    I've known this for ages. And, have taken steps to ensure I can't be "bitten" by it on all my UPSs.
    But, apparently, forgot to "fix" one of them -- a SmartUPS C1500. No doubt because it doesn't support a NMC (which is how I manage the herd).
    The symptoms are a rebooted computer -- but no "events" reported on the UPS (so, you figure it must have been a software crash). The TELL-TALE symptom is a computer that you find rebooted The Next Day... at virtually the same time (within seconds).
    What's happened is the UPS has done its daily self-test and the battery -- which displays as "100%" -- was unable to support the inverter. So, power to the PC fails. The UPS comes out of the self-test (reboots) and doesn't know that anything "bad" has happened (cuz it has forgotten!). The PC reboots and all is well -- until the next day, 24.00 hours later.
    The fix is to disable the self-test feature. Worst case, a battery that is in this condition (reporting 100% yet not able to support the inverter) will cause your system to crash WHEN THE POWER FAILS -- which is usually much less often than "every day"! You won't have to remember that the UPS "stages" a power failure every day as the reason why your machine is rebooted.
    Eventually, I'll figure out why the battery health reported is so wrong. But, as REAL power failures are few and far between, I can put that off for a while...
  • TechGeek
    Computer Geek
    • Jan 2015
    • 2254
    Re: Fwiw: Apc ups
    The real fix is to replace the faulty battery(ies) and run a runtime calibration.
    Permanently Retired Systems:
    Kooky and Kool Systems
    sigpic
    • Curious.George
      • Nov 2011
      • 2305
      • Unknown
      Re: Fwiw: Apc ups
      It's obviously more than that -- as the unit claims the battery is fully charged. A faulty battery would appear overcharged.
      Note that leaving the self-test configured to run periodically just gives you more opportunities for this "shutdown" to happen. APC simply skimped on their BMS when they designed these things in the hope that "staff" would eagerly replace batteries (instead of designing for longer battery life).
      [UPS should note the frequency of outages where it is deployed and adjust the battery management strategy to maximize battery "value", in those circumstances. I.e., in a deployment where outage are frequent and prolonged, you'd want to minimize recharge time to be prepared for the next outage. OTOH, where outages are infrequent or brief, the emphasis should be on being as "gentle" to the battery as possible -- to extend it's lifespan to cover more (infrequent!) outages.]
        • Jul 2011
        • 6070
        Re: Fwiw: Apc ups
        Why not use a line conditioner so you do have the battery backup stress out so much
        ( one note some battery backup do have a line conditioning to some existent but I do not necessarily trust that this function does not still have a stress on the battery )
        I had to this myself many years ago because of battery failure to often
        • petehall347
          • Jan 2015
          • 4448
          Re: Fwiw: Apc ups
          my ups did self test and failed at night then in the early morning i was awoken to a car battery exploding .. this thing doesn't even have a connection to a computer . well apart from the mains power bit . yes i run my emergency power off car batteries .
          • Curious.George
            • Nov 2011
            • 2305
            • Unknown
            Re: Fwiw: Apc ups
            We rarely have outages. At times, we encounter "switching transients" as the utility changes how our portion of the network is fed. These are just "light blinks" but can crash some devices with poorly sized power supplies.
            I believe the problem lies in how APC deals with the battery and its maintenance. They are too aggressive in getting it back online (at least, for MY needs cuz I can afford to wait 24 hours for it to replenish the charge consumed backing up my load for a 1 second "light flash").
            I've been salvaging MCUs from them with an eye towards reverse engineering the code to be less aggressive in their charging strategy...
            But, it's not risen to a high enough level of importance to preempt any of the more interesting things I'm working on (I can always just buy/rescue batteries to kick the problem down the road)
              • Jul 2011
              • 6070
              Re: Fwiw: Apc ups
              If you ever figure out how to make this less aggressive please post what you did to fix this issue
              • Curious.George
                • Nov 2011
                • 2305
                • Unknown
                Re: Fwiw: Apc ups
                As I said, the RIGHT solution is for the UPS to "take notes" about the conditions its been operating in (after all, it is likely on 24/7/365!) and how often it encounters outages, how long they are, how deeply the battery discharges, how long before the NEXT outage, etc.
                That's far too much work for me -- as I already KNOW how the UPSs are "taxed" by my loads and local power.
                So, I'll just tweek things to fit THAT sort of operating environment instead of trying to "do it right" (APC isn't paying me so why should I do their work for them?)
                • Per Hansson
                  • Jul 2005
                  • 5895
                  • Sweden
                  Re: Fwiw: Apc ups
                  Please check out the APC Smart-UPS float voltage experiment:
                  https://www.badcaps.net/forum/showthread.php?t=7872
                  • Curious.George
                    • Nov 2011
                    • 2305
                    • Unknown
                    Re: Fwiw: Apc ups
                    You can't "fix" the problem by tweaking the analog portion of the circuit. You need to add smarts to how (and when) you apply charging rules. You do that by tweeking the code in the microcontroller.
