Biomass Boiler not driving cleaner motor relay. ENERTRES BIOMASA BI-650

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • edugimeno
    Badcaps Veteran
    • May 2017
    • 581
    • Spain

    #1

    Biomass Boiler not driving cleaner motor relay. ENERTRES BIOMASA BI-650

    Hi everyone!
    I have this board that suddenly stopped supplying power to an output that drives an interchanger cleaner motor.
    I checked while the board was in place with all wires attached and there's no AC voltage on the corresponding plug X5
    This X5 is driven by fuse F8 (tested OK) which comes from the second orange relay
    To make sure there are no charcoaled contacts inside the relay, I got a 24VDC power supply and got it ready to manually power up the coil side of these relays.
    I respected the polarity, positive to cathode of protecting diode
    So provided all the positives to all coils are common, I soldered + to this rail, and then applied negative to the other side of the relay coil.
    With the first relay (not the faulty one), it clicked correctly on and off several times according to each time I touched it
    With the second relay (faulty output), it clicked slowly and like "lazy" both for ON and OFF (some delay) and I got some smoke smell right away. Turned the board upside down and felt heat around both small Q's that drive this coil.
    Can I have damaged the Q's that drive it? As the polarity is granted, they are all going + - + - + -....
    Or is this just a sign that these transistors were the culprit for this issue?
    I don't really understand the schematic (see images) for the driving Q's, it's like 2 different lines can drive independently the negative side?

    Any help would be appreciated!
    Thanks in advance
    Attached Files
  • edugimeno
    Badcaps Veteran
    • May 2017
    • 581
    • Spain

    #2
    Oh also I can see in my own pictures.. .that the second Q at the second relay is burnt by the end of the letter W...And I measured resistance from E to C in this transistor and it has 30 ohm on both polarities, which is not happening on all the other Q's
    Should I just replace this Q?
    Last edited by edugimeno; 04-18-2024, 02:25 PM.

    Comment

    • edugimeno
      Badcaps Veteran
      • May 2017
      • 581
      • Spain

      #3
      Anyone? Thanks

      Comment

      • petehall347
        Badcaps Legend
        • Jan 2015
        • 4426
        • United Kingdom

        #4
        yes replace relay driver and check the flyback diode

        Comment

        • truclacicr
          Badcaps Veteran
          • Apr 2019
          • 316
          • australia

          #5
          http://markingcodes.com/search/c/1gw

          1GW = BC847CW or BC847C

          Comment

          • edugimeno
            Badcaps Veteran
            • May 2017
            • 581
            • Spain

            #6
            Yes I have 5x BC547C ordered at the local store, arriving next week.
            Will see how I manage to desolder/resolder them, Im not very proud of my smd soldering skills...neither my sight

            Comment

            • petehall347
              Badcaps Legend
              • Jan 2015
              • 4426
              • United Kingdom

              #7
              good magnifier with light. and hot air works a treat .

              Comment

              • edugimeno
                Badcaps Veteran
                • May 2017
                • 581
                • Spain

                #8
                And does it sound reasonable that feeding 24V to the relay coil pins (correct polarity) the transistor started to smoke? Is this a hint that the Q was already blown?

                Also can I have damaged any other electronics before the transistor driver (like an IC) maybe getting these 24V to get back to the IC?

                Thanks

                Comment

                • edugimeno
                  Badcaps Veteran
                  • May 2017
                  • 581
                  • Spain

                  #9
                  Originally posted by petehall347
                  good magnifier with light. and hot air works a treat .
                  I will prpbaby get one of those magnifiers with a weight. I don't have hot air, only a gas powered soldering iron that has a point for hot air, but having some other tiny smd R's very close, I tend to belive that with hot air all the stuff around is going to get loose

                  Comment

                  • petehall347
                    Badcaps Legend
                    • Jan 2015
                    • 4426
                    • United Kingdom

                    #10
                    Originally posted by edugimeno

                    I will prpbaby get one of those magnifiers with a weight. I don't have hot air, only a gas powered soldering iron that has a point for hot air, but having some other tiny smd R's very close, I tend to belive that with hot air all the stuff around is going to get loose
                    i dont have trouble with components this size they are pretty big compared to the real small ones . thing is with an iron its difficult to hot up 3 legs at the same time . what i do is add new solder with my iron then hot air .

