Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
Hi.
I intended to do some temperature and frequency measurements.
The circuit had some more damage to traces and I attempted to repair them.
However, when i powered on the circuit for the second set of measurements, there was a short, open circuit, or other issue.
R0, R8, and Q1 were damaged. R0 is open circuit, R8 is open circuit, and Q1 is short circuit.
On the first set of measurements, there was no frequency measured (possibly because of an open circuit trace).
On the second there was the issue I mentioned, so there were no readings for temperature or anything else.
So, that's the end of this project. I was sure U1 was the issue after F1 and a bulged capacitor.
Now there are some more broken components.
I have learned a lot about fault finding and that was the purpose of this project.
Thanks for advice.
trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
Collapse
X
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
I have a universal 12 V supply but I am afraid if I connect this to U1 it will break. Are you sure I can connect this adaptor to U1 VDD and ground and not break it? I might prefer 1 or 2 last mains powered measurements rather than risk breaking my power supply.
Your adapter also may be good designed (with protection) or crapy, with proper or "only working yet" components...
I suggest if it is only adapter you have, and it is so valuable, that you dont using it on irelevant purpose like this.
I using small adapter from some router, 12v 1.2A with chinese module who limit current and can lowering voltage. Nothing fancy. If it stop working for any reason I do not drop any tears...
This tips for connecting a limited current to circuit with low resistance is common method to finding short component. The set voltage must not exceed maximum ratings of any component connected on that rail, lower voltage can be obtained if is left enough power to disipate heat.
I might look at reading a current too. What sort of amps should I be looking for?Leave a comment:
-
Re: Learning to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
So you are bringing conclusion via elimination proces... I think.
At least you can check and confirm where is this component with 62 ohm resistance. When I see the pulsating output, I suspect for external short and IC is fighting against them... but may be intenal also. 62R is unusual value for short circuit.
Be sure to unplug from mains voltage, and put 12Vdc directly on IC** and you may notice a hotspot, around 2.4W disipation of heat on a problematic component. You can spot it via finger tip or with spilled alcohol who evaporated quickly on that problematic component.
**it will be idealy that you can control and monitor passing current, you can use 12vdc from any wall adapter rated over 300mA, and monitor current with multimeter.
Thank you.
The advice on using a 12V power supply is very helpful since that would make it safer. I have a laser pointer thermometer and protective goggles, and the thermometer that measures up to around 400 C, and can measure the temp on U1 when I get it wired up.
I have a universal 12 V supply but I am afraid if I connect this to U1 it will break. Are you sure I can connect this adaptor to U1 VDD and ground and not break it? I might prefer 1 or 2 last mains powered measurements rather than risk breaking my power supply.
I would like to get a temperature reading just to confirm the short in U1. Now I know how to switch on Q1 I think U1 overheats and will show.
About other components. I have tested all the other components so it must be U1 internal. I am so much convinced U1 is broken I am no longer trying to find another cause. All the diodes and resistors that feed U1 are working so it has to be U1, since Q1 was proven to work with the proper gate voltage.
I might look at reading a current too. What sort of amps should I be looking for?
I am thinking of changing the title of this thread to "Learning to fix..." since I don't think I want to spend the money to replace U1. Anyone know how to change the title?
Edit: I got the handheld oscilloscope so I will probably take a frequency measurement on the gate.Last edited by Tarot Superstars; 10-04-2023, 03:34 PM.Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
check out this voltage divider circuit .you will soon see why the voltage is low at the ic . input 2.4 meg . and 62 ohms . and 335 volts
https://ohmslawcalculator.com/voltag...der-calculator
Thanks for the link.
I'm glad that I found which componet was broken. The purpose of this was to learn about basic electronics fault finding, and I think I learned some theory and practical.Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
Result Power On Reading U1 wire 1 to wire 5
Voltage ~1.29 V DC, (data reads it should be 9.5 V to 15V)
Voltage = 0 V AC.
(with and without bridging R2)
Test 2 wire 1 to wire 2. That is U1 ground to U1 gate.
Voltage = 0.4V DC to -0.1V DC, (changing quickly from one value to another).
