Re: Transformer substitution - Sanyo DP42849-01
That would probably be a good idea. I hadn't thought of that. There isn't a whole lot of extra room on the bobbins though. Maybe I could go up a half gauge. Not much more though.
Transformer substitution - Sanyo DP42849-01
Collapse
X
-
Re: Transformer substitution - Sanyo DP42849-01
wouldnt it be better to oversize a little - given that the original design dies a lot?
your difference there is hardly small - 10% diameter, but the actual area is probably closer to 20Last edited by stj; 08-20-2014, 03:54 PM.Leave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
The wire I used is .0005 smaller than the original. 0.0045 instead of 0.005. 35awg triple insulated. It was supposed to be 0.005. I should have sent it back when it was smaller than it should have been. I didn't think it would make this much difference though.Last edited by lookimback; 08-20-2014, 03:50 PM.Leave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
was the heat on the primary side, or secondary?Leave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
OK, laser temp probe arrived today.
Good board with stock transformer, after about an hour, secondaries were about 163°.
Board with rebuilt transformer, 190-199°.
And those are open air readings. I suppose they would be hotter if enclosed in the TV. Definitely not safe. These will not be sold. I have one more awaiting rebuild and I'm going to try a larger gauge wire. If that makes a difference, I will attempt to disassemble the ones I rebuilt already. To my advantage, I know what epoxy I used and have some left. So, I'll make some samples and see what solvents will work best to break it down. At least I'm learning from doing this.Leave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
Turn count is definitely correct. I was meticulous with that. I get what you are saying about inductance. So if the core is saturating, that would mean the inductor never reaches it's resonant frequency. Correct? Would the impedance of the inductor affect it's resonant frequency and result in saturation? There's certainly more to this than rewinding the transformer. I'll put some more time into this tomorrow. Thanks again too.Leave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
It could be the inductance, the DCR, and the turn count, or the core is being saturated so the inductance will drop and cause more current draw. When they design the circuits, they take lots of values into account.
http://www.edaboard.com/thread199057.htmlLeave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
Could the wire gauge be the cause? Resistance is 12 ohms higher (6 per side) than the average working transformers.
Here's the readings.
Board with original transformer: 0.038vdc
Board with rebuilt transformer: 0.041vdcLeave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
You have to measure across the resistor, not ref to the circuit ground (the negative leg of the cap). You will put one probe on each end of the R322 which is very low Ohm resistor to measure the Voltage drop on the resistor, then you can calculate the current draw, but since you already made the current measurement then you already know the re-built Xformer is drawing more current (16% higher) than the original, just have to figure out why.Last edited by budm; 08-15-2014, 09:42 PM.Leave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
I finally came up with another working board with a stock transformer. That board draws 1.45 amps and both with rebuilt transformers draw 1.68 amps. It's also the same if I put them on different boards, as I have a few spares without transformers. I ordered a laser temperature probe. When it arrives, I'll see what the actual temp differential is. I have a feeling I am going to have to up the gauge on the magnet wire. Also, I got the exact same voltage on both sides of resistor R322. Maybe I didn't do it right. I measured from the negative pin of the main filter cap C821.
Got the digital proximity sensor counter installed and working in my winding jig too. Pic attached.Leave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
OK, I will take the readings tomorrow and post back with the results and calculations.Leave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
It looks like you will be measuring the DC Voltage across fusible resistor R322 which is fed by the B+ from the positive pin of the main filter cap C821, this resistor will show the total current draw of the Inverter, standby power supply and the third supply I cannot clearly see from the picture, but this will give you some idea of the current draw, the inverter circuit will draw most of the current.Leave a comment:
-
-
Re: Transformer substitution - Sanyo DP42849-01
There may be a fusible resistor for feeding the Voltage to that inverter circuit where the power MOSFETs are mounted on that heat sink to the right of the inverter transformer. You can then check the voltage drops on that fusible resistor to calculate the current draw.Leave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
I get 1.68 amps. And as stated, I don't currently have a board with an original transformer. I have 2 more coming though so I might have a good one within a week. I'll cross my fingers and hope one is good. I've worked on at least 10 of these so far though and only 3 had good transformers, so the odds are not in my favor.Leave a comment:
-
-
Re: Transformer substitution - Sanyo DP42849-01
Yes, I am surprised that it only has one fuse.Leave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
Only has the 1 fuse on it. So I would pull the fuse then and connect the meter in series. OK. Thanks.Leave a comment:
-
Re: Transformer substitution - Sanyo DP42849-01
You will use your digital meter in DC A mode and connect it in series with power supply line that feeds the inverter circuit to see the circuit current draw, or if it has the fuse for each section of the transformer drive circuit then you can put your meter in place of the fuse to see current draw of that section and compare it to the section that has original transformer.Leave a comment:
Related Topics
Collapse
-
by mikey5791Hi all,
Got this local made DC power supply (12/14V) given free as the transformer has melted. There is no marking or indication to identify what type or rating of transformer used.
Fyi,. I had a busted autogate mainboard with transformer with marking 13-0-13 . Is this the 13v dc type transformer?
My questions are
1. How do i test to see if the transformer is in good working condition?
2. Can this transformer (marking 13-0-13) be used to replace the melted transformer on the DC power supply?
Hope you guys understand what i was asking. My intention is... -
by ohrenHello!
I'm looking at an original Xbox PSU: Foxlink ftps-0002 rev. B. The 12 V output is too low, and the 5 V output is too (?) high. Unfortunately I don't have an oscilloscope but only a DMM for diagnosis.
Measured voltages with no load:
After rectifier diodes
12V: 6.17 V
5V: 5.67 V
Secondary transformer pins AC measurement (really don't know if this says anything)
12V: 2-2.5 V
5V: 1.04 V
I also have another (working) Xbox psu from Delta. The same measures there, in order, being: 10.79,... -
by dennis_elx33Hello All,
i would like to post an interesting topic regarding 3-phase stepdown transformer which we suspect to cause an overcurrent (138A) which resulted to power tripped off of the HV power supply (80KV output).
Problem statement: Power tripped Off
Initial Problem: Found 2 IGBT and 2 rectifier diodes shorted (burnt).
Action Done:
1) Replaced the faulty parts with good spare.
2) Measured impedance of the 3phase input lines and found that L2 to L3 has 23.3ohm while other pairs are 51Kohm. This pins will... -
This specification for the ASUS Transformer T101HA - X5DHD Hybrid (2-in-1) can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the T101HA - X5DHD boardview and T101HA - X5DHD schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet,...09-06-2024, 04:40 PM
-
This specification for the ASUS Transformer T304UA-P71SP-CA Hybrid (2-in-1) can be useful for upgrading or repairing a laptop that is not working. As a community we are working through our specifications to add valuable data like the T304UA-P71SP-CA boardview and T304UA-P71SP-CA schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet,...09-06-2024, 12:00 PM
- Loading...
- No more items.
Leave a comment: