Finding the wrong part at a loooong led strip, part works fine, part flickers, all parallel...
  • edugimeno
    • May 2017
    • 581
    • Spain
    Hi There!
    I'm trying to help my friend who owns a restaurant be just bought.
    He has a very long LED strip running along all the walls and columns. The strip is attached facing down 2in above the floor, using a wall panel that ends in a metal rail that finishes the panel underneath
    It's stuck using, I guess, the 2 sided tape that comes with the strip
    The issue is that like 1/2 of the full length, including 1/2 one wall, another entire wall, and one column, flickers after 4 or 5 minutes ON. Particularly it flashes staying OFF most of the time and flashing ON for 1 tenth of second every 2 seconds, aprox
    We checked the transformer and it seems ok, with constant voltage all time. One thing that caught my attention is that this 12V, 21A transformer, using a multimeter is only providing 5Amps for this entire led strip. And we made sure there's no other transformer as as soon as we took one of the 12V leads out of it, the entire (working fine part and flashing part) would shut off, so it all comes from it, but looks like too low current to me for a led strip that's probably 20-30m long
    So the wiring is not all continous, we went down underneath the part where the OK leds are and where the FLASHING leds start, and we found that it's another section, with no connection between both, and the second one is being powered from a further connection far from there, with a tight junction of wire coming and hidden behind the wall panels. We realized that there were several connections coming down behind the wall panels powering different parts, probably the builder bought short strips and had to power them all individually, or maybe he wanted to avoid voltage drop by not going all in cascade.
    Thorough and manual diagnosing the strip is a little hard and annoying, as it's all upside down so close to the floor, we need to move all the restaurant tables and use a mirror to see the connections and leds.
    Also I measured the voltage at the failing section and V goes up and down around 4-8V (digital, slow multimeter, probably would reach to 12V, flash, and then drop)
    Question is:
    • Provided the information you've read, and if you have worked with these led strips, what type of issue can you look at?
    • Assuming the transformer is OK is saf, right? Provided hundreds of LEDS work fine with no flickering
    • Should I look for a strip short into the aluminium plate?
    • Should I look for a shorted LED? If so would it look blackened?
    • How can one part of the strip be 100% stable while another part is flickering, when it's all connected in parallel?
    • Any other smart hint to help diagnose where's the failing part?
    We can definitely replace the whole strip but this would take too long, detaching the strips from the plate, removing all solders everywhere, and redoing the thing without having found the real issue...
    Thanks in advance!
    • 31017
    power the flashing section with some fresh wire to test it.
    it sounds like a wiring problem.
    you have to power the strips every 5-10m because of voltdrop - thats directly from the manufacturers instructions.
    if you have a 10m strip you power both ends for even brighness for example.
    • edugimeno
      • May 2017
      • 581
      • Spain
      Ok yes this is something I can try and it's not that hard, as there are +/- leads everywhere at the cut points...
      So you think some power points have a bad connection? Don't you think a faulty led would do this?
      What would be your procedure, I mean, if I start applying 12V to all points in the faulty section, what would I do if I find a point where the extra 12v stops the flickering?
      THANKS!
        • 31017
        just connect 12v to the flickering section and see if it works o.k.
        if it does then you need to find the bad wire joint.
        if an led fails it shouldnt effect the rest because they are in parallel
        • edugimeno
          • May 2017
          • 581
          • Spain
          Thanks, but the problem is that the failing section is very very long and implies 2 large walls and 2 columns (4 sides each obviously) , hard to find where the connections come from (somewhere behind the panels, can't see them) and where the sections are joined together. I will give it a try thou
            • 31017
            if it's that long you need to inject power at several points along it's length.
            if not then it may blow a track open from the current flow!
            • edugimeno
              • May 2017
              • 581
              • Spain
              Ok I will start supplying 12V on all connection leads I see and try to find out whats wrong after I see the results
              Thanks a lot!
