Xantrex Powersouce 1800 Overloading (Error E03)

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • smorg
    Member
    • Oct 2015
    • 18
    • Canada

    #1

    Xantrex Powersouce 1800 Overloading (Error E03)

    Hi there, thanks for the great advice in these forums. I'm hoping to find a bit of specific advice on a Noma-branded Xantrex Powersource 1800 battery backup.
    It's an old unit, with maybe 10yrs service as a sump pump backup, so the batteries inside are not holding a charge anymore, but it does still supply non-sine AC power when connected with booster cables to a running automobile's red battery terminal and engine block.
    It is rated 1800W continuous and 3600W peak, but it is cutting out with an overload error (E03) with even just a 900W space heater or 1/2hp water jet pump plugged in by itself.
    None of the components on the circuit board seem to show any signs of physical damage or burn marks, and all eight 30amp fuses look ok.
    It might possibly have received a shock when a tree in the backyard was hit by lightning while it was in the basement, unsure on that.
    Here are a few pics of the setup and circuit board.
    There are reports online of this Powersource unit having transformer problems.
    Can these components be DIY repaired or otherwise jury rigged for a quick fix?
    I only have a basic digital multimeter for testing, and am learning as I go what can be tested for what.
    Thanks for any advice that will get this unit running strongly again, it'd be great if it could power the oil furnace too!
    Attached Files
  • smorg
    Member
    • Oct 2015
    • 18
    • Canada

    #2
    Re: Xantrex Powersouce 1800 Overloading (Error E03)

    Any thoughts, please? Thank you!

    Comment

    • stj
      Great Sage 齊天大聖
      • Dec 2009
      • 30944
      • Albion

      #3
      Re: Xantrex Powersouce 1800 Overloading (Error E03)

      could be dry caps.

      i would replace all the small ones wih panasonic FR,
      i wouldnt just replace the large ones because they are expensive - i would desolder and test them with an esr & capacitance meter.

      Comment

      • smorg
        Member
        • Oct 2015
        • 18
        • Canada

        #4
        Re: Xantrex Powersouce 1800 Overloading (Error E03)

        Hi stj, thanks for your idea! Is this testable somehow without buying the new parts in advance?
        -
        Update: Have been using the unit as described to run a small 2.5 amp jigsaw, and other small electronics (charging the laptop, phone, etc.), but any larger loads cause the overload error.
        Thanks for your advice, any other thoughts out there?

        Comment

        • Behemot
          Badcaps Legend
          • Dec 2009
          • 4845
          • CZ

          #5
          Re: Xantrex Powersouce 1800 Overloading (Error E03)

          With ESR/capacitance meter.

          You may get any of low-ESR caps, Chemi-Con, Rubycon, Nichicon. Panasonic is usually overpriced, NCC is among the cheaper ones.

          Running any motor on non-sinewave source is just wrong.
          Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

          Exclusive caps, meters and more!
          Hardware Insights - power supply reviews and more!

          Comment

          • smorg
            Member
            • Oct 2015
            • 18
            • Canada

            #6
            Re: Xantrex Powersouce 1800 Overloading (Error E03)

            Thanks for the tips on caps brands.
            I understand that non-sine AC is hard on motors, but we're just looking for temporary backup for our home's main systems like water, heat, etc. in case of an outage.

            Comment

            • fzabkar
              Badcaps Veteran
              • Mar 2009
              • 772
              • Australia

              #7
              Re: Xantrex Powersouce 1800 Overloading (Error E03)

              What is the battery voltage when the 900W load is connected? Measure the voltage at the battery and at the Xantrex unit.

              PowerSource 1800 Owner’s Guide:


              E03

              Overload shutdown while supplying backup power. The AC product(s)
              connected are consuming more than PowerSource 1800’s power rating. Use products with a total power consumption within PowerSource 1800’s continuous power rating of 1440 W.


              The AC products connected have a surge power that exceeds
              PowerSource 1800 surge capability. Use products with a total starting surge power within PowerSource 1800’s capability of 2880 W.


              One or more of the connected products are damaged. Have the damaged product serviced by a qualified technician.
              Last edited by fzabkar; 10-31-2015, 10:42 PM.

