    Re: Powerware 9120 Online UPS

    I'm a new member. I have a problem whit my 9120 6kva. on display appears the message "O/V low"; infact when it begins working it's ok, but after 20 second the ups goes in bypass and the message that I said, appea.
    Can somebody help me? thanks

    Comment

    • magdtron
      New Member
      • Dec 2012
      • 1
      • egypt

      #22
      Re: Powerware 9120 Online UPS

      I have something different with powerware 9120 3000 w , it works perfectly without unplug ac cable - backup mode - when you plug the ac and begin to change over commercial AC, i hear very loud desirable sounds, i cant wait to expect the worst, have to unplug the ac cable at once

      Comment

      • Behemot
        Badcaps Legend
        • Dec 2009
        • 4845
        • CZ

        #23
        Re: Powerware 9120 Online UPS

        Bad relay maybe?
        Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

        Exclusive caps, meters and more!
        Hardware Insights - power supply reviews and more!

        Comment

        • morphis
          New Member
          • Aug 2015
          • 2
          • Australia

          #24
          Re: Powerware 9120 Online UPS

          Hi just repaired a Powerware 9120 700VA that was showing 'DC BUS FAULT'.

          At first I pulled C14 and others ( C10, C40 C42 & C48 as they are in close prox. to heat sources )
          I measured the capacitance of the pulled caps, But the were all within 10-15% of there rating. So I though bummer this is not going to be easy as I don't have an ESR meter.

          But then I found this video "#135: Measure Capacitor ESR with an Oscilloscope and Function Generator" and last year I purchased a Rigol MSO1104Z-S so after a couple of minutes setting up and testing known good and bad caps as a test. Was able to very quickly go thru and test the pulled caps.

          So C14 was like 89uF so thats within 11% of 100uF and on a 20% spec cap it still looked ok to the DMM but its ESR was off the charts.

          The rest of the caps were perfect.

          So if you have a 'DC BUS FAULT' and you have measured C10 and C14 and you still think they are ok, REPLACE THEM.

          Replaced: C10 with Nichicon 100uF 63V 105ºC and remounted the nearby diodes slightly off of the board as its looks like they get nice and toasty.

          Comment

          • morphis
            New Member
            • Aug 2015
            • 2
            • Australia

            #25
            Re: Powerware 9120 Online UPS

            Hi just repaired a Powerware 9120 700VA that was showing 'DC BUS FAULT'.

            At first I pulled C14 and others ( C10, C40 C42 & C48 as they are in close prox. to heat sources )
            I measured the capacitance of the pulled caps, But the were all within 10-15% of there rating. So I though bummer this is not going to be easy as I don't have an ESR meter.

            But then I found this video "#135: Measure Capacitor ESR with an Oscilloscope and Function Generator" and last year I purchased a Rigol MSO1104Z-S so after a couple of minutes setting up and testing known good and bad caps as a test. Was able to very quickly go thru and test the pulled caps.

            So C14 was like 89uF so thats within 11% of 100uF and on a 20% spec cap it still looked ok to the DMM but its ESR was off the charts.

            The rest of the caps were perfect.

            So if you have a 'DC BUS FAULT' and you have measured C10 and C14 and you still think they are ok, REPLACE THEM.

            Replaced: C10 with Nichicon 100uF 63V 105ºC and remounted the nearby diodes slightly off of the board as its looks like they get nice and toasty.



            I also have a Powerware 9120 1000VA.
            I replaced C10 and remounted the diodes the same as the 700VA just to be on the cautious side.
            Theres not 'Fault' but I think it might be the same as magdtron its making a to so nice sounds while charging the batteries.

            - The sound disappears after a Battery test for awhile but then returns after about a 30 secs.
            - Also disappears when Mains supply is removed.
            - In HE (High Efficiency) mode or Bypass Mode the sound still exists if Mains supply is connected and the batteries are being charged.


            Also I found out that the Powerware/Eaton EBM connector is 5x shrouded 4mm banana plugs in a moulded connector.
            So I'm going to design a 3D printed plug to hold off shelf shrouded 4mm banana plugs, Custom EBM

            Comment

            • Behemot
              Badcaps Legend
              • Dec 2009
              • 4845
              • CZ

              #26
              Re: Powerware 9120 Online UPS

              Yeah that's exactly what we keep repeating here - you won't tell bad cap with just capacitance meter. If you want entry-level professional ESR meter/capacitometer, I can supply ya. You can use O-scope but that's really for telling way-off caps only.
              Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

              Exclusive caps, meters and more!
              Hardware Insights - power supply reviews and more!

