    Powerware 9120 Online UPS

    This is another freebie I found recently. It came with 2 12V 9AH batteries that are not completely dead. It seems they still have ~1/3 of their initial capacity.

    The UPS works, but displays “DC bus fault” the first time it starts. I looked around and it is probably cap related:
    http://oh2mp.ham.fi/misc/powerware9120/english.html
    http://www.fixya.com/support/t133894..._fault_problem

    I tested every capacitor on it and only the C14 = 100 uF 63V Jamicon TK is bad (capacity: 103uF, esr: 28).

    1) Do I need to change the other cap mentioned in the links?
    It is a Chemicon SME 2200 uF 16V with capacity: 2400uF and esr: 0.04-0.06, tested on circuit (datasheet)
    Is Chemicon SME a reliable series?

    2) Can I replace the Jamicon TK 100 uF 63V with Rubycon YXF 100uF 63V?
    Attached Files
  • japlytic
    Badcaps Legend
    • Oct 2005
    • 2086
    • Australia

    #2
    Re: Powerware 9120 Online UPS

    Nippon Chemi-Con SME appears to be a reliable series, and has been superseded by SMG or SMQ.
    You can replace the Jamicon TK with Rubycon YXF.
    Check for shorts on the DC bus as well from C40 and C42 (after discharging them), including checking for shorts on Q11 and Q12 on the power board.
    My first choice in quality Japanese electrolytics is Nippon Chemi-Con, which has been in business since 1931... the quality of electronics is dependent on the quality of the electrolytics.

    Comment

    • goodpsusearch
      Badcaps Legend
      • Oct 2009
      • 2850
      • Greece

      #3
      Re: Powerware 9120 Online UPS

      I replaced the bad 100uF 63V Jamicon TK with Rubycon YXF 100uF 63V and now the UPS works... I'll test it more thoroughly tomorrow.

      Btw it has a very useful feature. It can display the Watts and VAs of the devices that are connected to it realtime.

      How accurate can I except it to be? Does it mean that I can calculate the power factor by dividing Watts with VAs?
      Attached Files
      Last edited by goodpsusearch; 04-03-2011, 06:35 PM.

      Comment

      • japlytic
        Badcaps Legend
        • Oct 2005
        • 2086
        • Australia

        #4
        Re: Powerware 9120 Online UPS

        Originally posted by goodpsusearch
        Btw it has a very useful feature. It can display the Watts and VAs of the devices that are connected to it realtime.

        How accurate can I except it to be? Does it mean that I can calculate the power factor by dividing Watts with VAs?
        I guess so, and how the UPS calculates Watts and VA should be fairly accurate.
        My first choice in quality Japanese electrolytics is Nippon Chemi-Con, which has been in business since 1931... the quality of electronics is dependent on the quality of the electrolytics.

        Comment

        • biserko
          New Member
          • Nov 2012
          • 6
          • croatia

          #5
          Re: Powerware 9120 Online UPS

          can help
          My board is a model 098-12101-04 PSDR-1112NN P.W
          P / N :12101-09p-638 (e1)
          I appeared on the display DC BUS Fault

          Comment

          • Behemot
            Badcaps Legend
            • Dec 2009
            • 4845
            • CZ

            #6
            Re: Powerware 9120 Online UPS

            Seems that this usually means shorted transistors and/or dried caps near heatsink. Do you have digital multimeter? Any other equipment?
            Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

            Exclusive caps, meters and more!
            Hardware Insights - power supply reviews and more!

            Comment

            • biserko
              New Member
              • Nov 2012
              • 6
              • croatia

              #7
              Re: Powerware 9120 Online UPS

              Originally posted by Behemot
              Seems that this usually means shorted transistors and/or dried caps near heatsink. Do you have digital multimeter? Any other equipment?
              Can you write in more detail which transistors, and where they are on the plate ...

              Comment

              • Behemot
                Badcaps Legend
                • Dec 2009
                • 4845
                • CZ

                #8
                Re: Powerware 9120 Online UPS

                If you provide good enough pictures If it is more or less the same as in the first post, than that would also be capacitor C14, it's the 63V/100uF cap. Check all those transistors attached to the big heatsink in there, if you have DMM, that's a minute to check them all.
                Last edited by Behemot; 11-29-2012, 10:41 AM.
                Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                Exclusive caps, meters and more!
                Hardware Insights - power supply reviews and more!

