crown xli 3500.NTC Thermistor

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • spiros.p
    Senior Member
    • Dec 2020
    • 89
    • Greece

    #1

    crown xli 3500.NTC Thermistor

    i have amp that sometimes on startup trip the 16A cirquit breaker.I see on distro amp meter over 20A to 30A current .the amp use the 10d20 ntc and relay. can i connect two ntc 10d20 in series (not paralel) to avoid this shutdown? or i have to keep the ntc s resistance to 10R?and use instead two 20R ntc s?or use one bigger amperage 10R ntc? thanks for any help.
    Last edited by SMDFlea; 10-24-2022, 04:42 AM.
  • stj
    Great Sage 齊天大聖
    • Dec 2009
    • 30932
    • Albion

    #2
    Re: Ntc

    it sounds more like the relay circuit is bad.
    remove the ntc and see if the amp still starts

    Comment

    • SMDFlea
      Super Moderator
      • Jan 2018
      • 20338
      • UK

      #3
      Re: Ntc

      Originally posted by spiros.p
      i have amp that sometimes on startup trip the 16A cirquit breaker.I see on distro amp meter over 20A to 30A current .the amp use the 10d20 ntc and relay. can i connect two ntc 10d20 in series (not paralel) to avoid this shutdown? or i have to keep the ntc s resistance to 10R?and use instead two 20R ntc s?or use one bigger amperage 10R ntc? thanks for any help.
      Post the amp model number please...
      All donations to badcaps are welcome, click on this link to donate. Thanks to all supporters

      Comment

      • spiros.p
        Senior Member
        • Dec 2020
        • 89
        • Greece

        #4
        Re: Ntc

        i have all ready replace the ntc with same type .nothing change and instal again the original part.the amp is crown xli 3500.before replace i have measured the original ntc and looks ok i only change to be sure.

        Comment

        • R_J
          Badcaps Legend
          • Jun 2012
          • 9515
          • Canada

          #5
          Re: crown xli 3500.NTC Thermistor

          Check if the power in delay relay is operating correctly, maybe the relay contacts are sticking. Is the 16amp circuit breaker weak? I would think an amp this size would require a 20 amp circuit
          Last edited by R_J; 10-24-2022, 12:38 PM.

          Comment

          • redwire
            Badcaps Legend
            • Dec 2010
            • 3900
            • Canada

            #6
            Re: crown xli 3500.NTC Thermistor

            Assuming the 24VDC rail has come up part ~13V, there is the on/off switch opto-coupler and time delay, whereby the relay will pull in.
            Crown XLI3500 schematic but I see some versions have SMPS.

            Comment

            • spiros.p
              Senior Member
              • Dec 2020
              • 89
              • Greece

              #7
              Re: crown xli 3500.NTC Thermistor

              the psu is linear with massive traffo.i think to the relay have problem and sometimes sticking. the fuse breaker is ok.one time a week a go is triping the 25A mains three fase breaker.is not happen all the time one's in ten times when i power on.that's strange.

              Comment

              • redwire
                Badcaps Legend
                • Dec 2010
                • 3900
                • Canada

                #8
                Re: crown xli 3500.NTC Thermistor

                What is happening is the power transformer has residual magentism when you turn OFF the amplifier.
                It depends upon where in the mains sine-wave you switched it off, but the core gets some magnetism.
                If you switch ON power at the same sine-wave polarity, I think the transformer saturates and causes very high inrush current.

                You're not supposed to have this problem if the NTC and relay are working properly.
                Attached Files

                Comment

                • spiros.p
                  Senior Member
                  • Dec 2020
                  • 89
                  • Greece

                  #9
                  Re: crown xli 3500.NTC Thermistor

                  bad news guys after desolder and instal the optocoupler and relay to measure and check is booth good the amp goes in protect mode the fans at full power and front red leds light.no clicks and other action from amp.i keep only seconds on just to measure if low voltage is present and close because the ntc gets hot.��opto is ok with variable volt input and measure the resistance changing.the relay clicks ok with 18v and close contact on the other side.i think i have sean the low voltage for soft start supply 13v is not ok.on manual said 24v anyway i check again.under the main board i measure all the smd components for delay start and found nothing suspisious.i miss only the Q64.the Q63 is on board together with D92 zener.is other version the schematic from my amp?thanks again for any info .

                  Comment

                  • spiros.p
                    Senior Member
                    • Dec 2020
                    • 89
                    • Greece

                    #10
                    Re: crown xli 3500.NTC Thermistor

                    ok i check i have 13v and 10v to delay
                    Last edited by spiros.p; 10-26-2022, 07:26 AM.

                    Comment

                    • spiros.p
                      Senior Member
                      • Dec 2020
                      • 89
                      • Greece

                      #11
                      Re: crown xli 3500.NTC Thermistor

                      Attached Files

                      Comment

                      • spiros.p
                        Senior Member
                        • Dec 2020
                        • 89
                        • Greece

                        #12
                        Re: crown xli 3500.NTC Thermistor

                        found broken smd darlington transistor on relay supply.wait for replace part and see if it works

                        Comment

                        • stj
                          Great Sage 齊天大聖
                          • Dec 2009
                          • 30932
                          • Albion

                          #13
                          Re: crown xli 3500.NTC Thermistor

                          was going to say, if the relay clicks on and the contacts are o.k. then the ntc should cool down - because it's bypassed.