              Comment

              • feil
                Member
                • Jun 2015
                • 10
                • austria

                #27
                Re: Powerware 9120 Online UPS

                hello,
                someone still reading this?^^

                i have also an ups like that, with the DC Bus Fault Error
                i have now changed the 2 caps c10 c14 for trying, but still doenst work,
                someone any suggestions what else it could be?

                regards
                clemens

                Comment

                • goodpsusearch
                  Badcaps Legend
                  • Oct 2009
                  • 2850
                  • Greece

                  #28
                  Re: Powerware 9120 Online UPS

                  I would check every capacitor on it with an esr / capacitance meter.
                  Last edited by goodpsusearch; 04-13-2016, 08:04 PM.

                  Comment

                  • feil
                    Member
                    • Jun 2015
                    • 10
                    • austria

                    #29
                    Re: Powerware 9120 Online UPS

                    Originally posted by goodpsusearch
                    I would check every capacitor on it with an esr / capacitance meter.
                    i dont have something like that

                    any suggestions witch one i could try to replace?^^
                    regards
                    clemens

                    Comment

                    • goodpsusearch
                      Badcaps Legend
                      • Oct 2009
                      • 2850
                      • Greece

                      #30
                      Re: Powerware 9120 Online UPS

                      It could be any capacitor that may have gone bad without bulging.

                      You can buy something like this:

                      http://www.ebay.com/itm/New-Quality-...IAAOSwo6lWOFOW

                      http://www.ebay.com/itm/2015-LCD-128...YAAOSwBLlVLeOR

                      http://www.ebay.com/itm/2015-LCD-128...cAAOSwPgxVMBnp

                      Comment

                      • Behemot
                        Badcaps Legend
                        • Dec 2009
                        • 4845
                        • CZ

                        #31
                        Re: Powerware 9120 Online UPS

                        Just remember these AVR meter toys can not measure in circuit, they have no protection agains charged caps and those without casing can be potentialy lethal.

                        I got entry-level professional ESR/capacitance meter with relay protection if you want something of decent quality. It is possible that soon I'll also add advanced version of that AVR thing to my offer.
                        Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                        Exclusive caps, meters and more!
                        Hardware Insights - power supply reviews and more!

                        Comment

                        • goodpsusearch
                          Badcaps Legend
                          • Oct 2009
                          • 2850
                          • Greece

                          #32
                          Re: Powerware 9120 Online UPS

                          It is highly unlikely that he is going to spend 35€ + for a dedicated esr/C meter. These ~10€ AVR tools are the best option for someone who just wants to fix something / a casual hobbyist.

                          Comment

                          • Behemot
                            Badcaps Legend
                            • Dec 2009
                            • 4845
                            • CZ

                            #33
                            Re: Powerware 9120 Online UPS

                            You never know…there are dozens of ppl here who started repairing stuff regularly as soon as they acquired the knowledge.
                            Last edited by Behemot; 04-16-2016, 05:19 AM.
                            Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                            Exclusive caps, meters and more!
                            Hardware Insights - power supply reviews and more!

                            Comment

                            • goodpsusearch
                              Badcaps Legend
                              • Oct 2009
                              • 2850
                              • Greece

                              #34
                              Re: Powerware 9120 Online UPS

                              That's true!

                              Comment

                              • feil
                                Member
                                • Jun 2015
                                • 10
                                • austria

                                #35
                                Re: Powerware 9120 Online UPS

                                can you recommend some esr/C meter ?^^
                                so round about 0-100 dollar if possible.
                                can i test with them condensators without desoldering?
                                until now i only have repairdes thing where i have seen the bad caps, but im interested to do more than that^^
                                regards
                                and thanks. clemens

                                Comment

                                • Behemot
                                  Badcaps Legend
                                  • Dec 2009
                                  • 4845
                                  • CZ

                                  #36
                                  Re: Powerware 9120 Online UPS

                                  I am distributing the ESR Micro v4.0si. You can buy directly according to current exchange rate for CZK, or for fixed price at Bonanza.

                                  Direct competitor for it is the Atlas ESR70 from Peak, though I think it is somewhat more precise and has faster cap discharge, it has smaller range and costs as much as twice the price.
                                  Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                                  Exclusive caps, meters and more!
                                  Hardware Insights - power supply reviews and more!

                                  Comment

                                  • alltvrepairs
                                    Badcaps Veteran
                                    • Jan 2014
                                    • 247
                                    • Malta

                                    #37
                                    Re: Powerware 9120 Online UPS

                                    Hi,
                                    Its my turn now

                                    I have the 5KVA model with same DC Bus Fault. Have thoroughly followed this thread. My main board is more complicated. I have changed the capacitors marked in RED in the DC-DC section.