AC = -0.4V (ripple?)
...
Testing D8 (RS1M)
Testing red probe to cathode = 0.697 V, black to cathode 0.064 V but there are other paths to the circuit.
both sides of this diode measure continuity to wires 1,2,3, and 5 of U1 and continuity from each side of the diode, but there are other paths.
I think this test shows that RS1M (D8) works fine.
So you are bringing conclusion via elimination proces... I think.
At least you can check and confirm where is this component with 62 ohm resistance. When I see the pulsating output, I suspect for external short and IC is fighting against them... but may be intenal also. 62R is unusual value for short circuit.
Be sure to unplug from mains voltage, and put 12Vdc directly on IC** and you may notice a hotspot, around 2.4W disipation of heat on a problematic component. You can spot it via finger tip or with spilled alcohol who evaporated quickly on that problematic component.
**it will be idealy that you can control and monitor passing current, you can use 12vdc from any wall adapter rated over 300mA, and monitor current with multimeter.Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
check out this voltage divider circuit .you will soon see why the voltage is low at the ic . input 2.4 meg . and 62 ohms . and 335 volts
https://ohmslawcalculator.com/voltag...der-calculatorLeave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
yes U1 isnt looking goodLeave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
Thank you.
You are correct it was a little bit of a risk.
I did check min and max input voltage of Q1 and it's 2 V to 4 V, so 3 V should be ok.
Also, I checked that, when Q1 is powered up, source to drain is supposed to be almost no resistance, so bridging is similar to no resistance.
I checked the junctions of Q1 after and they are fine with no short circuits.
I used wires, croc clips, wore an insulated jacket, and heavy duty rubber gloves, and wasn't anywhere near the circuit when powered up.
If there were anything else wrong with the circuit, and I powered it up, then as you say, smaller components might have been fried. I am happy that I have managed to get some power to the primary coil, and have proven the open circuit to that coil is the mosfet, and the cause of that may be U1 not providing enough voltage at the gate.
C3 is new and so are all of the other capacitors, since I replaced all of the electrolytics. I have not found a single diode shorted or conducting reverse biased, or oc sc resistors, so U1 is looking like the most likely broken part.
I have not checked the sensing circuit or the feedback. I don't know much about PWM but I am guessing a broken sensing circuit or feedback circuit might cause U1 to not provide enough voltage at Q1 gate. That seems like the only other possible cause and I am not betting on that much since all those components are smd capacitors and resistors, and a SMD rectifier bridge (in one package). I have checked all of the resistors and no oc or sc. I doubt the smd cap (grey one) is sc oc but could bridge that too.
So, really, the SMD bridge rectifier (RS1M) is the only other realistic possible cause. Correction it's a rectifier.
I would like to know how to deduce if U1 were broken had I not thought of this test though. Pete's conclusions did not come with much explanation.
RS1M has a cathode mark so should test like any other diode.
Testing D8 (RS1M)
Testing red probe to cathode = 0.697 V, black to cathode 0.064 V but there are other paths to the circuit.
both sides of this diode measure continuity to wires 1,2,3, and 5 of U1 and continuity from each side of the diode, but there are other paths.
I think this test shows that RS1M (D8) works fine.
That leaves U1 as the broken component, I think.Last edited by Tarot Superstars; 10-02-2023, 10:34 AM.Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
2. If I bridge Q1 source to drain with a wire, Q1 will be permanently switched on source to drain.
...
I bridged source drain of Q1 and measured voltage at primary coil
4. With a current limiter bulb connected in series with this adaptor, the bulb will light when current is drawn, and the bulb will not light when current is not drawn.
But now, after testing it seems the mosfet is ok...
Mosfet in this configuration is not intended to be permanently switched on, he must pulsing very fast.
Look this video, its explain how your device work, it is almost identical, but mosfet is in same package with ic...
https://www.youtube.com/watch?v=lM_JZ6_YELY
This SMPS Power Supply Has No OptoIsolator or TL431. How Does It Work? Switch Mode RepairLeave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
U1 VDD to U1 ground resistance measures 61.9 ohms.
