element eldft551 not turning on
+ More Options
Posts
    Re: element eldft551 not turning on
    If you monitor the 24V or the 12V output, do you see the output voltages jump for seconds when the TV is turn on, that will give us the clue if the power supply did try to start up and then goes into shutdown for some reason.
    • cashkennedy
      • Aug 2011
      • 668
      Yes the 24v / 12v and 5v (not the 5vsb) all come on for 1-2 seconds when its first turned "on". After that 1-2 seconds they all go away the STB stays on (4v) and the blue light remains lit, and I have to unplug to set to turn "off".
      Is the protection mode supposed to trip if there is not enough load on the 12 and 24? or only if it doesn't feel its accurately making those voltages?
      All 3 voltages that come on temporarily appear to reach a correct voltage (and not go over) , but there could be a limit to my multimeters ability to see quick changes. (all voltages were within 2% of correct value)
      Fixed so far 12 lcd's , 1 plasmas, 5 monitors, 0 dlp's (plan to keep the dlps at 0). and 3 atx power supplies, and 2 motherboards.
      • cashkennedy
        • Aug 2011
        • 668
        Which optocoupler is responsible for the protection mode?
        From what I can make out PC1B is to sense when to turn on the power supply. So I would assume PC3B and PC4B are involved in monitoring the voltages on the secondary?
          4V seems strange for standby?
          PC4B seems to be the OVP (over-voltage protect) optocoupler for 24V, 12V (and possibly 5VSB) lines, it triggers if PC3B or associated circuitry fails.
          PC3B looks to be 12V (and by relation, 24V) regulation.
          PC2B looks to be 5VSB regulation.
          PC1B looks to be on/off control.
          • cashkennedy
            • Aug 2011
            • 668
            STB is the "PS_ON" for this power supply. the 5VSB is 5.0v and after pressing the power button STB goes from 0 to 4v and stays that way till I unplug the set.
            I tested the voltage on the SHUTDOWN pin of UA4 (I assume that's how PC4B tells the power supply to go into protect mode?) and I get 4.1 V there after the set has been on for 1-2 seconds.
            The way the datasheet describes shutdown , makes it sound like id need a oscilloscope to properly monitor it though, as it may be pulsed to control the output / or steady to turn off the output.
              https://cdn.badcaps-static.com/pdfs/...c49d47f310.pdf
              Looks like SHUT controls CSS (soft start capacitor.)
              A high signal on SHUT will kill the oscillator and discharge CSS, disabling the IC. Once SHUT is released, CSS will have to charge to a set point voltage, at a constant current, then the oscillator begins. (The voltage on the CSS pin may also act to limit the current when first starting up.) CSS limits inrush current and gives everything a little while to start up (PFC bus etc) when the PSU is first turned on.
              Things that could cause SHUT to be high (more than about 1V in this case):
              VCC2 undervoltage monitor (ZA4, R93, R94, R96, D29) - The voltage on VCC2 must exceed the zener voltage plus base voltage of D29 (probably should be Q29?) Check ZA4 is not open circuit (should measure as diode one way.) Check the base voltage of D29, see if it is sufficient (>0.6V.) This might fire during operation if the startup cap is bad and it will keep SHUT high briefly on first startup, I think.
              Some kind of strange current-limit detect circuit(?) comprised of CA16, RA42, RA8, DA8, R74 and DA13. Looks like more than ~2.4V (two diode drops 0.7V each plus ~1V required for SHUT) across CA17+R08+R07 will fire SHUT.
              The OVP circuit on PC4A: Check zeners and diodes for shorts in that portion of the PSU.
              • cashkennedy
                • Aug 2011
                • 668
                Im pretty sure DA5 and DA13 don't exist, let me go get the board back in my hands and confirm. (as in they weren't soldered to the board / those protection schemes were not implemented)
                  Pin 10 is the shutdown control pin.