                                    Anyone was able to find a schematic? Its a pity not being able to fix this old but good UPS.

                                    PSDR-1112NN

                                    Thanks!
                                    Attached Files

                                    Comment

                                    • ToryStreetLights
                                      TerryS
                                      • Jun 2017
                                      • 3
                                      • New Zealand

                                      #38
                                      Re: Powerware 9120 Online UPS

                                      Anybody still listening :-) I have a Powerware 9120 700 watt version that appears to be working perfectly but not charging the battery. The MUR460 gets very hot and had shorted, it's 1k 5 watt power resisistor load gets very hot, as does the chopper Fet driving it and the small Fet further on in the chain. Replacing the MUR460 with similar diodes immediately creates their demise with a short again. There doesn't appear to be any circuits around for this machine which I find very unusual, as I have worked at board level for over 50yrs.

                                      Any observations will be gratefully accepted - Thankyou in advance :-)

                                      Comment

                                      • Behemot
                                        Badcaps Legend
                                        • Dec 2009
                                        • 4845
                                        • CZ

                                        #39
                                        Re: Powerware 9120 Online UPS

                                        Just a general idea since I don't even know how this one looks like.

                                        The CPU is usually powered from the same stand-by PSU and sometimes some small transistors this road go bad so try to check that out.
                                        Less jewellery, more gold into electrotech industry! Half of the computer problems is caused by bad contacts

                                        Exclusive caps, meters and more!
                                        Hardware Insights - power supply reviews and more!

                                        Comment

                                        • ToryStreetLights
                                          TerryS
                                          • Jun 2017
                                          • 3
                                          • New Zealand

                                          #40
                                          Re: Powerware 9120 Online UPS

                                          Originally posted by Behemot
                                          Just a general idea since I don't even know how this one looks like.

                                          The CPU is usually powered from the same stand-by PSU and sometimes some small transistors this road go bad so try to check that out.
                                          Thank you for your observations I will look along that track. When operating under normal conditions the battery has a permanent drain of 300 ma until it is exhausted when the UPS shuts down.

                                          Comment

                                          Related Topics

                                          Collapse

                                          • Document Archive
                                            ACER Aspire XC-330 Aspire XC A4-9120 Specification for Upgrade or Repair
                                            by Document Archive
                                            This specification for the ACER Aspire XC-330 can be useful for upgrading or repairing a desktop PC that is not working. As a community we are working through our specifications to add valuable data like the Aspire XC-330 boardview and Aspire XC-330 schematic. Our users have donated over 1 million documents which are being added to the site. This page will be updated soon with additional information. Alternatively you can request additional help from our users directly on the relevant badcaps forum. Please note that we offer no warranties that any specification, datasheet, or download for ACER...
                                            09-12-2024, 03:28 PM
                                          • petehall347
                                            100nf and 100uf precision capacitors
                                            by petehall347
                                            i am wanting to calibrate my multimeters and for this i require a 100nf and 100uf precision capacitors . trouble is i can't find them ....
                                            08-13-2024, 06:56 AM
                                          • ten-d
                                            Nippon Chemi-con 100uf 100v BP electrolytic cap
                                            by ten-d
                                            Hi all!

                                            I just bought a pair of ADS L810 speakers, which I've heard are some of the best speakers from that time (late 70's) into the early 80's. I was super excited to test them out and hooked them up and I was very underwhelmed by the treble. The treble was awfully muffled. I've been doing some restoration work on 70's stereos and a couple of speakers here and there so I am really just a beginner. I do know that capacitors in speaker crossovers filter out the lows to allow only the highs up to the tweeters and mids. Inductors filter out the highs to allow the lower frequencies to...
                                            01-30-2024, 05:18 PM
                                          • RUllER
                                            chemicon produced by fuhjyyu
                                            by RUllER


                                            This is not a fake Chemicon, it is genuine
                                            Many companies are outsourcing to Chinese factories....
                                            01-29-2024, 12:22 AM
                                          • iMic
                                            Vintage AT Power Supplies - Selecting Capacitors
                                            by iMic
                                            Hi,

                                            Back after a long hiatus with some old power supplies that need repairing. I've recently picked up a couple of 386SX systems, two 486DX systems, a SiliconGraphics Indy and an iMac G3 that either have verified leaking capacitors in their power supplies, or are likely to in the near future. For the sake of simplicity, instead of tackling all at once, I'm starting with the 386's and one of the 486's.


                                            The 386's power supplies are Seasonic SS4040A's, with caps that are visibly leaking, and 9 replacement caps per unit are required. Most appear to be from the Rubycon...