Incidentally U1 VDD to the near side of D4 measures 62.5 ohms and continuity.Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
just measure ohms U1 VDD to ground .Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
OK. We are heading towards trying to verify if U1 is broken. By measuring VDD to ground of U1. I don't want to desolder U1 to test resistance to avoid damage.
I have performed some more tests.
Theory
1. If Q1 (mosfet) is not working, it won't switch on the source drain voltage and no current will flow to the primary coil. If it is working it will switch on current to the primary coil.
2. If I bridge Q1 source to drain with a wire, Q1 will be permanently switched on source to drain.
3. If I apply 3 V battery power to Q1 gate to drain it will switch on source to drain and conduct current source to drain.
4. With a current limiter bulb connected in series with this adaptor, the bulb will light when current is drawn, and the bulb will not light when current is not drawn.
5. Previously U1 gate to Q1 gate voltage measures -0.1 V to 0.9 V changing rapidly. No voltage measured at the primary coil.
I bridged source drain of Q1 and measured voltage at primary coil
Result
Primary coil voltage
1.1 V DC.
0.6 V AC.
The current limiter light bulb goes on.
I removed the bridge on Q1 source to drain and put 3 V battery power to Q1 gate to drain (to switch on Q1 mosfet)
Result
Primary coil voltage
1.1 V DC.
0.6 V AC.
The current limiter bulb lights up.
I removed the 3 V battery power to Q1 gate to drain
Result
Primary coil voltage
0 V DC.
0 V AC.
current limiter bulb goes out.
Summary
With or without Q1 source to drain bridged, applying 3 V battery power gate to drain switches on Q1 and causes the current limiter light bulb to light up and the primary coil to measure a voltage. Removing the 3 V battery from Q1 gate to drain causes the light bulb to go out and the primary coil measures 0 voltage.
Conclusion
It seems that it is possible (but not certain) that the pulsing voltage from U1 gate to Q1 gate measured previously ~ 0 to 0.9 V DC, is not enough to switch on Q1 or there is a problem with the feedback or current sensing so that U1 won't switch on Q1. But then why any pulse?
Discussion
Do you think these tests show that the Q1 mosfet works?
Can we discount Q1 as the cause of no voltage at the output?
Even though there is voltage to the primary coil, it is very low, and I wonder if everything else (especially U1) were working properly and a changing voltage being produced, would that be enough to produce 6 V DC at the output. Or maybe the voltage is low because there is no load on the output.
Could U1 being broken account for the low voltage AND Q1 not switching on and then off?
Any advice is appreciated.Last edited by Tarot Superstars; 10-02-2023, 06:48 AM.Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
Sounds like the mosfet doesn’t wanna switch. You got power full bore after the bridge rectifier into the main filter cap. So you can have few problems. R1 open (or going higher in resistance than it should), the cap failed, diode shorted, or U1 is buggerd up. Make sure you get proper Vcc to pin 5. Look at the spec pdf what it needs. And measure DC voltage between pin 5 and main filter capacitor ground for proper voltage. If you deterrent that the voltage is too low at the chip, replace the resistor, check that diode. Still doesn’t work, repale uLeave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
I mean voltage going through the transistor source to gate, not parallel with it (possibly only going through the multimeter).Last edited by Tarot Superstars; 10-01-2023, 04:33 PM.Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
Is there any way I can check that there really is a voltage between source and drain, in circuit, with power on?
Source to Drain
Voltage = 335 V DC.
Voltage = 0 V AC.
Are you expect some other reading? Is mosfet tested good?
I have purchased a Vellerman HSP5 handheld oscilloscope, and it has a bandwidth of 1MHz and max voltage of ~ 600V, so that I don't have problems with grounding my CRT analogue oscilloscope.
It is nice have a different equipment, but oscilloscopes are usualy used to see how stuff works, and not how to not work in lack of power.Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
I previously measured voltages across source and drain of the mosfet Q1 with power on. But this doesn't tell me if there is any real connection between those two wires (which there should be) because I have really just bridged those two points and the voltage could be going to those two wires but not through Q1.
