    Isolation Transformers

    Looking to start servicing power tools. I’m looking for isolation transformers for 415/230/110V either separately or combined/tapped, above 5KVA. I’m based in the UK. Any suggestions on where I can source?
  • stj
    Great Sage 齊天大聖
    • Dec 2009
    • 30956
    • Albion

    #2
    415 is 3 phase 240v
    240 is negative bonded to ground,
    110v is usually center tapped 55-0-55 to ground.
    so know what your actually working with.
    for 110 just get a yellow site transformer,
    240 i wouldnt bother frankly - it will kill you through a transformer anyway - just use an RCD.
    a transformer if you did get one would defeat an RCD anyway.

    do you have 3phase?
    last person i heard of having it installed got charged over £7000 for the install.
    better to use an invertor from 240

    Comment

    • OddJohnny
      New Member
      • Feb 2024
      • 4
      • United Kingdom

      #3
      Thanks for the reply.
      I'm currently in the planning phase for a new business. Much of the work I'll be doing is for local government & they require ISO. H&S has to be independently verified to obtain ISO. Most of the work will be PAT failures. Trying to avoid RCDs as I've found live testing can cause tripping. Risk assessment will allow non-RCD outlets provided use of isolation transformer(s) & PPE. I do have 3ph at the unit but 1ph currently supplied. Obviously, I'd like to spend as little as possible, but it wouldn't be worth more than £2k to me. Manufacturers direct are more than double that.

      Step up transformer I hadn't really considered tbh.

      If there are recommendations for makes/models & sources of reliable transformers, I'd be most grateful.

      Many thanks.

      Comment

      • stj
        Great Sage 齊天大聖
        • Dec 2009
        • 30956
        • Albion

        #4
        government agencies are stupid.
        isolation transformers wont limit the current in any way that will prevent death or a big bang and fire.
        if your dealing with PAT stuff then 99% of it will be bad cables - the rest will be psu damage related to wrecked metal-oxide varisters because the stupid fucks dont know you arent supposed to pat-test electronic supplies or devices fitted with them.
        you also arent supposed to pat anything with removable cables or any fixed equipment.
        PAT = PORTABLE appliantce test.

        no legal requirments for it even.
        it's a big fucking scam and a lot of "test" companies get big money damaging stuff so they can put a little green sticker on it.
        better read this (government) link,
        and never test equipment with more that it's rated voltage - if you insulation-test at 500 or 1000v you do slow damage to the surge suppressors inside
        https://www.hse.gov.uk/electricity/f...ce-testing.htm

        use an RCD for final test - they dont "false trip"
        if they trip the device has a ground fault

        Comment

        • petehall347
          Badcaps Legend
          • Jan 2015
          • 4425
          • United Kingdom

          #5
          pat testers should not trip the power line unless its faulty in itself . think mine is fitted with an isolation transformer .

          Comment

          • stj
            Great Sage 齊天大聖
            • Dec 2009
            • 30956
            • Albion

            #6
            i dont understand how you trip an rcd pat testing,
            the pat test device is battery powered - the device under test is not connected to power.
            unless we are dealing with a total noob doing ground current tests to a device while it's wired-in.
            i would throw such a person through the window and tell them if they come back it will be from the roof next-time.
            a stupid act like that can cause a plasma-arc explosion.

            all this miss-placed electrical testing is a joke anyway from a government that removes safety requirements for food and pharmacuitical products!
            and the people doing these tests dont need any electrical knowlege or skills - just a £300+ tester and a roll of stickers!

            Comment

            • petehall347
              Badcaps Legend
              • Jan 2015
              • 4425
              • United Kingdom

              #7
              Originally posted by stj
              i dont understand how you trip an rcd pat testing,
              the pat test device is battery powered - the device under test is not connected to power.
              unless we are dealing with a total noob doing ground current tests to a device while it's wired-in.
              i would throw such a person through the window and tell them if they come back it will be from the roof next-time.
              a stupid act like that can cause a plasma-arc explosion.