              Comment

              • Behemot
                Badcaps Legend
                • Dec 2009
                • 4845
                • CZ

                #8
                Re: Xantrex Powersouce 1800 Overloading (Error E03)

                Originally posted by smorg
                Thanks for the tips on caps brands.
                I understand that non-sine AC is hard on motors, but we're just looking for temporary backup for our home's main systems like water, heat, etc. in case of an outage.
                It's hard on both systems, UPS generaly don't like inductive load unless they are somewhat built for that. It may very well have killed it. But yeah, what's the state of the batt?
                Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                Exclusive caps, meters and more!
                Hardware Insights - power supply reviews and more!

                Comment

                • smorg
                  Member
                  • Oct 2015
                  • 18
                  • Canada

                  #9
                  Re: Xantrex Powersouce 1800 Overloading (Error E03)

                  Hi thanks for the replies!
                  With the booster cables attached and the car running the battery reads 13.5V.
                  Once disconnected, it drops to 0.1.
                  As soon as the 900W is connected there is an overload error.
                  I'll have to check again to see if there is a visible voltage drop before the unit shuts off.
                  Thanks!

                  Comment

                  • Behemot
                    Badcaps Legend
                    • Dec 2009
                    • 4845
                    • CZ

                    #10
                    Re: Xantrex Powersouce 1800 Overloading (Error E03)

                    If I understand it correctly, the battery reads 0.1 V? I guess it is completelly dead. Seems like some cell went bad and now there is discontinuity so it reads as 0.
                    Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                    Exclusive caps, meters and more!
                    Hardware Insights - power supply reviews and more!

                    Comment

                    • budm
                      Badcaps Legend
                      • Feb 2010
                      • 40746
                      • USA

                      #11
                      Re: Xantrex Powersouce 1800 Overloading (Error E03)

                      'I'm hoping to find a bit of specific advice on a Noma-branded Xantrex Powersource 1800 battery backup.
                      It's an old unit, with maybe 10yrs service as a sump pump backup, so the batteries inside are not holding a charge anymore'
                      So the batteries (3) are 10 years old?
                      Never stop learning
                      Basic LCD TV and Monitor troubleshooting guides.
                      http://www.badcaps.net/forum/showthr...956#post305956

                      Voltage Regulator (LDO) testing:
                      http://www.badcaps.net/forum/showthr...999#post300999

                      Inverter testing using old CFL:
                      http://www.badcaps.net/forum/showthr...er+testing+cfl

                      Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                      http://s807.photobucket.com/user/budm/library/

                      TV Factory reset codes listing:
                      http://www.badcaps.net/forum/showthread.php?t=24809

                      Comment

                      • jojo69
                        Member
                        • Nov 2015
                        • 25
                        • US

                        #12
                        Re: Xantrex Powersouce 1800 Overloading (Error E03)

                        get those dead batteries out of it and recycle them down at the port

                        I believe that the poor contacts and small diameter wires you are connecting to your 12VDC source are insufficient for your load. You need some heavy cabling for this, heavy and short as possible with solid contacts

                        For a 900W load you would be pulling 75A at 12V f the inverter were 100% efficient, which it is not. Probably need closer to 100A...your toy jumper cables just aren't going to do that mate. And that is assuming that your vehicle alternator can make that, which I doubt.
                        Last edited by jojo69; 11-02-2015, 11:25 PM.

                        Comment

                        • smorg
                          Member
                          • Oct 2015
                          • 18
                          • Canada

                          #13
                          Re: Xantrex Powersouce 1800 Overloading (Error E03)

                          Hi Thanks for your messages.
                          Yes, the batteries seem to be dead, understandable since they are 10 years old.
                          Yesterday, tried plugging in the 900W heater with voltmeter attached and watched it drop from 13.5 to about 10.3 before overload cutoff.
                          Today, tried it again (in light rain) and -Surprise!- the heater ran without overloading the box. Didn't get the volt reading though - will try again later.
                          Thanks again.