                          Comment

                          • spiros.p
                            Senior Member
                            • Dec 2020
                            • 89
                            • Greece

                            #14
                            Re: crown xli 3500.NTC Thermistor

                            so the supply darlington trans is ok the problem was bad solder on smd's.i descover that when i want to move a little the amp and heard the relays clicking.resolder all part's on soft start supply side and relays click ok.so far so good.problem keep going now on jfet.the amp starts but the output protection is on found a jfet short.don't know what causes jfet to fail.i desided to resolder the whole smd part's of the amp.and now wait again for the new jfet part to replace.will see what comes next.

                            Comment

                            • spiros.p
                              Senior Member
                              • Dec 2020
                              • 89
                              • Greece

                              #15
                              Re: crown xli 3500.NTC Thermistor

                              hi change jfet change all op amps now i have everywhere - and + 15v like on manual but protect still on.i have check 10 times all parts on output all diodes and resistors i get mad.the only thing on power in delay i have 13v instead of 24v says on manual.there is only q63 and on manual is q63 and q64.

                              Comment

                              • spiros.p
                                Senior Member
                                • Dec 2020
                                • 89
                                • Greece

                                #16
                                Re: crown xli 3500.NTC Thermistor

                                just for future reference the amp is repaired.the Q63 was leaky i have desolder one's last week and measure and looks ok and solder again thats confuse me and search the whole cirquit for fault.yesterday i desided to change the Q63 LMBT5551 because the 13.4volt don't look good on manual say 24v.solder one TO92 2n5551 the original SMD part is not available here.give power and everything clicks.the only negative the amp don't power of when push the power button.i suspect there is problem with the 2n5551 is bit diffrent i instal one other 4 pole rocker switch and now the amp powers of.no more inrush current on start up.

                                Comment

                                Related Topics

                                Collapse

                                • nmbb
                                  Can not find Model/Value of Thermistor.
                                  by nmbb
                                  Machine: Autoclave.
                                  Brand/Model: SANYO MLS-3780
                                  Manual: (Sorry search option not working on this PDF)



                                  Hello guys, this autoclave running with 2 thermistors already connected TH1 and TH3(on CN1,CN2 sockets). One for the water temperture and second one for chamber temperature. But there is another emtpy socket for optional third thermistor CN2 wich is for TH2 for object temperature. I wanna add the third thermistor TH2 to CN2 socket. But i can't figure what model/brand/value i need to use. In manual document, there is no info about TH1 and TH3 model number...
                                  06-02-2022, 05:55 PM
                                • jm1234
                                  9V relay temperature 40C
                                  by jm1234
                                  Hi, I'm seeing one 9V relay having temperature 40C on its 9V (primary) side. Does that seem right? I switched 2 relays on that board and the temperature was the same (on the same position), so I'm sure it's not a faulty relay. I measured voltage on that relay and it was 9.5V DC, so that looks good. I don't see any other relay on that board having that kind of temperature and they have 9V on them too.
                                  I thought maybe the transistor that is switching this relay keeps switching on/off, so I also checked for AC and there was almost none: 0.3V using mV range. No steady frequency was shown, but...
                                  05-09-2024, 03:03 AM
                                • edugimeno
                                  Biomass Boiler not driving cleaner motor relay. ENERTRES BIOMASA BI-650
                                  by edugimeno
                                  Hi everyone!
                                  I have this board that suddenly stopped supplying power to an output that drives an interchanger cleaner motor.
                                  I checked while the board was in place with all wires attached and there's no AC voltage on the corresponding plug X5
                                  This X5 is driven by fuse F8 (tested OK) which comes from the second orange relay
                                  To make sure there are no charcoaled contacts inside the relay, I got a 24VDC power supply and got it ready to manually power up the coil side of these relays.
                                  I respected the polarity, positive to cathode of protecting diode
                                  So provided all...
                                  04-18-2024, 01:15 PM
                                • sam_sam_sam
                                  Mitsubishi CNC switching power supply board dead / relay board bad diode failure
                                  by sam_sam_sam
                                  I was working on this CNC machine today found no keyboard functioning no control relay powering on
                                  The screen powered on and was giving an operation error but the manual was not very clear about what the error exactly was but with a little bit of troubleshooting and finding out that the control relays not powering on and no keyboard functions we narrowed down to this one switching power supply which of course does not have any indicator LED light they are on the keyboard interface/relay controller board

                                  Found shorted diodes on main controller relays there are 3 of them that...
                                  01-07-2023, 05:43 PM
                                • fadi90
                                  PILZ PNOZ X4 Safety Relay
                                  by fadi90
                                  Hi everyone,

                                  I'm working on repairing a Pilz PNOZ X4 safety relay module. When I opened it up, I found some of the connector pins detached from their pads. I replaced the connector with individual wires, but the issue remains.

                                  The module is set to dual-channel mode with manual start. In this mode:
                                  • Y36-Y37 and Y1-Y2 are bridged.
                                  • 24VDC is applied across A1-A2.
                                  • It monitors two emergency circuits (S11→S12 and S11→S52).
                                  • When both are closed (24V present on S12 and S52) and the start button is pressed (S33 connected to S34), the NO contacts (13-14, 23-24, 33-34)
                                  ...
                                  06-07-2025, 01:21 AM
                                • Loading...
                                • No more items.
                                Working...