              all this miss-placed electrical testing is a joke anyway from a government that removes safety requirements for food and pharmacuitical products!
              and the people doing these tests dont need any electrical knowlege or skills - just a £300+ tester and a roll of stickers!
              my pat tester is mains powered .. Clare A255 .. cant see how a load test can be done otherwise .
              https://flameport.com/documentation/...Clare_A255.pdf

              Comment

              • sam_sam_sam
                Badcaps Legend
                • Jul 2011
                • 6030
                • USA

                #8
                Very interesting article about safety testing

                Comment

                • stj
                  Great Sage 齊天大聖
                  • Dec 2009
                  • 30956
                  • Albion

                  #9
                  flameport? john ward?
                  that guy has a youtube channel, he thinks the electrical regulations (that constantly change and are partial bs these days) should be treated like the bible!

                  Comment

                  • OddJohnny
                    New Member
                    • Feb 2024
                    • 4
                    • United Kingdom

                    #10
                    PAT is a requirement under Electricity at Work Regulations, although this is an implied requirement rather than specified. If you have employees that get killed/seriously injured by faulty equipment & you don’t have all the necessary H&S in place, you’re going to jail. Employees need to be trained on a piece of equipment before they can use it. This involves checking the equipment for faults prior & post use, reporting systems for faults/suspected faults, regular maintenance & checks by a qualified person. It’s only criminal not to have done it if there’s an accident involving faulty equipment. Lots of insurance companies require PAT as part of their policies. Government & agencies are sticklers for it, many requiring that a valid PAT be produced before use of the equipment is permitted on their sites with many larger businesses following suit.

                    It’s a huge industry with potential to expand &, although around 95% of failures can be found visually inspecting equipment, each failure also brings additional business in the way of fixing &/or procurement.

                    PAT is undertaken on site by us, but the failures are removed back to our workshop for analysis & reporting back to our clients. Testing & repairs in our workshop sometimes require the appliance be live &, given the items are faulty, likely to trip MCBs/RCDs, etc.. Live & under a thermal camera is the quickest way I’ve found to identify shorts. The independent H&S consultants we use will allow faulty equipment to be made live, but only if it’s via an isolation transformer, with PPE & under strict conditions. We have to be in compliance with the H&S to achieve ISO status needed to maintain the contract.

                    For the amount of work that failure repairs produces at the moment, it’s not worth spending £5k+ on a custom transformer station.

                    As for experience, I’ve almost 20 years experience in electrical & PAT, qualified as an electrician to C&G Design & Verification. Person’s undertaking PAT are required to be suitably qualified &, although a monkey with some stickers could do a test, if the equipment were faulty & someone was injured, there’d be a lot of uncomfortable questions to answer that would almost certainly end with a minimum of a fine & possible criminal conviction.

                    Dismissing PAT… it’s highly profitable with little in the way of overheads. The work is easy & clients are professional. Businesses not doing it are liable to damages & in worst case scenarios, their CEOs end up in prison &/or with a criminal record. Having regular checks done on equipment also saves injuries & lives. You’d be surprised how many people would use faulty equipment just to get a job done, regardless of whether it would injure or kill them. People’s knowledge of the equipment they use is also often lacking &, supplying training for use of equipment is also another opportunity to provide a service that benefits.

                    Comment

                    • sam_sam_sam
                      Badcaps Legend
                      • Jul 2011
                      • 6030
                      • USA

                      #11
                      Originally posted by OddJohnny
                      PAT is a requirement under Electricity at Work Regulations, although this is an implied requirement rather than specified. If you have employees that get killed/seriously injured by faulty equipment & you don't have all the necessary H&S in place, you're going to jail. Employees need to be trained on a piece of equipment before they can use it. This involves checking the equipment for faults prior & post use, reporting systems for faults/suspected faults, regular maintenance & checks by a qualified person. It's only criminal not to have done it if there's an accident involving faulty equipment. Lots of insurance companies require PAT as part of their policies. Government & agencies are sticklers for it, many requiring that a valid PAT be produced before use of the equipment is permitted on their sites with many larger businesses following suit.

                      It's a huge industry with potential to expand &, although around 95% of failures can be found visually inspecting equipment, each failure also brings additional business in the way of fixing &/or procurement.