              • Jamram109
                • Nov 2024
                • 3
                Yes what he said 👆🏼
                Power injection is key to those long runs of LEDs, especially when the white color (all three LEDs light up to make white) lights up. I have to do this for my Christmas light decorations when using addressable LEDs (pixels) with XLights. Good luck ☺️
                Jaime
                • edugimeno
                  • May 2017
                  • 581
                  • Spain
                  Ok thanks but these led strips have been working properly at this restaurant for several years, and I've seen many lines coming down the wall to provide extra power supply points mid-length, but for some reason a big chunk of the whole setup started failing and I need to find out how to repair it without having to remove the whole thing, which is very long and very uncomfortable to work with, as it is installed facing down under a frame that's like 2-3 inches above the floor level
                    • 31017
                    read the voltage at the end of each supply cable then.
                    see if one is lower
                      master hoarder
                      • May 2008
                      • 12175
                      • Bulgaria
                      12V LED strips are typically made of small sections (about 5 cm long), wired with 3 series LEDs followed by a 120 Ohm resistor (in series) to limit the current. Thus, if an LED goes bad (open-circuit or intermittent die connection), you won't loose an entire meter-long section. You would just loose the 3 LEDs that make up the small 5 cm section and the rest would be working fine.
                      So I concur with STJ - you probably have a wiring issue somewhere to the section that is flickering. Try using a multimeter to check the voltage in the flickering section... though I suspect you'll likely find it's low / intermittent as well. Easiest way to troubleshoot without removing any of the LED strips is to directly inject 12V in the faulty/flickering section to see if it comes up OK (it should.) For this, it would be helpful to get another 12V power supply... 12V 6 Amp adapter or small 12V UPS battery should do (though be careful if you do use a UPS battery, since those can provide pretty large currents if something goes wrong - you don't want to start a fire inside the place.)
                      • edugimeno
                        • May 2017
                        • 581
                        • Spain
                        Yes due to the hard access to the upside down led strip and being so close to the floor, I will probably prepare some handmade adapter with + and -. contacts at the proper place to push current to the strips one by one and see which one needs a proper voltage.
                        • G-Sting
                          iPad Pro A1876 SHORT Part Identify Help Needed
                          by G-Sting
                          So My iPad was not charging and booting up . i went to a local technician and he checked with thermal and this Part marked in 1st Photo is Short.
                          So then i went on to boardview and downloaded the schematics and identified this part in 2nd Photo. Now i am confused what exactly is the part called ? where should i get this from ?
                          i contacted my technician and he sent me his BoardVIew screenshot in 3rd Photo. In his Boardview the part is called X2826.... Something
                          SO My main concern is what part should i order what should i search the name for ?
                          on Ipad...
                          05-15-2025, 09:30 AM
                        • Yanleb
                          Panasonic part number in service manuals
                          by Yanleb
                          In the Panasonic service manuals, both in the board schematics and in the part listing, the part numbers that are given are Panasonic part numbers instead of the actual part numbers.
                          This is especially annoying for small SMD components like diodes and transistors when you only have 1-3 digits printed on the component body.
                          For an example, look at the attached PDF.
                          Do you have a way to cross reference the Panasonic part number with the actual part number?
                          Thanks....
                          07-03-2023, 08:16 PM
                        • FreakyMex
                          Trouble to identify part (Lunii screen) for replacement
                          by FreakyMex
                          Hello guys. I'm a complete noob in electronics. I'd like to repair my child Lunii's (a "story box"), basically an audio player that allows the childs to choose between several options the places, characters, objects of the story, and then play a story according to the choice of the child. There is a screen that display the selected option before each choice. The Lunii fell and the screen is now broken.
                          I'd like to repair it (probably just have to change the part, because the lunii still works perfectly fine) but I can't manage to identify the part/order it online. Do you have any...
                          02-17-2025, 01:16 AM
                        • esinior
                          Smd code to part number
                          by esinior
                          Hi i have a smd part with probably mark "QO 11" or "Q0(zero) 11" on it, and its package is SOT89, i doubt its KTB1260 PNP transistor, but in measuring with diode mode of multimeter it shows number 1.4 between emitter and collector pins and its not open circuit, and .59 from collector to base and .8 from emitter to base , and these numbers doesn't match a pnp transistor, i couldn't find any part number and datasheet for it, does anybody have information for that part number?
                          I've attached pics of this part
                          Thanks...
                          08-20-2024, 02:50 AM
                        • benareeno
                          Adjustable dc power supply and tcl led strip
                          by benareeno
                          I wonder if i shorted the whole strip...where to put pos and neg to just light up a single diode...or the entire strip. The strip lit for a second...so maybe i fried it? What say you?
                          I have an adjustable dc power supply and was trying around 9 volts.
                          I have a pic of a single diode...where to put pos and neg terminals to light it up?
                          Pic of middle of strip..is this where i light the entire strip?
                          And pic of end...or does this light the entire strip?
                          Where to put pos and neg for single diode..multiple diodes and the entire...
                          07-11-2021, 02:31 PM
