Whirlpool gas oven ps/control board burnt resistor
  • CapLeaker
    Leaking Member
    • 8214
    Re: Whirlpool gas oven ps/control board burnt resistor
    its a viper12a, post #14
    • R_J
      • 9555
      I must have missed that, so the board could be a universal input, if that's the case the main filter should be rated at 450v. but it is only connected across L1 and neutral, according to the diagram so that would be 120vac. A simple check of the ac input to the board could confirm it.
      • CapLeaker
        Leaking Member
        • 8214
        I actually think there is nothing much wrong with that little supply. Maybe that L3 that has a crack and needs to be replaced. I believe that something draws too much from that supply causing r71 to open. Instead of looking at the PSU, we should be looking at whatever uses this supply.
        • R_J
          • 9555
          There is nothing else that uses the supply other than the controller itself, the oven temp sensor would be minimal, the door position switch would be nothing, the only extra current draw would be when a relay coil is energized and that would only be a few milliamps extra. The fan motor, oven elements etc. are only "switched" by the relay contacts, and don't draw current from the controller. If it works on the bench it should work in the stove.
          Maybe it was being installed with the stove live? and something touched ground during the install?
          • redwire
            • 3910
            All outputs from the board are done with mains relays. Bake, Broil, Convection fan, Oven Light.
            Only the board's inputs- door lock switch and temperature probe input are the other connections that could cause trouble.
            If the board does power up OK on the bench, then I say there is a ground fault in the inputs, or a wiring mistake when installing the board.
            I'm not sure what Q14 (TO-220) is doing. It's the only other power component. Must be a 7805.
            Whirlpool W10349742 Rev. FV3.12, SF5113
            Robertshaw LCC190 Electronic Range control
            • CapLeaker
              Leaking Member
              • 8214
              I dunno... maybe there is a wire somewhere pinched to the metal grounding it out and it has to be an input, not anything that is hooked to the relays. Only thing one can do is to just put the board in by itself and nothing connected, then plug in one thing after the other, until r71 blows again. I am not sure what Q14 is doing either.
                • Jul 2011
                • 6041
                If the controller board runs off of 120 volts and works fine on the bench
                I would strongly recommend that you check and make sure that you have a good neutral because most controller boards are 110 volts I have only seen a few of them that were 220 volts
                Most of the time the board will tell you what voltage they are if this one does not then check the two wires that power the controller ( on the oven or range ) and see what voltage you are getting
                I would check the neutral wire with a 100 watt incandescent bulb not a meter because you might get fandom voltage feedback you want to test this way ( L1 to neutral ) and L2 to neutral ) to know for sure that you have a good neutral on the outlet
                Next ( the power cord going to the range or oven ) ———>
                Use Caution doing this part———>
                on the back of the unit be careful doing this one because the power cord ( lugs ) most power cord are very short most of time and may not give very much room to test it this way with out using a lamp cord hook on the power cord lugs
                If it test good then you need make sure that you do not have a short to ground on the range or oven that is hook to the controller board
                Or you could do this that was suggested earlier but I would use a bulb that is used in small night light old school ( incandescent ) in place of the resistor that keeps burning out because this resistor in this circuit the way you show it in your diagram is no more than a fuse
                One note if this light bulb is very bright then you have a big problem you need find out why you are pulling this much current
                I hope this helps you
                • greezmky
                  • Aug 2019
                  • 11
                  • US
                  #28
                  We need not speculate any further and I APPRECIATE everyones contributions!!!!
                  Ultimately the procedure was similar to what we all have discussed in the last few posts. I plugged in the board with a hot and neutral in the stove. All the connectors are spades in molded plastic so I hooked up the dc side plug only and began testing voltages out as my brother picked bake, broil, etc. The light showed hot no matter what but only like 70vac, so I proceeded to desolder the K1 relay. We tested it with a 9v battery and it was good, that left us scorching our heads, soldered it back in and it had 110vac out?