                    • Per Hansson
                      • Jul 2005
                      • 5895
                      • Sweden
                      Re: Fwiw: Apc ups
                      I didn't know you had access to the APC source code.
                      I think you mentioned elsewhere that you do not buy original batteries from APC.
                      That is good because they are crap and have a lifetime of 2 to 3 years tops in my experience.
                      For me I have had great success with CT Leader batteries that have a 10 year design lifespan.
                      I have gotten from 5 to 7 years out of them which I think is phenomenal.
                      Elfa orderno: 169-47-907 CT Leader CTH17-12 for use in APC Smart-UPS 1500
                      Elfa orderno: 169-10-293 CT Leader CTH7-12F1 for use in APC Smart-UPS 750
                      • Curious.George
                        • Nov 2011
                        • 2305
                        • Unknown
                        Re: Fwiw: Apc ups
                        I don't. Instead, I "pull" the MCUs from UPSs and decompile the code. They aren't particularly complex devices (the only complexity resides in the NMCs and understanding those isn't essential to understanding how the UPS is designed to operate -- esp as many treat NMCs as "options").
                        They're relatively trivial devices, few I/Os, etc. And, obviously built around hardware that doesn't place battery life at the top of its priorities. (I can't begin to tell you how many "bulging batteries" I've encountered in APC products)
                        They are also overpriced.
                        Thanks for the tip. Most of my batteries are rescue from UPSs that I'm not otherwise interested in rescuing (we see A LOT of discarded UPSs... pallets at a time!). For that reason, I've tried to only use UPSs that are (mechanically) built around 12V 7.5AHr batteries -- typically 4 of these in a "module".
                        One reason I'm hesitant to rescue the Matrix 5000 is that it is built around 75AHr batteries... considerably harder to come across and very expensive to replace!
                        • Sofian75
                          Dell Inspiron 5502 i7 C-state Crash
                          by Sofian75
                          Turning off C-State in the bios makes the laptop works fine, but with C-State turned on the laptop will crash quickly once Windows has booted.
                          What is managing C-State on the hardware level? What should I check?...
                          09-02-2025, 08:50 AM
                        • cappernicus
                          Satellite r945-p440 - Hard crash coming out of sleep
                          by cappernicus
                          Toshiba Satellite r945-p440
                          Motherboard: FAM2SY2 A3256A
                          I do not have a schematic or board file
                          I usually let it go to sleep every time I use it because it is nearly always plugged in, with occasional shutdowns to reset things. Then it started to hard crash every time it tried to come out of sleep. The lights would come on for half a second but before anything shows on the screen they would all shut off and it would boot up as if I had shut it down completely (except that windows knows it didn't), and when it comes back on the fan ramps up to full and stays there perpetually...
                          04-16-2025, 05:31 PM
                        • Track4207
                          Hisense H50N5300UK reboots when showing full red images
                          by Track4207
                          Hi all! A bit of an interesting and unusual problem: as the the title suggests I have a Hisense H50N5300UK that reboots when showing fullscreen solid red images (and some other solid colours, but red generally causes the issue the fastest). I first came across the problem assuming it was an intermittent issue, but later lucked into finding out that a title sequence of a show I watch happened to trigger the reboot.
                          What happens:
                          • TV appears to operate normally, for an indefinite amount of time until a problem image appears
                          • The problem image is displayed very briefly, then the
                          08-30-2023, 11:58 AM
                        • HelpMeRepair
                          6800XT artifact on benchmark and crash
                          by HelpMeRepair
                          Hi guys , thanks for the help and hint in advance
                          I have a 6800XT that is detected , but im not able to memtest it ( says it cant buffer )
                          if i try to benchmark it , it goes artifact and crash after few seconds.
                          anyone have a clue ? thanks !
                          card is a AMD FE 6800XT , and any hardware mem guide checkup can help if you have any tuto too !😀
                          edit : component looks good after visual inspection .
                          11-05-2024, 09:41 AM
                        • x_orange90_x
                          Philips 55pfl5766/f7 Software crashes
                          by x_orange90_x
                          I received this tv stuck in a boot loop and was able to get it working after letting it sit and reboot several times. Whenever I try do things in the settings it will crash back to the main screen, lock up, or reboot itself. I tried doing a Reset on it and after it rebooted nothing was changed. The Google account used was still present, and the downloaded apps were all still there. I can sometimes get further into settings such as setting up my wifi, not most times it will crash and reboot. I even manually removed the Google account and it CAME BACK after rebooting the tv. Before it rebooted one...
                          10-05-2024, 11:29 AM