                  From spec sheet:
                  "An alternate approach is the use of the shutdown circuitry
                  of Pin 10 which has been improved to enhance the available
                  shutdown options. Activating this circuit by applying a
                  positive signal on Pin 10 performs two functions: the PWM
                  latch is immediately set providing the fastest turn–off signal to
                  the outputs; and a 150 mA current sink begins to discharge
                  the external soft–start capacitor. If the shutdown command is
                  short, the PWM signal is terminated without significant
                  discharge of the soft–start capacitor, thus, allowing, for
                  example, a convenient implementation of pulse–by–pulse
                  current limiting. Holding Pin 10 high for a longer duration,
                  however, will ultimately discharge this external capacitor,
                  recycling slow turn–on upon release.
                  Pin 10 should not be left floating as noise pickup could
                  conceivably interrupt normal operation."
                  As you can see on page two of the SCH, pin 10 (shutdown) is connected to OR GATE Diodes DA13, DA5, D31: anyone of those Diode when the Anode is HIGH will cause the IC to go into shutdown.
                    Interestingly, it appears the error detect for OVP is a latch (NPN, PNP bipolar latch circuit.) Only a power cycle can reset the latch, which may explain the symptoms observed.
                      Yes, that is the latching circuit when it detects OV of the 12V and the 24V outputs.
                      • cashkennedy
                        • Aug 2011
                        • 668
                        Yall are over my head now.... I have checked most of the diodes involved with the overvoltage protection areas, there are a few parts that seem to be mislabeled or changed name /
                        Parts DA5 and DA13 were not soldered to the board ever from what I can tell (the rest of the parts in circuit around those are still there though)
                        There is no Q6 , the part on my real board that seems equivalent is D29.
                        The part in the schematic labeled D29 is labeled Q16 on the actual board.
                        So far the everythings tested as working the way it should though.
                        Is there a way to test PC4B on the secondary side? Im not sure what voltage I should be expecting to be crossing there to indicate an error. And is that error signal only supposed to exist for a second or two while the 24v is on?
                        • cashkennedy
                          • Aug 2011
                          • 668
                          I also don't get the difference between brown ground (the heatsinks) and negative of the filter cap. They are about 10 ohms apart, not sure what they should be apart.
                          Are there 4 different "grounds" on this board ? lol
                            So are you getting DC voltage at pin10 the shutdown pin after the TV is turn on?
                            • cashkennedy
                              • Aug 2011
                              • 668
                              Yes I get 4.1 vDC at the shutdown pin 1-2 seconds after turning it "on". It stays at 4.1 vDC till I unplug the set.
                                See if you can measure voltage at anode of D31, if this is high, then we know for sure it is OVP circuit detecting fault.
                                • cashkennedy
                                  • Aug 2011
                                  • 668
                                  There is 5.01 vDC at the anode of D31.
                                  This circuit only detects over-voltage? No possibility the error is from under voltage? And is over voltage possibly from a lack of load?
                                    Looks to detect over-voltage and something on 5VSB, not sure what, need to analyse circuit a bit more.
                                      The OVP OPTO is fed by Diodes OR gate:
                                      DA7 + ZA1 for 24V OVP. ZA1 may be leaky.
                                      DA7 +ZA2 for 12V OVP. ZA2 may be leaky.
                                      DA4 (Dual Diode) is fed by the window comparator UF4A/B. The input to the comparator resistor-string (RA61, RA32, RA34, RA35) is connected to the GND of the 24V power supply but it looks like the GND of the 24V is not tied to secondary side circuit ground like the 12V power supply section up above. The only thing I can think of is that it is looking to see if the GND of the 24V is grounded to the gorund of the Inverter board which is grounded at the inverter board chassis mounting screw. You can verify that by measuring the Ground pin of the 24V connector to see if it shows oepn circuit, then check againg when the cables are attached to the inverter board. The 5VSTB for the comparator circuit is B+ for running the two op-amps.
