resistor values for 2n2222a w/ SSR
  • evilkitty
    • Nov 2017
    • 299
    So if I take a 2N2222A transistor and a G3MB-202P relay and 3.3v logic controller
    What resistor value should I be using for the base? Normally i would just take a ~1k resistor and go, but i need to work every time and not fail
    The problem I am trying to solve: my dad hates 3 way switches (he is not even the one wiring them) and insist on the only way to get through a room at night is to turn the light on, go to the other side of the room and turn that light on, go back and turn the 1st light off, then go back again and turn that light off, screw that I'll make a software light switch that uses door sensors (more reliable than a motion sensor working)
    second question if i use the same logic wire can i make a double throw SSR switch by using 2 of these one on a 2N2222A and a P2N2222A or would i have issues with overlap there both are on/off at the same time (not sure if that is even a issue for my thermostat)
    • 31159
    Re: resistor values for 2n2222a w/ SSR
    most ssr's use an optocoupler and can run down to 3v
    to answer the question, you need to find out how much current the ssr needs, then look at the 2n2222 hfe and then you can calculate the current.
    ir just experiment starting with 10k
      • 31159
      a PIR sensor on the ceiling works well btw, i have done it on a staircase once
      • evilkitty
        • Nov 2017
        • 299
        The relay pulls 7.5mA when wired to my usb port, so what resistor range/value be?
        i know there is a formula, but i am not sure what values to use
        note that my final circuit will be using 5.2-5.35v, however there will be around 25-30 ft of telephone wire to the relay
        as for the second part of the question, it seems i have 2N3906 for PNP, would (would have issue with a double on for state for a moment?) this work see attachment
        maybe i need a schottky diode on the PNP base?
        again not sure what resistor value to use
        • eccerr0r
          Solder Sloth
          • Nov 2012
          • 8701
          It looks you're just using common ground level shifting you need NPN transistors and the PNP probably is not useful here if you can't get the shifted voltage elsewhere.
          Since the relay is only 7.5mA (and will be even less current with the 30ft wire plus transistor saturation voltage) you don't need to current limit collector, and you don't need much base current to keep the driving transistor on. A 1K base resistor should be sufficient for even weak 2n2222a's and you can do 470Ω if you want to pound the transistor even more.
          • redwire
            • 3912
            The Omron G3MB-202P DC5 relay is an SSR, which is basically an LED and 440Ω resistor inside (for the 5V model) and roughly around 10mA load.
            With a lazy 2N2222 beta of 75, base-drive 2.6kΩ or lower would be plenty, and 1kΩ is fine. The RP2040 GPI/O's output 3.3V and typ. 4mA but note their are settings gpio_set_drive_strength can also move it from 2,4,8,12mA in software.
            You need an NPN to keep the higher SSR voltage away from the RP2040.
            • evilkitty
              • Nov 2017
              • 299
              Thanks, now i know what resistor to use for my DIY smart light socket
              Now as for that dual relay setup, i want to emulate the logic of my mechanical relay (SPDT)
              PNP and NPN transistors have opposite switching characteristics
              i have access to my data pin, 3.3v, 5v, and ground and very little pcb space
              • eccerr0r
                Solder Sloth
                • Nov 2012
                • 8701
                Use another npn transistor as an inverter... or use another gpio pin and do the same except write it with the opposite phase...
                • eccerr0r
                  Solder Sloth
                  • Nov 2012
                  • 8701
                  BTW thought PN2222A TO92 pinout was E-B-C when looking at the flat face with pins pointing down... that picture was really bothering me beyond just the lack of details...
                  • evilkitty
                    • Nov 2017
                    • 299
                    just used a random npn transistor i found on google images
                    i already modded my ethernet cable to have 9 conductors, getting a 10th is not happening
                    • harp
                      • Jun 2022
                      • 616
                      • Planet Earth
                      I am not shure that your problem is clear to me, but maybe you can consider a implementation of some logic gates, that if two switches in opposite side of room is in same state there is no light, else it is. In this case, wire can be a small diameter and easely 'glued' on wall with (in) wall paint.
                      • redwire
                        • 3912
                        I'm not sure what you are trying to make - "... can i make a double throw SSR switch..." I take to mean DPST? This is like connecting the two SSR inputs in parallel, so the one 2N2222 powers both at the same time.
                        If you want a SPDT switch then you need another transistor.
                        You want to make one end of a 3-way light switch?
                          • 31159
                          why not use cordless switches??
                          • evilkitty
                            • Nov 2017
                            • 299
                            did not know that was a thing... well i have the relay installed and wired at this point and i can make the smartest auto light you have ever seen on my pico now (photocell, door sesnors/switch input as well as buttons at each door)
                            i want to make a SPDT out of 2 SSR relays for my thermostat that has had a few of those mechanical cheap blue relays die (so when the next one fails i can permanently fix it)
                            all i needed to know for the light switch problem was the base resistor value (Thanks redwire)
                            the issue was my dad hates 3 ways and so he does not want them installed (i think they confuse him somehow), well since i am installing a pico in this room i figured i would make a smart light so i can have a light to use to get though the room without relying on any switches, he had to use these super old T12 8 ft fixtures (from ~1995 new in box he never got around to installing), i checked the power draw with my clamp meter... 540 watts for 2 fixtures, he plans to have four and another four 4ft fixtures and there are another 4 light bulb sockets fixtures on this circuit, good thing we replaced that piece of 14awg on the 20 amp circuit from the panel (everything else was 12awg)
                              • 31159
                              https://www.youtube.com/watch?v=abJCIgRKQk0
                              https://www.youtube.com/watch?v=9Pw7U0XFgUM
                              • evilkitty
                                • Nov 2017
                                • 299
                                This should work in theory, still not sure about about the resistor values, but there are some issues
                                • debug led has 1.95 fV, maybe i should just put 1 led in the 3.3v logic (or the 5v logic), with a mechanical relay i could just put it in parallel with the relay, but with a SSR i would only expect the device with a lowest forward voltage to turn on
                                • not sure about resistor values
                                • when logic goes high i think both relays will be on for a ~250ns
                                  • off-off is fine
                                  • on-on could be a issue, not sure if my HVAC cares but it could (even if it does i doubt that is long enough to be a issue, but idk)
                                2n2222A has a turn on time of 35ns and a turn off time of 300ns
                                • redwire
                                  • 3912
                                  That would work, I tried to do it with two transistors but it would be finicky so I did not post the idea.
                                  The debug LED's lose too much voltage though, so the SSR does not get enough voltage. You have 5V subtract the debug LED let's say 2.2V and 0.1V for the transistor on, and that leaves 2.7V but the SSR minimum is 4V. So you would move the debug LED to be in parallel with the SSR drive (adding a resistor for the LED like 1k).
                                  The intermediate transistor can use high resistor value say 10k on the base, and no need for the second R2 at the base. R2 to 5V still around 2.2k
                                    • Jul 2011
                                    • 6058
                                    Bump
                                      • Jul 2011
                                      • 6058
                                      I would suggest the following
                                      What is the voltage to the blue relays I am guessing that they are 5 volts if they are you can use a 4N25 with a drop down resistor for each relay coil power and then use the 24 volts from the transformer of the air conditioner or use much better relays or a SSR on separate board in an enclosure
                                      Do not be tempted to use the power of the thermostat electronic output directly to power your up graded relays or SSRs this not good idea because these thermostat boards are very easily damaged by voltage spikes and static electricity and some of these thermostat are not cheap sometimes over $100.00 depending on the features that it has
                                      One note if you go this route please make sure that the thermostat still function correctly before attempting to do this upgrade
                                      I had a customer that had one of these electronic thermostat that had a relay issue but also had an issue with the outside temperature sensor not reporting so they want to replace the thermostat so I got them a replacement thermostat but unfortunately it would not operate the defrost function correctly because this one of those air conditioning units that has to use a special thermostat
                                      But a few months later the compressor would not turn on now the real issue was that the thermostat wires were so full corrosion that wires were coming apart after running new thermostat wires I was able to get back the outside temperature sensor function and the heating issue and the cooling issue with there original thermostat that I thought was the issue because I know about the relay issue that these thermostat have