I am going this route because I am wondering why I have voltage across Q1 but nothing on the primary coil. There must be some open circuit or it's not switching on or something. So, I am trying to trace the voltage to the coil. I haven't finished reverse engineering the circuit yet so I haven't got far.
Is there any way I can check that there really is a voltage between source and drain, in circuit, with power on?
I have purchased a Vellerman HSP5 handheld oscilloscope, and it has a bandwidth of 1MHz and max voltage of ~ 600V, so that I don't have problems with grounding my CRT analogue oscilloscope.
Maybe this can be used to do some more checks, when I receive it.Last edited by Tarot Superstars; 10-01-2023, 04:57 AM.Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
because of the voltage right across R1Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
How did you come to the conclusion that there is a short circuit in the capacitor, diode, IC or that R1 is open circuit?
Also If i remember correctly R1 reads 2.4 mega ohms.Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
there is a short circuit . its the capacitor or diode or ic chip .or R1 is open circuitLast edited by petehall347; 09-30-2023, 04:00 AM.Leave a comment:
-
Re: trying to fix a 6V 0.5A T1 (Transformer) AD050120T2 power supply
What ohms?
Also you said U1 should have 15V across wire 1 and 5. Now you don't seem so sure.
Also, correction to the reverse engineering jpeg. Feedback (FB) is not disconnected. I'm not removing anything that is likely to break or break a trace until I have take lots more voltage readings.Last edited by Tarot Superstars; 09-30-2023, 02:36 AM.Leave a comment:
Related Topics
Collapse
-
by KYBOSHPicked up a Tektronix type 422 oscilloscope locally for a few bucks last year.
It wouldnt power on at all so I stowed it away under my bench for later testing.
Today I remembered it was down there and pulled it out to see what was what.
I checked for continuity and everything checked out.
There was a burned smell and a resistor was replaced with a temporary replacement (see yellow box in picture).
The burned smell is very pungent/acidic and I am not familiar with these vintage electronics to know whether I am smelling the remains of the replaced resistor or...1 Photo -
This is my first attempt at troubleshooting a board like this, I know I could just buy a new board but I'm curious to figure out how this works. I've been testing different components in the evenings this week and I think the problem is with the IC failing to start up for some reason. When the board is plugged in there is no standby voltage.
Then today it randomly sprung to life like a zombie but shortly died thereafter. I have no idea why it would have done that and its the first time I've seen it running. I discharged capacitors on the board last night, then it was sitting today.... -
by privato89Hello everyone,
I'm facing an issue with a HEG-001 motherboard that is unable to complete the Second-Stage Boot. I'd like to start directly with my conclusion, which is the decision to replace the MAX77621AEWI chip, and understand if it could be a correct evaluation.
Before I dive into the process that led me to this decision, I want to mention that I have a fully equipped lab where I can perform any kind of tests.
Let's begin:
Following some guides online, I tried to understand how the Boot phase of the Nintendo Switch works, and what are the... -
by AstonishedHi friends of electronics
What you see in the video and pictures attached is the circuit for charging the batteries of a DC motor.
The problem is that this circuit cannot charge the batteries (3 1800mAH NiMH batteries) any more. When the circuit was OK, its green LEDs lit up one at a time to show that the batteries have charged more. But now that the circuit is flawed, LEDs light up as you see in the video and at the same time successive beeps are heard.
Please help me fix this circuit.
(the datasheet of the IC: https://pdf.datasheet.live/28... -
by mikey5791Hi to all forum members,
This psu (Tiny Tech model ATX 480W) had been installed in a very old Windows XP PC but recently i pulled it out as the pc cannot start. To test it, i jumped the green wire and black wire on the 24 pin connector. The psu fan jerk a bit but not spinning. I used my dmm to check dc voltage on output connector wire, the 5v red wire keeps ticking a bit at around dc1v....then drops and ticking again around 1v. It is the same situation with the 12v yellow wire.
Fyi, i desoldered the secondary side electrolytic cap those over 1000uf... - Loading...
- No more items.
Leave a comment: