Gateway FPD1530 works for a second then dark
+ More Options
Posts
  • freakytiki4u
    Coolest Member
    • Aug 2009
    • 130
    I have a Gateway FPD1530 Flat Panel LCD Monitor. When turned on it lights up and you can see the picture perfectly for about 1 second then the screen go's dark. Flashlight test reveals the picture is still there, its just dark. Power light stays solid green. Pictures of the Logic Board are attached. I cant see any bad caps or dry solder joints. Any ideas will be greatly appreciated.
  • freakytiki4u
    Coolest Member
    • Aug 2009
    • 130
    Re: Gateway FPD1530 works for a second then dark
    Also, does anyone know of a device to test Capacitors in circuit?
    • PlainBill
      • Feb 2009
      • 7034
      This is a classic description of the 'two seconds to black' symptom. I've marked up the top picture. Try measuring the AC voltage from point A to Gnd and from point B to Gnd while the backlights are on. Also check the inverter transformers for bad solder joints.
      By the way, this is a picture of the inverter / power supply, not the Logic Board. (Pictures of the right board, you just gave it the wrong name.)
      PlainBill
      • freakytiki4u
        Coolest Member
        • Aug 2009
        • 130
        A gets near 10 volts AC for a split second and B gets near 6 volts AC for a split second. I have to turn the monitor on and off to make that happen while holding meter leads to proper spots. I will resolder transformer joints just to be sure. Next Sir ?
        • freakytiki4u
          Coolest Member
          • Aug 2009
          • 130
          Resoldered joints on both small transformers, still does the same thing. Would bad caps cause this? They dont appear to be bad (not swollen).
          • PlainBill
            • Feb 2009
            • 7034
            No, it's unlikely bad caps would cause this. You are measuring the voltage on the return line, which is proportional to the current. If you tried several times to read the voltage and got consistent results, the only conclusion I can come to is one CCFL is carrying more current than the other.
            NOW, we have to figure out why. If you look at the top of the board near each of the connectors for the CCFLs you will see the transformers. If you look at the underside you will see the transformer pins are numbered 1-6 (primary side) and 7 & 8 on the secondary side. With power off, measure the resistance of each secondary.
            PlainBill
            • freakytiki4u
              Coolest Member
              • Aug 2009
              • 130
              How do I measure resistance? (I know, Im a doofus) I have a multimeter.
              • PlainBill
                • Feb 2009
                • 7034
                (Well, as long as you know.) Disconnect the power supply / inverter board from the rest of the monitor turn it face down in the same position as the picture. Set the DMM to the 2K ohms range. In the lower left corner of the board you will see two points labeled 7 and 8, with the 8 above the 7. Put one probe on the pin labeled 7 and the other on the pin labeled 8. Write down the reading. Now look at the lower right corner of the board. You will see two more pins, but this time the 8 is to the left of the 7. Measure the resistance between the two points.
                PlainBill
                • freakytiki4u
                  Coolest Member
                  • Aug 2009
                  • 130
                  lol, my wife is usually first to admit Im a doofus and I runa close second.
                  ok, my MM only has 1K Ohm and 10 Ohm Setting so I used !k Ohm Setting.
                  I will post 4 pictures.
                  The 1st one shows my MM at rest.
                  The 2nd one show my MM with leads touching so you can see what it reads.
                  The 3rd shows the secondaries reading closest to the power plug.
                  The 4th shows the secondaries reading farthest away from the power plug.
                  I await your directions and Im sorry to be such a pain.
                  • PlainBill
                    • Feb 2009
                    • 7034
                    Try it again on the X10ohm scale. That should give you a reading closer to mid scale. We are looking at what might be very small differences in resistance.
                    PlainBill
                    • freakytiki4u
                      Coolest Member
                      • Aug 2009
                      • 130
                      ok on the 10 Ohm scale I get a consistent reading on both secondaries of 60 ohms resistance. See attached Pic of reading
                      • PlainBill
                        • Feb 2009
                        • 7034
                        By any chance is there enough slack in the wires so you can repeat the original test, but swapping wires to the opposite connectors?
                        PlainBill
                        • freakytiki4u
                          Coolest Member
                          • Aug 2009
                          • 130
                          Do you mean test the secondaries by swapping the meter leads around? If so, Yes, and reversing the wires gives the same 60 Ohm result on each secondary.
                          • PlainBill
                            • Feb 2009
                            • 7034
                            No, let me explain what I meant. Review posts 3 and 4. In those steps you measured the return voltages and discovered there was a difference between the two sides. The latest test indicates there is no difference between the secondaries of the two transformers. That presents a problem - ordinarily the next step would be to measure the output voltage of each transformer. However, that could easily fry your VOM (been there, done that with 5000 volts, didn't get a tee shirt, and don't want to see it done again). And we still have a problem. Is the 'B' return current lower because the 'B' transformer is not putting out high enough of a voltage, or because there is a problem with the 'B' CCFL or it's wiring OR because the 'A' CCFL is drawing too much current?