                                      • evilkitty
                                        • Nov 2017
                                        • 299
                                        just 5v songle relays i got for ~0.25 each
                                        Are you talking about the board in the HVAC unit? if you are talking about inside my thermostat, i have VERY dumb (actually quite a clever design) but it was designed to not need any electronics
                                        my dad was complained saying the tubes were 'sticking' guessing there is some metal fatigue going on and it is not as accurate as it used to be, i was looking at how i was gonna solve this and asked my self why am i trying to replace all of this, the only issue is the tubes, one is a double throw switch and the other is a single throw switch and a pair of mechanical relays would do the exact same thing, then i decided to log the temp and the tube states so i can log there behavior and se how much variance they have
                                        my dad had gotten a new thermostat and returned it cause it did not seem to properly support aux heat, our unit has 2 heat levels, low and high, with my current design i have had issues cause of the contact wearing out in the relay
                                        wait i can put it in parallel and it work? i forgot i am not trying to use a common resistor, though in the interest of saving board space how about this? [attached]
                                        i should not really need 2 LEDs assuming my 5v wire is working and if i cared about that i would have a power led on the board (clearly i do not have this, but if i did there is no need to make that function part of the relay circuit)
                                        ** added my single throw relay to the image (also have a input pin from the tubes, a DS18B20, and a LED)
                                        the top double throw does heat/cool and the bottom does more heat
                                        BTW i have those snubber caps on by board (for the mechanical relay), should i remove them? when i do this modification, would it hurt anything? would it help anything?
                                        • Kobok
                                          Different (lower) resistor values on PCB?
                                          by Kobok
                                          Dear Alls,
                                          For sure it id a stupid question, but help me to understand. I am in a Dell 2007WFP revitalizing project - searching reason why not starting. Some resistors needed to replaced is is obvious. When I have soldered some resistors the measured (with multimeter) values were sometimes rather different written on them. I supposed these are wrong units so I desoldered and made a checking measurement and voilá the values is the same is written on. This happens only in case of a few resistors, most have the same values (+/- 10%) are written on it. "strange" SMD resistors =>103...
                                          09-19-2022, 07:30 AM
                                        • jinu_j
                                          by jinu_j
                                          Hi
                                          05-03-2025, 10:51 PM
                                        • madushanka 1234
                                          need to find RESISTOR values of mising LA-E831P
                                          by madushanka 1234
                                          need to find mising parts LA-E831P
                                          need to find values of this marked resistors...
                                          another shop mixed this marked 5 resistors...
                                          please check 3rd photo
                                          (rt3661b section/puz1)
                                          thank you
                                          02-17-2025, 07:26 AM
                                        • chronic519
                                          HP EliteBook 845 G8 (need resistor values by EC chip please)
                                          by chronic519
                                          Hello, I have an EliteBook 845 G8 motherboard sitting here. Customer knocked of 2 resistors by the EC chip. I cannot find schematics, board view or anything related to ID these 2 resistors.
                                          If someone has this board, could you please tell me the values of these 2 resistors?
                                          I hate to see this board be unusable due to something so minor....
                                          Thanks...
                                          02-14-2025, 10:36 AM
                                        • Crystaleyes
                                          Calculating resistor values in parallel with Caps
                                          by Crystaleyes
                                          Hi all.
                                          I recently picked up a dead car amplifier from the flea market, with the intention of learning some more in the area of audio repair.
                                          It has a stereo output with an added mono woofer output. The stereo channels are on one board, whilst the woofer section is on a separate board. There are also three large (ish) transformers.
                                          Apart from the fact that it was seriously dirty inside, it seems to be essentially complete with the only clearly damaged component being a toasted 1/4 watt resistor on the woofer board and it is this which I am wondering...
                                          05-21-2023, 07:35 PM