                  At this point we decided it was time to sacrifice another R71 but I got to watch as my brother used a power strip (so that we had a switch). Upon turning on the switch there were sparks and a burnt resistor but the sparks were from the door light switch ??????. I had tested that all and even had that connector plugged in so all the dc stuff was powered with not ac stuff powered. I replace R71 and unplugged the switch for the door light and tested, now it is working!!!!
                  We decided for now it was best to jump out the switch and tape it up so that my mom still has a switched light just no automatic on light when the door opens.
                  Why this caused too much draw on the ac side I do not know as it is controlled by dc seems as if it would have killed something on that side?
                  The Issue:
                  Exploded:
                  Normally I would take it all apart and clean/fix but not taking the chance here.
                  Thank you ALL VERY MUCH!!!!!!
                    • Jul 2011
                    • 6041
                    Well I am glad that you figured out what was causing your problem
                    What happens when you hook the two wires together with out the switch does it still burn out the resistor
                    If the inside the switch has a crack and has a carbon track to ground that would explain why you were having this problem
                    • greezmky
                      • Aug 2019
                      • 11
                      • US
                      #30
                      Thank you
                      I see no crack but the carbon track could be it, who knows it is the most actuated switch in the system. My dad was never behind the stove when trying it so he could not see it but it lit up pretty good.
                      I'm just glad I got it fixed and saved them $250, the switch is an expensive little bugger at $50-$70. I may try to find some other switch though. This one takes a rod from the front to the switch, kind of dumb if you ask me but maybe it gets to hot right under where you would expect the door switch to be.
                      • R_J
                        • 9555
                        I can't see the switch itself causing a problem unless it was shorting to the stove metal chassis. I would check the two wires between the switch and controller, one might be shorted to ground. That could blow the resistor because the power supply is not isolated.
                        You could check the resistance between each switch wire to metal ground, it should be almost infinite. Check with a used appliance shop, they might have a good used part.
                        Just a note regarding the switch, the oven self clean feature may not function without the switch.
                        It looks like there may have been some arcing between the conection and the ground clip, if you choose to reassemble it use the other two holes.
                          • Jul 2011
                          • 6041
                          I would not recommend using just any kind of switch for this application because that switch is an input for the controller board if you can use it with out the switch it might be better if you do not want to spend the money on it
                          The switch case might be made out of Bakelite if this is the case then that would explain why it is exspenive and it is used because of the heat so do not use just any kind of switch for this use a switch that is rated for heat
                          • redwire
                            • 3910
                            Wow, I see where the door switch back-plate carbon-tracked. I would say the lightning arc'd across the bakelite insulation, but not sure what grounded metal is nearby? The mounting clip it did not arc to, it was something outside.
                            Gotta admit it's a weird problem, door switch shorts and takes out control board.
                            Parts for this oven are silly expensive. $52 for a door switch and I'm seeing the control board sell for $380! OUCH! You saved the oven from needing to be replaced just due to ripoff repair costs.
                            W10627802 Range Oven Door Switch is replaced by WP9757262, a newer part.
                            OP, if you still have electrical problems in the house, it might be getting big overvoltage transients. This failure I would say is due to lightning or repeated spikes on mains and other items in the house might get damaged. A bad neutral can also do it, or bad earth ground in the service. Something to keep an eye out for.
                              • 31086
                              that shit switch would be illegal in europe, the clearance between the contacts and the clip is too small.
                              • CapLeaker
                                Leaking Member
                                • 8214
                                finally! Congrats fixing the range! I never seen a bad door light switch going bad like that. Weird.
                                  • Jul 2011
                                  • 6041
                                  I have seen carbon tracking to ground before but it not a common problem but most of the time it happens at higher voltages but if lightning hit near the house that would explain how this could happen
                                  Carbon tracking is something to keep in mind it does happen
                                  It has taken out my garage door opener two different times by lighting hitting near the house and both times it fried the photo electric eyes to the controller board and I ended up having to buy another garage door opener both times because it also fried the controller board as well
                                  It also had carbon tracking in parts of the controller board
                                  • R_J
                                    • 9555
                                    Just a note in post #31 I mentioned the self clean may not work, I was wrong about that, this switch is only for the oven lamp, and not the door lock.
