views:	0 Size:	3.30 MB ID:	3307364
    Why do you not have this cable in a outdoor rated conduit in this country you are required to use outdoor conduit for running electrical wiring except for landscaping lighting 12 volts or under that voltage if I was running landscaping lighting and it was going to be permanent I would use conduit even for this

    Leave a comment:


  • CapLeaker
    replied
    Sweet! I figured it would fail that insulation test and there must be some trouble somewhere. Glad you found it.

    Leave a comment:


  • petehall347
    replied
    mystery solved when one of the lads was looking for the resin joint i did years ago after some idiot lit a fire on it . this is jcb damage from a year or two back . i did warn him about the cables . looks like he badly damaged it then attempted to do a quick tape up job . .. makes the mind boggle it does . now we have to get another resin kit and do a proper repair .. Click image for larger version  Name:	20240711_191347.jpg Views:	0 Size:	3.30 MB ID:	3307364

    Leave a comment:


  • petehall347
    replied
    insulation test failed . especially live to ground and ground to armour 0.0 others at 0.3 .. they all should be better than 1.0 hardly any difference testing from both ends of the swa cable .

    Leave a comment:


  • CapLeaker
    replied
    Originally posted by petehall347 View Post

    if you mean with the megger not yet . will do once i have the new switch and wires disconnected both ends , i could also do a psc test but not sure if that will help here
    this is same as my insulation tester .
    Click image for larger version

Name:	86.jpg
Views:	87
Size:	74.2 KB
ID:	3306371
    Yes, with a Megger or equivalent. This should show leakage real fast. I use the Fluke 1587FC for all these leakage tests. I don't use it every day, but every time I need it, it's a freaking god send for me.

    Leave a comment:


  • petehall347
    replied
    Originally posted by CapLeaker View Post

    Did you do an insulation test yet?
    if you mean with the megger not yet . will do once i have the new switch and wires disconnected both ends , i could also do a psc test but not sure if that will help here
    this is same as my insulation tester .
    Click image for larger version

Name:	86.jpg
Views:	87
Size:	74.2 KB
ID:	3306371
    Last edited by petehall347; 07-10-2024, 05:43 AM.

    Leave a comment:


  • CapLeaker
    replied
    Originally posted by petehall347 View Post

    yes i know it should only connect at supply end really in case of a fault that could make all grounds live . anyway both ends disconnected for testing at the moment . i cant see this causing a problem just when it rains
    Did you do an insulation test yet?

    Leave a comment:


  • petehall347
    replied
    Originally posted by stj View Post
    the armor is supposed to be earthed, the metal bits that mount the wire to a box see to that.
    yes i know it should only connect at supply end really in case of a fault that could make all grounds live . anyway both ends disconnected for testing at the moment . i cant see this causing a problem just when it rains

    Leave a comment:


  • stj
    replied
    the armor is supposed to be earthed, the metal bits that mount the wire to a box see to that.

    Leave a comment:


  • petehall347
    replied
    Originally posted by redwire View Post
    The 60k reading will move - the multimeter (Ohms) DC current causes electrolysis like charging a battery with the water and metals there. Try flip polarity and watch the reading.
    Another approach is measure DCV to get an idea if it's wet. 3-wire? Or measure Ohms between all conductors and the armour, 4 possible readings to see if how much is leaking to what.
    Line/Hot will make water boil and steam and make gurgling sounds if immersed, as a give away.
    If many wet readings, I'd prepare to dig up the splice. The water will eventually corrode the conductors and the cable go open circuit.

    Do you have frost and soil heaves? That moves cables around unless 1-2m below surface here.
    yes its 3 wire but now using 2 of them . the armour is also floating but appears to be grounded somehow so the outer casing is compromised maybe at the splice but i would expect that to stay wet longer being buried . one thing to note is only some of the cable is buried the rest is laying on the ground . i am very tempted to cut it roughly in half to see which half the problem is in . then if definitely in one half cut that one in half and replace the bad quarter to save him loads of money .

    Leave a comment:

Working...
X