                          Comment

                          • jojo69
                            Member
                            • Nov 2015
                            • 25
                            • US

                            #14
                            Re: Xantrex Powersouce 1800 Overloading (Error E03)

                            recommend you stop playing like this, you risk overloading your vehicle alternator or melting those little jumpers

                            this inverter requires a serious source of 12V for large loads

                            I think the inverter is fine, you need to invest in a way to feed it.
                            Last edited by jojo69; 11-03-2015, 10:21 AM.

                            Comment

                            • smorg
                              Member
                              • Oct 2015
                              • 18
                              • Canada

                              #15
                              Re: Xantrex Powersouce 1800 Overloading (Error E03)

                              Tried retesting the 900w heater, dropped from 13.7 volts to 10.7 then cut out.
                              Checked the 10yr old batteries after an hour on the car and they measured 5.5 volts.
                              Thanks!

                              Comment

                              • fzabkar
                                Badcaps Veteran
                                • Mar 2009
                                • 772
                                • Australia

                                #16
                                Re: Xantrex Powersouce 1800 Overloading (Error E03)

                                The Owner's Guide specifies a "low battery shutdown" voltage of 10.5 V (nominal).

                                Comment

                                • smorg
                                  Member
                                  • Oct 2015
                                  • 18
                                  • Canada

                                  #17
                                  Re: Xantrex Powersouce 1800 Overloading (Error E03)

                                  Originally posted by fzabkar
                                  The Owner's Guide specifies a "low battery shutdown" voltage of 10.5 V (nominal).
                                  That is interesting. Seems to indicate that the unit is operating normally then?
                                  Not sure how to reconcile that with it's claims of handling 1800W continuous.
                                  The built in terminal cables don't seem that much more substantial than my booster cables (but much shorter obviously).
                                  Perhaps that's the limiting factor?
                                  Thank you all, for your input!

                                  Comment

                                  • budm
                                    Badcaps Legend
                                    • Feb 2010
                                    • 40746
                                    • USA

                                    #18
                                    Re: Xantrex Powersouce 1800 Overloading (Error E03)

                                    Continuous rating is only 1440 W per user manual.
                                    'Not sure how to reconcile that with it's claims of handling 1800W continuous.' Marketing error/ploy?
                                    Last edited by budm; 11-04-2015, 01:34 PM.
                                    Never stop learning
                                    Basic LCD TV and Monitor troubleshooting guides.
                                    http://www.badcaps.net/forum/showthr...956#post305956

                                    Voltage Regulator (LDO) testing:
                                    http://www.badcaps.net/forum/showthr...999#post300999

                                    Inverter testing using old CFL:
                                    http://www.badcaps.net/forum/showthr...er+testing+cfl

                                    Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                                    http://s807.photobucket.com/user/budm/library/

                                    TV Factory reset codes listing:
                                    http://www.badcaps.net/forum/showthread.php?t=24809

                                    Comment

                                    • jojo69
                                      Member
                                      • Nov 2015
                                      • 25
                                      • US

                                      #19
                                      Re: Xantrex Powersouce 1800 Overloading (Error E03)

                                      Originally posted by budm
                                      Marketing error/ploy?
                                      or as Dave Jones over at EEVBlog calls it "marketing wank"

                                      Yes OP, the length of the wires is very much a factor when trying to move very high currents like this, as is the contact area of the actual connections.

                                      The good news is that your inverter is very probably just fine, you just need to build a solid, dedicated battery bank to power it.

                                      Comment

                                      • budm
                                        Badcaps Legend
                                        • Feb 2010
                                        • 40746
                                        • USA

                                        #20
                                        Re: Xantrex Powersouce 1800 Overloading (Error E03)

                                        If you look at the spec sheet:
                                        Internal battery capacity 51 amp-hours (3 x 17 amp-hour batteries)
                                        Internal battery voltage 12 VDC (nominal)
                                        It uses three 12V batteries rated at 17AH each for total of 51AH (connected in parallel).
                                        So per spec sheet it can continuously put out 120V @12A = 1440 Watts.
                                        So we have 12VDC to power the inverter circuit to create 1440W of power, for the sake of calculation we make it 100% conversion efficiency (which cannot be) that means the current draw from the batteries 120A! (12V x 120A = 1440 WATTS). Can it actually do that?
                                        I do not see run time rating at full load.
                                        It shows Microwave 920W for 12 minutes.
                                        Last edited by budm; 11-04-2015, 10:25 PM.
                                        Never stop learning
                                        Basic LCD TV and Monitor troubleshooting guides.
                                        http://www.badcaps.net/forum/showthr...956#post305956