                                      • cashkennedy
                                        • Aug 2011
                                        • 668
                                        I tested ZA1 and ZA2 earlier and they showed diode readings only 1 direction ( I assume a leaky one would have a large diode reading (large reading = little voltage going through, right?) in the reverse direction?, or would i not notice a small leak with my multimeter?)
                                        All the grounds comming from the inverters are part of a continuous ground plane that also includes the screw that holds the power supply in , so I dont think there is a special ground coming from the inverter that is being monitored.
                                        • cashkennedy
                                          • Aug 2011
                                          • 668
                                          Although they didnt mark the GND with a red triangle, it does have a GND yellow flag at the end of the path for 24V. I think it was just an ommission, as you'll see in the picture all ground pins for all connectors are all tied to the same ground, which screws the power supply to the frame.
                                          What voltages should i be hoping to see leaving the comparators? (im pretty sure the comparators are both inside a 8 pin IC? the one that has no markings / posisbly cause they burned off ...
                                          • flysky
                                            Gigabyte H610M S2H V2 help to identify the element.
                                            by flysky
                                            There is a motherboard Gigabyte H610M S2H V2 (DDR5), I can't find boardview
                                            Help to identify the element, marking on the element - C31PH. It stands next to the USB 3.0 and it looks like it is ESD Protect chip. We need a datasheet to this element. Maybe someone has already identified such an element. Help please.​
                                            01-23-2025, 07:21 PM
                                          • прямо
                                            Viper22A 5VSB circuit
                                            by прямо
                                            So I have a cheap non working ATX PSU that I was learning to repair a decade ago. At the time, it blew the main fuse, bridger rectifier, NTC, and primary 9A 900V MOSFET. Replaced all except the MOSFET. 5VSB came back online. Then I poked around in it so much, measuring components one by one to a point I accidentally made the 5VSB circuit primary side went bang. Blown the AP8022 (Viper22A) PWM chip, along with a low resistance resistor and the PC817 opto isolator. I replaced them all.
                                            In the process of poking around, I also lost a zener diode that stabilize the voltage coming from...
                                            01-13-2024, 07:05 PM
                                          • EasyGoing1
                                            The best way to drive a heating element?
                                            by EasyGoing1
                                            I've got this circuit that I've been playing with on a breadboard. I'm not happy with it mainly because the MOSFET gets too hot and generally controlling the temp of the heating element with the Arduino has proven to be a little more cumbersome than I would like.
                                            What I would like to know, is what is the best way to set up a circuit like this? The heating element is just a PCB and its going to be mounted under a 3D-printed enclosure that a lizard will use to warm his belly.
                                            This is the general setup that I have now.
                                            This is what the...
                                            01-25-2023, 11:29 AM
                                          • kotel studios
                                            FSP300-60GTF - no 5VSB, PS_ON; 5VSB carnage
                                            by kotel studios
                                            Finally replaced all of the shorted 4148's and resistors and an blown tl431 on my FSP300-60GTF after 5VSB going crazy and destroying it self. Those components also made the secondary transistors appear shorted (while in reality they weren't).
                                            Powered it on through my dim bulb tester and they (bulbs) only flash once meaning primary caps are getting charged, but that's it. No 5VSB, PS_ON voltages.
                                            I am sure I have replaced the components correctly and that there weren't any shorted/blown traces left.
                                            Any ideas where to go next?
                                            02-23-2025, 11:47 AM
                                            Heater element wire type instead of a fuse when troubleshooting a short circuit DIY
                                            by sam_sam_sam
                                            I was Ollie today which is a close out / surplus outlet store I do not go in there to often because you find things that you should not be tempted by but that is a another story
                                            I saw a small space heater that used a wire type of heater element which I been looking for a while but not really hard mind you but when I saw this I grabbed it I going to go back tomorrow and buy the last one that is like the one I bought today because I need the heater element and the ceramic insulators and more of heat element wire because this one has two different wattage settings one 1300 watts ( tap...
                                            12-16-2023, 08:39 PM