                                    • redwire
                                      • 3910
                                      In North America there is one multinational mega-corporation making appliances under a ton of brand names.
                                      Whirlpool Corp. makes Whirlpool, Maytag, KitchenAid, Jenn-Air, Amana, Hotpoint, Sears Kenmore, Inglis, Acros, Diqua, Estate, Brastemp, Bauknecht, Indesit, and Consul etc.
                                      So this oven switch (with a bad design) ends up in a zillion appliances, world wide. I would not be surprised to see it in European appliances.
                                      • greezmky
                                        • Aug 2019
                                        • 11
                                        • US
                                        #39
                                        I will not be using the old switch, just not worth the chance of actually killing the board. I have checked all the wiring. I feel like the carbon track is the most viable explanation and that it was arcing on the metal clip which is chassis ground. I guess, sort of tracing the whole board out that the increased load drew too much for the resistor on the ac side.
                                        • sjw
                                          Computime CANh011 Kitchen Oven controller burnt resistor what value?
                                          by sjw
                                          Hello. I'm having a go at repairing my neighbours electrolux oven. This controller board mounts a tier display and has 3 button inputs. I have been given only the board.
                                          There is a large 2Watts? Resistor that is on a power bus that goes to what i'm assuming is heating element and to a power supply that gives the board microprocessor power.
                                          I don't know the value of the resistor its too burned.
                                          Ideally I would like schematics or the probable value if people are familiar with repairing such devices.
                                          Failing that any advice on this from what i...
                                          09-14-2022, 03:30 AM
                                        • CG2
                                          LED uplighter dimmer burnt resistor
                                          by CG2
                                          I've got a 240v LED uplighter which isn't working. Pulling it apart shows a clearly burnt resistor on the circuit board, and I'm hoping some of you will have suggestions on what to replace it with. First, here are some photos. Power comes in, through the fuse and choke, then through the big blue variable resistor labelled B500K (ignore the similar blue component at the bottom - it's a simple switch for an attached reading lamp). It then passes through the burnt resistor (or at least did once), through diac DB1 and the unburned 30 ohm resistor to the gate of the triac.Now I assume there's a simple...
                                          02-14-2024, 09:23 AM
                                        • trickartt
                                          Allen & Heath Xone:02 (DJ Mixer) - Burnt out Resistor
                                          by trickartt
                                          Hello Badcaps!
                                          I am trying to troubleshoot my Allen & Heath Xone:02 DJ mixer. I have had this for somewhere close to 20 years and have played music through it in one form or another pretty much every single day since I've had it, though these days it's usually from a wireless streaming receptacle (Apple Airport) more than the turntables that are also connected to it.
                                          This week my music stopped working, and after a bit of a wild goose chase, I realised my mixer was dead. I checked the 500mA fuse in the device beside the power supply and found it was blown, so I replaced...
                                          05-04-2024, 12:07 PM
                                        • sparcktikus
                                          Ersa Rds 80 soldering station burnt resistor
                                          by sparcktikus
                                          Hi
                                          I have an Ersa rds 80 soldering station which has developed a fault and just showing err on display
                                          I have found a burnt resistor on pcb can anyone help me identify this resistor if you have a circuit diagram or similar unit
                                          The printed circuit board markings are rd80 ver 2.0 and the resistor in question is R6
                                          Many thanks...
                                          04-04-2023, 04:29 AM
                                        • DennisH
                                          Need Help Identifying This DIODE mounted on a Frigidaire oven control PN:316131600
                                          by DennisH
                                          This diode is mounted on a Frigidaire electronic oven control PN:316131600. This diode runs hot enough that the PCB is showing slight burn marks (black soot looking area on PCB above the diode). It looks to me to be coming from the body of the diode.
                                          The oven control is 22 years old and still works, but I can't get a new replacement, so I'm doing preventative maintenance and replacing a few parts on it that I think could fail - and this is one of them.
                                          Can any of you identify this diode (see pic) and suggest a replacement that can handle more heat - or if not, can...
                                          10-18-2022, 07:24 PM