                      PAT is undertaken on site by us, but the failures are removed back to our workshop for analysis & reporting back to our clients. Testing & repairs in our workshop sometimes require the appliance be live &, given the items are faulty, likely to trip MCBs/RCDs, etc.. Live & under a thermal camera is the quickest way I've found to identify shorts. The independent H&S consultants we use will allow faulty equipment to be made live, but only if it's via an isolation transformer, with PPE & under strict conditions. We have to be in compliance with the H&S to achieve ISO status needed to maintain the contract.

                      For the amount of work that failure repairs produces at the moment, it's not worth spending £5k+ on a custom transformer station.

                      As for experience, I've almost 20 years experience in electrical & PAT, qualified as an electrician to C&G Design & Verification. Person's undertaking PAT are required to be suitably qualified &, although a monkey with some stickers could do a test, if the equipment were faulty & someone was injured, there'd be a lot of uncomfortable questions to answer that would almost certainly end with a minimum of a fine & possible criminal conviction.

                      Dismissing PAT… it's highly profitable with little in the way of overheads. The work is easy & clients are professional. Businesses not doing it are liable to damages & in worst case scenarios, their CEOs end up in prison &/or with a criminal record. Having regular checks done on equipment also saves injuries & lives. You'd be surprised how many people would use faulty equipment just to get a job done, regardless of whether it would injure or kill them. People's knowledge of the equipment they use is also often lacking &, supplying training for use of equipment is also another opportunity to provide a service that benefits.
                      How often do eco get prosecuted for there negligence of the standards that you have outlined above because in this country they have standards but rarely enforce and when is enforced they are just doing to set an example to detour someone else from doing the same thing
                      Last edited by sam_sam_sam; 02-23-2024, 06:12 AM.

                      Comment

                      Related Topics

                      Collapse

                      • t4796
                        Fender Mustang non valve guitar amp - owner connected 110v amp to 220v.
                        by t4796
                        Hi all,

                        I recently picked up this amp as not working. I took it as is. Didn't notice until I got home it had foreign power plug and was marked 110v and our local voltage is 220v so then I knew what had happened to it.

                        Opened it up and was able to find the schematic online. In the schematic I have uploaded I have erased the parts for 220v operation to make it easier for me to visualise however I have since added the two additional diodes and remove the wire link from the power supply so I can test it easier on 220v

                        From the FAQ I learnt that for 110v the power...
                        10-25-2024, 06:59 PM
                      • maleksa
                        Yamaha SY85 power board 220v or 110v?
                        by maleksa
                        I need help to ascertain if the power supply on my Yamaha SY85 keyboard is 110v or 220v or both.

                        I have attached the schematics below....
                        07-01-2023, 08:49 PM
                      • angelos
                        Variac Transformers and switch mode power supplies.
                        by angelos
                        Hello everyone,

                        I was wondering if anyone in the forum can tell me how they use the variac transformer to check a switch mode power supply that they had just repaired.
                        I wanted to know how they adjust the votlage, do they start from zero and turn it up slowly or rather switch on that about 60V ac ( My country we use 220V ac) and hope for the best.
                        Also what sounds the PSU should make, what sounds wrong etc. Also if i have a scope what can i check for.
                        The reason why i am asking is i have a Sony LED TV PSU whose PFC circuit shorted out and upon closer inspection a...
                        11-27-2024, 03:16 AM
                      • harp
                        isolation transformer from two 240/12, wiring?
                        by harp
                        When is talk about making isolation transformer on poor-man way, always I see schematic 240/12-12/240.
                        So, I wonder, is this wiring from my attachment it work, bringing some good feature or it is bad idea and why?...
                        11-25-2022, 05:11 PM
                      • Amraks
                        Roland vg-8
                        by Amraks
                        Anyone got any idea what voltages these transformers run this was 117v transformer plugged into Australian mains power.

                        2 red wires are center tapped.

                        I'm just trying to get a understanding of the specs I should go before getting a custom r-core built via China.

                        I don't really trust what is written on the transformer to what I see in the vg-88 schematic which uses the same part number.

                        The voltages here seem a bit low in comparison to what people have measured else where.

                        Filter caps are 16v
                        And 2 other filter caps are 25v...