                            The test I am proposing is to plug the 'A' CCFL into the 'B' socket, and the 'B' CCFL into the 'A' socket. If the return voltage at the 'A' socket is still higher, that tells us the problem lies in the inverter. If the 'B' voltage is now higher, that tells us the problem lies in the CCFLs and associated wiring.
                            PlainBill
                            • elbtax
                              • Apr 2008
                              • 59
                              Just repaire an Viewsonic Optiquest Q7 displaying same problem. Removed the inverter and none of the six caps were bulging. Checked all problems PlainBill suggested above and transistors. All good. The caps were Elite so they were suspect right away. Replaced 2, 220uf-25v with Nichicon same values RZ(M) series. Replaced 2, 680uf-16v with Nichicon 1000uf, 16v.(All i had) PB(M) series. Left the high voltage cap alone and a small 50v cap.
                              Put back together and has been burning in with a beatiful screen since 3pm EST. So, just cause caps aren't bulging does not mean they are not bad. Hope this helps...
                              • mcfischer
                                • Dec 2008
                                • 12
                                I fixed many of these by replacing the 2 1Uf caps at the top edge of the board (between the bulb sockets)
                                Mike
                                • PlainBill
                                  • Feb 2009
                                  • 7034
                                  Mike
                                  Are you referring to the two electrolytic caps?
                                  For what it's worth, I'm trying to put together a systematic approach to the 'Two Seconds to black' problem. That is one cause I hadn't encountered yet.
                                  PlainBill
                                  • mcfischer
                                    • Dec 2008
                                    • 12
                                    Bill,
                                    Yes the two electrolytics. I replace them with 2.2 uF just to feel better. Been doing this stuff a long time and I think it may help in the long run.
                                    I have fixed more than 50 this past 2 years, same caps....
                                    Mike
                                    • rokkaholik
                                      • Jul 2010
                                      • 21
                                      I also have this same monitor with the same problem. Which caps on which are you referring to mcfischer? Possible pics?
                                      • PlainBill
                                        • Feb 2009
                                        • 7034
                                        How about this? You're the one with the monitor, you provide the picture of the inverter. If mcfischer isn't around to answer you, I'm pretty sure I can supply the identification.
                                        PlainBill
                                        • Rozp
                                          70LE660U dark cloud or black screen with sound.
                                          by Rozp
                                          Hello Everyone,
                                          This is my first post so I will try to be as precise as possible without making this post too long winded. Unfortunately I don't have pictures of the original problem but I included images of the TV internals.
                                          I have a Sharp 70LE660U. The problem started a few months ago with the bottom row looking out of sync and was dark on the left side and then fading to transparent on the right side. Shortly after, a dark cloud appeared in the center of the screen. The dark cloud started small and shaded but the image was visible. It also affected the menu area....
                                          08-29-2023, 05:25 PM
                                        • CapLeaker
                                          Dell ATX PSU won’t start, but forcing it works fine?
                                          by CapLeaker
                                          Got a case of something new weird at work. There is an old 2nd gen Intel i3 in an old “Pizza box” shell that has a small form factor power supply. Unfortunately I forgot to take pictures and model number off it.
                                          Anyway, I get to work and get to look at this computer. Standby LED on the PSU is on, but the computer won't start. Hmm o.k. take the battery out of the main board try again, nothing. O.k. then… unplug the power supply from the main board and put in a full size ATX PSU (yeeeesss! Exact that blown Powerman IP that I fixed a while back), plug it in and the old...
                                          10-28-2024, 06:59 PM
                                        • rounin
                                          MacBook Air A2337 (820-02016) USB-C Port Issue – Only Works in One Orientation (CC Line Problem?)
                                          by rounin
                                          🛠 Original Issue
                                          ⚠️ New Problem: One USB-C Port Only Works in One Orientation...
                                          04-19-2025, 01:18 AM
                                        • ex250
                                          Kenwood SW-505D no sound issue and pops from time to time when it works
                                          by ex250
                                          Hello mates,
                                          I bought this subwoofer a few days ago used and blind and it works erratically, as far as I could see, it has been tampered with, the speaker is not the original one and of 8 Ohm when it should be of 4, and there are some welds like reworked by the boards.
                                          It doesn't have much power (expected more from it) and it distorts if you increase the volume over the middle, maybe it's because of the high impedance of the speaker. The problem is that it has sound when it wants, the led panels all work correctly, you can hear the power relay on power on, but right now...
                                          12-29-2024, 03:27 PM
                                        • eurowill
                                          a2141 820-01700 internal display not working / external works
                                          by eurowill
                                          Hey ya'll this is my first post on here. I recently aquired a used/broken 2019 mbp 16 a2141 with the 820-01700 board. Seller told me that the laptop needed a new lcd. However upon doing some troubleshooting i found out the lcd is fine.
                                          Laptop boots like a normal, plays chime, touchbar lights up however there is no image on the internal lcd. If i connect and external monitor while its already on, nothing happens and no image is displayed on external. However if i restart or boot the machine while its plugged in, the external then works and a backlight is now visible on the laptop....
                                          07-23-2024, 10:06 AM