                Comment

                • Jooo
                  Badcaps Veteran
                  • Oct 2011
                  • 222
                  • Finland

                  #9
                  Re: Powerware 9120 Online UPS

                  I have the 3000VA version of this. It works nicely, except it starts to make annoying squealing noise after about 5 mins of running. BUT only when connected to mains, and even if batteries are full.

                  However, in battery mode, this squealing doesn't happen, even after long time.

                  Any clues what can cause this, and is it fixable?

                  Comment

                  • goodpsusearch
                    Badcaps Legend
                    • Oct 2009
                    • 2850
                    • Greece

                    #10
                    Re: Powerware 9120 Online UPS

                    Originally posted by Jooo
                    I have the 3000VA version of this. It works nicely, except it starts to make annoying squealing noise after about 5 mins of running. BUT only when connected to mains, and even if batteries are full.

                    However, in battery mode, this squealing doesn't happen, even after long time.

                    Any clues what can cause this, and is it fixable?
                    You should check every capacitor in it (please be careful, some of them retain their charge for hours) starting from those 2: http://oh2mp.ham.fi/misc/powerware9120/english.html

                    Comment

                    • biserko
                      New Member
                      • Nov 2012
                      • 6
                      • croatia

                      #11
                      Re: Powerware 9120 Online UPS

                      Originally posted by Behemot
                      If you provide good enough pictures If it is more or less the same as in the first post, than that would also be capacitor C14, it's the 63V/100uF cap. Check all those transistors attached to the big heatsink in there, if you have DMM, that's a minute to check them all.



                      where it would be located capacitor C14, it's the cap 63V/100uF

                      thanks

                      Comment

                      • biserko
                        New Member
                        • Nov 2012
                        • 6
                        • croatia

                        #12
                        Re: Powerware 9120 Online UPS

                        Originally posted by biserko

                        where it would be located capacitor C14, it's the cap 63V/100uF

                        thanks





                        Comment

                        • biserko
                          New Member
                          • Nov 2012
                          • 6
                          • croatia

                          #13
                          Re: Powerware 9120 Online UPS










                          Comment

                          • Behemot
                            Badcaps Legend
                            • Dec 2009
                            • 4845
                            • CZ

                            #14
                            Re: Powerware 9120 Online UPS

                            Hmm, seems like different design. OK, let's start. You have photos so you know where every cable belongs. So, disconnect everything and remove the main board.

                            I would personally begin with the section between blue and red wire, there is some silicone with only small heatsink and some even without any. Check it. What are the small capacitors in there? They may be baked, I can imagine some heat is being produced arround those components.
                            Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                            Exclusive caps, meters and more!
                            Hardware Insights - power supply reviews and more!

                            Comment

                            • biserko
                              New Member
                              • Nov 2012
                              • 6
                              • croatia

                              #15
                              Re: Powerware 9120 Online UPS

                              We replaced the components that you have said, but the problem is what are the other of components very very hot, you can not keep your finger on how many of them are hot ...

                              Comment

                              • Behemot
                                Badcaps Legend
                                • Dec 2009
                                • 4845
                                • CZ

                                #16
                                Re: Powerware 9120 Online UPS

                                Does it work now?

                                Well yeah, you can think about adding some bigger heatsinks or doing some ghetto mods like resistor fly mod and so. If it is worth it…
                                Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                                Exclusive caps, meters and more!
                                Hardware Insights - power supply reviews and more!

                                Comment

                                • davor
                                  Member
                                  • Dec 2012
                                  • 13
                                  • Croatia

                                  #17
                                  Re: Powerware 9120 Online UPS

                                  I have blown one IRF3710, near 2 caps mentioned before, and glass fuse on board (5A).
                                  Replaced IRF and fuse but it blows fuse again. On LCD is "DC Bus Fault".
                                  Any idea what next?

                                  Comment

                                  • mariushm
                                    Badcaps Legend
                                    • May 2011
                                    • 3799

                                    #18
                                    Re: Powerware 9120 Online UPS

                                    A blown fuse rarely happens without a cause.

                                    Maybe look at the traces going to the IRF and follow them back checking components in the path?