                                        Voltage Regulator (LDO) testing:
                                        http://www.badcaps.net/forum/showthr...999#post300999

                                        Inverter testing using old CFL:
                                        http://www.badcaps.net/forum/showthr...er+testing+cfl

                                        Tear down pictures : Hit the ">" Show Albums and stories" on the left side
                                        http://s807.photobucket.com/user/budm/library/

                                        TV Factory reset codes listing:
                                        http://www.badcaps.net/forum/showthread.php?t=24809

                                        Comment

                                        Related Topics

                                        Collapse

                                        • Green Probe
                                          Mosfet Advice
                                          by Green Probe
                                          Hi, Im looking to replace some EMP21N03 mosfets on an Alienware motherboard, but I'm having trouble finding a legit supplier. The ones that are available from China have pictures with the engraved logo looking very scratchy and sketchy. Nobody in the US sells them. I'm trying to find a compatible mosfet, but I'm not well versed enough to be confident im making the right choice. Does anyone have a suggestion or advice that could help me find the right mosfet? Thanks!
                                          05-22-2025, 10:49 AM
                                        • user234
                                          Gigabyte Eagle 3060 Ti - Boardview / Advice request please
                                          by user234
                                          Hi all,

                                          Recently installed a new motherboard but during the process I seemed to have damaged my Gigabyte Eagle 3060 Ti card.

                                          My motherboard ROG STRIX B550-A is detecting an issue with the VGA (light ON)

                                          I have attached 2 photo's of my GPU board, one above and the other is what I believe to be the 5V - as you can see, this has visual damage so looks suspicious to me.

                                          If I replace this part what are the odds this will resolve the issue? - any additional information on where to source the parts would be much apricated too!

                                          This is...
                                          05-10-2025, 04:25 AM
                                        • artvandalai
                                          Advice on rewiring this stepup transformer?
                                          by artvandalai
                                          I bought this Chinese made step up transformer to run some 220v appliances. Some of the wires were brittle and broke off. I attempted to improve some of the wiring with spade terminals and heatshrink tubing as the wires were just soldered straight to the connectors. Any advice on how to rewire the broken wires on this step up transformer? I'm unsure how to go about rewiring this to a better safe working condition.
                                          01-14-2025, 01:00 AM
                                        • wattsRpower
                                          MBP 820-00928a need advice
                                          by wattsRpower
                                          I'm working on an a1707 macbook pro for a friend of mine that said it had stopped working and will not turn back on. After opening up the laptop I discovered a short on C7382 which took the PPBUS_HS_CPU to gorund.
                                          After fixing the cap issue, I had 12.6 volts on the line. Not sure what or when something happened, but I am now getting 3.6 to 3.8 volts fluctuating. I was taking some volt readings and I'm not sure if I shorted something or if something else has happened.
                                          At this point, I'm not sure where to start looking for something to fix. Maybe the cpu fried anyway when the PPBUS_HS_CPU...
                                          10-12-2024, 04:55 PM
                                        • Ven
                                          Seeking Advice on Enhancing Heatsink for Main Processor on SAMSUNG TV Motherboard
                                          by Ven
                                          Hello everyone,

                                          I'm looking to upgrade the heatsink on the main processor of my TV's motherboard for better cooling performance.

                                          The current heatsink is a square-shaped one (2.8cm x 2.8cn) with a basic design, and I believe a more efficient heatsink could help with thermal management and potentially extend the life of the TV.

                                          I'd appreciate any advice on the best type of heatsink to use, specific product recommendations, and tips for installation.

                                          If you've done a similar upgrade, I'd love to hear about your experience and any challenges you...
                                          07-08-2024, 09:32 AM
                                        • Loading...
                                        • No more items.
                                        Working...