                    Comment

                    • edugimeno
                      Badcaps Veteran
                      • May 2017
                      • 581
                      • Spain

                      #11
                      Originally posted by petehall347

                      i dont have trouble with components this size they are pretty big compared to the real small ones . thing is with an iron its difficult to hot up 3 legs at the same time . what i do is add new solder with my iron then hot air .
                      Suppossedly flux around would help getting the heat spread around the whole transistor, that's my hope...Will see when they come

                      Comment

                      • edugimeno
                        Badcaps Veteran
                        • May 2017
                        • 581
                        • Spain

                        #12
                        Im back, my local shop received the new SMD transistors. Instead of 1GW, I got K1M, do you believe they would fit?
                        Also I got one of the 2 transistors on another relay shorted too. My 2nd question is, being that I only applied direct voltage to the coild of these 2 relays (correct voltage, correct polarity), and there are only shorted transistors in the relays I checked, is there any chance that I could hve burned these transistors just by having tested the coils in circuit? Once I felt smoke at the second relay, I stopped checking all the other relays, but I don't know if it was me who was burnng them and the original issue was other...

                        Thanks

                        PS: I was able to remove the old transistors with no much effort just by using a normal solder iron, switching from one side to another quickly and pushing gently with tweezers. I removed the relay to make some room, which was way harder to remove than the Q's using a basic desoldering pump

                        Comment

                        • harp
                          Badcaps Veteran
                          • Jun 2022
                          • 599
                          • Planet Earth

                          #13
                          My 2nd question is, being that I only applied direct voltage to the coild of these 2 relays (correct voltage, correct polarity), and there are only shorted transistors in the relays I checked, is there any chance that I could hve burned these transistors just by having tested the coils in circuit? Once I felt smoke at the second relay, I stopped checking all the other relays, but I don't know if it was me who was burnng them and the original issue was other...
                          So on what points you are injecting voltage, 24v?
                          Have you inspect conections from positive rail through relay and transistor to negative rail? Are negative rail ground? Coil resistance, driving voltage?
                          It is general bad idea to inject voltage without limit the current, but if you inject directly on coil, that should be the smallest resistance in this circuit, so the most current should pass through coil, not transistor...

                          Use multimeter in continuity mode and traceback schematic of that part of circuit.

                          And... 1GW = BC847CW or BC847C is not 5x BC547C... I not check datasheet.
                          Make sure that transistor is same type, voltage and current capabilityes.
                          Last edited by harp; 05-03-2024, 01:59 PM.

                          Comment

                          • edugimeno
                            Badcaps Veteran
                            • May 2017
                            • 581
                            • Spain

                            #14
                            Thanks. I directly injected 24V to the relay coils (across protetion diodes). I checked polarity, in this case the common point is the positive side, and then GND is switched by the driver transistors
                            I haven't checked all those parameters. All I have checked is the protetion diode and it tests OK
                            Yes the K1N transistor is an BT3904 NPN transistor which has Vce=40v (this board is powered at 24v), and has Ic=0.2 and P=350mW while the old one 1GW has Ic=0.1 and P=250mW, so it looks like it would work fine
                            Thanks!

                            Comment

                            • redwire
                              Badcaps Legend
                              • Dec 2010
                              • 3910
                              • Canada

                              #15
                              Injecting 24V across the relay coils causes back-feed through the transistors and can damage them. It's not a good idea.
                              I think what happens is reverse current flow throught the (zener) E-B junction and forward C-B junction diodes.

                              Comment

                              • edugimeno
                                Badcaps Veteran
                                • May 2017
                                • 581
                                • Spain

                                #16
                                Im a little confused on this. Per the schematic, it looks like these relays have 2 transistors that will drive the coils, mounted in parallel, like different sources will be able to independently drive them high.
                                If having fed 24V manually at the coil lead would damage the transistors, what if one transistor drives 24 to the coils? It would be also getting 24V in reverse to the other transistor in paralel right? So this leads me to think that if it's me who applies the 24V across the coils leads, the voltage seen by the transistors would be the same as if the other transistor would be providing it during normal circuit operation, and I wrong?

                                Thanks again!

                                Comment

                                • redwire
                                  Badcaps Legend
                                  • Dec 2010
                                  • 3910
                                  • Canada

                                  #17
                                  What schematic? Current flow normally is from emitter(s) to GND, leaving the coil(-). But it goes backwards when putting only 24V power on the coil, it is trying to power up the entire board! Flows into the emitter(s).

                                  For functional safety, sometimes a relay driver needs consensus from two microcontrollers or supervisor systems. As a redundant "AND" gate. So it will have two inputs- even though one is all you need and see on other control boards.
                                  But you seem to have an "OR" gate with the two transistors.
                                  Last edited by redwire; 05-05-2024, 02:05 PM.

                                  Comment

                                  • edugimeno
                                    Badcaps Veteran
                                    • May 2017
                                    • 581
                                    • Spain

                                    #18
                                    Im realizing... when I applied 24V across the protecting diode, all I did was applying +24v to the upper rail (already common +24v for all relays) and 24v GND to the other side of the coil, which is directly fed by both transistors, and driven to gnd by one of them when their source signals becomes high. Is putting their collectors to GND a source to backcurrent? I don't see how this can damage them. Not trying to argue, just not able to see it.
                                    And like I said, when one transistor switches on, the other, in parallel like an OR gate, would be "suffering" this backcurrent too, like when I manually applied this voltage to the whole pair, right?
                                    See attached reduced schematic...
                                    Thanks!
                                    Attached Files

                                    Comment

                                    • redwire
                                      Badcaps Legend
                                      • Dec 2010
                                      • 3910
                                      • Canada

                                      #19
                                      Click image for larger version

Name:	Relay coil backfeed.png
Views:	55
Size:	70.4 KB
ID:	3271042

                                      It's your fault. You blew it up lol. This is how I look at it...