                                    If something blows the IRF, something is probably shorted or a diode is faulty. I would go from the IRF solder points/holes back and check everything.

                                    Check diodes, check resistors, check for shorted capacitors and if you can their ESR/if they're leaky, check npn transistors (put meter on diode check, test 2 out of 3 pins in both directions as if they're diodes)

                                    If you can, take out the board and get a good camera with macro mode and snap some focused (not blurry) pictures of both sides, maybe someone with good eyes here can spot some components that look burnt out or some broken/burnt copper traces on the pcb.

                                    Comment

                                    • davor
                                      Member
                                      • Dec 2012
                                      • 13
                                      • Croatia

                                      #19
                                      Re: Powerware 9120 Online UPS

                                      Thanx. Its 22:00 and I've just replaced rest 3 IRF's (S/D=short) but spoted on 2 IRF's on the right, traces of some kind of burns/cuts of on source pins!!!
                                      Now Ive left UPS to filll batts to full and will post results tomorrow.
                                      1st IRF was burnt so hard that pin was in the air!!! Temp. was so high that components around have black marks!
                                      Fuse (5A) is soldered to the board as, by design, it's not ready for easy replace.

                                      Comment

                                      • davor
                                        Member
                                        • Dec 2012
                                        • 13
                                        • Croatia

                                        #20
                                        Re: Powerware 9120 Online UPS

                                        No change at all - fuse keeps blowing.
                                        Replaced also 2 condensers, checked diode near IRF (first from the left, traces of burning around it).
                                        With power cable connected fan starts (as before) and I can browse thru options on LCD but when I press power - bang.
                                        Tryed to start device just on batts but some smoke came out - didnt have time to spot from where and didnt want to do it again.
                                        Attached Files
                                        Last edited by davor; 03-23-2013, 04:05 PM.

                                        Comment

                                        Related Topics

                                        Collapse

                                        • Document Archive
                                          ACER Aspire XC-330 Aspire XC A4-9120 Specification for Upgrade or Repair
                                          by Document Archive
                                          This specification for the ACER Aspire XC-330 can be useful for upgrading or repairing a desktop PC that is not working. As a community we are working through our specifications to add valuable data like the Aspire XC-330 boardview and Aspire XC-330 schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet, or download for ACER...
                                          09-12-2024, 03:28 PM
                                        • petehall347
                                          100nf and 100uf precision capacitors
                                          by petehall347
                                          i am wanting to calibrate my multimeters and for this i require a 100nf and 100uf precision capacitors . trouble is i can't find them ....
                                          08-13-2024, 06:56 AM
                                        • ten-d
                                          Nippon Chemi-con 100uf 100v BP electrolytic cap
                                          by ten-d
                                          Hi all!

                                          I just bought a pair of ADS L810 speakers, which I've heard are some of the best speakers from that time (late 70's) into the early 80's. I was super excited to test them out and hooked them up and I was very underwhelmed by the treble. The treble was awfully muffled. I've been doing some restoration work on 70's stereos and a couple of speakers here and there so I am really just a beginner. I do know that capacitors in speaker crossovers filter out the lows to allow only the highs up to the tweeters and mids. Inductors filter out the highs to allow the lower frequencies to...
                                          01-30-2024, 05:18 PM
                                        • RUllER
                                          chemicon produced by fuhjyyu
                                          by RUllER


                                          This is not a fake Chemicon, it is genuine
                                          Many companies are outsourcing to Chinese factories....
                                          01-29-2024, 12:22 AM
                                        • iMic
                                          Vintage AT Power Supplies - Selecting Capacitors
                                          by iMic
                                          Hi,

                                          Back after a long hiatus with some old power supplies that need repairing. I've recently picked up a couple of 386SX systems, two 486DX systems, a SiliconGraphics Indy and an iMac G3 that either have verified leaking capacitors in their power supplies, or are likely to in the near future. For the sake of simplicity, instead of tackling all at once, I'm starting with the 386's and one of the 486's.


                                          The 386's power supplies are Seasonic SS4040A's, with caps that are visibly leaking, and 9 replacement caps per unit are required. Most appear to be from the Rubycon...
                                          02-19-2023, 06:45 PM
                                        • Loading...
                                        • No more items.
                                        Working...