                                      A BJT consists of two diode junctions inside. For a transistor to work, the C-B junction must be reverse-biased, and the E-B junction is forward-biased.
                                      But when you apply 24V across the coil, current flows backwards through the transistor's two diode junctions - the C-B junction is forward-biased on, and the E-B junction avalanches as a zener because they are around -7V only.
                                      Then current flow is from the GND, as the board also draws power. You end up supplying the board with 24V power flowing backwards through the transistor(s) and if the current is too high, it will damage them. Note the transistor base will appear negative V and the resistor protects the MCU output pin hopefully.

                                      If it was a 5V relay/power the transistor(s) E-B junction would not avalanche and conduct, so maybe this is why it can work then.
                                      I just remove relays that I suspect are bad and bench test them.

                                      Attached Files

                                      Comment

                                      • petehall347
                                        Badcaps Legend
                                        • Jan 2015
                                        • 4426
                                        • United Kingdom

                                        #20
                                        can always short relay driver c to e with board powered . or get real technical and monitor voltage on it base

                                        Comment

                                        Related Topics

                                        Collapse

                                        • CuriousJohn
                                          Burco boiler power problem
                                          by CuriousJohn
                                          Burco BCPLSAFWM5L 5 Litre Wall Mounted Automatic Water Boiler With Filtration UK 240v

                                          Does anybody have any experience with these Burco units at all there is no record of them on the forum lol and a proper service manual would be nice. I invite you all to pesuade me not to botch repair it with a 5v relay, read on.

                                          This unit was rescued from a skip 3 years ago, the only fault it had then was no backight display (plus it wanted a new probe set and top seal) but the screen was never an issue you can still see the screen as is and I just use it to get 5 Litres of very hot...
                                          12-22-2024, 10:25 AM
                                        • juergenb
                                          Nescafe Aeroccino, still fails with new Motor (red flashes only once)
                                          by juergenb
                                          Hi,

                                          i am asking for some Help.
                                          I have one of these Nescafe Aeroccino (Milk Frother) things with a bad motor.
                                          The Motor didn“t start anymore and internet is full of users just swapping the motor for a Mabuchi RF-500TB-12560.
                                          So i got a few of these from Banggood.

                                          I swapped the motor and now i have a new fault condition.

                                          In a working Frother you would press the start button, it will light red and work for a few minutes.
                                          If you press longer it will light blue and just mixup the milk.

                                          With the new Motor it just starts...
                                          03-23-2021, 11:24 AM
                                        • sbt123
                                          charnwood w821 mini wood lathe motor problem
                                          by sbt123
                                          hi there,im having a look at repairing a wood lathe for my dad,(charnwood w821)the problem is when turning up the variable speed control,the motor starts to stop and start by itself,if i continue to turn up the speed it will trip the mcb in the consumer unit,there is also a slight smell of burning from the speed controll box.,Another strange symptom is the lathe can be unplugged from the mains after switching it off and the motor will spin a couple of times by itself,so far ive put a new speed controll potentiometer on and new motor brushes,ive also tested the motor windings and everything looks...
                                          10-27-2024, 03:43 AM
                                        • jm1234
                                          9V relay temperature 40C
                                          by jm1234
                                          Hi, I'm seeing one 9V relay having temperature 40C on its 9V (primary) side. Does that seem right? I switched 2 relays on that board and the temperature was the same (on the same position), so I'm sure it's not a faulty relay. I measured voltage on that relay and it was 9.5V DC, so that looks good. I don't see any other relay on that board having that kind of temperature and they have 9V on them too.
                                          I thought maybe the transistor that is switching this relay keeps switching on/off, so I also checked for AC and there was almost none: 0.3V using mV range. No steady frequency was shown, but...
                                          05-09-2024, 03:03 AM
                                        • sam_sam_sam
                                          Mitsubishi CNC switching power supply board dead / relay board bad diode failure
                                          by sam_sam_sam
                                          I was working on this CNC machine today found no keyboard functioning no control relay powering on
                                          The screen powered on and was giving an operation error but the manual was not very clear about what the error exactly was but with a little bit of troubleshooting and finding out that the control relays not powering on and no keyboard functions we narrowed down to this one switching power supply which of course does not have any indicator LED light they are on the keyboard interface/relay controller board

                                          Found shorted diodes on main controller relays there are 3 of them that...